Ok, it sounds bizarre, but I want to know if I jack an additional section or two of hard suction 6" off of our first due engine, can I reach out 25' to 35' to a run off pond and draft horizontally to the supply engine?
The pond has a short levy that sits maybe 8' above the paved surface the truck will park on and it is about 25' to the edge of the water. The depth of the pond is about 10' (give or take a bit). This is at a somewhat water starved production plant. The hold pond is rather large so it seems it could be a viable source.
We do draft from the midmount pump to the nose of the engine (port-a-pond) with 20' of suction off the steamer regularly. So, how far horizontally can we go?
+ Reply to Thread
Results 1 to 20 of 27
-
08-09-2010, 07:17 PM #1
How far horizontally can you draft from a source?
A coward stands by and watches wrongs committed without saying a word...Any opinions expressed are purely my own and not necessarily reflective of the views of my former departments
-
08-09-2010, 07:23 PM #2
If you're only lifting 10' or so you should have no problem adding on multiple hard suction sections. 35' should be a cake walk as long as all your connections are good, although your priming may be longer due to the amount of air that will need to be evacuated.
"We accept great personal risk to save another person's life; We accept moderate personal risk to save another persons property; We accept no personal risk to save what is already lost"
Visit us on the web @ www.saltspringfire.com
-
08-09-2010, 11:17 PM #3Forum Member
- Join Date
- Jul 2007
- Location
- Windsor, MA
- Posts
- 238
Like Saltspringfire said, when drafting you are only really concerned with the vertical distance from source to pump. Adding horizontal distance theoretically won't change anything.
Realistically, extra horizontal distance will get you more friction loss, extra couplings could leak air and make obtaining and maintaining a prime difficult, and longer suction hose means the primer will have to run for a longer period of time to get water up to the pump.
-
08-09-2010, 11:29 PM #4Forum Member
- Join Date
- Nov 2007
- Location
- Orygun
- Posts
- 167
I don't any pics, but we've drafted through six or seven 10' lengths of 6" hard suction. It was for training, not on a fire call. It did take a little while to prime though.
-
08-10-2010, 12:32 AM #5Forum Member
- Join Date
- May 2001
- Location
- Greensboro, NC USA
- Posts
- 1,265
Last Friday night, I pulled a draft through dual 6" suctions, each 60' long, up a 17½' lift, and still flowed 1,500 GPM. So I say go for it.
It took about 45 seconds to prime the first line, after we back flushed it. The second was primed using the centrifugal pump, not the primer pump.
If you're worried about length, just back fill from you tank, that will help flush out a horizontal line real quick.Last edited by txgp17; 08-10-2010 at 12:35 AM.
The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America
-
08-10-2010, 10:52 AM #6MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Rural Iowa
- Posts
- 3,107
Or get a turbodraft or two. Quicker and easier to set up.
-
08-10-2010, 12:59 PM #7Forum Member
- Join Date
- May 2001
- Location
- Greensboro, NC USA
- Posts
- 1,265
Excellent point.
But, the TurboDraft works best with 5" hose. I don't know what size LDH his dept may have, but with 4" the TurboDraft wouldn't give more than 400 GPM.
A long stretch of 6" hard suction at a moderate lift will likely flow twice what the TurboDraft could hope to achieve.
When using dual TurboDraft's, then things start to look better. The bad thing about a TurboDraft is that once you exceed it's flow capability, your pump cavitates and everything shuts down, and you have to start over.
I'd much prefer 6" hard suction.Last edited by txgp17; 08-10-2010 at 03:17 PM.
The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America
-
08-10-2010, 01:10 PM #8
Theoretically, the only limitation to long horizontal suction is friction loss and airtight couplings.
"Nemo Plus Voluptatis Quam Nos Habant"
The Code is more what you'd call "guidelines" than actual rules.
-
08-10-2010, 03:38 PM #9
Thank you for the information. It pretty much confirmed what I thought I knew.
60'...?....Hmmm...we have another spot where the pond is about 40' from the trucks....
As for the prime and back flush...uh, I'm a lazy pump op and I usually back flush to clear most of the air before I prime anyway. (oops, did I admit that?)
We have jet siphons on the low levels but I will probably try and use a floater because I am not exactly sure what they lined that pond with and I care not to suck a super nasty item into the pump and make the truck go "clunk".A coward stands by and watches wrongs committed without saying a word...Any opinions expressed are purely my own and not necessarily reflective of the views of my former departments
-
08-10-2010, 03:53 PM #10
-
08-10-2010, 04:59 PM #11MembersZone Subscriber
- Join Date
- Feb 2000
- Location
- Willington F.D., CT
- Posts
- 139
Try installing a dry hydrant.
Lower friction loss (with properly sized piping)
Only one piece of hard suction is needed - Hopefully this means it is quicker to set up and more reliable because of fewer connections.
Easier to prime (most of the pipe is already full of water).
We have one with 180'+ horizontal run on a 10' lift - works just fine.
-
08-10-2010, 10:01 PM #12MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Rural Iowa
- Posts
- 3,107
I've only used 4" once (50') from foldatank to ditch. My WA estimate is 6-700gpm. I find TD literature to be pretty conservative.
Best use in my opinion of TD is to fill a foldatank and draft from the foldatank. Largely will eliminates the pump out running the supply. 5"S line holders are over priced though.
-
08-10-2010, 10:52 PM #13MembersZone Subscriber
- Join Date
- Jan 2007
- Location
- Pa Wilds
- Posts
- 526
NEIOWA: Expect to reduce your flow by about 100 gpm for every 10' joint of hard sleeve you add beyond 20 feet. For a 1500 gpm pump with 60' of hard sleeve you should get about 1100 gpm at a 10' lift. Be very careful as you throttle up. It will be easy to cavitate at high flow rates. Like others on here have said, "expect to have some long priming times." For pumps larger than 1500 GPM you need suction from two intakes to meet the pump spec. so with only one 6" sleeve, expect to see no difference between a 1500, 1750, or 2,000 gpm engines.
-
08-11-2010, 03:24 PM #14
A coward stands by and watches wrongs committed without saying a word...Any opinions expressed are purely my own and not necessarily reflective of the views of my former departments
-
08-11-2010, 08:33 PM #15MembersZone Subscriber
- Join Date
- Oct 2005
- Location
- Golden City 1 hour south of fort smith
- Posts
- 496
Wow glad I read this I was always told drafting more the 20 ft from any water source was about the limit didn't matter if it is was horizontal or virtical. So I guess I can start moving my dump tank alittle further way from the pumper ( assuming theres room) to give us more room to work around the pumper and get tools? Most firefighter around here insist the dump tank be right next to the pump panel or that won't use it and that use the nurse tanker set up which for me is 100 times harder and not as effective.
-
08-12-2010, 03:10 AM #16
I'm sure I'll be corrected, but if you're drafting off the dump tank, you DO want it as close as possible using the shortest length of hard line to draft with.
Originally Posted by volfireman034
Drafting horizontally and vertically are 2 different operations with 2 different results. Same with length of the hard line you are trying to draft with.
You lost me on the last comment. Hooked on phonics???
FM1I'm the one Fire and Rescue calls, when they need to be Rescued.
Originally Posted by EastKyFF
-
08-12-2010, 10:50 AM #17MembersZone Subscriber
- Join Date
- Apr 2009
- Location
- SW Missouri
- Posts
- 1,083
FM
We use 10, 20, or 30 feet with a porta tank. It just depends on tank placement and the surrounding. Of course less is better because of set up times and less chance of air leaks.
-
08-12-2010, 04:28 PM #18MembersZone Subscriber
- Join Date
- Oct 2005
- Location
- Golden City 1 hour south of fort smith
- Posts
- 496
There are times when setting up the dump tank several feet behind the pumper would work much better for a tanker (tender) to drop their load, but most departments around here insist on dump tank 3 feet in front of pump panel or nothing. When I use the term nurse tanker, for us, that means a tanker pulls up near the pumper and we pull ( or push if tanker has a pump) the water directly from the tanker to the pumpers intake. Problem is when the tanker is empty you have to disconnect everything move that tanker out of the way then move the next tanker in place and rehook. All of which takes way to much time.
-
08-12-2010, 09:06 PM #19Forum Member
- Join Date
- Aug 2007
- Location
- West Burlington, IA
- Posts
- 106
The problem with setting a dump tank up behind the primary pumper is not many pumpers are equipped with an intake on the rear of the vehicle. That is why it works best to put it either directly on the side, the best route, or out front off a front suction intake on the bumper. Not to mention the amount of hard suction you'd require to bend off the side intake, or front even, to get the suction hose back to a drop tank set up behind a standard pumper.
Placing the tank in front of the engine works well in that the pump operator can easily check on the status of available water, plus if shorthanded, its allows him to direct the tanker/tender driver into place without having to walk all around the engine.
More often than not, the drivers get short-sighted and pull right up into the driveway instead of backing in. If they took the extra 30-45 seconds to back in, putting a drop tank up front would be the best solution. Instead, they get tunnel vision and go in nose-first. Then you get stuck performing nursing operations, which as pointed out, are slow and more labor intensive.
-
08-17-2010, 04:03 PM #20
We've been training on that very tactic.
The hypothesis at this point is to place the pond at the end of a drive (country setting) across the first lane of traffic. The idea is that a tanker(tender) can drive to the side of the pond and side dump or pull past and then back in and rear dump.A coward stands by and watches wrongs committed without saying a word...Any opinions expressed are purely my own and not necessarily reflective of the views of my former departments
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Pulling a draft
By FFTrainer in forum Fireground TacticsReplies: 41Last Post: 04-29-2008, 08:26 PM -
Single Source And Warranty Work
By DRAFTMASTER30 in forum Firefighters ForumReplies: 19Last Post: 04-19-2007, 08:30 AM -
Aid and Comfort to the Enemy
By GeorgeWendtCFI in forum The Off Duty ForumsReplies: 490Last Post: 05-06-2006, 02:19 PM -
legal question on CO call
By SMCAPT7 in forum Firefighters ForumReplies: 11Last Post: 03-18-2005, 08:26 PM -
Armed Services Draft
By mustang911 in forum The Off Duty ForumsReplies: 61Last Post: 09-25-2004, 10:44 AM

LinkBack URL
About LinkBacks