the water level indicator lights on my pump panel are blinking. I hear that they can be reset with a magnet with a certain sequence. Does anyone happen to know what it is? It's a piece waterous pump.
+ Reply to Thread
Results 1 to 8 of 8
-
01-26-2011, 02:21 AM #1
Blinking indicator lights on panel
-
01-26-2011, 03:22 AM #2Forum Member
- Join Date
- May 2006
- Location
- Bryn Athyn, Pa.
- Posts
- 1,570
Gauges made by Innovative Controls of Turtle Creek, Pa. can be set that way. Some Waterous branded gauges are made by I/C. I have their instruction sheet in the station. Give me a fax number and I'll send it to you or you can call them; they'll send it to you. They were very helpful to me when I called them. 412.824.2264
You do need a small bar magnet. The first time I tried to do it I was using a pretty big horseshoe magnet and it didn't work well at all.
-
01-26-2011, 05:18 AM #3
Really easy.
You can use any magnet you have. They say you need to use the "North Pole", but I've found that as long as it changes the blinking sequence, then you are good to go.
Make sure your tank is empty, and you're ready to fill the tank. Then follow along.
Swipe the "Cal" (small circle bottom of gauge) 3 times (quickly) until you see the top 3 lights blinking together. Slowly open your intake valve. When your tank is full, by the water gushing out, swipe the magnet again, 3 more times.
Wait about 10 seconds, and all the lights should be lit up to show a full tank.
Some tanks are shaped differently and need to be calibrated differently. This is the non-linear way to calibrate all tanks, and is more accurate.
FM1I'm the one Fire and Rescue calls, when they need to be Rescued.
Originally Posted by EastKyFF
-
01-26-2011, 05:20 AM #4
http://www.fireresearch.com/pdfs/wla200.pdf
Here is the link to recalibrate it.
FM1I'm the one Fire and Rescue calls, when they need to be Rescued.
Originally Posted by EastKyFF
-
01-26-2011, 08:53 AM #5Forum Member
- Join Date
- May 2002
- Location
- NY
- Posts
- 156
i always used the magnet thats on the end of one of those small scredrivers.
-
01-26-2011, 11:16 AM #6Forum Member
- Join Date
- May 2006
- Location
- Bryn Athyn, Pa.
- Posts
- 1,570
Our tank is a very irregular shape. The I/C gauge has ten increments on it including "Full" and "Empty." I was able to "customize" the settings to give a little grace period at the bottom. A former member has water meter which we borrowed and rigged up to adapt to garden hose. Each time we got to the next higher desired level of water in the tank, we shut the water off and set the gauge to that level, then continued on. We set the "Full" light so that it goes out after less than 50 gallons is used.
-
01-26-2011, 03:14 PM #7Forum Member
- Join Date
- Aug 2007
- Location
- West Burlington, IA
- Posts
- 106
We had an engine that the indicator lights would blink when the water level was between amounts, like when it was between full and 3/4 and so on. It was built and planned this way.
-
01-28-2011, 08:49 AM #8Forum Member
- Join Date
- Oct 2008
- Posts
- 26
If this is a class1 display, those blinking lights are basically a trouble code.
It may just need to be recalibrated, but it's likely there is a problem elsewhere. (pressure transducer, wiring, or the display itself)
http://www.class1.com/_Downloads/cla...ip%20empty.pdf
Read this and see if it looks like what you have. I think Class1 made a 5 light version for pierce, but everything else should be the same. If yours doesn't resemble this, disreguard this message..If you can't fix it with a hammer, you have an electrical problem.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
New type of switch panel system
By Recelect in forum Apparatus InnovationReplies: 24Last Post: 01-06-2011, 12:29 PM -
Pump panel question.....
By KevinFFVFD in forum Firefighters ForumReplies: 40Last Post: 01-12-2010, 02:44 PM -
Charleston Listens to Preliminary Panel Recommendations
By devildog4 in forum Firefighters ForumReplies: 1055Last Post: 10-26-2007, 09:28 AM -
RFP's
By D Littrell in forum Apparatus InnovationReplies: 1Last Post: 09-08-2000, 06:36 PM

LinkBack URL
About LinkBacks