    Default Pump governors sensing cavitation?

    Just had an apparatus salesman (and asst. fire chief of a fire district) tell me that pressure governors will idle the engine for at least 45 seconds when they sense cavitation, and they cannot be reset during this time to restore pressure. I know the loss of supply will cause this, and cavitation is related, but my prior experiences have been contrary. He was also throwing around the name "pump boss" a lot, but he made it sound like this was all governors.

    HELP!?

  2. #2
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,619

    Default

    Quote Originally Posted by CCCFire09 View Post
    Just had an apparatus salesman (and asst. fire chief of a fire district) tell me that pressure governors will idle the engine for at least 45 seconds when they sense cavitation, and they cannot be reset during this time to restore pressure. I know the loss of supply will cause this, and cavitation is related, but my prior experiences have been contrary. He was also throwing around the name "pump boss" a lot, but he made it sound like this was all governors.

    HELP!?
    Go into Fire Research Corp.'s web site and pull up their Pump Boss Product Manual. There is a page on its operation in "Pressure" mode. It doesn't directly say that the unit will detect cavitation, but it does describe what happens under conditions where cavitation would be expected. Read it through carefully and understand what it is saying. You may come to the conclusion that some of the statements that have been made to you are misquotes.

    We have one on our Toyne/Spartan (we just upgraded to the PBA 400 that you will see there), and it works as they describe.

  3. #3
    Forum Member

    Join Date
    Sep 2009
    Location
    Nova Scotia, Canada
    Posts
    62

    Default

    It sounds to me like it was a mis quote. I'm not familar with teh "pump boss" but I am familar with the calss 1 govenors and if I'm not mistaken a pressure loss of more than 30 psi will cause the pump to return to idel and flash a warning. Or if it can't regain pressure within 5 seconds it will return to idle and flash a warning. But you can override the warning by taking a corrective action.

    I would suspect it essentialy the same thing you need to read the manual on it and understand what to do in that kind of a situation. If you know that what they told you isn't right becuase you've proved it wrong then you probably know more than your sales guy. Even if they are a firefighter they don't neccasarily have to know how to use what they are selling they just have to know how to sell it.

    As for a salesman misquoting information "cough" that never happens "cough cough"

  4. #4
    Forum Member

    Join Date
    Mar 2006
    Location
    Colmar, PA
    Posts
    32

    Default

    We have a FRC governor on our 2009 KME. It senses incoming pressure and displays a "Low Water" message prior to complete loss (i believe it is kicking in about 5 PSI, need to verify with the manual when I get back to the station) the engine goes to idle and you have to start over. This occurs in the pressure setting, in RPM mode it maintains the engine speed. However, we have been able to initiate draft in the pressure mode with no problems.

    This is different from our Fire Commander governors on our 200 and 2001 apparatus. Not sure if newer units perform in the same manner as the current FRC govenrors.

    Our engineers are still getting use to this feature. We had a drill where we kept the incoming pressure low to simulate a large fire and get them use to how the truck responds. first time it happened, most were a bit confused.

  5. #5
    MembersZone Subscriber

    Join Date
    Sep 2005
    Location
    So of Can. / N. of Mexico
    Posts
    869

    Default Pressure Gov.

    Call me old fashion and resistant to change, but I'll take a hand throttle with a manual pump relief valve and a well trained engineer/operator any day before an electronic Gov.

  6. #6
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,619

    Default

    Quote Originally Posted by donethat View Post
    Call me old fashion and resistant to change, but I'll take a hand throttle with a manual pump relief valve and a well trained engineer/operator any day before an electronic Gov.
    I'm older and in some ways more resistant to change. But we're the ones who will be exiting, to be replaced by people who have no concept of stuff that doesn't run on computers. So the best thing we can do is get used to it and learn to deal with it. The incoming generation of firefighters won't understand the stuff you can actually see working, like a throttle linkage. Reality is, though, that computers and electronics are quite reliable now and are getting better as time goes by.

    One of my pet sayings is that each new advance ENABLES us to think and function differently. Each new advance REQUIRES us to think and function differently. I don't think that was ever driven home to me as much as when we went from 2-1/2" and 3" supply line (yes, we did that) to 5".

    Mike, which FRC governor to you have on the KME? Also, next Engineers' meeting is Wednesday evening, Oct. 20, at Oreland.

  7. #7
    Forum Member

    Join Date
    Mar 2006
    Location
    Colmar, PA
    Posts
    32

    Default

    Sam

    The InControl 400. Also for us old guys it has a throttle (although it is clockwise versu counter clockwise - traditional throttle) instead of the push buttons.


    It works nice, we gave E-12 a workout in Bridgeport a couple of weeks ago - 5 hrs at 1500 GPM at draft (for those outside of SE PA the fire was in an old mill complex during 95+ degree weather).

    Will put the Engineer's meeting on the calendar, had a conflict with a Township Public Safety committee for the last meeting

    Mike

  8. #8
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,619

    Default

    Quote Originally Posted by Squirt1262 View Post
    Sam

    The InControl 400. Also for us old guys it has a throttle (although it is clockwise versu counter clockwise - traditional throttle) instead of the push buttons.


    It works nice, we gave E-12 a workout in Bridgeport a couple of weeks ago - 5 hrs at 1500 GPM at draft (for those outside of SE PA the fire was in an old mill complex during 95+ degree weather).

    Will put the Engineer's meeting on the calendar, had a conflict with a Township Public Safety committee for the last meeting

    Mike
    You would have the newer version of the InControl, then. We might have gone with that but a J-1939 version wasn't available then. At the time, FRC said they weren't going to develop one, either, so we went with the Pump Boss. It works well and we're happy with it, especially after we upgraded to the PBA 400. It will be interesting to compare the two after a few years. Thanks.

  9. #9
    Forum Member
    FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,401

    Default

    Quote Originally Posted by donethat View Post
    Call me old fashion and resistant to change, but I'll take a hand throttle with a manual pump relief valve and a well trained engineer/operator any day before an electronic Gov.
    You are old fashioned and resistant to change.
    "Loyalty Above all Else. Except Honor."

  10. #10
    Forum Member

    Join Date
    Mar 2006
    Location
    Colmar, PA
    Posts
    32

    Default

    Sam

    We looked at both as well as Class I. The biggerst difference between the Pump boss and InControl appears to be having the digital master gauges. This allows you to drop the main gauges from the panel. We kept them on ours, Upper Black Eddy has only the govenor displays on their tanker (2008? 2009 KME Tanker) The layout also fit better into the pump panel design

    Having both on the panel confuses the new engineers since they are not identical readings. we tell them to focus on one set or the other instead of both. The compund reading appears to be low on the intake presure, however it is great when drafting knowing where you stand on the vacuuum side. On the Pressure guage, the reading is within 5 PSI through the range of the normal pressures we use

    Has anyone tried to resolve the discrpancy between the two readouts?

  11. #11
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,619

    Default

    Quote Originally Posted by Squirt1262 View Post
    Sam

    We looked at both as well as Class I. The biggerst difference between the Pump boss and InControl appears to be having the digital master gauges. This allows you to drop the main gauges from the panel. We kept them on ours, Upper Black Eddy has only the govenor displays on their tanker (2008? 2009 KME Tanker) The layout also fit better into the pump panel design

    Having both on the panel confuses the new engineers since they are not identical readings. we tell them to focus on one set or the other instead of both. The compund reading appears to be low on the intake presure, however it is great when drafting knowing where you stand on the vacuuum side. On the Pressure guage, the reading is within 5 PSI through the range of the normal pressures we use

    Has anyone tried to resolve the discrpancy between the two readouts?
    Good point, Mike. I don't know if anyone has. Good question for the folks on Lorraine Av. You may remember that they started or participated in quite a brouhaha with the people in Wisconsin over a different point that affected the accuracy of gauges.

    Bring the question to Engineers' meeting. Panel gauges aren't known for super accuracy. I think NFPA allows +/- 5%. So on any pump panel you may see (and we do) varying readings. Example: Master gauge reads 100. Leave a discharge capped and open its valve. It may read anywhere from 95 to 105. And if the gauges were never zeroed from the start, the reading discrepancy may be even greater. And I'm sure they can vary throughout their lifetimes.

    It's one of the reasons that you hook up lab gauges to do pump tests.

  12. #12
    Forum Member

    Join Date
    Sep 2009
    Posts
    469

    Default

    Quote Originally Posted by donethat View Post
    Call me old fashion and resistant to change, but I'll take a hand throttle with a manual pump relief valve and a well trained engineer/operator any day before an electronic Gov.
    Agree there! Had a gov system fail with two men in a garage fire that as they arrived near the seat and needed to flow water. Just luckily (this isnt a norm) I had a second engine near the intersection and we pulled a line off it.
    Am I being effective in my efforts or am I merely showing up in my fireman costume to watch a house burn down? (Joe Brown, www.justlookingbusy.wordpress.com)

  13. #13
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,619

    Default

    Quote Originally Posted by Capt387 View Post
    Agree there! Had a gov system fail with two men in a garage fire that as they arrived near the seat and needed to flow water. Just luckily (this isnt a norm) I had a second engine near the intersection and we pulled a line off it.
    No matter what kind of throttle control you have now, it's electronic, and it feeds into a computer. Look behind the pump panel, there's no cable, just wires feeding the engine's computer. Whether you try to keep up with water flow demands by turning it manually, or whether you let the sensor make the changes instantly for you, the same thing is happening. The EPA took cables and linkages away from us during the early '90s.

  14. #14
    Forum Member

    Join Date
    Mar 2006
    Location
    Colmar, PA
    Posts
    32

    Default Correction

    My earlier post regarding the pump cavitation noted that the governor will go to idle at about 5 PSI on the Incoming pressure.

    After re-reading the operations manual for the FRC InControl 400 the actions by the governor are based on the discharge pressure not the incoming pressure. The governor will sense a sudden drop in discharge pressure (within preprogramed parameters) or a drop below 15PSI DP and respond with an increase in RPM. If the pressure does not increase within a specific time frame the governor will change to RPM limit mode or to idle depending on the condition. The governor is programed for "Running away from Water", Low Water Cycle, and No Supply Water".

    The key is that the unit is monitoring discharge pressure not incoming pressure for all of these functions even though it may look diferently when you are at the pump panel.

    Sorry if I confused anyone with my earlier post. Goes to show that the manuals have a purpose other than collecting dust on the bookshelf. The good news is that I now have some material for the next Engineers Class at the station. The scenarios should be easy to simulate. It also explains why the governor will not sense low water while at draft.

    Is this the same process used by Class 1?

    Mike

  15. #15
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    91

    Default

    Quote Originally Posted by Squirt1262 View Post
    My earlier post regarding the pump cavitation noted that the governor will go to idle at about 5 PSI on the Incoming pressure.

    After re-reading the operations manual for the FRC InControl 400 the actions by the governor are based on the discharge pressure not the incoming pressure. The governor will sense a sudden drop in discharge pressure (within preprogramed parameters) or a drop below 15PSI DP and respond with an increase in RPM. If the pressure does not increase within a specific time frame the governor will change to RPM limit mode or to idle depending on the condition. The governor is programed for "Running away from Water", Low Water Cycle, and No Supply Water".

    The key is that the unit is monitoring discharge pressure not incoming pressure for all of these functions even though it may look diferently when you are at the pump panel.

    Sorry if I confused anyone with my earlier post. Goes to show that the manuals have a purpose other than collecting dust on the bookshelf. The good news is that I now have some material for the next Engineers Class at the station. The scenarios should be easy to simulate. It also explains why the governor will not sense low water while at draft.

    Is this the same process used by Class 1?

    Mike
    This is a safety system that should be present in any new electronic pressure governor. The idea is that you don't want the pump catching prime again with the engine at max speed, otherwise the crew on a handline is going to be in for a wild and dangerous ride. As someone who has taken that ride on a pumper with an older electronic governor, I like the cavitation protection built into the new ones.
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

  16. #16
    Forum Member

    Join Date
    Sep 2007
    Posts
    308

    Default

    But really, shutting down for 45 seconds and not being able to resume pressure, seemed really fishy, especially since i have always been able to reset right off of the bat. (based on Pro-s)

  17. #17
    Forum Member

    Join Date
    Mar 2006
    Location
    Colmar, PA
    Posts
    32

    Default

    I agree waiting is not an option. The reset time is only for the Presure mode and is a built in safety so the engine does not cycle up and down while water supply is intermittent or not fully established. However, when it drops to idle the RPM mode is still available; so the operator can increase RPM to reestablish flow. When things stabilize, you can switch back to Pressure without any change in the DP - know this works on FRC and older (2000-2001) Fire commanders.

    In the RPM mode the operator needs to be very observent of the guages, especially when operating at low incoming pressure. The benefit is a more stable flow for the guys at the nozzle.

    Our operators are instructed to go to RPM in this situation if the governor does not automatically chang to this mode, re establish the appropriate DP if possible (based on water supply) and manage the process manually (throttle control) untill a stable water supply is established. We practiced this a few weeks ago flowing multiple lines and it gave the operators a real workout but waterflow was maintained.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. World Of Fire Report: 07-24-05
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 07-27-2005, 09:34 AM
  2. World Of Fire Report: 07-17-05
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 07-18-2005, 11:30 PM
  3. World Of Fire Report: 05-31-05
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 06-01-2005, 07:26 AM
  4. Pumper run away
    By *LHS in forum Apparatus Innovation
    Replies: 12
    Last Post: 07-17-2001, 03:10 PM
  5. RFP's
    By D Littrell in forum Apparatus Innovation
    Replies: 1
    Last Post: 09-08-2000, 06:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register