    Default Flow Capacities for fire hose

    I've googled and looked everywhere without success for a chart, or listing of flow capacities for fire hose for these sizes 1 3/4", 2 1/2", 3", and 5". If anyone could help with providing these figures (in terms of GPM's) or give a link to a source that could help, it would be greatly appreciated. Even "close" figures would be helpful.

    Woody

  2. #2
    MembersZone Subscriber

    Join Date
    Jan 2007
    Location
    Pa Wilds
    Posts
    598

    Default Flow volumes of fire hose

    Woodie:

    There is no single flow volume for fire hose. It all depends upon how much pressure you are able to supply in getting the water through the hose line. Then the length of the hose directly affects the amount of pressure it will take. For 1 3/4" hose at 125 gpm it takes about 16 psi per 100 ft. For a flow of 150 gpm it will take a pressure of 25 psi per 100 ft. At 180 gpm about 36 psi per 100 ft. If pumping a 200 ft. preconnected 1 3/4" line with a 150 gpm fog nozzle at 100 psi, you will need an engine pressure of 150 psi. That is 50 psi for overcoming the friction loss in the hose and 100 psi to properly operate the nozzle.

    When sending water through a 2 1/2" line at 100 gpm it takes about 2 1/2 psi per 100 ft. of hose. At the same flow rate, 500 ft. of hose will require 13 psi to move that volume of water. At 300 gpm through 2 1/2" hose it requires 22 psi per 100 ft., or 110 psi through 500 ft of 2 1/2" hose. At 400 gpm the 2 1/2" hose needs a pressure of 40 psi per 100 ft. to push it through, or 200 psi to move it 500 feet.

    3" hose has a loss about equal to the desired flow divided by 100 and that number squared. Example: 500 gpm through 100 ft. of 3" hose. Move the decimal 2 places to the left and the 500 becomes 5 then square the 5 or 5 X 5 = 25 psi per 100 ft. will be the friction loss at 500 gpm. You could force 1000 gpm through the 3" hose and would need a pressure of 10 X 10 = 100 psi to get that flow through one 100 ft section of 3" hose. If you try to move 1000 gpm through more than 250 ft. of 3", you will exceed the rating of your pumper at over 250 psi. Not only that, but you will need a 2,000 gpm pumper to reach the 1,000 gpm at 250 psi.

    5" hose has a friction loss equal to 1/15th that of 3" hose. The same 1000 gpm can be pushed through 100 ft. of 5" hose with only 6 psi. you can send that 1000 gpm through 2,500 ft. of 5" line with a pressure of 150 psi and could do it with a 1,000 gpm pumper.

    Kuh Shise

  3. #3
    MembersZone Subscriber

    Join Date
    Feb 2007
    Location
    Louisville, KY
    Posts
    23

    Default

    Sorry, I should have specified length of hose...per 100' of hose, I'm looking for the capacities, in gallonage, of flow for the specified diameters. For instance, I know that 200' of 1 3/4" attack line can flow upwards of 200+ gpm (obviously depending on nozzle and pressure) but, I was, I guess, looking for the max capacity of the specified gpm's for the specified hose diameters, or for that matter, the "typical" capacities for those diameters. Thanks Kuhshise.

  4. #4
    Forum Member

    Join Date
    May 2001
    Location
    Greensboro, NC USA
    Posts
    1,318

    Default

    Pressure Loss in PSI per 100' Hose
    If they don't list a specific flow, it's either impractical to do in real life, or the friction loss is negligible.

    The entire TECHNICAL DATA section of Elkhart's Catalog has a boatload on data.
    23 pages of it.

  5. #5
    MembersZone Subscriber

    Join Date
    Feb 2007
    Location
    Louisville, KY
    Posts
    23

    Default

    Thank you for the links!

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. nfa fire flow
    By chuck cooke in forum The Engineer
    Replies: 15
    Last Post: 04-05-2008, 07:31 PM
  2. Maximum flow for supply hose?
    By FatherPierce in forum The Engineer
    Replies: 22
    Last Post: 01-28-2008, 01:21 AM
  3. Maximum flow in supply hose?
    By FatherPierce in forum Firefighters Forum
    Replies: 7
    Last Post: 01-25-2008, 11:57 AM
  4. Fuel tank capacities
    By WRFDTO in forum Hazardous Materials General Forum
    Replies: 2
    Last Post: 10-25-2005, 12:35 PM
  5. Efficient Flow Of Hose
    By vindicator in forum The Engineer
    Replies: 19
    Last Post: 10-24-2005, 08:33 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register