    Default Residential Sprinklers

    I am looking at putting in an garage separate from the house. In this garage will be my workshop and the wood boiler for my home heat. Since this garage may not always be heated there is the possibility of freezing. So as I consider my design I thought it will be simple and inexpensive to add sprinklers. Which has me now thinking about how are these set up to work in areas that may freeze. I know that in industrial settings they have dry systems that only activate when there is a call for water. These must be hooked to air compressor and a supply of air must be there to keep the valve shut.

    So tell me, how are residential systems set up to work in attics and unheated spaces.

  2. #2
    Forum Member

    Join Date
    Nov 2008
    Location
    Mass
    Posts
    1,037

    Default

    Quote Originally Posted by ScareCrow57 View Post
    I am looking at putting in an garage separate from the house. In this garage will be my workshop and the wood boiler for my home heat. Since this garage may not always be heated there is the possibility of freezing. So as I consider my design I thought it will be simple and inexpensive to add sprinklers. Which has me now thinking about how are these set up to work in areas that may freeze. I know that in industrial settings they have dry systems that only activate when there is a call for water. These must be hooked to air compressor and a supply of air must be there to keep the valve shut.

    So tell me, how are residential systems set up to work in attics and unheated spaces.

    The type of system that is pressurized with air is called a Preaction system. Compressed air keeps the sprinkler valves clapper closed. If a sprinkler head is activated, the air is released which allows the clapper to open and water to flow.

    Preaction systems exists for residential use as well. That would be the solution to running lines in an unheated space. I have seen home built versions that simply pressureized the lines in the winter months with air. The will only work though if the sprinkler heads are not on drop lines (pendants). In other words, the sprinkler heads must be screwed in right on the supply pipe. The idea being is you do not want to have any locations where water can be trapped when the sytem is drained. A simple way to explain how that works is picture this...

    The supply valve to that section of pipe is located in a climate controlled area not subject to freezing. At that shutoff valve is a drain valve that is the lowest point in the system. At the very end of the piping should be another drain valve although this valve does not have to be at the low point on the system. Prior to winter months, shut off the water supply to that section and drain the water out of the system using both drain valves. The upper drain valve at the end of the system will assure that all water drains out from the bottom. Now attach your air compressor at the lower drain valve and blow the remaining water out through the upper drain. Then close the upper drain and pressurize the system at least 40psi above the water pressure. Obviously you want a gauge for this. Once that is done, close the drain valve and disconnect the air supply. Then open the water supply. If you did it correctly and there are no leaks, the system is now charged with air and is freezeproof.

  3. #3
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,911

    Default

    Not all, in fact most "dry sprinkler systems" are not preaction. Preaction systems require another initiating device such as smoke detectors or pull stations to release an electrically controlled device on the water supply. Then the water can fill the pipe bu not flow until the head is fused by the appropriate heat.

    I'm not specifically familiar with residential systems that are dry pipe, and have have mostly heard of glycol loops for areas that might freeze, which would require check valves to keep it separate from the typical water based system. The main reason this isn't a big deal is that residential systems are not normally designed for unheated attics or garages as they're not required in these not normally occupied spaces.

  4. #4
    Forum Member

    Join Date
    Nov 2008
    Location
    Mass
    Posts
    1,037

    Default

    Quote Originally Posted by RFDACM02 View Post
    Not all, in fact most "dry sprinkler systems" are not preaction. Preaction systems require another initiating device such as smoke detectors or pull stations to release an electrically controlled device on the water supply. Then the water can fill the pipe bu not flow until the head is fused by the appropriate heat.
    Thanks for catching that, i was confusing the dry type system with Pre-action. The pre-action system are in fact triggered by a pull station or flame, smoke or heat sensor and many are wired to turn off once the flames are gone and then turn back on again if they return.

  5. #5
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,586

    Default

    There are special heads designed for residential sprinkler systems that can be used in areas where there can be freezing temperatures.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  6. #6
    Forum Member

    Join Date
    Nov 2008
    Location
    Mass
    Posts
    1,037

    Default

    Quote Originally Posted by CaptainGonzo View Post
    There are special heads designed for residential sprinkler systems that can be used in areas where there can be freezing temperatures.
    Those are just when the sprinklers themselves will be in an unheated space, like a garage. They are extended pendants that keep the water back int he non-feezing area till they discharge. They are used in walk in freezers as well. But the supply lines still need to be somewhere protected from freezing.

  7. #7
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,586

    Default

    Quote Originally Posted by WD6956 View Post
    Those are just when the sprinklers themselves will be in an unheated space, like a garage. They are extended pendants that keep the water back int he non-feezing area till they discharge. They are used in walk in freezers as well. But the supply lines still need to be somewhere protected from freezing.
    well.. no duh!
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  8. #8
    Forum Member

    Join Date
    Nov 2008
    Location
    Mass
    Posts
    1,037

    Talking

    Quote Originally Posted by CaptainGonzo View Post
    well.. no duh!
    At least we are all clear on that..

  9. #9
    Forum Member
    FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,434

    Default

    Quote Originally Posted by ScareCrow57 View Post
    So tell me, how are residential systems set up to work in attics and unheated spaces.
    No, you tell us, since you know everything about anything else....Educate us, oh wise *** one.
    "Loyalty Above all Else. Except Honor."

  10. #10
    55 Years & Still Rolling
    hwoods's Avatar
    Join Date
    Jun 2002
    Location
    Glenn Dale Md, Heart of the P.G. County Fire Belt....
    Posts
    10,740

    Question Quick Question...........

    If your Wood Furnace is in the Garage, how is it unheated?.......
    Never use Force! Get a Bigger Hammer.
    In memory of
    Chief Earle W. Woods, 1912 - 1997
    Asst. Chief John R. Woods Sr. 1937 - 2006

    IACOJ Budget Analyst

    I Refuse to be a Spectator. If I come to the Game, I'm Playing.

    www.gdvfd18.com

  11. #11
    Forum Member

    Join Date
    Nov 2008
    Location
    Mass
    Posts
    1,037

    Default

    Quote Originally Posted by hwoods View Post
    If your Wood Furnace is in the Garage, how is it unheated?.......
    I guess when the wood furnace is not running? I know many people use them as supplemental heat. Since they need to be stoked manually.

  12. #12
    Forum Member
    nmfire's Avatar
    Join Date
    Nov 2002
    Location
    Maryland (DC Suburb)
    Posts
    5,738

    Default

    I would think the vast amount of hot air in ScareCrow's head could not only pressurize a high rise dry system but also heat the space quite efficiently at the same time. I don't see why he needs all this fancy stuff.
    Even the burger-flippers at McDonald's probably have some McWackers.

  13. #13
    55 Years & Still Rolling
    hwoods's Avatar
    Join Date
    Jun 2002
    Location
    Glenn Dale Md, Heart of the P.G. County Fire Belt....
    Posts
    10,740

    Post Umm... Ok............

    Quote Originally Posted by WD6956 View Post
    I guess when the wood furnace is not running? I know many people use them as supplemental heat. Since they need to be stoked manually.

    My Son and daughter-in-law have one on their farm, But it's a Combination thing that, when the Wood Fire dies below a certain temp, an Oil Burner comes on, (in a separate Firebox) and maintains the water temps to the Heat exchangers in the house. When the Wood Firebox is stoked up again, the oil shuts down.
    Never use Force! Get a Bigger Hammer.
    In memory of
    Chief Earle W. Woods, 1912 - 1997
    Asst. Chief John R. Woods Sr. 1937 - 2006

    IACOJ Budget Analyst

    I Refuse to be a Spectator. If I come to the Game, I'm Playing.

    www.gdvfd18.com

  14. #14
    Banned

    Join Date
    Jan 2008
    Posts
    8,677

    Default

    Quote Originally Posted by hwoods View Post
    If your Wood Furnace is in the Garage, how is it unheated?.......
    For those times when there is no fire (oil backup is in basement). Since it heats water an is insulated I don't know how much heat will be in the garage. This is a case of rather being safe than sorry

  15. #15
    Banned

    Join Date
    Jan 2008
    Posts
    8,677

    Default

    Quote Originally Posted by hwoods View Post
    My Son and daughter-in-law have one on their farm, But it's a Combination thing that, when the Wood Fire dies below a certain temp, an Oil Burner comes on, (in a separate Firebox) and maintains the water temps to the Heat exchangers in the house. When the Wood Firebox is stoked up again, the oil shuts down.
    Yea, I saw those. Of course I replaced my furnace about 5 or 6 years ago, so it is new and energy efficient. Imagine that, and improved more efficient furnace without government incentives.

  16. #16
    Forum Member

    Join Date
    Jan 2009
    Posts
    54

    Default supplemental heaters

    You could also add a couple Cadet Heaters with a manual thermostat to your garage, keeping the thermostat set at the minimum which I think is 50f wouldn't cost much. The good ones have a fan in them that looks like a squirrel cage, more expensive but worth it.

    Depending on where you live(and how cold it gets) you cold install pipe insulation around your pipes. You could also use wirsbo or pex style pipe that is not as fragile as other types(it can expand a lot).

    Usually I recommend that if you have to put pipes in an attic space or unheated ceiling area that you "bed" them in insulation and wrap them with foam pipe wrap.

    hope this helps..

  17. #17
    Banned

    Join Date
    Jan 2008
    Posts
    8,677

    Default

    Quote Originally Posted by hammerhome View Post
    You could also add a couple Cadet Heaters with a manual thermostat to your garage, keeping the thermostat set at the minimum which I think is 50f wouldn't cost much. The good ones have a fan in them that looks like a squirrel cage, more expensive but worth it.

    Depending on where you live(and how cold it gets) you cold install pipe insulation around your pipes. You could also use wirsbo or pex style pipe that is not as fragile as other types(it can expand a lot).

    Usually I recommend that if you have to put pipes in an attic space or unheated ceiling area that you "bed" them in insulation and wrap them with foam pipe wrap.

    hope this helps..
    Upstate NY and it gets into the high -20s or is that the low -20s? The heck with it call it -30F

  18. #18
    Forum Member

    Join Date
    Jan 2009
    Posts
    54

    Default

    i don't have any experience in that kind of temperature...keep the space heated! Well insulated and heated to a minimal temp would probably be your best bet, and fairly efficient when you factor the cost of replacing water damaged materials.

    I would assume that even the main up into the sprinkler system(even if the system weren't charged) would freeze unless it were located someplace else. Good luck.

    hh

  19. #19
    Forum Member

    Join Date
    Dec 2007
    Posts
    130

    Default

    ScareCrow 57

    See NFPA 13D it has various options for you. I believe antifreeze will be the cheapest option for you. NFPA 13D has specific types and concentrations for the antifreeze as well as piping configurations. Keeping the main water feed before the antifreeze sections can be a problem, you may need to install heat tape or an electric heater for this area.

    Do you have a good water supply in the garage? At least a 3/4 " line with about 60 psi? If not, a pump and tank may make this a very expensive install.

    Consider an off site alarm for water flow, it can call your cell phone, etc. If the pipe breaks or you have a fire, you want to be notified. A local bell can work if you have anyone that will hear it and respond.

    Garage doors will need sprinkler protection below the door rail guides. Install a side wall head on each door.

    Some plastic pipe can be exposed, see the mfg cut sheet. Pex pipe can not be exposed. You may want to use copper or steel pipe if you do not plan to sheet rock the ceiling to provide a fire barrier between the pipe and the space.

    Sprinklers near your boiler may need a higher temperature see NFPA 13D for what is needed.

    Do you plan on designing the system or do you have someone that can help? After you review NFPA 13D you will see what is required. Keep in mind a 13D is for life safety and not property protection. Meaning it is designed to get you out. BUT 99% of the residential fires have been extinguished by 1 head, so most time it will also safe property.

    How large of a garage do you plan on building?

    Hope this helps.
    Fire Sprinklers Save Firefighters’ Lives Too!

  20. #20
    Forum Member

    Join Date
    Dec 2007
    Posts
    130

    Default

    Quote Originally Posted by WD6956 View Post
    Thanks for catching that, i was confusing the dry type system with Pre-action. The pre-action system are in fact triggered by a pull station or flame, smoke or heat sensor and many are wired to turn off once the flames are gone and then turn back on again if they return.
    WD

    Most if not all pre-action sprinkler systems do not turn off after the fire is out. They must be turned off by the FD or building occupant.

    I have been inspecting pre-action sprinkler systems for 30 years and can count on one hand how many have been cycling on/off pre-action systems. You can not tell just by looking at the system if it is a cycling on/off pre-action system. You have to ask who ever installed the system how they programed the system to work. A hint is the type of detector used to set off the system. If it is cycling on/off pre-action system it will use restorable heat detectors. If you see a smoke detector it is not a cycling on/off pre-action system. Also if you see a heat detector it is not a cycling on/off pre-action system.

    Hope this helps.
    Last edited by InsuranceLCRep; 12-29-2009 at 08:39 AM.
    Fire Sprinklers Save Firefighters’ Lives Too!

  21. #21
    Forum Member

    Join Date
    Jul 2001
    Posts
    145

    Default

    Pre-action and FireCycle(Viking system) commonly use a rate of rise
    detecting device like these.

    Don
    Attached Images Attached Images   

  22. #22
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,911

    Default

    Quote Originally Posted by InsuranceLCRep View Post
    WD

    If you see a smoke detector it is not a cycling on/off pre-action system. Also if you see a heat detector it is not a cycling on/off pre-action system.

    Hope this helps.
    I always wonder why anyone installs heat detectors along with sprinkler heads? In the above case it would seem to be a complete waste of money to install a heat detector as an initiation device on a pre-action system? Would a rate of rise activate quickly enough to "out run" the sprinkler head temp? Special applications like high ceilings?
    Last edited by RFDACM02; 12-29-2009 at 09:06 AM. Reason: added questions

  23. #23
    Forum Member

    Join Date
    Dec 2007
    Posts
    130

    Default

    Quote Originally Posted by RFDACM02 View Post
    I always wonder why anyone installs heat detectors along with sprinkler heads? In the above case it would seem to be a complete waste of money to install a heat detector as an initiation device on a pre-action system? Would a rate of rise activate quickly enough to "out run" the sprinkler head temp? Special applications like high ceilings?
    Yes I agree when we see a heat detector most times we make a recommendation to install smoke detection. Why? because we want early detection and a call to the FD. If you went through the $$ to install a pre-action system it was an area that has a lot of $$ in one place. A heat detector will give you perhaps 10-30 seconds advance notification before the sprinkler activates, perhaps less with a quick response sprinkler. The smoke detector or even better a Vesda system will give you advanced notification.
    Fire Sprinklers Save Firefighters’ Lives Too!

  24. #24
    Forum Member

    Join Date
    Dec 2007
    Posts
    130

    Default

    Quote Originally Posted by don120 View Post
    Pre-action and FireCycle(Viking system) commonly use a rate of rise
    detecting device like these.

    Don

    Don,

    True BUT they must be self restoring, meaning when they cool down they reset. By doing this it signals the pre-action sprinkler panel the fire is out and to shut down the water flow. If the fire is not out, heat will build back up again, activate the heat detector, open the pre-action valve again, put water on the fire, cool down, valve shuts, etc etc. Thus a cycling on/off pre-action system.
    Fire Sprinklers Save Firefighters’ Lives Too!

  25. #25
    Forum Member

    Join Date
    Nov 2008
    Location
    Mass
    Posts
    1,037

    Default

    Quote Originally Posted by InsuranceLCRep View Post
    WD

    Most if not all pre-action sprinkler systems do not turn off after the fire is out. They must be turned off by the FD or building occupant.

    I have been inspecting pre-action sprinkler systems for 30 years and can count on one hand how many have been cycling on/off pre-action systems. You can not tell just by looking at the system if it is a cycling on/off pre-action system. You have to ask who ever installed the system how they programed the system to work. A hint is the type of detector used to set off the system. If it is cycling on/off pre-action system it will use restorable heat detectors. If you see a smoke detector it is not a cycling on/off pre-action system. Also if you see a heat detector it is not a cycling on/off pre-action system.

    Hope this helps.

    Thanks for taking the time to explain. Based on the cost and complexity, i figured they were going to be a rareley used system but they covered them with us because he have one of those systems in an area we cover. But good info, thanks.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. More residential fire sprinklers in local ordinances
    By DaSharkie in forum Firefighters Forum
    Replies: 0
    Last Post: 12-05-2005, 11:10 AM
  2. Residential sprinklers and wells
    By neiowa in forum Firefighters Forum
    Replies: 11
    Last Post: 12-20-2004, 11:18 AM
  3. Residential Fire Sprinklers
    By jtriolo90 in forum Fire Prevention and Life Safety
    Replies: 2
    Last Post: 09-09-2003, 04:53 PM
  4. Residential Sprinklers
    By mgoguen in forum Fire Prevention and Life Safety
    Replies: 5
    Last Post: 11-09-2000, 12:50 AM
  5. Incentives for Residential Fire Sprinklers
    By phxfyr in forum Fire Politics
    Replies: 1
    Last Post: 03-16-2000, 09:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register