How about those of us that routinely have 500'+ approaches down rural driveways, don't have a truck within 20 miles, and are typcially nosing-in to most of our occupancies? The front bumper pre-connects might not be the answer for all, but making a blanket statement about how they advocate poor engine company tactics isn't fair either.
Plumb them with 2.5" to the front bumper, no worries about the FL. How do I know? At work, we run a 2.5" front bumper discharge to a 150' 1.75" crosslay for interior attack on the small homes with about a 15' setback from the curb...and we're easily maintaining a 150gpm flow on it.
And I have to agree with the the brother about attempting lay in while backing up a 500' driveway....
+ Reply to Thread
Results 21 to 40 of 68
Thread: Front Bumper Speedlays ??
-
12-09-2010, 11:53 AM #21
Last edited by BoxAlarm187; 12-09-2010 at 11:56 AM.
Career Fire Lieutenant
Volunteer Chief Officer
Never taking for granted that I'm privilged enough to have the greatest job in the world!
-
12-09-2010, 02:23 PM #22
I'll edit my setiments to include "in urban settings".
Robert Kramer
cell #901-494-9437
Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.
"Everyone goes home" is the mantra for the pussification of the modern, American fire service.
Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.
-
12-09-2010, 04:24 PM #23MembersZone Subscriber
- Join Date
- May 2003
- Location
- Penny Lane
- Posts
- 390
Here's a second (or third) vote for the donut roll pre-connects (nice pics, Adam!) and for 2 1/2"-3" plumbing to the bumper.
Memphis:
In addition to the other reasons mentioned (long driveways, no truck co, etc) for bumper attack lines, I'd counter your statement by saying that they're the perfect complement to a good attack line setup in the rear bed. In our district, at least half of the time the truck company is going to be responding from the opposite direction, and a lot of the streets are narrow. If we pull past the building in those situations, we're actually blocking out the truck. Having both front and rear attack lines allows the flexibility for either condition.
-
12-09-2010, 07:28 PM #24MembersZone Subscriber
- Join Date
- Sep 2006
- Location
- Northeast Coast
- Posts
- 3,527
-
12-09-2010, 09:10 PM #25
We put a line on the bumper for car fires, pure and simple. We are often restricted by the NJSP on the interstate to operating in one lane or 2 lanes. So to flake out a crosslay may not work well.
For all other attacks, I don't know that I buy into the fact that a line coming off the side will set you back in your fire attack.I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.
"The last thing I want to do is hurt you. But it's still on the list."
"When tempted to fight fire with fire, remember that the Fire Department usually uses water."
-
12-09-2010, 10:08 PM #26Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,095
The friction loss is double? Absolute nonsense. The problem is not many people know how to spec piping for preconnects. We spec performance not pipe size. We set the performance for our 2 bumper lay 2 inch lines at a flow of at least 300 gpm each at no more than 20 psi friction loss. Guess what? The manufacturer exceeded our spec.
The system works very well for us and frankly since we have no truck, and both of our engines carry truck equipment, we don't need to leave room for a truck company.“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
12-10-2010, 02:06 AM #27
Easy big guy, it was just a number to throw out there while posting. Mistake on my behalf, yes.
Originally Posted by FyredUp
Is there a measurable difference from running a crosslay compared to a bumper line of the same size. YES.
FM1I'm the one Fire and Rescue calls, when they need to be Rescued.
Originally Posted by EastKyFF
-
12-10-2010, 07:46 AM #28Forum Member
- Join Date
- Jun 2009
- Location
- MD
- Posts
- 28
-
12-10-2010, 09:09 AM #29Forum Member
- Join Date
- May 2002
- Location
- NY
- Posts
- 156
On our units with 2 bumper preconnects, the only 90 degree bend is the swivel. the other 2 bends in the line are 45's (the one directing flow down from the valve, and the other directing the flow forward under the cab). the FL is negligible, and the gpm is slightly less than the crosslays, (less than 5 gpm difference). In other words, its plumbed right.
-
12-10-2010, 09:21 AM #30
We have a 90 on the front line which is a swivel.
All 3 of our crosslays have a 90, which is a swivel also.
I'll run the flow meter, cuz you have me curious. But I'm betting on FL difference between front and crosslays is really going to be minimal. We'll see...."This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?
-
12-10-2010, 05:43 PM #31Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,095
Sorry, but you couldn't possibly be more wrong. There is no difference IF YOU SPEC IT RIGHT. We specced our front bumper crosslays to flow EXACTLY the same as the over the pump crosslays. Minimum of 300 gpm with no more than 20 psi friction loss in the piping. And they both flwo what our spec calls for. Imagine that?
People run into trouble when they spec pipe size and not performance. You could spec 2 1/2 inch pipe for crosslays and have the manufacturer put in so many bends and elbows you gain nothing in performance. If you spec 300 gpm at no more than 20 psi friction loss it is up to the engineers to figure out how to make it work. Not for you to go after the purchse to say "Well they put in what we asked for, but it doesn't work."
Funny how people buying a piece of fire apparatus will spend all day writing performance specs for engines, transmissions, pumps, foam systems, generators, and lights...but not one second seriously thinking about performance for flow through preconnects and front and rear discharges. I say SHAME on salespeople for not asking what people expect to flow through those lines, and not what size pipe they want.“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
12-10-2010, 05:49 PM #32Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,095
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
12-10-2010, 05:53 PM #33
-
12-10-2010, 08:07 PM #34Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,095
Funny how Chicago can plumb an LDH discharge to the front of their engines, and so many can plumb 2 1/2, 3 or even LDH off the back of their engines, but a 300 gpm handline to the front bumper simply is nearly impossible. Golly,
what about all those rigs with front bumper master streams? How do they do it?
Once again, it is SIMPLE. Write the spec to say it MUST be done and write a performance spec for the builder to meet. If one builder can't or won't do it there are plenty of fish in the apparatus builder sea that will.
When we specced our front bumper crosslays the spec was crystal clear. We even sent 200 feet of our hose to the factory so they could make sure it fit. We specced flow and assumed that their engineering staff would figure it our. Guess what they did and it works perfectly. Two 200 foot 2 inch lines that flow 300 gpm each at actually less than 20 psi internal friction loss.
Finally if your new engine doesn't do what it was supposed to by spec...DON'T ACCEPT IT. It really is that simple.“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
12-10-2010, 11:42 PM #35Forum Member
- Join Date
- Oct 2010
- Posts
- 202
Sadly, I am a computer idjit, and never figured out how to do this
...
I won't be home for a couple of weeks yet, but there is a picture of this truck on our website. it's basically a "baby picture" but you can see the crosslays I'm talking about. Best way to find us is thru the Monroe County Fire Wire site, and look for the dept websites.
-
12-11-2010, 04:15 AM #36
The red section is my point. Reread what I posted FyredUp. Or better yet... is your bumper line piping THE SAME SIZE PIPING AS YOUR CROSSLAYS???? That is my point. Not that you spec'd it differently as needed.
We have 2 Pierce rigs with bumper lines piped the SAME SIZE as the crosslays. The loss is enough that the crews are NOT ALLOWED to use them as an interior attack line. PERIOD!!!!
So you get this straight, WE didn't order or spec them. They were adopted as that town was annexed by the City.
FM1I'm the one Fire and Rescue calls, when they need to be Rescued.
Originally Posted by EastKyFF
-
12-11-2010, 09:20 AM #37Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,095
I haven't a clue whether the piping is the same size or not. I will have to take a look next time I am at the FD. To be honest I couldn't care less what size the pipe is since we had a PERFORMANCE spec, not a pipe size spec. We told them the flow we wanted and expected them to figure out how to build it. They have ENGINEERS to figure out what it takes to meet the PERFORMANCE we wanted. Honestly I think anybody that writes a spec quoting pipe since instead of performance is really doing theor fire department a HUGE disservice.
And perhaps if you had said that in YOUR specific instance, engines that were poorly specced, have front bumper lines that were plumbed incorrectly and have friction losses twice that of your crosslays, there would have been no confusion as to what you meant.
I see 3 possible scenarios as to why those engines are plumbed as they are:
1) The spec committee said we want a front bumper pre-connect so lets plumb it the same as the crosslays so we get the same water. (Incorrect thinking)
2) We need a trash line off the front that flows 100 gpm or less for nuisance fires. (Short sited thinking, but not necessarily wrong.)
3) The salesman didn't know any better so he went along with what the FD wanted. (Possible and shameful if true.)“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
12-11-2010, 02:02 PM #38
-
12-11-2010, 04:30 PM #39
Hello? FM1 does ANY of this look FAMILIAR? BTW,this is NOT my statement,I'm QUITE sure it's YOURS. I don't know how stuff is done in YOUR neck of the woods,but HERE bumper lines are SPECCED to FLOW,they aren't glorified booster lines. Much like Fyred's,we have very little loss in our front line. They CAN be used for ANY attack that you might care to pull them for. Two of the rigs have Vindicators on the bumper lines. FWIW T.C.
-
12-11-2010, 04:55 PM #40MembersZone Subscriber
- Join Date
- Sep 2006
- Location
- Northeast Coast
- Posts
- 3,527
Sweet! Our Squid now has one bumper load with 15/16ths and the other with a Vindicator. We've flowed the Vindicator at 450 gpm off the bumper using 2.5" hose and 300 gpm through 1.75"! That's about max through the discharge with each set up, before the pump starts fighting itself. Again, the performance spec vs. just asking for two 1.5" male threads to attach hose to makes a big difference.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Front bumper hose lays
By taskforce16 in forum The EngineerReplies: 44Last Post: 03-04-2007, 05:49 PM -
Bumper pre-connect query
By confire in forum Firefighters ForumReplies: 34Last Post: 10-20-2005, 08:34 AM -
Residential Fire Scenario - YOU'RE THE CHIEF!
By PaulGRIMWOOD in forum Firefighters ForumReplies: 64Last Post: 10-11-2005, 11:07 PM -
Thermal Imaging SOG's
By wtfd92 in forum Firefighters ForumReplies: 23Last Post: 06-27-2001, 08:41 PM -
traashline in front bumper
By flash32 in forum Firefighters ForumReplies: 62Last Post: 04-17-2001, 09:58 PM

LinkBack URL
About LinkBacks