My volly FD has been using 2 inch hose exclusively for handline ops for a little over a decade now. When I say exclusively, I mean we have no other handline size for fire attack. Well, I guess that is not entirely true we use 3/4 garden hose and 1 inch forestry hose for brush fire operations. We use 2 inch for fire attack, 3 inch for extending handlines with an "apartment line" set-up, for supplying ground monitors, and for supplying FDCs, and 5 inch for water supply ops.
We did the usua change from 1 1/2 inch lines to 1 3/4 back in the late 70's, but failed to follow through with a nozzle change. We were still using the Akron Turbojet 30-60-95-125 GPM nozzles so our 1 3/4 inch hose line was nothing more than a low friction loss line with no increase in flow. Then one of our Chiefs bought into the TFT automatic nozzle hype and we bought those. Our experience with them was less than satisfying, we found that any time we tried to flow more than 150 gpm FFs would gate down the nozzle to make it easier to control. We found that often this reducd the flow to below 100 GPM.
We began our own research program looking at all types of nozzles, smoothbore, Dual-Force TFTs, selectable gallonage combination nozzles, single gallonage combination nozzles, and low pressure and 100 psi nozzles. We settled on Elkhart break a part low pressure 200 GPM at 75 psi combination nozzles with a 15/16 smooth bore slug. We underpumped the combination tip to around 55 PSI to get around 160 gpm for our starting flow. At this time we still had 2 1/2 inch hose lines although they were rarely utilized.
A nearby FD was looking to get rid of a couple hundred feet of 2 inch hose so we bought it to try it out. The guys preferred it to the 1 3/4 and the chief saw that at fire after fire when the crew would go to the back of the rig, past the crosslays and pull the 2 inch. He decided to replace all of our 1 3/4 inch hose with 2 inch and lady luck shined down on us when another nearby FD decided to sell their old 2 inch. We bought around 2000 feet of 2 inch for about 1/3 the cost of new. We tested it and found out to 300 feet a flow of 300 GPM was practical so we took our slug tip nozzles to a local machine shop and had them bored out to 1 1/4 so we could flow 300 at around 40 PSI at the tip. Now we had an all purpose line that could flow our initial 160 GPM at about 55 PSI, could go to 200 GPM at 75 PSI, and even by removing the combo tip and going to the slug tip flowing 300 GPM. The only downside we noticed was a loss of a cohesive stream from the slug tip past about 70 feet.
Both of our engines carry 200 and 300 foot 2 inch preconnects. They also have 3 inch "apartment lines" with a gated wye and 100 feet of 2 inch connected to them. We do carry another bundle pack for either extending that original 2 inch line or adding a second line.
Okay, why we wanted one all purpose line...We ran VERY shorthanded for years. During the day it was a good day time fire for us to get 4 out on the first rig (things are far better these days). We couldn't make the mistake of pulling the wrong line and having the second crew, with any kind of speed anyways, pull the right line. With our set-up we can flow down to a 1 3/4 inch line in flow or all the way up to a 2 1/2. We regularly move the line with 2 people and have no problems doing it.
I know I have talked about our set-up here many times but never telling the entire story all in one topic. So tell me your thoughts. Let's not turn this into a flame war because I am not saying what you do is wrong, just saying what we do.
+ Reply to Thread
Results 1 to 20 of 59
Thread: 2 inch hose...Are you using it?
-
03-31-2011, 10:26 PM #1Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
2 inch hose...Are you using it?
Last edited by FyredUp; 03-31-2011 at 11:43 PM. Reason: clarity
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
03-31-2011, 11:54 PM #2
Why, in fact, my department DOES use 2 inch hose... And oddly enough the same nozzles... And even stranger yet, the same crosslay setup with the apartment packs in the hose bed...
Awfully coincidental if you ask me....


-
04-01-2011, 12:27 AM #3
Father like Son!
Stay Safe
Bull
“Guys if you get hurt, we’ll help you. If you get sick we’ll treat you. If you want to bitch and moan, then all I can tell you is to flick the sand out of your slit, suck it up or get the hell out!”
- Capt. Marc Cox CFD
Nothing in life is so exhilarating as to be shot at without result.
-WINSTON CHURCHILL
http://sylvafiredeptnc.tripod.com
-
04-01-2011, 09:38 AM #4
We don't.
And really no reason other than the cost and keeping things "simple" for the guys. We simply can't afford to change out all of our 1 3/4" and 2 1/2" in 1 shot. And working in some 2" in the mix does not add enough bang for the buck to keep everyone functioning without added confusion.
I'll be honest, if we ever had the chance to switch out all the attack lines...it would definitely be tested."This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?
-
04-01-2011, 01:07 PM #5Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
We were lucky in that most of our 2 1/2 was ancient and we had already started the move to replacing it with 3 inch for apartment lines and FDC supply. We needed more attack line and the remaining 1 1/2 we had was also ancient so when the opportunity to buy that used 2 inch arose it was perfect timing.
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
04-01-2011, 02:44 PM #6
The logic makes sense.. I like the idea of a single line and single nozzle. KISS. The timing in your case sounds perfect too.
I'd like to try 2" with the Ekhart, or something similar. We run two 1.75" with TFT and smoothbore tips and 2.5" smoothbore. The 2" setup you have sounds like the best of both worlds.
Bones, as usual, has a good point on cost. That's something that would probably keep us out until the stars align.So you call this your free country
Tell me why it costs so much to live
-3dd
-
04-01-2011, 03:43 PM #7Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
Cost is an element I won't disagree with you on that. Especially if you are going radical and making a complete changeover to something different. For us to switch back to "conventional" 1 3/4" and 2 1/2" hose would be quite expensive at this point since we don't have any of either size anymore. I guess I just don't see it happening at this juncture.
We were lucky in finding that used 2 inch to get our program started. Further we got a Fire Act Grant to purchase more new hose and in the long run we have replaced all the old 2 inch with Key 2 inch rubber nitrile 100 foot lengths with 5 piece 1 1/2 inch couplings.
What we have done works well for us and really has carried the "KISS" principle to its fullest. All of our preconnect gauges are marked for the 3 flows we use for quick reference. There is never pulling the wrong sized line. There is no nozzle confusion because they are all the same.
The nozzle is an Elkhart B-375GAT pitol grip shut off with the integral slug tip. Ours came originally with 15/16 tips and we had them bored out locally to 1 1/4 inch. The 1 1/4" slug was not available from Elkhart when we had ours bored out, now it is. The combo tip is an Elkhart 4000-24 that flows 200 GPM at 75 PSI. (NO, I don't sell Elkhart nozzles. I just like them!)“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
04-01-2011, 07:08 PM #8MembersZone Subscriber
- Join Date
- Aug 2004
- Posts
- 191
what size couplings are you guys using on the hose 1 3/4 or 2.5? Just curious, if you're using 1 3/4 I take it there's not much interference.
-
04-01-2011, 07:47 PM #9
A coward stands by and watches wrongs committed without saying a word...Any opinions expressed are purely my own and not necessarily reflective of the views of my former departments
-
04-01-2011, 08:25 PM #10MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Central NJ
- Posts
- 1,214
I'm not a fan of 2" hose for anything other than standpipe racks, and in that application its arguable at best. Een though its marginally bigger, I don't see a place where it presents with a major advantage over our 1 3/4" and 2 1/2" options. I get what you're saying but it see it as a "compromise".
We have a 400' 1 3/4" preconnect with a 1 1/8" slug and a 200@100 fog tip. Similar principle. 240 GPM with fog tip, 180 GPM with fog tip, same pump pressure. Pump pressure is 170 if memory serves me correct. Ponn Conquest (I know its like 1.89 ID)
For what its worth, we will stretch a 2 1/2" line with one man, with the driver helping...if we have to.Last edited by MG3610; 04-01-2011 at 08:30 PM.
-
04-01-2011, 11:34 PM #11Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
The coupling size is 1 1/2" just like on 1 1/2" or 1 3/4" hose. We flow tested everything using a calibrated flow meter and we did not find a noticable loss because of the coupling size. Our 3 inch hose has 2 1/2inch couplings which in this area anyways is common so I guess to me the smaller coupling size is inmconsequential.
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
04-02-2011, 12:02 AM #12Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
Like I said in my original post, I don't want this to become a flame war over what we do. We aren't gping to change anytime soon and in reality I don't expect anyome to change what they do based on my little blurb here. It works for us and that is what matters to us. I posted this to try and get people to look at an alternative idea.
Last edited by FyredUp; 04-02-2011 at 12:26 AM.
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
04-02-2011, 12:05 AM #13
-
04-02-2011, 12:29 AM #14Forum Member
- Join Date
- Oct 2010
- Posts
- 203
When I first joined, we used 2" (with 1.5" couplings) for handlines, and 3" for bomb lines and leader lines. Nozzles were a combo of TFT Handlines and Smoothbores w/15/16" tips. The hotel packs on the engine were 1.75" hose with Akron turbojets- the OLD school ones. ( 39/60/90/125 gpm, left over from our 1.5" days)
The three inch was old- the newest and best leftover when we switched to 5" supply years before. As a handline, it SUCKED. Sticking a 100psi automatic on the end just insured it never got pulled... Extremely hard to move, and the nozzle reaction was nuts, plus that size is just plain hard to grip with gloves on.
We ended up switching to 1.75" and 2.5" as part of a capitol improvement project. We also get new hose, nozzles and appliances with each new truck. When we bought our quint, we got Elkhart breakapart playpipes for the deuce and a half lines. The crosslay has the smoothbore tips on it. The selecto-matic auto tips live in the cmpt.
I do not know why we went with the 1.75" handlines. The members absolutely appreciated the switch to 2.5" for the big lines, though! Esp with the smoothbores- they're much more user friendly. I'd have preferred to keep 3" for the leader lines, but as we are all volunteer, we needed to KISS. No need to further confuse the pump operator. We do have 3" donuts for hydrant lines- along with the 5.
I've long been an advocate for the type of nozzle layout Fyredup uses- low pressure breakaparts. The same shut-off can be used with a combo tip, a smoothbore tip, or it can be used for break and extend ops. ( One could also add a length of 1" to it for overhaul) At least trading the 100 psi autos for a low pressure model or for Chiefs/Assaults. The TFT's are pretty popular though. ( they do make a low pressure version) Not to mention EVERYONE uses them around here...
Personally, I like the 2" line. Less friction loss means longer lays are possible, and there are no shortage of those around here!
-
04-02-2011, 07:38 AM #15MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Central NJ
- Posts
- 1,214
I just answered what we do, in keeping with the title of the post. I never said anything against what you do. It seems like you are going on defense already.
Our dept is combo paid/vol. Our paid engine runs with 2 members. We initiate fire attack with anywhere from 2 to 7 members. Our staffing sucks.
Our pump pressure is 170 PSI. This was verified with a pitot tube calibrated flow meter, not a formula. I do all of these tests. Our fire hose provided surprising flow results. All of our preconnects are flow tested and the panel is labelled accordingly.
I can run a 2 1/2" line flowing 250 GPM (smooth bore) standing up by myself, or 320 sitting down. I bet im smaller than most guys too. Just sayin!
I know our hose is not "true" 1 3/4", thats why I stated so.
Please understand I am not saying my way is better than yours, I just replied with what we do and why. I think the process by which your dept has come to its current setup is admirable and shows that you have people with open minds willing to think. For us, a change is not in order. We already tried that change, it showed no appreciable benefit. We have done many other things to make limited manning firefighting easier, u can see my thread about our 2007 KME engine for some examples. Buying lighter weight ladders was one of those things, but I will not poison a hose discussion with knuckle dragger tools LOL.
Last minute FWIW. We have a stack of 2" hose on our rack. Its used in our standpipe racks, because switching to 2 1/2" would freak people out. We used to have the 2" on our 400' line, but when we got more conquest we put it on n place. At one point our engine had 1", 1 1/2", 1 3/4", 2", 2 1/2", 3" and 4". It was a mess. We retired the 1 1/2" and 2" from the hosebeds.
For the record, I believe 1 3/4" and 2 1/2" is the only right answer.
I'd actually like to go back to 1 1/2" some days! No flaming here, unless youre lighting your flamethrower!
Last edited by MG3610; 04-02-2011 at 07:53 AM.
-
04-02-2011, 08:03 PM #16
-
04-02-2011, 08:27 PM #17Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
04-02-2011, 10:32 PM #18MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Rural Iowa
- Posts
- 3,107
Any issues with kinking at 55psi? Or settle on brand _______ hose you find to be better than another to avoid kinking?
I have AFG coming to replace all our handlines and and LDH. Now using OLD 1-1/2" and mix of 2-1/2" and 3" on our pumper.
Enough $ to consider options though stuck with Protech 100psi combination nozzles on pumper. Tanker Pumper is CAFS with Akron breakapart smoothbore (with 200gpm 75psi Turbojets as water only backup). No particular benefit to 2" for a CAFS line. In fact less "scrubbing" action means longer minimum stretch. Also have a quickattack monitor in the grant for each unit.
-
04-02-2011, 10:44 PM #19Forum Member
- Join Date
- Feb 2009
- Location
- virginia
- Posts
- 508
Interesting thoughts in this thread
Whats the weight per 50' section of 2'' versus 1 3/4'' versus 2 1/2''? Yes I could do the math and figure it out and i plan on it, but to lazy to do it right now. I'm on a v day so cut me some slack.
Is the 2 inch hose that you all use now a true 2 inch hose or is it one of the "low friction loss" 2 inch. The reason why i ask is we just switched to ponn conquest 1 3/4 which if i recall correctly is 1.96 or something close to that when charged. So it is basically only .04 inches less then a true 2 inch hose close enough for government work.
We have found through flow testing with a flow meter that our 150' preconnect with a tft dual force nozzle in the red setting flowing 150 gpm the pdp is only 90 psi. Very impressed so far with the results. Reaction force is pretty much non existant.
Do anyone know how much of a difference the ponn is compared to 2" hose in terms of friction loss?
-
04-02-2011, 11:06 PM #20Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,311
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
3 INCH vs 5 INCH Hose for supply
By BURNSEMS in forum Fireground TacticsReplies: 58Last Post: 01-31-2010, 08:24 PM -
ISO Company Personnel
By FIRE549 in forum Firefighters ForumReplies: 20Last Post: 05-16-2007, 06:15 PM -
Hydrant outlet Q
By Firetacoma1 in forum Firefighters ForumReplies: 27Last Post: 06-16-2006, 05:46 PM -
5 Inch Hose
By Almavillefire15 in forum Volunteer ForumReplies: 19Last Post: 04-20-2006, 01:53 AM -
Hey Woody, Down Low or Low Down?????? Fairly New Part II
By AVFR452 in forum Firefighters ForumReplies: 466Last Post: 03-10-2002, 08:22 AM

LinkBack URL
About LinkBacks




It takes the right circumstances, and people willing to just look beyond the way it has always been done, to find local answers to local problems.