    Default Emergency Station Generator

    We as a department are just starting to look into a station generator and the chief gave me the go-ahead to get the facts on them I do have a few questions though. First off, what size should we look at? We need to be able to open the garage doors, power the base radios, the E.O.C. and the A.C./heat since we are an emergency cooling/heating center. What are the advantages/disadvantages to diesel and gas? Diesel would be preferred since we have a diesel pump on site but if gas has some winning advantages we could go with the idea. I thought I remember reading somewhere that the DOD or some place, has large, diesel generators with low hours for free or close to. Did I remember that right or am I just filling in the memory gaps with my old thoughts? Thanks for taking the time to read and hopefully help us find one that will work for us.

    FF M. Schabacker

  2. #2
    Forum Member
    mtg55's Avatar
    Join Date
    Feb 2010
    Location
    Pennsylvania
    Posts
    1,313

    Default

    Best bet would be to contact a generator suplier or electrician to tell you what size you need. We have a large Onan that is fed by natural gas. If you have natural gas to or near your building that would be the optimal choice, as you don't have to worry about filling a tank. The DOD does have them every now and then, but they are mobile mostly (trailers) and I can't remember if they are free or auction. Just make sure you check with someone in the electrical/generater field to find out how big a unit you will need. Happy hunting.
    Matt G.
    Battalion Chief
    IACOJ-Member
    FTM-PTB

  3. #3
    Forum Member
    islandfire03's Avatar
    Join Date
    Oct 2006
    Posts
    2,587

    Talking

    There are many low hour diesel gensets available from the government. some with as little as 25 hours on them. Range from 10 kw on up to 100 kw. Contact NEIOWA by PM for the best info on how to acquire.
    He is the FEEP guru.

  4. #4
    Forum Member
    CGITCH's Avatar
    Join Date
    Dec 2009
    Location
    Sumner IA
    Posts
    496

    Default

    Since my old man is an electrician, we have sold a couple ATS type generators. I think most of them use propane since they are on farms. Maybe one uses natural gas, I can't remember. Pretty much what we reccomend, is find your service amperage, and get one that size. If you are going to take the time to put one in, make it equal to your line service. When installed, they run once every week, automattically switching on and off.

  5. #5
    Forum Member
    mtg55's Avatar
    Join Date
    Feb 2010
    Location
    Pennsylvania
    Posts
    1,313

    Default

    Quote Originally Posted by islandfire03 View Post
    There are many low hour diesel gensets available from the government. some with as little as 25 hours on them. Range from 10 kw on up to 100 kw. Contact NEIOWA by PM for the best info on how to acquire.
    He is the FEEP guru.
    Thanks for clearin that up, I knew Btown was on the right track
    Matt G.
    Battalion Chief
    IACOJ-Member
    FTM-PTB

  6. #6
    MembersZone Subscriber

    Join Date
    Apr 2009
    Location
    SW Missouri
    Posts
    1,154

    Default

    First have an elctrictian come to the station and figure out what size you need. If you have the funds to do so get it oversized, because you never know when you will add on to the station or something new comes along and you'll need more power than you are currently using.

    There are lots of DOD generators out there. I know that we took a pass on three last month. There we all large KW and had very few hours on them. Once again the electrictian will come in handy to tell you what you need to hook up your station to the generator.

    If you are looking at new and have natural gas I would give it a long hard look. I would also look at spending the money to have auto-switching installed.

    Look into how you are going to fuel the generator, if it is to be used for an extended time. (thats the reason we went with NG)

  7. #7
    Forum Member
    nmfire's Avatar
    Join Date
    Nov 2002
    Location
    Maryland (DC Suburb)
    Posts
    5,738

    Default

    LP or CNG is the way to go for sure. Remember, its going to sit for a long time without being used. That is not a good scenario for gas and diesel fuels.
    Even the burger-flippers at McDonald's probably have some McWackers.

  8. #8
    Back In Black
    ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Hate to disagree... but Diesel is the best choice for an emergency generator.

    Believe me, I love the convenience of LPG or CNG, but in a TRUE emergency, there could be supply disruptions.

    Diesel, on the other hand can be carried in barrels if needed or siphoned out of DPW trucks, etc.

    It's a bit more of a pain, but my vote is Diesel.

    We have hundreds of diesel generators around the country and they run every week automatically for an hour with no load and once a month for an hour on a load. You should exercise them at least monthly. The five hundred gallon tanks get filled every 18 months unless they have run for other reasons. No problems with the fuel.
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  9. #9
    Forum Member
    CGITCH's Avatar
    Join Date
    Dec 2009
    Location
    Sumner IA
    Posts
    496

    Default

    Quote Originally Posted by rm1524 View Post
    I would also look at spending the money to have auto-switching installed.
    Anymore, ATS (what you call auto-swithing), or Automatic Transfer Switching, is pretty much a standard option. I would say definitely get the ATS. Much more convenient, and it automatically runs the generator every week, two-weeks, month, etc...

  10. #10
    Forum Member
    islandfire03's Avatar
    Join Date
    Oct 2006
    Posts
    2,587

    Talking

    Quote Originally Posted by mtg55 View Post
    Thanks for clearin that up, I knew Btown was on the right track
    I forget the link but a few months ago i looked at a list that had over a hundred gensets on it. many were at letterkenney army depot in PA. Some had only 5 hours run time on them. FEEP is the federal excess property branch. In most states the contact person is in the forestry dept. Most can be obtained for little cost outside of pickup and shipping cost. Probably something you want to send someone who knows there way around to inspect before toting it home.

  11. #11
    MembersZone Subscriber
    tree68's Avatar
    Join Date
    Aug 2003
    Location
    Jefferson County, NY USA
    Posts
    2,285

    Default

    We opted for a 15KVA gas powered generator on a wheeled frame. We don't have a good spot for a permanently installed generator, and since it's stored inside the station, we know it's relatively warm at all times.

    The appropriate cable stays with the generator and there is a cutover switch and appropriate female plug installed on an outside wall. Once the generator is connected, up, and running smoothly, we simply throw the switch.

    We haven't tested the generator with the siren, but it does a good job for everything else, including the water pump, doors, and lights.

    Our social hall is a separate building, available for use as a shelter. After the 1998 Ice Storm, FEMA offered matching grants for generators and we acquired a 45KVA diesel generator for that purpose. It also is stored in the fire station but can be quickly towed to the social hall, connected, and fired up. It will support the entire load of the building, including a walk-in cooler, all lighting, and the HVAC.
    Opinions my own. Standard disclaimers apply.

    Everyone goes home. Safety begins with you.

  12. #12
    MembersZone Subscriber

    Join Date
    May 2005
    Posts
    1,167

    Default

    I would contact your local FEMA representative. We just received a grant to out fit all of our buildings with GenPaks. The stations are 50kw natural gas and HQ and communications are much bigger, although I am not sure how big.
    ChiefKN make a valid point, but I would recommend natural gas with a 250 gallon LPG back up. Natural gas (not CNG) has the advantage of not needing to be shipped in as long as your local provider's system is online. LPG does not go bad, as gasoline or diesel can. Also with the tri-fuel LPG\natural gas\gasoline units you could also have a aluminum fuel cell to use gasoline, if the LPG or natural gas supply is disrupted.
    When buying a generator make sure you allow for room to grow. In the event you need to supply add on equipment you could burn up a generator by over taxing it. We found that out the hard way during Katrina and Rita.
    Good luck.

  13. #13
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    We have a very large Caterpillar diesel powered generator behind our HQ station. If I recall correctly, there is a 2K diesel tank it runs off of.

    HQ is also the main emergency operations center for the City.

    The other 2 stations have natural gas powered generators.

    All three stations generators are setup to run for an hour every week.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  14. #14
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,678

    Default

    Had an electrician do some modification on our electric panel. Gave us the ability to plug anyone of the 4 truck generators into our building and power the basics when needed. Electrician donated the work. Can't beat a zero cost solution.

    Had that setup for 10 years. Then got an Onan generator from a FireAct grant. Permanent solution. Total cost, with installation, around $50k.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  15. #15
    MembersZone Subscriber

    Join Date
    Jul 1999
    Location
    West Oneonta,NY 13861
    Posts
    137

    Default

    If memory serves me right, there is an NFPA standard out for standby generators. Ours is a 60kw diesel sitting atop a 140 gallon fuel tank. It seems to hit me that it has to have a fuel supply for minimum 24 hour run and be tested weekly and have automatic switching. I'll look to see if i can find standard. stay safe

  16. #16
    Forum Member

    Join Date
    May 2010
    Posts
    7

    Default

    These guys are right on track. First you will need to determine the service amps for your station. For example our station #2 has a 600 amp service and we have a 50 KW generator on the roof (on the coast and prone to hurricanes). It is run on LP gas and will run the entire station with the exception of the emergency heat strips and the elevator. Station #1 which is also the PD and dispatch center has a 1600 amp service, this requires a little larger gen set, the 250 KW is to large to run off LP and runs on diesel. This one is also mounted up on the roof and fuel is pumped up to it from a sealed tank in the ground. Not sure where the cut off is for LP gas powered gen set is but know that the old stations had 25 KW gen sets which where diesel so using a diesel set so that shouldn't be problem. They are also correct with the automatic transfer switch and weekly test. You must also maintain a generator test log for these weekly tests. Hope this helps.

  17. #17
    MembersZone Subscriber
    LVFD301's Avatar
    Join Date
    Jun 2006
    Posts
    3,956

    Default

    Lots of great ideas. I have a number of both propane and diesel gensets scattered across the US, and like both propane and diesel.

    Both can be refueled via alternative means. Diesel is a bit more of a hassle with fuel storage, spills, etc. Propane is easier to store, and in my experience more trouble free.

    However, my BIG gensets, like 260kw, are diesel due to the amount of propane they eat through at that size. I can't imagine you needing one that size.

    I had a jet powered generator - ran off Kerosene. Way bigger than you would need, but nothing beats the sound!

    Sizing? http://www.yamaha-motor.com/outdoor/...or/sizing.aspx
    is a method, but I prefer like mentioned, match your service entry. If you have a 200 amp
    service, make sure you get one that will support a 200 amp draw. Lots less rewiring or
    even thought during use. Just run stuff like normal.

    Your state forester is your source for surplus DOD gensets - they will probably require
    some modifications for the ATS, but certainly a deal!

    Remember, any genset installation is only as good as your maintenance program.

  18. #18
    Forum Member
    FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,401

    Default

    Quote Originally Posted by Btownguy View Post
    First off, what size should we look at? We need to be able to open the garage doors, power the base radios, the E.O.C. and the A.C./heat since we are an emergency cooling/heating center.
    Don't forget, that in larger storm situations, or a very large fire where there may be evacuations, or long-duration outages, you will need to be able to cook food for yourselves as well as anyone sheltering in your station.
    "Loyalty Above all Else. Except Honor."

  19. #19
    MembersZone Subscriber

    Join Date
    Feb 2006
    Location
    Erie, PA/ Home of Lake Effect Snow
    Posts
    314

    Default

    To put things in perspective, we just had a 100k Onan installed in our main station. It ran us about $65k. That included the genset, transfer switch, electrical work, and reblumbing the station for medium pressure natural gas. With something that big you're going to have to upgrade your service lines. We got lucky as the larger lines were at the other end of the property.

    Your best bet to get things started is get a hold of a few of your local commercial electricians and have them come in and let them figure out how much generator you need. When our bids came back, we were able to save $6-7 thousand from one reputable contractor to another. It was quite a difference.

  20. #20
    MembersZone Subscriber
    LVFD301's Avatar
    Join Date
    Jun 2006
    Posts
    3,956

    Default

    Ok, I have the perfect solution for sizing. Don't play around, get this genset.

    Might be a little hard to install at first, but it should give you all the power you need, with just a tad left over.

    http://www.youtube.com/watch?v=unAsUugK9zw

  21. #21
    MembersZone Subscriber

    Join Date
    Apr 2009
    Location
    SW Missouri
    Posts
    1,154

    Default

    Quote Originally Posted by LVFD301 View Post
    Ok, I have the perfect solution for sizing. Don't play around, get this genset.

    Might be a little hard to install at first, but it should give you all the power you need, with just a tad left over.

    http://www.youtube.com/watch?v=unAsUugK9zw
    Go big or go home.

  22. #22
    Forum Member

    Join Date
    Apr 2004
    Location
    Bossier Parrish, Louisiana
    Posts
    10,593

    Default

    Only our Central Station has a backup generator.

    The station portion, which covers the bays, offices, communications and sleeping quarters is 45KW.

    The training building, which would likely be used as CP in a major storm-related disaster, is 30KW.

    Both run off natural gas.

  23. #23
    MembersZone Subscriber

    Join Date
    Dec 2002
    Location
    Rural Iowa
    Posts
    3,106

    Default

    Quote Originally Posted by LVFD301 View Post
    Ok, I have the perfect solution for sizing. Don't play around, get this genset.

    Might be a little hard to install at first, but it should give you all the power you need, with just a tad left over.

    http://www.youtube.com/watch?v=unAsUugK9zw
    On similar note local electric utilities have been scrapping 1930s vintage Fairbanks Morse genset. In working order used only for peak shaving. selling at scrap price. Replacement typically is "highspeed" CAT genset. CAT salesman can show how even when run 5 days or so a year get a positive payback. And nice shiny yellow paint. Totally moronic.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. How many stations does your FD Have?
    By Engine 101 in forum Firefighters Forum
    Replies: 81
    Last Post: 07-05-2008, 07:01 AM
  2. Fla--Polk & Osceola Counties Open Joint Station on County Line
    By captstanm1 in forum Firefighters Forum
    Replies: 1
    Last Post: 05-30-2005, 03:23 PM
  3. 2004 report by IAFC report on the volunteer fire service
    By HeavyRescueTech in forum Firefighters Forum
    Replies: 0
    Last Post: 09-02-2004, 09:55 AM
  4. Pasco County Opens Fire Station 26
    By captstanm1 in forum Florida
    Replies: 0
    Last Post: 06-18-2003, 10:46 AM
  5. World Of Fire Report: 09-11-01 Remembered
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 09-11-2002, 07:23 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register