I was searching for information on hydrants with two 4½" outlets and found this post from and 8 year old thread. Anyone got any details?
Do you think a dual steamer hydrant, provided it was on an adequate main and had a substantial barrel, would provide more H2O than a traditional 4½x2½x2½?
firehydrant.org's website seems to have crashed today, so I can't look there. The google cache at least lets me read the data. They mention 3,000 GPM.
+ Reply to Thread
Results 1 to 20 of 24
-
08-18-2010, 08:28 PM #1Forum Member
- Join Date
- May 2001
- Location
- Greensboro, NC USA
- Posts
- 1,265
Hydrants with dual steamer outlets. Anyone have any experience or details?
The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America
-
08-18-2010, 08:56 PM #2
In theory? Sure it could. In practice? I'm not sure you're going to find too many situations where such a monster main and hydrant barrel exist nor many good reasons to tap two steamers from one hydrant instead of one steamer each from two seperate hydrants. (Any such theoretical water system with such monster mains and hydrant barrels would surely have close spaced hydrants, right?)
"Nemo Plus Voluptatis Quam Nos Habant"
The Code is more what you'd call "guidelines" than actual rules.
-
08-18-2010, 09:42 PM #3Savage / Hyneman 08'
- Join Date
- Oct 2006
- Location
- Earth
- Posts
- 446
I've seen a few municipalities around here go with double steamers. Yes higher flows are one reason.
One other reason is because we don't need the 2 1/2 ports on a hydrant for anything anymore. Since the cost of a double steamer is about the same price ( I was told within $10, no storz fittings just 4 1/2 theads ) why not get a hydrant with what you use on it?
It works for them. It might not for you.We do not rise to the occasion. We fall back to our level of training.
-
08-18-2010, 11:01 PM #4
I would be happy to see all of our hydrants with one steamer outlet. Let alone two. Makes it extremely difficult to use LDH without a steamer on all our hydrants. With the dual steamers, can you theoretically hook two engines to one hydrant?
-
08-18-2010, 11:13 PM #5Forum Member
- Join Date
- Feb 2009
- Location
- virginia
- Posts
- 490
wouldnt you get close to the same flow by using the 2 2.5 oulets in addition to the steamer connection? As far as hooking two engines to one hydrant just run one to the steamer and the other to the 2 2.5 outlets. I would think the flows would be close to the same as running with two steamer outlets. This is just a wild ***** educated guess, i would have to run the numbers to be sure.
If all else fails just dual pump the hydrant! That is always fun.
-
08-19-2010, 11:18 AM #6
Assuming you have the mains to supply it, a dual steamer hydrant will definitely deliver more water than using one steamer and a 2.5" outlet. You are reducing a major choke point for water flow. Keep in mind that you need more than three 2.5" openings to equal the area of a 4.5" opening. The area of a 2.5" circle is 4.909 square inches vs 15.904 square inches for a 4.5" one.
If you are going to use a 2.5" outlet on a hydrant for an additional intake, use a 2.5" to LDH adapter and run LDH from the outlet to the pump. You will get vastly increased flow over running a 2.5" or 3" line. We found in some cases we could get nearly 1000 GPM through a 2.5" hydrant outlet through 4" LDH. To be fair, my city has an excellent water supply system though.Just a guy...
Lieutenant - Woodbury, MN FD (Retired)
Road Captain - Red Knights MC, MN4
Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.
-
08-19-2010, 11:26 AM #7
-
08-19-2010, 11:28 AM #8
-
08-19-2010, 11:50 AM #9
Nah, you can get more than that. the 2.5" opening on a hydrant is somewhat like a 2.5" smooth bore nozzle. If you have 60 psi flowing from the outlet you'd be getting 1168 GPM. I should have clarified that I meant we got nearly 1000 GPM in addition to what we were getting from the 4" connected to the steamer outlet on the hydrant. We were actually getting somewhere in the neighborhood of 2600 GPM from that hydrant with the two lines connected.
I remember that, at some point, we tested it running a third 4" from the second 2.5" outlet as well, but I don't recall what we got out of it at that point. We did all of this testing as part of some engineering drills like 12 years ago.Just a guy...
Lieutenant - Woodbury, MN FD (Retired)
Road Captain - Red Knights MC, MN4
Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.
-
08-19-2010, 12:02 PM #10
I know you can, it was just a figure that stuck in my head for one typical setup. I recall it from the early days of LDH and some experiments to see what the best way to get water into LDH from a hydrant with no steamer.
(single reducing adaptor, 2 bootlegged 2 1/2"s, etc.) It worked out that a single reducing adaptor provided the best flow.
My hunch is that you'd lose ground with 3 lines due to the increased turbulence in the hydrant barrel -- that was one of the factors that made a single reduce better than a bootleg.I remember that, at some point, we tested it running a third 4" from the second 2.5" outlet as well, but I don't recall what we got out of it at that point. We did all of this testing as part of some engineering drills like 12 years ago."Nemo Plus Voluptatis Quam Nos Habant"
The Code is more what you'd call "guidelines" than actual rules.
-
08-19-2010, 12:31 PM #11
We definitely didn't lose ground, but I seem to remember the third line wasn't as effective as the second one was, which makes logical sense. I just checked with our hydrant guys in the office and they said the standpipe we use on the traffic hydrants we make is 7.5" ID. IIRC the valve opening at the main is like 5.25".
Just a guy...
Lieutenant - Woodbury, MN FD (Retired)
Road Captain - Red Knights MC, MN4
Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.
-
08-19-2010, 01:14 PM #12MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Rural Iowa
- Posts
- 3,107
As I recall there was a thread on here a couple of years ago where someone did flowtest (thru a pumper) with steamer, then one 2-1/2" and plus 2x 2-1/2". Who is the flowtest variables guy?
-
08-19-2010, 01:19 PM #13MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Rural Iowa
- Posts
- 3,107
That's reason for jumbo siamese. 2x 2-1/2" to 5"S and you have decent hydrant pressure you may not even need a pumper at the hydrant.
I'll loan you one if you want to try it out. We have a 3x 2-1/2" valved x 5"S siamese we use for relay pump from our fire pond (no large diameter discharge plumbing on the rural pumpers in the area).
-
08-19-2010, 03:34 PM #14Forum Member
- Join Date
- May 2001
- Location
- Greensboro, NC USA
- Posts
- 1,265
I've gotten 1,500 GPM from a 2½" outlet alone using a 2½x4" adapter and 50' of 4" hose. The flow was measured using a 2½" pitot set used for service testing. Maximizing Hydrant Connections - Water Flow Test Results
The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America
-
08-19-2010, 04:12 PM #15MembersZone Subscriber
- Join Date
- Sep 2006
- Location
- Northeast Coast
- Posts
- 3,527
You may need 2.5" ports
Our water company asked us about the dual steamers and we stuck with the old standby's. The reason is that we've always required our personnel to dress hydrants with a 2.5" gate as well as the steamer. This allows us to clamp off the LDH line when the hydrant stem breaks (yes they do and not as rare as you'd think). Without the ability to open a valve and redirect the water, your pump is stuck on the hydrant until the shutoff is found and close. Not to mention the obvious ability to add the second line via a 2.5"x5" Storz.The first reason we've used more often than the latter. You could buy a 5" valve
$$$$$!
-
08-19-2010, 04:39 PM #16
-
08-21-2010, 05:15 PM #17Savage / Hyneman 08'
- Join Date
- Oct 2006
- Location
- Earth
- Posts
- 446
That is exactly the way most around here dress a hydrant. Those with double steamers get a 5" valve instead of the 2.5" valve.
5" has become the standard in this area for anything other than attack lines. Hydrant to engine, relay pumping, tanker filling, all get 5". The trend also includes doing away with the fittings for the smaller supply hose as well. Double steamer hydrants, LDH discharges for relay pumping, no more siamese into 5".
Some area depts are still adapting from 4", but 3" for supply went away a while ago. Now we only use 3" to supply the blitz monitors.We do not rise to the occasion. We fall back to our level of training.
-
08-24-2010, 05:03 PM #18
Photo of an hydrant with the first line off and a gate on the other outlet, and its being supplied.
If all you need is a 2-1/2"; 3" or 3-1/2" line, put a reducer on the hydrant nipple.Last edited by CaptOldTimer; 07-08-2011 at 01:53 PM.
Stay Safe and Well Out There....
Always remembering 9-11-2001 and 343+ Brothers
-
08-24-2010, 05:22 PM #19Just a guy...
Lieutenant - Woodbury, MN FD (Retired)
Road Captain - Red Knights MC, MN4
Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.
-
08-24-2010, 10:32 PM #20
Originally Posted by madden01
"and everyone is encouraged to use Plain, Spelled Out English. I thought this was covered in NIMS training."
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Lealman--Major 2003 Fire leads to new hydrants
By captstanm1 in forum FloridaReplies: 0Last Post: 05-01-2005, 05:10 PM -
Specifying the Location of rural hydrants
By neiowa in forum Firefighters ForumReplies: 5Last Post: 04-23-2005, 04:01 AM -
Orange City Replacing Defective and Broken Hydrants
By captstanm1 in forum FloridaReplies: 0Last Post: 09-28-2003, 10:10 AM -
Breaking News--St Petersburg Fla--5-Alarm Apt. Fire, Residents & Firefighters Injured
By captstanm1 in forum Fire WireReplies: 11Last Post: 09-28-2003, 09:50 AM -
Isle of Capri Asks County to Install Hydrants
By captstanm1 in forum FloridaReplies: 0Last Post: 06-13-2003, 09:10 AM

LinkBack URL
About LinkBacks