    Default Flammable liquids live training

    Hi,

    I'm teaching at an industrial site, and they have a pit for live training on flammable liquids. The last training was done 25 years ago so no one can tell me how much fuel to put in. The pit is 30 inches deep with 12 inches of water in it.

    Is there a formula using square footage for how much fuel to put in? I've searched but haven't found anything helpful. I want just enough in there. Not enough - poor fire, too much - my partner and I are there all day as we are to burn off the remainder after training is done.

    I'm thinking an 80% diesel 20% gasoline mix, but need to know how much total.

    Any ideas??

    Thanks

  2. #2
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,895

    Default

    Maybe there is a reason it has not been used in so many years

    How is the fire going to be extinguished?? Extinguisher, hand line???

    What is the diameter??

  3. #3
    MembersZone Subscriber

    Join Date
    May 2007
    Location
    Rochester, MN
    Posts
    73

    Default

    Reason it hasn't been used, no one knows,

    Extinguishing with 1 3/4" line with foam.

    Pit is approx. 20' x 20' square. will measure tomorrow.

    I have watched the initial burn on tape, when elkhart brass ran a class on all the new equipment the site purchased in 1985.

    they put it out in about 20 seconds

  4. #4
    MembersZone Subscriber

    Join Date
    May 2005
    Posts
    1,167

    Default

    Try contacting the Wisconsin Fire Academy.

    Wisconsin Fire Service Education and Training

  5. #5
    Forum Member

    Join Date
    Nov 2006
    Location
    N. Ridgeville, Ohio
    Posts
    811

    Default

    This is the training site that I have been to in Ohio. They used to be part of the Ohio Fire School. This is the type of thing they do there all the time. http://www.marad.dot.gov/about_us_la...ing_center.htm
    Jason Brooks
    IAFF Local 2388
    IACOJ

  6. #6
    Forum Member
    MemphisE34a's Avatar
    Join Date
    Jan 2004
    Location
    Memphis, TN - USA
    Posts
    2,526

    Default

    As much as many of the "sallies" on here are going to hate this statement, I would wing it. I doubt such a calculation even exists.

    Fuel it up until youy think it's enough.

    If it goes out too quickly put more in next time. If it takes to long to extinguish, put less.

    It's in a pit, it's not gonna go anywhere. Don't make it harder than it has to be.
    RK
    cell #901-494-9437

    Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.

    "Everyone goes home" is the mantra for the pussification of the modern, American fire service.


    Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.

  7. #7
    MembersZone Subscriber

    Join Date
    Jan 2007
    Location
    Pa Wilds
    Posts
    586

    Default

    I would only use #2 fuel oil and start with about 200 gal for a 30 ft diameter tank. This will give a fuel depth of about 3/8" and should last about 10 minutes. Burn rates will increase as the temperature of the water increases after a number of burns. If your crews get carried away and cause the fog pattern to be driven into the fuel, you will get some mixing of water and fuel as well as entrained air. This can be difficult to light. Use a small container (1/2 cup or less) of gasoline dumped on the froth or fuel as an aid to ignition. When delivering the gas, keep the torch man a long way away from the pit until after the cup is dumped.
    As some others have said, adjust the fuel quantity acording to the ability of the crews. A clear pit is not a realistic scenario for a real refinery fire, so if possible arrange some metal to block the ability to sweep the flame off the surface with the fog pattern. Some training actually teaches techniqies to "run" the flame off the surface if the flammable is contained in a definite area (dike). Using a gasoline mixture (low flash point liquids) can make flash backs a real possibility when using water fog for extinguishment. Crude spills can be pretty hairy since there can be a significant amounts of pentanes and hexanes in the mixture. It is much safer to use refined product with a flash point above 100 deg. F. Check out photobucket http://s679.photobucket.com/albums/v...t=100_0495.jpg
    Last edited by KuhShise; 10-13-2010 at 11:36 PM.

  8. #8
    Forum Member
    CaptOldTimer's Avatar
    Join Date
    Jun 1999
    Location
    Virginia
    Posts
    7,242

    Default

    Not sure about other areas but around here the fire departments can't get a liquid burn permit from the EPA for this.

    Most everything now has been reduced to LP trees, or burners inside burn building. Sometimes you can have a pallet or two inside with a couple bales of hay and ignite them.
    Stay Safe and Well Out There....

    Always remembering 9-11-2001 and 343+ Brothers

  9. #9
    Forum Member

    Join Date
    Aug 2007
    Location
    Southern Indiana
    Posts
    497

    Default

    Quote Originally Posted by CaptOldTimer View Post
    Not sure about other areas but around here the fire departments can't get a liquid burn permit from the EPA for this.
    That is really sad. How can you be expected to deal with a liquid fire if you have never seen one before? I understand the pollution aspect but in the grand scheme of things, to me, doing the training with pollution is a lesser evil than potentially sending crews into a situation without as good of training as you can give them.

  10. #10
    MembersZone Subscriber

    Join Date
    May 2007
    Location
    Rochester, MN
    Posts
    73

    Cool

    Burn is done, about 100 gallons 80% #2 diesel, 20% gasoline worked well. Pit was about 30' square.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. College credit for firefighter training
    By MikeWard in forum Firefighters Forum
    Replies: 9
    Last Post: 08-13-2012, 12:47 PM
  2. Proposed NFPA 1001 changes for 2007
    By SWLAFireDawg in forum Volunteer Forum
    Replies: 83
    Last Post: 06-23-2007, 05:42 PM
  3. Live fire training? What do your rules say?
    By Station7Cadet in forum Fire Explorer & Jr. Firefighting
    Replies: 3
    Last Post: 03-30-2002, 05:33 PM
  4. Building a live fire training facility
    By FyredUp in forum Firefighters Forum
    Replies: 5
    Last Post: 03-29-2001, 10:37 PM
  5. Regulating the manufacture & use of TIC's
    By FireFLIRMgr in forum Thermal Imaging Cameras
    Replies: 16
    Last Post: 05-16-2000, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register