Being an arrogant know-it-all, I'm going to butt in here (mostly just 'cause Josh likes to come butting into the Illinois forums....

)
If youse guys are running combos on 1 3/4" or 1 1/2", are these low-pressure fogs? Cause if they are conventional, you are way under-pumping them at PDP of 110-120psi. Is that a big deal? Only if....
I'll explain: I have in my hand a fog rated at 125 gpm. That rating is with 100 psi
at the nozzle. If I've got 200 feet of 1 3/4", I have to compensate at the pump for friction loss through the hose. (Illinois State Fire Marshal says 33psi per 100'. We KNOW this to be wrong by way of flow testing. But that's another story). If I pump at 110psi PDP, there may only by 70psi or less at the nozzle. Is that a big deal? It depends on a couple of things: IF you are not expecting 125gpm, no problem. If you ARE, you could have trouble.
Here's our deal:
We run one preconnect 150' 1 3/4" with adjustable gallonage fog. We normally have this set at 125gpm. By way of flow testing, we found we need 135psi PDP to get 100psi at the nozzle. This is easily managed with two firefighters. The other preconnect is 200' 1 3/4" with a 7/8" smoothbore. Again, by flowtesting, we found that if we pump that line at 100psi PDP, we flow about 180gpm. That's a helluva lot of firefighting punch. Best thing: one guy can manage it without trouble (remember, SB are designed to operate at 50psi nozzle pressure).
Some interesting things came out of flow testing:
1. We also were under pumping our preconnects. We were averaging about 90gpm on the fog. Again, it's okay, if that's what you are expecting, and you pre-fire plans are based on this.
2. By swithing our 200' to a SB, we designated that our first-off line for a residential, confined fire (i.e. one or two rooms and contents). Plus, it's highly manueverable. AND, it packed damn near as musch punch as our 2 1/2" with a 1" tip. DOWNSIDE: that lower pressure can lead to kinked hose. Again, not a problem if you are expecting it.
3. Our 2 1/2" preconnect is 200' also. We ended up taking off one of the stacked tips (it's now a 1 1/8"). This should flow over 200gpm. Again, 50psi on the tip. We found that we only needed 80psi PDP for this line at this flow.
Flow testing smooth bores is a piece of cake. All you need is a pitot gauge and a chart. Flowing fogs a little more complicated; you need a flow meter. Most salesmen can get one; call your local Akron or Elkhart rep and tell him you want to evaluate nozzles. You can flow test yours and see what's new in low pressure fogs.
I'll get the heck out of here now. Sorry, Josh!