    Post Tulsa Fire Hydrant Inspections Questioned

    www.fox23.com

    You drive by them and may not give them a second thought. One of them may be right outside your home or very nearby. Fire hydrants. We just assume they work. But that could be a dangerous assumption. FOX 23’s Douglas Clark reports on the call for improved hydrant inspections in Tulsa.

    With thousands of fire hydrants around Tulsa, fire officials say they only have time to inspect them once every three years. But some city leaders are concerned that may not be enough.

    The National Fire Protection Association recommends fire hydrants be inspected, at a minimum, every year.

    “It’s absolutely a public safety issue,” says District 9 Councilor G.T. Bynum.

    He began asking questions when he found out hydrant inspections were not meeting national recommendations. In fact, in 2007, the fire department did not perform any inspections on city hydrants because it began designing a new computer system to streamline the process.

    “We have a great fire department and firefighters. But if they get there and a hydrant doesn’t work because we haven’t done the right level of inspection on it, that’s a serious public safety concern,” says Bynum.

    There are roughly 16,000 fire hydrants in the city of Tulsa, each requiring 15-20 minutes per inspection.

    “It’s really a workload issue,” says Tulsa Fire Captain Michael Baker.

    He says the department simply doesn’t have enough people to inspect every hydrant every year.

    “To be able to do it on an annual basis, we’d have trucks inspecting hydrants all the time,” says Baker.

    Instead, every year, a third of city fire hydrants get inspected.

    “I’m concerned about the safety of our homes and businesses in the area. And that would concern me if it came time to use it and it wasn’t usable,” says Tulsa resident Ginger Heald.

    Baker admits only a small percentage of hydrants fail inspection. Those that do are immediately reported to public works for repair. But he says there are backups in place when a hydrant experiences a problem during a fire.

    “The backup is that we carry enough water on the fire truck to allow us to do an initial attack on a fire or a rescue. So we have 500 gallons on those trucks. That’s enough for us to get in there and make any intervention we can,” says Baker.

    Firefighters also carry 1,000 feet of hose to tap into a working hydrant.

    There is a bill moving through the state legislature that would require cities to inspect hydrants every year. But it was recently amended to require inspections once every three years at the request of Mayor Kathy Taylor, who said an annual inspection procedure would be a financial burden for the city of Tulsa.

    Councilor Bynum would like to see the responsibility of inspecting hydrants shifted to the public works department, so the fire department can concentrate on fighting fires. Fire officials say they would support that idea, as long as it does not affect their personnel or budget in any negative way.


    Watch the Video
    http://www.fox23.com/news/local/stor...7nzl17AAQ.cspx

  2. #2
    MembersZone Subscriber

    Join Date
    Apr 2008
    Posts
    179

    Default

    Since you brought the issue of hydrants up, what exactly is the minimum NFPA required flow rate of hydrants...we have hydrants that barely work. We have some that don't work at all. We make notes of those and send them up the chain. But what constitutes a "Bad" hydrant, other than the ones that don't work? Does the NFPA have a minimum hydrant output standard?

    Thanks...

  3. #3
    Forum Member
    ThNozzleman's Avatar
    Join Date
    Jun 2002
    Location
    Jefferson City, TN
    Posts
    4,339

    Default

    For a hydrant to be really useful, it should be able to provide sufficient fireflow without dropping below 20 psi residual. The codes adopted by your authority having jurisdiction will dictate how many, spacing, and minimum flow. These requirements are generally based on the size and type of occupancies protected by the hydrant. They also dictate the size of the mains supplying them. Some buildings such as schools and nursing homes may be under the jurisdiction of the state and the life safety codes they have adapted. Most water districts do not allow connection to low-flow hydrants to prevent possible backflow of contaminated water into the system. To really (and I mean really) generalize, all hydrants should be capable of at least 500 gpm fire flow at 20 psi residual, and spaced so that they are actually useful, based on the tactics and size/amount of supply hose you use. If not, they are not useful for anything much, except for the water department guys to bleed air out of the system after a repair.

  4. #4
    Forum Member
    ThNozzleman's Avatar
    Join Date
    Jun 2002
    Location
    Jefferson City, TN
    Posts
    4,339

    Default

    You might find this useful if you don't have access to the full NFPA documents...scroll down to Chapter 8.
    http://www.nfpa.org/assets/files/PDF...8-ROPDraft.pdf

  5. #5
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    In my community... the Water and Sewer division of the Department of Public Works is responsible for the inspection and maintenance of hydrants.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  6. #6
    Forum Member
    ThNozzleman's Avatar
    Join Date
    Jun 2002
    Location
    Jefferson City, TN
    Posts
    4,339

    Default

    In my community... the Water and Sewer division of the Department of Public Works is responsible for the inspection and maintenance of hydrants.
    Not here; we lazy firemen have to get up out of our recliners and do our own hydrant testing and maintenance.
    Can I get the number for your mayor?

  7. #7
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    Quote Originally Posted by CaptainGonzo View Post
    In my community... the Water and Sewer division of the Department of Public Works is responsible for the inspection and maintenance of hydrants.
    Ditto. And we have a separate water company that has a transfer line through part of our town that we forced to test their hydrants.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  8. #8
    Forum Member
    ThNozzleman's Avatar
    Join Date
    Jun 2002
    Location
    Jefferson City, TN
    Posts
    4,339

    Default

    And we have a separate water company that has a transfer line through part of our town that we forced to test their hydrants.
    How much do you guys trust these other entities to get the job done right? Or done at all? Ever have any trouble with them? I believe a fire in Knoxville a couple of years ago revealed that even though the utilities guys were charged with annual testing and maintenance, they were actually not getting them done. In fact, a hydrant the fire department tried to use during that fire was completely rusted up and would not operate, inspite of records indicating it had been tested and maintained every year prior.

  9. #9
    the 4-1-4
    Jasper 45's Avatar
    Join Date
    Dec 2002
    Location
    ...A great place, on a Great Lake
    Posts
    2,784

    Default

    Quote Originally Posted by ThNozzleman View Post
    How much do you guys trust these other entities to get the job done right? Or done at all? Ever have any trouble with them?

    We actually have a great water system, and we operate with a separate water utility.
    The biggest problem we have with hydrants is with 'em freezing in the winter, and them being used as summertime neighborhood sprinklers.

    Other than that the water utility does a very good job at keeping our hydrant system up and running.

    We do absolutely nothing with our hydrants for testing or maintenance.

  10. #10
    Forum Member

    Join Date
    Nov 2000
    Location
    Houston, TX
    Posts
    84

    Default

    We're responsible for checking our own hydrants as well. The number of hydrants in an engine's territory are divided by four (for four shifts) and each hydrant has to be inspected twice per year. Besides the inspection factor it's an excellent way to learn where the hydrants are in your territory.

  11. #11
    Forum Member
    CaptOldTimer's Avatar
    Join Date
    Jun 1999
    Location
    Virginia
    Posts
    7,257

    Default

    My old city department had over 7,000 hydrants planted all over. They belong to the public utilities but the fire department inspects them.


    All hydrants in each companies district is divided by three for the three shifts so each shift will have their fair share.

    There is a physical check on each hydrant twice a year and on those that has been repaired or replaced throughout the year. Each hydrant is checked for water and the flow. Caps and other parts are checked to be sure they are connected to the hydrant and also to the caps. In the spring the hydrant is flowed and afterwards it is painted. Paint and equipment is furnished by the utilities dept. Plus each month grass and over growth is cut away from all hydrants having it growing at or near them.

    In the fall the inspection consists of making sure no water is standing in the barrel. Sometimes the weap hole may be blocked by debris or trash. If is is the companies make a connection to a 2-1/2 " outlet on the pumper to a 2-1/2 ' outlet on the hydrant. After making sure the hydrant is closed, the operator charges that line and applies pressure to the hydrant. This normally will blow out the weap hole. Everything it shut down and the caps removed from the hydrant and inspected. Should water is still there the public utilitiy dept is notified and they will repair the hydrant.

    We also make sure the street valve is fully open, as sometimes workers will close the valve while working on the mains and or hydrant and think they may have it fully opened.

    This has been done for years by the department. It is a learning tool as members learn the district as well as the hydrants.

    Of course the company is always ready to take a run if one is transmitted for them.
    Stay Safe and Well Out There....

    Always remembering 9-11-2001 and 343+ Brothers

  12. #12
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    Quote Originally Posted by ThNozzleman View Post
    How much do you guys trust these other entities to get the job done right? Or done at all? Ever have any trouble with them? I believe a fire in Knoxville a couple of years ago revealed that even though the utilities guys were charged with annual testing and maintenance, they were actually not getting them done. In fact, a hydrant the fire department tried to use during that fire was completely rusted up and would not operate, inspite of records indicating it had been tested and maintained every year prior.
    We run a hydrant or 2 of theirs every now and then. This transfer line is the main water supply for 2 towns south of me and part of the condition for allowing them to run it through our town was that they had to add a hydrant every 1500 feet for our use. These are "bonus" hydrants that were added to an already hydranted area. Our existing hydrants are our main source, these are secondary. We are a small enough town that when they are testing those hydrants, we see them.

    As for my own water department and our hydrants...we may argue the numbers they report, but we know the hydrants are working.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Fire Inspections
    By FMFFPB in forum Fire Prevention and Life Safety
    Replies: 2
    Last Post: 11-16-2008, 10:47 PM
  2. Utah-Fatal Fire Response time questioned
    By UTFFEMT in forum Fire Wire
    Replies: 0
    Last Post: 05-18-2004, 01:12 AM
  3. CD Player, Refrigerator Questioned on New Fire Truck
    By CollegeBuff in forum The Off Duty Forums
    Replies: 19
    Last Post: 01-26-2004, 10:06 PM
  4. Replies: 1
    Last Post: 06-03-2003, 07:55 PM
  5. Inspections of Fire Houses
    By Capt217 in forum Fire Prevention and Life Safety
    Replies: 4
    Last Post: 02-04-2003, 04:52 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register