Originally Posted by
RFDACM02
I'm going to go out on a limb and propose that any sprinkler system with any FDC should be supplied at 150 psi. I base this on the fact that someone somewhere hoped to make some of this stuff as "easy" on our end as possible. The diameter of the pipe and the connection may be related to the overall design flow, but does not necessarily require less pressure as in most cases smaller diameter equals higher pressures.
As reference I found this in NFPA 13D (Sprinklers for 1 and 2 family dwellings):
4.3.2 Where a fire department pumper connection is provided, the system shall pass a hydrostatic pressure test performed in accordance with NFPA 13, Standard for the Installation of Sprinkler Systems.
From NFPA 13:
24.2.1.1 Unless permitted by 24.2.1.2 through 24.2.1.6, all piping and attached appurtenances subjected to system working pressure shall be hydrostatically tested at 200 psi (13.8 bar) and shall maintain that pressure without loss for 2 hours.
As I think it through, would't the heads require the same pressure as any other system? So like a nozzle they should require the same "nozzle pressure"?