    This may seem like a dumb question to you city boys, but what is the best way to pump through storz LDH? We are a rural department that only drafts but come the first of the year there is a chance we could be using some hydrants that are very spread out so we would probably have to pump from the hydrant to the attack engine.

  2. #2
    MembersZone Subscriber
    Dickey's Avatar
    Join Date
    Feb 2000
    Location
    Wisconsin
    Posts
    5,111

    Default

    Quote Originally Posted by Georgetown18 View Post
    This may seem like a dumb question to you city boys, but what is the best way to pump through storz LDH? We are a rural department that only drafts but come the first of the year there is a chance we could be using some hydrants that are very spread out so we would probably have to pump from the hydrant to the attack engine.
    If you will be using hydrants, they are a positive pressure system meaning you don't have to suck it out of the hydrant, it comes to you under pressure.

    You can lay your supply line of LDH from the hydrant to the attack engine without the need of an engine in the middle, that is if the water pressure is adequate.

    You may pump through LDH just like any size hose, it's just a bigger hose.

    Some departments always operate with an engine at the hydrant pumping to the attack engine to ensure water pressure is not an issue. Personally, in my department, I am not always guaranteed enough personnel to staff a second engine. We operate the first in engine drops a hydrant person and hose at the nearest hydrant, drive to the fire and commence fire attack. The hydrant person makes the connection, and the driver advises the hydrant person they have made the connection to the truck and they can turn on the hydrant. The hydrant person then comes back to the engine to be part of the back up team.
    Jason Knecht
    Assistant Chief
    Altoona Fire Dept.
    Altoona, WI

    IACOJ - Director of Cheese and Whine
    http://www.cheddarvision.tv/
    EAT CHEESE OR DIE!!

  3. #3
    Forum Member

    Join Date
    Dec 2007
    Posts
    22

    Default

    I guess I misphrased my question... I completely understand the concept. Im just unsure of what hardware is best for the situation.

  4. #4
    MembersZone Subscriber
    tree68's Avatar
    Join Date
    Aug 2003
    Location
    Jefferson County, NY USA
    Posts
    2,302

    Default

    Check out the friction loss information for your chosen LDH. Up to a point the loss is negligible - laying in off the hydrant and working with hydrant pressure will work just fine for you.

    Beyond a certain point you'll need to help it out a bit, usually with an engine at the hydrant. Consider your flows and the potential length of your lays.

    We are also rural and generally end up drafting, at least from a drop tank. We are surrounded by villages with hydrant systems, however, as well as Lake Ontario and the St Lawrence River. Our LDH has been off the truck for a fair number of incidents both in hydranted area and where we've been drafting.

    Another plus, LDH gives you the ability to move your tanker shuttle operation away from the fire scene, possibly even keeping it on a main road.
    Opinions my own. Standard disclaimers apply.

    Everyone goes home. Safety begins with you.

  5. #5
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    You'll want a hydrant assist valve on the hydrant. First pumper lays into the fire, a second pumper can then pump the hydrant through the HAV to maximize the water flow.

    A "Z valve" can be used inline for long lays, a Z valave opeatresin a similat fashion, allowing an engine to boost the pressure tot he attack pump.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  6. #6
    Forum Member
    nmfire's Avatar
    Join Date
    Nov 2002
    Location
    Maryland (DC Suburb)
    Posts
    5,738

    Default

    You should have a gated Piston Relief Valve (PRV) on the engine's intake with a stortz fitting that matches your hose (4" or 5"). You should have a hydrant to stortz adapter for the hydrants. You may also want to get some gated wyes and a syamese. Maybe a manifold.

    Other than that, its just a big hose.
    Even the burger-flippers at McDonald's probably have some McWackers.

  7. #7
    MembersZone Subscriber
    Dickey's Avatar
    Join Date
    Feb 2000
    Location
    Wisconsin
    Posts
    5,111

    Default

    Oh yes, forgot that part.

    make sure you have the proper adapters and train with them before you actually need to use them for real.
    Jason Knecht
    Assistant Chief
    Altoona Fire Dept.
    Altoona, WI

    IACOJ - Director of Cheese and Whine
    http://www.cheddarvision.tv/
    EAT CHEESE OR DIE!!

  8. #8
    Forum Member
    nmfire's Avatar
    Join Date
    Nov 2002
    Location
    Maryland (DC Suburb)
    Posts
    5,738

    Default

    Also, most LDH is limited to 200psi. This is what limits your length. With 5" LDH flowing 1000gpm on flat ground, you are limited to about 1,800ft because more than that will require more than 200PSI at the pump discharge. As you lower the GPM, you lower the pressure and subsequently can use more and more LDH.

    By placing a relay pumper in the middle, you can double your distance.
    Even the burger-flippers at McDonald's probably have some McWackers.

  9. #9
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    Quote Originally Posted by nmfire View Post
    You should have a gated Piston Relief Valve (PRV) on the engine's intake with a stortz fitting that matches your hose (4" or 5"). You should have a hydrant to stortz adapter for the hydrants. You may also want to get some gated wyes and a syamese. Maybe a manifold.

    Other than that, its just a big hose.
    I forgot that too... chalk it up to cranial flatulence.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  10. #10
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,047

    Default

    In case you have two ways(hydrants) - have several stortz X 2-1/2" hydrant adaptors in addition to the 4-1/2" X stortz. A 3 way manifold (stortz X three - 2-1/2"males "triplex") can come in handy , have dbl females attached so it can "swing both ways"

  11. #11
    MembersZone Subscriber
    tree68's Avatar
    Join Date
    Aug 2003
    Location
    Jefferson County, NY USA
    Posts
    2,302

    Default

    And, a little trivia I figured out some time ago:

    Five inch LDH holds about a gallon per foot. That means it weighs something over 8 pounds per foot - once it's full, it pretty much stays put.

    And, if you lay out 1000' (which is what we carry) you'll empty your booster tank charging the line (if you're drafting from a drop tank and waiting for water, and assuming you have a 1000 gallon booster tank).

    Also, in 5" LDH flowing 1000 GPM the water is moving at about 11 MPH. Open and close valves s-l-o-w-l-y. That's a lot of momentum.

    That all assumes I did the math right.

    Back on topic - make sure you have adapters to fit your neighbors as well. We have a neighboring department with 4" LDH. We have 5" LDH. We carry 4"x5" Storz adapters for that reason.

    If you use a manifold, it should also have a pressure relief valve.
    Opinions my own. Standard disclaimers apply.

    Everyone goes home. Safety begins with you.

  12. #12
    Forum Member
    Jonnee's Avatar
    Join Date
    Oct 2005
    Location
    Virginia
    Posts
    1,256

    Default

    Our procedure is to not lay over 800 feet on a relay. This allows you a section or two in case you have a bad coupling or burst section. Safety is always first.

    Plus is necessary it also allows you to get the replay pumper out of the middle or edge of the road if the road is narrow.

  13. #13
    Forum Member
    L-Webb's Avatar
    Join Date
    May 2009
    Location
    GA
    Posts
    519

    Default

    I have a question too.

    Is there a min flow the hydrant needs to have to use LDH. I have been told that if the flow is below 500 gpm, then it could cause problems and you would be better off laying dual 3 inch lines. Is this true?

    Can you get 1000 GPM out of dual 3 inch lines @1000 feet?
    Bring enough hose.

  14. #14
    Forum Member

    Join Date
    Jan 2007
    Posts
    2,802

    Default

    Quote Originally Posted by Georgetown18 View Post
    I guess I misphrased my question... I completely understand the concept. Im just unsure of what hardware is best for the situation.
    You'll want some 2 1/2 to however big your house inch Storz for hooking to hydrants and for working with other departments if they don't use storz LDH. You'll need adapters for the intakes and discharges for your own engines.

    If surrounding departments use other sized LDH you might want some storz to storz adapters to compensate for the difference in size.

  15. #15
    Forum Member
    MemphisE34a's Avatar
    Join Date
    Jan 2004
    Location
    Memphis, TN - USA
    Posts
    2,526

    Default

    Quote Originally Posted by L-Webb View Post
    I have a question too.

    Is there a min flow the hydrant needs to have to use LDH. I have been told that if the flow is below 500 gpm, then it could cause problems and you would be better off laying dual 3 inch lines. Is this true?

    Can you get 1000 GPM out of dual 3 inch lines @1000 feet?
    No and no.
    RK
    cell #901-494-9437

    Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.

    "Everyone goes home" is the mantra for the pussification of the modern, American fire service.


    Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.

  16. #16
    Forum Member

    Join Date
    May 2006
    Location
    Bryn Athyn, Pa.
    Posts
    1,623

    Default

    Quote Originally Posted by L-Webb View Post
    I have a question too.

    Is there a min flow the hydrant needs to have to use LDH. I have been told that if the flow is below 500 gpm, then it could cause problems and you would be better off laying dual 3 inch lines. Is this true?

    Can you get 1000 GPM out of dual 3 inch lines @1000 feet?
    The only problem would be the length of time it takes to get water from one end to the other. A good head math number is that 5" hose holds about one gallon per foot. So if you have 1000 feet out, once your hydrant is open and flowing, it will take about two minutes to get water flowing at the scene end. But your friction loss will be minimal.

    On your 1000 gpm through dual 3" lines, do the math. All things being equal, each of the lines is flowing 500 gpm. A tolerably decent head math number there is 20 psi loss/100 ft. That would say 200 psi loss end to end. If you want 50 psi coming in to your relay engine, now you're at 250 psi. Not impossible, but not good practice either.

  17. #17
    Forum Member

    Join Date
    Sep 2009
    Location
    Nova Scotia, Canada
    Posts
    62

    Default

    Quote Originally Posted by nmfire View Post
    Also, most LDH is limited to 200psi. This is what limits your length. With 5" LDH flowing 1000gpm on flat ground, you are limited to about 1,800ft because more than that will require more than 200PSI at the pump discharge. As you lower the GPM, you lower the pressure and subsequently can use more and more LDH.

    By placing a relay pumper in the middle, you can double your distance.
    I have to disagree with that satement (a bit) it is not totally acurate. One of our negibouring departments has 5500 feet on one truck wich we use a supply truck. We have no hydrants other than dry hydrants so we do all of our pumping from draft. The truck has a 1750GPM pump on it and we can pump at around 150 to 175 and provide a fire flow of around 250 gpm (on a flat) of course if we drop trucks in every 1000 feet or so we can drive that up significantly. And it all depends on the terrain as well pumping downhill will take less pressure and provide more flow than up hill. I know for a fact I recently worked a large commercial fire and I was being fed through 3000' of 5" over ups and downs in the road with one truck. I was supplying off my truck 3 - 1", 1 - 2" at about 150psi, and a deck gun at about 80psi. The truck feeding me was at 150psi and I was getting about 100psi and I was maintaining a residual pressure of about 30 to 40psi.

    I guess the main point I'm getting at is we train with it and use it on a regular basis so we know what we can do with it. It's like anything in the service use it and know it. Just becuase the book say's something doesn't mean it's right.

    As for gear and hydrants know the fittings you'll need get at least one gate two is better it would suck if you had to shut the hydrant down for some reason to hook another line on. And maybe do a hydrant bag up to carry everything you need

  18. #18
    MembersZone Subscriber

    Join Date
    Dec 2002
    Location
    Rural Iowa
    Posts
    3,106

    Default

    For rural water supply, including LDH relay, best reference I know of is from isoslayer (Larry Stevens wrote).

    Download "ASK ISO" from http://isoslayer.com/Links.html

  19. #19
    MembersZone Subscriber

    Join Date
    May 2000
    Location
    SW MO
    Posts
    4,249

    Default

    Quote Originally Posted by nameless View Post
    You'll want some 2 1/2 to however big your house inch Storz for hooking to hydrants and for working with other departments if they don't use storz LDH. You'll need adapters for the intakes and discharges for your own engines.

    If surrounding departments use other sized LDH you might want some storz to storz adapters to compensate for the difference in size.
    No matter what size of hose you're using, you're not going to get more than the hydrant or other supply restrictions will provide. If you're only getting 250 gpm out of a hydrant, you're only going to be able to push 250 gpm.

    Where LDH comes in is that you can push that gpm further with less effort due to the decreased friction loss. Dual 3's is better than a single, a single 5" is better than dual 3's.

  20. #20
    Forum Member

    Join Date
    Jan 2007
    Posts
    2,802

    Default

    Quote Originally Posted by Catch22 View Post
    No matter what size of hose you're using, you're not going to get more than the hydrant or other supply restrictions will provide. If you're only getting 250 gpm out of a hydrant, you're only going to be able to push 250 gpm.

    Where LDH comes in is that you can push that gpm further with less effort due to the decreased friction loss. Dual 3's is better than a single, a single 5" is better than dual 3's.
    Thats great, but what does that have to do with my post?

    The guy asked about hardware, and all of you guys are jabbering about hydraulics. Just answer the poor guys question.

  21. #21
    MembersZone Subscriber

    Join Date
    Jan 2007
    Location
    Pa Wilds
    Posts
    590

    Default

    NAMELESS: slackjawedyokel mentioned a "Triplex" and setting it up to act as both a distributor and a siamese by adding double female 2 1/2's to the ends and pumping it backwards. This technique might be the only way to move large volumes of water from the supply engine, if your engine is older with only 2 1/2" discharges. Most of the current engines used to protect high hazard locations are designed with one or more discharges of 3 1/2" valves or larger. You should expect very high losses from a 2 1/2" outlet at flows above 500 gpm. I have seen losses of 80 psi and more at 1,000 gpm through a single 2 1/2" outlet. Try to select the largest discharge on the officers side with the least number of elbows. Otherwise use the triplex as a siamese and feed it from two or three discharges.
    Also never try to bring large volumes into the attack engine through the pony (gated 2 1/2") suction. NMFIRE recommended a gated relief valve on the intake of the attack engine. Be sure to set the relief at or below 180 psi to prevent blowing your LDH in the event all flow is stopped while the supply engine continues to pump water. Do not adapt from Storz to your hard sleeve, as the regular Storz couplings are not designed for vacuum (drafting) operations. There are Storz specially designed for use on suction sleeves, but not the normal type used on LDH.

  22. #22
    Forum Member

    Join Date
    Sep 2009
    Location
    Nova Scotia, Canada
    Posts
    62

    Default

    Quote Originally Posted by KuhShise View Post
    NAMELESS: Do not adapt from Storz to your hard sleeve, as the regular Storz couplings are not designed for vacuum (drafting) operations. There are Storz specially designed for use on suction sleeves, but not the normal type used on LDH.
    Just a quick note to add to that. Most hard sleeve suction is not designed to take pressure and will pop if you try. If you are going to use hard sleeve for pressure make sure it is rated to do so.

    We used to use stortz fittings for drafting but got away from it due to too many issues getting good seals even with the proper gaskets.

  23. #23
    Forum Member

    Join Date
    May 2001
    Location
    Greensboro, NC USA
    Posts
    1,312

    Default

    Quote Originally Posted by nmfire View Post
    You should have a gated Piston Relief Valve (PRV) on the engine's intake with a stortz fitting that matches your hose (4" or 5").
    This, in my opinion, is one of the worst things you can do.

    Find an intake valve that you can use for drafting and LDH. The TFT Jumbo Ball Intake valve is my favorite. Do not commit to having the Storz threads on the valve. Get drafting threads on the valve, and keep a thread/storz adapter preconnected, or in a compartment.

    Piston Intake Valves suck for use while drafting. One of the worst inventions for firefighting I've ever seen.
    Last edited by txgp17; 04-15-2011 at 01:17 AM.
    The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America

  24. #24
    Forum Member
    FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,411

    Default

    Quote Originally Posted by txgp17 View Post
    This, in my opinion, is one of the worst things you can do.

    Find an intake valve that you can use for drafting and LDH. The TFT Jumbo Ball Intake valve is my favorite. Do not commit to having the Storz threads on the valve. Get you drafting threads on the valve, and keep a thread/storz adapter preconnected, or in a compartment.

    Piston Intake Valves suck for use while drafting. One of the worst inventions for firefighting I've ever seen.
    Why use ANY type of device for drafting? Go straight into the steamer. Removing them only takes a few seconds at most and reduces a huge friction loss.
    "Loyalty Above all Else. Except Honor."

  25. #25
    Let's talk fire trucks!
    BoxAlarm187's Avatar
    Join Date
    Jan 2003
    Location
    Virginia
    Posts
    3,325

    Default

    Quote Originally Posted by txgp17 View Post
    Find an intake valve that you can use for drafting and LDH. The TFT Jumbo Ball Intake valve is my favorite. Do not commit to having the Storz threads on the valve. Get you drafting threads on the valve, and keep a thread/storz adapter preconnected, or in a compartment.

    Piston Intake Valves suck for use while drafting. One of the worst inventions for firefighting I've ever seen.
    However, for those who only draft once a year at the annual pump test, PIV's are a god-send....including the TFT Jumbo Ball valve with Storz.

    Or, you can put a PIV on your officer's side (keeping that blasted 5" hose from beneath the pump operator's feet) and put a butterfly (Keystone) valve on the driver's side in case you do need to draft. This is our SOP at work and the VFD both. Works great!
    Career Fire Captain
    Volunteer Chief Officer


    Never taking for granted that I'm privileged enough to have the greatest job in the world!

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Grant Info for Large Diameter Hose
    By brvolk in forum Federal FIRE ACT Grants & Funding
    Replies: 5
    Last Post: 03-15-2006, 03:24 PM
  2. Water Thiefs and LDH Manifolds
    By 42VTExplorer in forum Firefighters Forum
    Replies: 8
    Last Post: 08-25-2004, 12:13 AM
  3. Pumping LDH
    By WBFD324 in forum The Engineer
    Replies: 17
    Last Post: 06-01-2004, 05:13 PM
  4. Ldh
    By firemanjmp80 in forum Volunteer Forum
    Replies: 6
    Last Post: 03-19-2004, 10:38 PM
  5. LDH planning and usage - longlay
    By neiowa in forum Firefighters Forum
    Replies: 18
    Last Post: 08-20-2003, 10:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register