    Default 3" vs 4" Tank to Pump

    Looking at purchasing a water tanker/ tender. Have a question and was wondering if anyone out there could help me out? We are looking at a darley hm500 gpm or darley psp 1250 gpm pump. Can anyone tell me the flow rates of a 3" vs 4" tank to pump for both of these pumps? If so is there a chart I could find this info on? Thanks

  2. #2
    MembersZone Subscriber

    Join Date
    Jan 2007
    Posts
    97

    Default

    The quick answer is get the 3" with the 500 and the 4" with the 1250.

  3. #3
    Forum Member
    GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,060

    Default

    I am sure Darley should be able to tell you. If memory serves me correctly NFPA requires a 600 GPM tank to pump valve on 1250 GPM pumps. Not sure what size that would equate to though.
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  4. #4
    Forum Member

    Join Date
    Aug 2009
    Posts
    56

    Default 3" or 4"

    The 3" will be plenty to handle the 500 GPM pump capacity.

    Our 750 GPM pump equipped tankers (some are Hale, some are Waterous) have 4" tank to pump piping and will flow 950 GPM from the tank. I do not know the pump models but they are mid-ship single stage with a 4.5 steamer on each side, PTO driven.

    What I have found is keep the pipe short and straight - tight turns will affect flow.

  5. #5
    Forum Member
    HuntPA's Avatar
    Join Date
    May 2010
    Location
    Northwest PA
    Posts
    488

    Default

    Easier way, and what we did on ours. . . . . .
    Spec that the pump must be able to operate at capacity from the tank. We have a 1500 gpm pump and they gave us (2) 4" lines with 3" valves. We let them do the calculations and the plumbing and also take the responsibility.

  6. #6
    Forum Member
    GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,060

    Default

    Quote Originally Posted by HuntPA View Post
    Easier way, and what we did on ours. . . . . .
    Spec that the pump must be able to operate at capacity from the tank. We have a 1500 gpm pump and they gave us (2) 4" lines with 3" valves. We let them do the calculations and the plumbing and also take the responsibility.
    Only because I have never heard of this, why would you ever need a pump that could reach capacity from tank water?
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  7. #7
    Forum Member
    HuntPA's Avatar
    Join Date
    May 2010
    Location
    Northwest PA
    Posts
    488

    Default

    We use this as a tanker, a pumper, and a nurse tanker all depending on the situation. If we are hooked to our engine (1500 gpm) and using the deck gun on the engine, we want to be able to supply it with the tanker water to save the engine water for hand lines on a quick hit.

    In other words, if we roll up on a fully involved single family dwelling with all occupants out, we can lay in with the LDH on the engine, attach to the LDH discharge on the tanker, and use the deck gun for a quick knock down while setting up for drafting operations or have the tank used as a nurse tank from other incoming units.

  8. #8
    Forum Member

    Join Date
    May 2002
    Location
    NY
    Posts
    165

    Default

    if it seems to work fine, or better when flowing larger volumes, it may be an indication "ramp" adjustments may need to be made.

  9. #9
    Forum Member

    Join Date
    May 2002
    Location
    NY
    Posts
    165

    Default

    sorry, my message above was supposed to be on another thread...duh

  10. #10
    Forum Member

    Join Date
    Oct 2006
    Posts
    35

    Default

    Quote Originally Posted by ffp20 View Post
    sorry, my message above was supposed to be on another thread...duh
    That's ok, it sounded impressive.

  11. #11
    Forum Member
    GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,060

    Default

    Quote Originally Posted by HuntPA View Post
    We use this as a tanker, a pumper, and a nurse tanker all depending on the situation. If we are hooked to our engine (1500 gpm) and using the deck gun on the engine, we want to be able to supply it with the tanker water to save the engine water for hand lines on a quick hit.

    In other words, if we roll up on a fully involved single family dwelling with all occupants out, we can lay in with the LDH on the engine, attach to the LDH discharge on the tanker, and use the deck gun for a quick knock down while setting up for drafting operations or have the tank used as a nurse tank from other incoming units.
    Still not following. Around here if we were to blitz attack with the deck gun off of tank water we would looking at around 500 GPM. How much water is on your engine?
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  12. #12
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,860

    Default

    Quote Originally Posted by GTRider245 View Post
    Only because I have never heard of this, why would you ever need a pump that could reach capacity from tank water?
    If you have an around the pump Class B foam system. In this case, you cannot supply the pump from a positive water source, unless you put the water straight into the tank, then pull it from the tank. Two of our engines are set up this way to flow capacity for that reason.

  13. #13
    Forum Member

    Join Date
    May 2002
    Location
    NY
    Posts
    165

    Default

    on a rig we had the around the pump proportioner, we used 2 4" tank to pump lines. we were able to make 1400 gpm of solution with it.

  14. #14
    Forum Member
    HuntPA's Avatar
    Join Date
    May 2010
    Location
    Northwest PA
    Posts
    488

    Default

    Quote Originally Posted by GTRider245 View Post
    Still not following. Around here if we were to blitz attack with the deck gun off of tank water we would looking at around 500 GPM. How much water is on your engine?
    We have 2 tips for our deck gun, a 500 and a 1250.

    Our engine carries 1,000 gallons of water.

  15. #15
    Forum Member
    GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,060

    Default

    Quote Originally Posted by RFDACM02 View Post
    If you have an around the pump Class B foam system. In this case, you cannot supply the pump from a positive water source, unless you put the water straight into the tank, then pull it from the tank. Two of our engines are set up this way to flow capacity for that reason.
    I completely forgot about this. Being as these systems are not prevelant around here I never think about them. Our newest engine has a direct tank fill that was factory (we didn't spec it); I am assuming because so many trucks are going with the CAFS systems and the like that they just started putting the tank fills on all the trucks.
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  16. #16
    Forum Member

    Join Date
    Jan 2008
    Posts
    198

    Cool

    on both of our pumper tanker's they have 4inch tank to pumps. one is a 500 front mount and the other is a 750 watours with caf's midship pump

  17. #17
    Forum Member

    Join Date
    May 2001
    Location
    Greensboro, NC USA
    Posts
    1,312

    Default

    The Tank to Pump line is the only place where you can have a valve larger than 3" and not have a slow-close mechanism. So upgrading a P2T line from 3" to 4" wouldn't be expensive compared to the same action for an intake or discharge.

    I'd go with the 4".
    The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America

  18. #18
    Forum Member

    Join Date
    Jul 2011
    Posts
    14

    Smile

    4" is better then 3". 4" is give better flow then 3" pipe.

  19. #19
    MembersZone Subscriber
    npfd801's Avatar
    Join Date
    Aug 2002
    Location
    Somewhere in Illinois
    Posts
    2,220

    Default

    Quote Originally Posted by SuperFire View Post
    4" is better then 3". 4" is give better flow then 3" pipe.
    Unless you can justify the need, it costs. If you're really going to flow what a 4" tank to pump is going to give you off of the actual tank water, then go for it.

    As a guy that sells the stuff, it really adds up when you have $500 here, $1,000 there in options that you really maybe will use once or twice in a rig's life.
    "Share your knowledge - it's a way to achieve immortality." - Stolen from Chase Sargent's Buddy to Boss program

  20. #20
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,108

    Default

    Quote Originally Posted by npfd801 View Post
    Unless you can justify the need, it costs. If you're really going to flow what a 4" tank to pump is going to give you off of the actual tank water, then go for it.

    As a guy that sells the stuff, it really adds up when you have $500 here, $1,000 there in options that you really maybe will use once or twice in a rig's life.

    We went with a 4 inch line on our newest pumper. Why? We wanted to be able to flow a minimum of 1000 gpm from the tank for Blitz attacks with either the deck gun or multiple handlines. We figured that by the time we dumped the tank we would have a water supply established either from a hydant of shuttle.

    Minimum staffing allowing for maximum water.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  21. #21
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,036

    Default

    I once saw a tanker/pumper that had dual tank to pump lines(3"). one on each end of the tank -it was for spotting it on steep hills. reasoning being you could get that last 100 gallons from the lowest end. I never asked the flow from tank.
    ?

  22. #22
    Forum Member

    Join Date
    Nov 2002
    Posts
    1,170

    Default

    Quote Originally Posted by slackjawedyokel View Post
    I once saw a tanker/pumper that had dual tank to pump lines(3"). one on each end of the tank -it was for spotting it on steep hills. reasoning being you could get that last 100 gallons from the lowest end. I never asked the flow from tank.
    I think Pierce is doing this as a standard feature on their tankers. We have a Pre-Con meeting in a few weeks, I'll double check that then.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. switching from tank to pump to draft
    By engineer1654 in forum The Engineer
    Replies: 23
    Last Post: 04-15-2008, 12:02 AM
  2. Tank to Pump Flows
    By jrcarespfd in forum The Engineer
    Replies: 13
    Last Post: 11-28-2006, 04:18 PM
  3. World Of Fire Report: 07-21-05
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 07-24-2005, 08:05 AM
  4. World Of Fire Report: 09-26-04
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 09-30-2004, 09:12 AM
  5. do you keep your tank to pump open??
    By Svfman in forum The Engineer
    Replies: 17
    Last Post: 07-27-2004, 12:22 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register