For reference, FL in 5" hose (theoretical) is losted below for GPM (left column) and FL per 100' of hose in right column.
350-1
400-1
450-2
500-2
550-2
600-3
650-3
700-4
750-5
800-5
850-6
900-6
950-7
1000-8
1250-13
1500-14
1750-20
2000-26
Closed Thread
Results 21 to 23 of 23
Thread: Pros and Cons to LDH..
-
07-17-2009, 12:18 PM #21MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Central NJ
- Posts
- 1,214
-
07-17-2009, 12:19 PM #22
Contrary to popular belief, friction loss does occur between the hydrant and the attack pumper. Next time you train put a gauge on one of the 2 1/2" outlets and see the pressure difference between the hydrant and the intake on your pump. You will be amazed at the pressure drop when flowing the maximum amount of water with the set-up that you are working with.
I would recommend if you need big-water pump the hydrant. Another recommendation is to stretch 2 five inch supply lines from the hydrant to the supply pumper. This allows more water to flow into the pump at basically the same hydrant pressure.I believe them bones are me. Some say we are born into the grave. I feel so alone, gonna end up a big ol' pile a them bones
-J. Cantrell
-
07-17-2009, 12:21 PM #23
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
pros/cons
By dazeoff10 in forum Firefighters ForumReplies: 6Last Post: 09-28-2004, 07:20 PM -
Pros and Cons of......
By fyrbreathrEMT in forum Firefighters ForumReplies: 7Last Post: 03-01-2002, 01:46 PM -
Pros and Cons
By nsfirechap in forum Thermal Imaging CamerasReplies: 2Last Post: 04-21-2001, 03:07 AM -
KME pros and cons
By ultrafire in forum Apparatus InnovationReplies: 16Last Post: 08-27-2000, 12:46 AM

LinkBack URL
About LinkBacks