    Default What's wrong with this picture? - Pumper Capacity Certification Plate

    See anything odd?

    Image edited to hide manufacture's name.
    The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America


  2. #2
    Forum Member FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    9,851

    Default

    Capacity 1500, yet it is rated at 1260 at 150 psi.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  3. #3
    MembersZone Subscriber
    Join Date
    Dec 2001
    Location
    Lusby, MD
    Posts
    1,033

    Default

    Like Fyred, I see capacity listed as 1500, but only getting 1260 at 150 psi.

    What's the story behind this, where did you find it?

  4. #4
    Truckie SPFDRum's Avatar
    Join Date
    Mar 1999
    Location
    St Paul, MN
    Posts
    2,513

    Default

    Pesky details......
    My posts reflect my views and opinions, not the organization I work for or my IAFF local. Some of which they may not agree. I.A.C.O.J. member
    "I ask, Sir, what is the militia? It is the whole people. To disarm the people is the best and most effectual way to enslave them."
    George Mason
    Co-author of the Second Amendment
    during Virginia's Convention to Ratify the Constitution, 1788
    Elevator Rescue Information

  5. #5

    Join Date
    May 2008
    Posts
    4

    Default

    It could very well be that this unit is destined for Canada. Canadian apparatus should be tested in either Imperial GPM or liters per minute. 1500 US GPM translates to roughly 1250 Imperial GPM. I say "roughly" because if you were to use a mathematical formula to convert US GPM to Imperial GPM the answer you get will be rounded off to come up with the Imperial GPM equivalent.

    For instance, roughly, 500 US GPM = 420 IGPM, 750 = 625, 1000 = 840, 1250 = 1050, 1500 = 1250, 1750 = 1500, 2000 = 1750 etc.

  6. #6
    Forum Member FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,354

    Default

    Maybe a 1500 was installed in anticipation of future expansion?????
    "Loyalty Above all Else. Except Honor."

  7. #7
    Forum Member
    Join Date
    Apr 2008
    Location
    Ontario
    Posts
    405

    Default

    Quote Originally Posted by FWDbuff View Post
    Maybe a 1500 was installed in anticipation of future expansion?????
    They were asking 1500, but got 1260 instead! good deal?

  8. #8
    Forum Member FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,354

    Default

    Quote Originally Posted by CanadianFyrTrks View Post
    They were asking 1500, but got 1260 instead! good deal?
    What I meant was, maybe they ordered a 1500, but only have enough discharges (right now) for 1250?????????? Perhaps they want to expand in the future- add a deck gun?
    "Loyalty Above all Else. Except Honor."

  9. #9
    Forum Member FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    9,851

    Default

    Quote Originally Posted by FWDbuff View Post
    What I meant was, maybe they ordered a 1500, but only have enough discharges (right now) for 1250?????????? Perhaps they want to expand in the future- add a deck gun?
    Sorry not buying that.

    I believe one of 2 things is happening here:

    1) Stupid mistake by whomever made the pump plate.

    2) For some reason, horsepower, or whatever, the pump was unable to make 1500 gpm so was down rated to 1260.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  10. #10
    Forum Member FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,354

    Default

    Quote Originally Posted by FyredUp View Post
    Sorry not buying that.

    I believe one of 2 things is happening here:
    I don't either, but a mistake by whomever made the plate was too obvious, and not being able to put out 1500 is just such a HUGE boo-boo that I wanted to offer the benefit of the doubt.
    "Loyalty Above all Else. Except Honor."

  11. #11
    MembersZone Subscriber npfd801's Avatar
    Join Date
    Aug 2002
    Location
    Somewhere in Illinois
    Posts
    2,216

    Default

    I've never sold one, nor have I seen one, but I have heard of folks buying more "pump" than they need so as the rig ages, it will still maintain the desired pump rating certification. So instead of being at the bitter edge of driving a pump with just enough horsepower, they have some room to compensate for future powertrain losses.

    Not saying it is right, but I've heard that argument before.
    "Share your knowledge - it's a way to achieve immortality." - Stolen from Chase Sargent's Buddy to Boss program

  12. #12
    Forum Member
    Join Date
    May 2001
    Location
    Greensboro, NC USA
    Posts
    1,294

    Default

    Quote Originally Posted by FWDbuff View Post
    What I meant was, maybe they ordered a 1500, but only have enough discharges (right now) for 1250?????????? Perhaps they want to expand in the future- add a deck gun?
    According to Table 16.7.1 of NFPA 1901, it has adequate discharges for a pump rated up to 2,000 GPM.

    It's being driven by a Cummins ISM, rated at 450 HP/1,450 tq, so horsepower isn't a problem.

    Also, every Qmax pump made is designed to flow 2,250 from a draft, assuming you give it adequate intakes, discharges, and horsepower. (This comes verbatim from Gary Handwerk's mouth.)



    Ponder this other question for a moment...
    Here's a picture of the piping feeding the crosslays and the tankfill.


    Note that a single pipe below the valves feeds all three, but they're in a series teed off the single pipe. I don't know if this is 3" or 2Ĺ" piping, but consider a scenario where both crosslays are being used for interior attack, both actively flowing no less than 150 GPM each.

    What happens to the flow pressure of the preconnects if the operator opens the tank-fill completely? Since it's first in the lineup, it would sap a huge amount of water from the piping. Remember a tank-fill has no nozzle orifice, so the flow is fairly substantial.
    Last edited by txgp17; 03-24-2010 at 02:51 AM.
    The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America

  13. #13
    Forum Member
    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,614

    Default

    Quote Originally Posted by txgp17 View Post
    According to Table 16.7.1 of NFPA 1901, it has adequate discharges for a pump rated up to 2,000 GPM.

    It's being driven by a Cummins ISM, rated at 450 HP/1,550 tq, so horsepower isn't a problem.

    Also, every Qmax pump made is designed to flow 2,250, assuming you give it adequate intakes, discharges, and horsepower. (This comes verbatim from Gary Handwerk's mouth.)



    Ponder this other question for a moment...
    Here's a picture of the piping feeding the crosslays and the tankfill.


    Not that a single pipe below the valves feeds all three, but they're in a series teed off the single pipe. I don't know if this is 3" or 2Ĺ" piping, but consider a scenario where both crosslays are being used for interior attack, both actively flowing now less than 150 GPM each.

    What happens to the flow pressure of the preconnects if the operator opens the tank-fill completely? Since it's first in the lineup, it would sap a huge amount of water from the piping. Remember a tank-fill has no nozzle orifice, so the flow is fairly substantial.
    I've seen this setup before. At least one builder uses it pretty much as standard, but I can't remeber who it is. If the manifold pipe is of adequate size and looped (tied in on both sides of the pump discharge casting) it wouldn't be too bad. This one looks to be 3-1/2" or 4" which I really don't think would be enough if you opened the tank fill completely.

    We learned very quickly about opening the tank fill completely. One of our members called me one morning saying that he doing a weekly run of the CAFS compressor. He was getting an overheat warning for the compressor oil. When I arrived at the station and he recreated what he had done it became apparent very quickly. He had opened our 2" tank fill all the way. He was getting exactly what you describe. All of the water that was being circulated was going right back into the tank through the fill. Because the "nozzle" pressure was so low, none of the water was going into the compressor oil cooler. I got out a triangular file and filed a groove on the valve's operating rod about 1-1/2" in. Our operating instructions now say that when using CAF, do not open the tank fill past that groove.
    Last edited by chiefengineer11; 03-21-2010 at 08:48 PM.

  14. #14
    Forum Member
    Join Date
    Nov 2005
    Posts
    15

    Default

    Withdrawn because of previous post
    Last edited by fire2eagle; 03-23-2010 at 07:58 AM.

  15. #15
    Forum Member
    Join Date
    May 2001
    Location
    Greensboro, NC USA
    Posts
    1,294

    Default UPDATE - Error made by the builder

    OK folks,
    Garage Supervisor called the Salesman, and the Salesman was not happy. The pump was supposed to be UL tested at 1,500, and in fact, the pump model plate provided by Hale is marked "QMAX150-23L", which translates to:
    • Qmax Pump
    • 1,500 rating
    • "L" series pump transmission
    • 2.28 drive ratio
    Basically, someone got the facts mixed up for the UL Certification Test.

    We performed our Acceptance Test at 1,500 GPM, and it passed with flying colors.

    Also, I've secured permission to use this truck for the Practical Portions of a Service Testing class on Thursday and Friday. When I get it hooked up, I'll measure the actual flow loss in that discharge header extension when the tank-fill is opened.

    I'll do it once when both preconnects are flowing 150 each (300 total), and 200 each (400 total). Facts will be posted then.
    Last edited by txgp17; 03-24-2010 at 11:51 AM.
    The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America

  16. #16
    Forum Member FIREMECH1's Avatar
    Join Date
    Apr 2008
    Location
    HUSKER LAND
    Posts
    2,425

    Default

    Thanks for the info on the screw up.

    I'm also very interested in what you get when you perform your tests. I don't have that set up, but the info would be nice to have, to put in the gray matter.

    FM1
    I'm the one Fire and Rescue calls, when they need to be Rescued.

    Quote Originally Posted by EastKyFF
    "Firemens gets antsies. Theys wants to goes to fires. Sometimeses they haves to waits."

  17. #17
    Forum Member CaptOldTimer's Avatar
    Join Date
    Jun 1999
    Location
    Virginia
    Posts
    7,202

    Default

    Quote Originally Posted by txgp17 View Post
    See anything odd?

    Image edited to hide manufacture's name.



    Probably made and installed by a goofy mechanic, aka -> parts changer!!

    Stay Safe and Well Out There....

    Always remembering 9-11-2001 and 343+ Brothers

  18. #18
    Forum Member
    Join Date
    Jan 2007
    Posts
    2,802

    Default

    the capacity was done in U.S. dry gallons and the pump test data is in U.S. wet gallons.

  19. #19
    Forum Member GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,056

    Default

    Quote Originally Posted by txgp17 View Post

    What happens to the flow pressure of the preconnects if the operator opens the tank-fill completely?
    You rob the pump of water in a hurry. I figured this out when our newest engines was delivered. If the tank fill is more than cracked the EPG will sense low supply and shut it down.

    Crappy design in my book.
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  20. #20
    Forum Member FIREMECH1's Avatar
    Join Date
    Apr 2008
    Location
    HUSKER LAND
    Posts
    2,425

    Default

    Quote Originally Posted by txgp17
    What happens to the flow pressure of the preconnects if the operator opens the tank-fill completely?
    Quote Originally Posted by GTRider245
    You rob the pump of water in a hurry. I figured this out when our newest engines was delivered. If the tank fill is more than cracked the EPG will sense low supply and shut it down.

    Crappy design in my book.
    I'm not sure if I am reading what "txgp17" is asking is right, or not. But if your flowing water through the preconnects and open the tank fill valve, you are going to have some very unhappy guys holding the line.

    If you have the newer electronic governor set in pressure mode, it should ramp up quite a bit to keep the pressure up on the preconnect, depending on the size of the pipe to the tank.

    This is also controlled by your water source at the intake. If you have a good hydrant system, then there shouldn't be a problem.

    Please correct me if I'm wrong on what I think is being asked.

    FM1
    I'm the one Fire and Rescue calls, when they need to be Rescued.

    Quote Originally Posted by EastKyFF
    "Firemens gets antsies. Theys wants to goes to fires. Sometimeses they haves to waits."

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Whats wrong with this picture???
    By smokebuster in forum The Off Duty Forums
    Replies: 34
    Last Post: 08-12-2007, 12:28 AM
  2. What's wrong with OUR picture?
    By WTFDChief730 in forum Ohio
    Replies: 14
    Last Post: 02-12-2004, 12:09 AM
  3. Whats wrong with this picture?
    By backdraft663 in forum Firefighters Forum
    Replies: 51
    Last Post: 11-27-2003, 11:11 PM
  4. What's Wrong with this Picture?
    By dragonfyre in forum Emergency Services Training
    Replies: 16
    Last Post: 02-26-2003, 08:15 PM
  5. What's Wrong With This Picture?
    By Jon Shaw in forum Line of Duty: In Memory Of
    Replies: 0
    Last Post: 12-13-1999, 02:20 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts