    Default Hydrant Maintenance

    Just curious what your fire department does when it comes to maintaining and testing fire hydrants???? Do they send out the firemen or is it water department or something else???

  2. #2
    Forum Member

    Join Date
    Nov 2009
    Location
    Somewhere in the southeast.
    Posts
    1,072

    Default

    Dalton used to send out companies to their respective districts to maintain, test, and paint the hydrants. They realized that it was far more productive, and less waste of deisel fuel, to send out crews of four firefighters, two to a pick-up truck, to do the annual maintenacne, flows, and painting. It is somewhat of a special detail as firefighters really like to be on the detail. It is one of the details I do miss about being at Dalton, fun times.

  3. #3
    Forum Member
    GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,060

    Default

    Pull caps, grease them. Operate the stem and let water run for a little while. Replace caps. Paint, sticker and weedeat as needed. Report any problems to water works.

    Neither of my departments do testing. Waste of time IMO.
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  4. #4
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,039

    Default

    There is a NFPA standard for maintence and testing , but in a nutshell we -1 visiual inspection (obstructions -visible damage) 2 pull one 2-1/2 cap and flush 3 shut down and attach gauge to open cap 4 open again and check static 5 shut down (a-pull caps and check gaskets, grease threads , pull set screw and oil with approved stem oil - 6 flow steamer with diffisuer & pitot
    attached and take reading of pitot and note resudial - we used to go to the next hydrant and take a resuidal while flowing , but the ISO inspector said it was a waste of time.
    ?

  5. #5
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,895

    Default

    Quote Originally Posted by slackjawedyokel View Post
    There is a NFPA standard for maintence and testing , but in a nutshell we -1 visiual inspection (obstructions -visible damage) 2 pull one 2-1/2 cap and flush 3 shut down and attach gauge to open cap 4 open again and check static 5 shut down (a-pull caps and check gaskets, grease threads , pull set screw and oil with approved stem oil - 6 flow steamer with diffisuer & pitot
    attached and take reading of pitot and note resudial - we used to go to the next hydrant and take a resuidal while flowing , but the ISO inspector said it was a waste of time.
    This flow test method does not sound good

  6. #6
    Forum Member
    DeputyMarshal's Avatar
    Join Date
    Apr 2005
    Location
    Connecticut, USA
    Posts
    2,638

    Default

    Quote Originally Posted by slackjawedyokel View Post
    There is a NFPA standard for maintence and testing , but in a nutshell we -1 visiual inspection (obstructions -visible damage) 2 pull one 2-1/2 cap and flush 3 shut down and attach gauge to open cap 4 open again and check static 5 shut down (a-pull caps and check gaskets, grease threads , pull set screw and oil with approved stem oil - 6 flow steamer with diffisuer & pitot
    attached and take reading of pitot and note resudial - we used to go to the next hydrant and take a resuidal while flowing , but the ISO inspector said it was a waste of time.
    The ISO inspector was a fool. Taking the residual pressure from the same hydrant you're flowing isn't going to give you a valid reading.
    "Nemo Plus Voluptatis Quam Nos Habant"

    The Code is more what you'd call "guidelines" than actual rules.

  7. #7
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,895

    Default

    That's another way to say it

  8. #8
    Let's talk fire trucks!
    BoxAlarm187's Avatar
    Join Date
    Jan 2003
    Location
    Virginia
    Posts
    3,320

    Default

    Quote Originally Posted by irons33fd View Post
    Just curious what your fire department does when it comes to maintaining and testing fire hydrants???? Do they send out the firemen or is it water department or something else???
    In both my volly county and at work, the public works/utilities departments handle maintenance, inspection, testing, and painting.
    Career Fire Captain
    Volunteer Chief Officer


    Never taking for granted that I'm privileged enough to have the greatest job in the world!

  9. #9
    Forum Member
    snowball's Avatar
    Join Date
    Nov 2000
    Location
    Just North of South Central
    Posts
    2,740

    Default

    Here the city works like this. The water department owns the hydrants. Fire maintains them twice a year. We have a wet season and a dry season. Wet season they get flowed, the caps get greased and depending on the hydrant, the street valves get exercised.
    Dry season, the plugs get painted and if need be, re-numbered. The water department takes care of any broken hydrants. When new ones are installed, or a well is added to the grid, we do the initial flow, then paint the top accordingly.
    Every time we touch a hydrant, the water department gets a bill. I think it's like $25 each.
    IAFF

  10. #10
    Forum Member

    Join Date
    Feb 2011
    Posts
    11

    Default

    Here's how we do it where we're from. The DPW owns the hydrants. Twice a year, we pay them about $100K for "maintenance." By "maintenance," I mean they don't do anything with them. No flushing, painting, clearing, nothing. I think every once in a while, when they have an extra guy with nothing to do, they might send him out to flow a couple, but not pump it out or anti-freeze it. If they break, repairs are included in said fee, but don't hold your breath.

    I guess it's politics.

  11. #11
    Forum Member
    rescue10lt's Avatar
    Join Date
    Nov 2001
    Location
    Miami, Florida
    Posts
    41

    Default

    Here's how we do it: Flow the hydrant, shut it down. Get knocked to the ground by some POS with a gun. Hand over your valuables, run like hell. Duck for cover as POS fires gun at you as you exit stage left. Shake your head as you remember how the local politicians said your job was no more dangerous than a window washer and took 30% of your pay last year. Go back to work for your next shift and do it all again.
    Not the best system but it's all we got.

  12. #12
    Forum Member

    Join Date
    Nov 2009
    Location
    Somewhere in the southeast.
    Posts
    1,072

    Default

    Oh yeah, I forgot. Before we ever turn the hydrant on we take a dipstick and dip it into the barrel of the hydrant to ensure that the barrel is indeed dry and that it does not have standing water above the valve. If it has water then the utilities company gets a work request from us to get it fixed before winter hits.

  13. #13
    Forum Member

    Join Date
    Nov 2009
    Location
    Somewhere in the southeast.
    Posts
    1,072

    Default

    Quote Originally Posted by GTRider245 View Post
    Neither of my departments do testing. Waste of time IMO.
    Why, wouldn't you rather know if you're hooking up to a 1000 to 1500+GPM hydrant compared to a 999GPM or lower hydrant?

    Perhaps where you are at that isn't an issue, but a lot of cities have orange top and red top hydrants still. I remember one hydrant, which utilities finally took out, that wouldn't even register a 0 on the pitot. Had we not tested it and assumed it was a good hydrant where would we have been if the apartment building next to it caught fire? Fortunately there were two blue tops just down from the complex that were maybe a 200 and 300 foot supply stretch respectively.

    Not saying your wrong, as you stated it's your opinion, just curious as to your reasoning brother.

  14. #14
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,689

    Default

    Water department flows them twice a year. They get painted eventually. All markings of flow rate are now gone as they all get painted the same color.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  15. #15
    Forum Member

    Join Date
    Feb 2008
    Location
    Northeast
    Posts
    53

    Default

    So our Water Department is a Private company and they charge our department about 600K a year and for that they are supposed to test yearly. Well I for one live across the street form a hydrant and have never seen the Water company even check the hydrant. We went as far as a few years ago to tape the bottom of a Hydrant cap on a particular hydrant and for over 1 year the tape was never broken. We are instructed not to service a hydrant because we are not trained to do so and it is not our responsibility.

  16. #16
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,039

    Default

    For ten years we flowed the steamer , took readings both upstream and down stream , also opened a hydrant fully up stream and noted the drop in our flow. Very time consuming - the ISO inspector , picked out 5 plugs - used a hand held pitot and took a reading. thats it-
    Also I forgot -when you shut the plug down , hold your hand over a discharge and make sure the drains are working. -
    ?

  17. #17
    Forum Member

    Join Date
    Apr 2004
    Location
    Bossier Parrish, Louisiana
    Posts
    10,611

    Default

    Quote Originally Posted by Bones42 View Post
    Water department flows them twice a year. They get painted eventually. All markings of flow rate are now gone as they all get painted the same color.
    I can see not painting them if most if not all of the flows are very similiar, which was the case in the town served by my previous VFD.

    Unfortuanltly we have a very wide range of flow here - anywhere from 250-300 gpm up to 1800-1900. In addition the flows can vary greatly from street to street, so being able to identify the flow from the hydrazntg color is fairly significant peice of information.

    For example, if we see a red hydrant we'll likely not even lay from it and simply go immediattly into atanker shuttle operation as we can easliy double or triple that with a shuttle operation.
    Train to fight the fires you fight.

  18. #18
    Forum Member
    DeputyMarshal's Avatar
    Join Date
    Apr 2005
    Location
    Connecticut, USA
    Posts
    2,638

    Default

    Quote Originally Posted by slackjawedyokel View Post
    the ISO inspector , picked out 5 plugs - used a hand held pitot and took a reading. thats it-
    Apparently your ISO inspector was only interested in a poorly estimated average and not the actual flow capacity of any given hydrant.
    "Nemo Plus Voluptatis Quam Nos Habant"

    The Code is more what you'd call "guidelines" than actual rules.

  19. #19
    Forum Member

    Join Date
    Nov 2009
    Location
    Somewhere in the southeast.
    Posts
    1,072

    Default

    Quote Originally Posted by no1special View Post
    So our Water Department is a Private company and they charge our department about 600K a year and for that they are supposed to test yearly. Well I for one live across the street form a hydrant and have never seen the Water company even check the hydrant. We went as far as a few years ago to tape the bottom of a Hydrant cap on a particular hydrant and for over 1 year the tape was never broken. We are instructed not to service a hydrant because we are not trained to do so and it is not our responsibility.
    Not too sound condescending, but it sounds like your municipality/department is playing Russian Roulette with your hydrants. Better pray each time you go out on a fire that the hydrants are working properly. As for training, what training is involved? All you have to do is get the proper hydrant servicing and flow procedures and you're set. As far as repair goes though, that definitely shouldn't be your responsibility.

    I personnally would rather not rely on the word of someone that isn't going to be needing that hydrant to work as to whether it is in working condition or not, much less what they got for a flow on it. That's how our department viewed it anyway. There once was talk about shifting the responsibility of maintaining, flowing, and painting the hydrants to the utilities department, but the fire admin fought that tooth and nail. Sure, that would have been more time freed up for other training, but we'd rather be sure that the hydrant was done right and not just pencil wipped.

  20. #20
    Forum Member

    Join Date
    Apr 2009
    Location
    KY USA
    Posts
    6

    Default winterization

    In early spring we flow all of the hydrant (93) and get our readings. contact the local county jail and have the inmates paint any hydrant that needs to be repainted because of flow changes or just needs an all new paint job (the county jailer is also a fire chief). (we sit right between the main resivoir for the area and a pump house for our city to the north plus have high pressure main [46 in] that goes 2 counties over so water pressure is not constant). in the fall (mid to late October) will flow again. will not paint till next summer. As soon as the from the water distric tells us they are done flowing the second time the next day we go out and pump out any standing water and check till there is no water in any of the hydrants. Our freeze came very early last year and most of the local fd did not get a chance to winterize. a mutual aid fd had a fire and had to pull water some 5 to 6 block away because of frozen hydrants (it emptied out almost 6 fds). so needless to say as soon as the WD is done we winterize now. while we are doing our maintence we will not cut obstructions but take a picture show it to the AC and he tells us he sent a letter telling them to cut back.

  21. #21
    Forum Member
    JayDudley's Avatar
    Join Date
    Jan 2006
    Location
    Idaho
    Posts
    1,272

    Default Hydrants

    Our crews go out and test,flow,clean,lube and mark all of the hydrants in our Fire District. Results are printed up and presented to the respective Water Departments for repairs.
    Respectfully,
    Jay Dudley
    Retired Fire
    Background Investigator
    IACOJ-Member
    Lifetime Member CSFA
    IAFF Alumni Member

  22. #22
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    The water and sewer division of the City's Department of Public Works flow tests, flushes and maintaons the City's 1500+ fire hydrants.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  23. #23
    Forum Member

    Join Date
    Dec 2006
    Posts
    477

    Default

    Hydrants owned by the water authority, which the town rents. One or twice a year the hydrants are flowed- to flush sediment out of the mains. They don't test, and we're not allowed to. Probably costs us an ISO grade according to the chief.

    Ive actually heard of some towns where the authority that owns the hydrants doesn't even call them "fire hydrants." They're "water main flushing devices."

  24. #24
    MembersZone Subscriber
    Dickey's Avatar
    Join Date
    Feb 2000
    Location
    Wisconsin
    Posts
    5,111

    Default

    Quote Originally Posted by GTRider245 View Post
    Pull caps, grease them. Operate the stem and let water run for a little while. Replace caps. Paint, sticker and weedeat as needed.
    Our water department takes care of this. They let us know if there are any problems or hydrants out of service.
    Jason Knecht
    Assistant Chief
    Altoona Fire Dept.
    Altoona, WI

    IACOJ - Director of Cheese and Whine
    http://www.cheddarvision.tv/
    EAT CHEESE OR DIE!!

  25. #25
    Forum Member

    Join Date
    Feb 2008
    Location
    Northeast
    Posts
    53

    Default

    Quote Originally Posted by firefightinirish217 View Post
    Not too sound condescending, but it sounds like your municipality/department is playing Russian Roulette with your hydrants. Better pray each time you go out on a fire that the hydrants are working properly. As for training, what training is involved? All you have to do is get the proper hydrant servicing and flow procedures and you're set. As far as repair goes though, that definitely shouldn't be your responsibility.

    I personnally would rather not rely on the word of someone that isn't going to be needing that hydrant to work as to whether it is in working condition or not, much less what they got for a flow on it. That's how our department viewed it anyway. There once was talk about shifting the responsibility of maintaining, flowing, and painting the hydrants to the utilities department, but the fire admin fought that tooth and nail. Sure, that would have been more time freed up for other training, but we'd rather be sure that the hydrant was done right and not just pencil wipped.

    No offense taken. We are serviced by a great hydrant system most if not all hydrants have static pressures of 100-110 PSI with volumes that are just as good.(Dead end hydrants usually can flow estimated gpm of 600 or better. and when we drill we open hydrant at whatever the location of the drill is. We also require the Chaueffer to operate any hydrant they pull up to regardless of whether it will be used or not. I agree that there is no "training" to turn on and check a hydrant for obstructions and operation but as for testing we receive a report from the Water company yearly on hydrants they "tested". We also receive yearly reports on hydrants in need of drain issues or known issues. But we also forward our list of deficient hydrants or issues to the Water company and they usually get to it quickly you know like in a year or 2. I personally think it is a lot to pay for a what I think is a fudged report and the ability to flow any hydrant at any time.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Replies: 23
    Last Post: 08-06-2006, 02:25 PM
  2. Fire Hydrant Maintenance
    By Co11FireGal in forum Firefighters Forum
    Replies: 20
    Last Post: 02-11-2005, 11:25 PM
  3. Hydrant Maintenance
    By mcarter1023 in forum Firefighters Forum
    Replies: 24
    Last Post: 02-14-2004, 04:01 PM
  4. Finding ISO Department Data
    By 640SATFD in forum Apparatus Innovation
    Replies: 12
    Last Post: 03-11-2003, 12:05 AM
  5. Civilian Fire Fatalities
    By DCFF in forum Firefighters Forum
    Replies: 38
    Last Post: 02-08-2002, 08:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register