    Hello, I am a brand new registrant to the FireHouse forum. Was a fire officer in Colorado, but moved onto my sailboat in 2004 and sailed away. I am now on the Western Pacific Micronesian island of Pohnpei. Newly hired as "Emergency Services Unit Administrator" for the next two years to improve EMS/Fire/Rescue/HazMat/MCI.
    My question is regarding use of seawater in firepumps. I have no experience with this issue coming from Colorado. Can I get some input from those of you with experience pumping seawater and the care/maintenance concerns for the apparatus/pumps?

  2. #2
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,623

    Default

    Quote Originally Posted by RickH View Post
    Hello, I am a brand new registrant to the FireHouse forum. Was a fire officer in Colorado, but moved onto my sailboat in 2004 and sailed away. I am now on the Western Pacific Micronesian island of Pohnpei. Newly hired as "Emergency Services Unit Administrator" for the next two years to improve EMS/Fire/Rescue/HazMat/MCI.
    My question is regarding use of seawater in firepumps. I have no experience with this issue coming from Colorado. Can I get some input from those of you with experience pumping seawater and the care/maintenance concerns for the apparatus/pumps?
    Navy (and Coast Guard) ships use seawater for firefighting and many other uses. The pumps that I remember from my Navy days ('59 - '63) were all bronze. Most of them never saw fresh water. Some other pumps, such as portables, also pumped sea water but were flushed with fresh water after each use, when possible.

    I remember being in Hahn's factory in Hamburg, Pa. when our '68 Hahn was being built. There was another engine being built at the same time, for West Palm Beach, Fla. It had an all bronze pump. I was told that they spec'd bronze because they frequently pumped salt water. I presume that they also flushed the pump after using salt water. I don't know if they still spec bronze pumps or not. I'm sure that there are others that do, too.

  3. #3
    Forum Member
    FIREMECH1's Avatar
    Join Date
    Apr 2008
    Location
    HUSKER LAND
    Posts
    2,425

    Default

    Actually the make up and build materials for "true" salt water pumps have a chemical composition of nickel, aluminum, and bronze. As far as I remember, this was the best to defeat the corrosion of salt water.

    Not knowing what RickH has for pumps, I would assume they are still cast iron, unless built with the "bronze" material.

    Either way, if you pump seawater, take the time after operations to flow some fresh water through the whole system and all the discharges. This should lengthen the life of the whole system from problems and corrosion.

    FM1
    I'm the one Fire and Rescue calls, when they need to be Rescued.

    Quote Originally Posted by EastKyFF
    "Firemens gets antsies. Theys wants to goes to fires. Sometimeses they haves to waits."

  4. #4
    Forum Member

    Join Date
    Mar 2010
    Location
    Australia
    Posts
    31

    Default

    We were told you can use seawater, but to make sure everything is flushed after with fresh water. We were also told about a pump that was used for salt water, that wasn't flushed. They ended up blowing a 20cent size hole in the side of the pump 2-3 months down the track.

  5. #5
    Forum Member
    nmfire's Avatar
    Join Date
    Nov 2002
    Location
    Maryland (DC Suburb)
    Posts
    5,738

    Default

    Up in my old neck of the woods last week, there was a large residential structure fire at huge McMansion on the water. The city water system in this small town was overtaxed in about five minutes so they have two or three trucks drafting out of the ocean. I'm sure the engineers cringed, but as long as you flushed it out and follow the manufacturers recomendations, I'm sure it will be fine.
    Even the burger-flippers at McDonald's probably have some McWackers.

  6. #6
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,896

    Default

    http://www.firehouse.com/topics/stra...n-water-system


    Wonder what the fire boat pumps are made of????

  7. #7
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,896

    Default

    Call pump maker for recommend practices

  8. #8
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    Well, we've been using sea water for about 75 years. After operations, we flush with "fresh" water. Haven't had a pump issue yet.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  9. #9
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,623

    Default

    Quote Originally Posted by Bones42 View Post
    Well, we've been using sea water for about 75 years. After operations, we flush with "fresh" water. Haven't had a pump issue yet.
    If anyone would know, you'd be it.

  10. #10
    Forum Member

    Join Date
    Aug 2010
    Posts
    2

    Default thanks for input

    Thank you for the feedback, it sounds like doing a freshwater flush is the main thing, luckily it rains tons here. I'll do a specific check with the pump manufacturer to double check, but it sounds like there is not issues with seals, etc. as long as the flush is done religiously.

  11. #11
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    98

    Default

    If you are going to be pumping seawater on a regular basis you will want to use a bronze pump with a monel shaft. Most bronze pumps also use seals with different materials designed to withstand harsher water conditions. This is the type of pump that is used in saltwater fire boats. Most major pump manufacturers offer some, if not most, of their pumps in bronze. Waterous offers many bronze models including CM and CS midships.

    An iron pump will tolerate occasional seawater usage as long as it is thoroughly flushed with clean water afterward. Keep in mind that in order to flush it properly you must also flush the tank and ALL intake and discharge piping if you want to keep things from corroding away.
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

  12. #12
    Forum Member
    islandfire03's Avatar
    Join Date
    Oct 2006
    Posts
    2,593

    Talking

    Just saw this thread:
    Being on Islands surrounded by the briny deep we used to have an engine with bronze pump and manifolds with bronze valves. It has been retired now.

    Most of the problems with pumping seawater is going to occur in the newer delrin or other synthetic "Ball" valves in use today. They and the combo nozzles really catch heck from all the smaller grit and contaminates found floating in the ocean. Flushing the plumbing thoroughly will keep the damage down but not eliminate it completely. Make sure to check the anodes and keep a set of spares as seawater will speed the consumption of them.

  13. #13
    MembersZone Subscriber
    npfd801's Avatar
    Join Date
    Aug 2002
    Location
    Somewhere in Illinois
    Posts
    2,220

    Default

    Doesn't Hale make a stainless pump? Not saying that's the answer, but it is out there...
    "Share your knowledge - it's a way to achieve immortality." - Stolen from Chase Sargent's Buddy to Boss program

  14. #14
    Forum Member
    Fire304's Avatar
    Join Date
    Jun 2002
    Location
    At the Helm
    Posts
    1,174

    Default

    Quote Originally Posted by fire49 View Post
    Wonder what the fire boat pumps are made of????
    Actually most "modern" ones are just cast iron, but they are protected by sacrificial anodes (zincs). Back in the day they they were special bronze construction, but that's just too expensive for most people these days.

    One other food for thought, all them dissolved solids in salt water can prevent your foam from sudsing up, make sure if you use foam it is salt water compatible.
    ______________________________ __________________
    If you are new to posting please CLICK HERE for an essential lesson
    ______________________________ __________________
    A bad day in the boat is better than a good day in the office. And in my case the office is a boat!

    IACOJ Fire Boat 1

  15. #15
    Forum Member

    Join Date
    May 2001
    Location
    Greensboro, NC USA
    Posts
    1,312

    Default

    Quote Originally Posted by npfd801 View Post
    Doesn't Hale make a stainless pump? Not saying that's the answer, but it is out there.
    Actually, they'll make any cast iron pump they offer in bronze, but you have to order at least two if I recall correctly.

    EDIT TO ADD: Hale Product Application Guide, page 29.
    Pumps available as single unit order in bronze:
    QSMG
    QG
    CBP
    AP (APS)
    PSD
    RSD
    DSD
    CSD
    8FG
    RMB
    RMC
    RME
    All multiple order pump models are available in bronze as a special order
    For the record, I've never operated a pump with salt water, but I have operated a few boats in it.

    Salt water is nasty stuff. It will corrode almost anything and everything; it's just a matter of time. But, getting salt water on things usually doesn't hurt them. It's leaving salt water on or in them that ruins them.

    If you adopt a meticulous practice of completely flushing the entire pumping system after using salt water, I doubt you will have any problems.

    Also, the US Navy has used cathodic protection on their ships for decades. While this technique isn't effective on automobiles (they're not grounded, because of rubber tires), you could employ such a system while you're pumping the sea water. Hale already offers sacrificial anodes. By applying the proper electrical charge to them, they become even more effective.
    Last edited by txgp17; 02-07-2011 at 07:15 PM.
    The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. HOUSTON walked away from this contract
    By Firewalker1 in forum Firefighters Forum
    Replies: 71
    Last Post: 05-17-2007, 12:34 AM
  2. SAPPHIRE fire suppression system
    By WaffleHut in forum Firefighters Forum
    Replies: 4
    Last Post: 11-21-2006, 04:14 PM
  3. Request for Firefighters for Fire Suppression (NOT THE FEMA REQUEST!)
    By rjtoc2 in forum Hurricane Katrina & Rita Forums
    Replies: 6
    Last Post: 09-06-2005, 09:21 AM
  4. AFFF or FFFP
    By Lallo in forum Firefighters Forum
    Replies: 6
    Last Post: 03-18-2002, 08:34 PM
  5. Investigative information for Suppression Crews
    By smokehiker in forum Fire Investigation
    Replies: 1
    Last Post: 09-04-2000, 12:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register