Just looking for some rough estimates for GPM in the following situations:
1- 1 3/4" line, 200' long, w/ standard combi tip @ 125psi = ? gpm
1- 2 1/2" line, 150' long, w/ 1" straight bore tip @ 70psi = ? gpm
1- truck mounted deck gun w/ 3" plumbing and 1 1/4" straight tip @ 100psi = ? gpm
+ Reply to Thread
Results 1 to 6 of 6
Thread: GPM estimates
-
01-11-2012, 02:59 PM #1Forum Member
- Join Date
- Apr 2010
- Posts
- 22
GPM estimates
-
01-11-2012, 03:30 PM #2Forum Member
- Join Date
- Jul 1999
- Location
- Rural Wisconsin, work in the burbs of Milwaukee
- Posts
- 8,120
Last edited by FyredUp; 01-12-2012 at 02:07 PM.
“The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia
This place gets weirder and weirder every day...
-
01-11-2012, 03:58 PM #3
Last edited by CaptOldTimer; 01-11-2012 at 04:00 PM.
Stay Safe and Well Out There....
Always remembering 9-11-2001 and 343+ Brothers
-
01-11-2012, 08:12 PM #4MembersZone Subscriber
- Join Date
- May 2000
- Location
- SW MO
- Posts
- 4,244
Are the PSI's nozzle pressure, PDP, or what?
As far as your straight streams, that's what that 29.7 x D(squared) x √NP formula is for
Fogs it's going to depend on what the setting is.
Most of your hydraulics books will have the formulas you need.
-
01-12-2012, 11:29 PM #5MembersZone Subscriber
- Join Date
- Jan 2007
- Location
- Pa Wilds
- Posts
- 530
3260e: Assuming that your psi numbers refer to engine pressure, then the following answers will be valid.
1. With an automatic (TFT) nozzle or an Akron Turbojet set at 95 gpm your engine pressure of 125 psi supplying a 200 ft. preconnect of 1 3/4" hose will deliver 95 gpm. This is an inadequate flow to meet the NFPA suggested minimum flow of 150 gpm for structure fires. This line needs to be pumped at 165 psi with an automatic, a 150 gpm nozzle, or a 3/4" solid stream tip (88 psi nozzle pressure)
2. The 150 ft. of 2 1/2" supplied at 70 psi of engine pressure with a 1" SS nozzle will deliver around 214 gpm with a friction loss of 17 psi and a nozzle pressure of 52 psi.
3. Depending upon plumbing and elbows (2) and a straight run of 10 feet of 3" the prepiped nozzle with a 1 1/2" tip should deliver 600+ gpm at an engine pressure of 100 psi.
-
01-27-2012, 10:35 AM #6Forum Member
- Join Date
- May 2001
- Location
- Greensboro, NC USA
- Posts
- 1,265
The combination nozzle is dependant of what pressure/flow it was designed for, and this varies greatly between all the brands and models.
The 1" tip at 70 psi is 250 GPM, most people flow it at 50 psi producing 200 GPM. With a solid bore nozzle, if you want more GPM, then get a bigger tip and keep the nozzle pressure at 50, a 1⅛" tip @ 50 has less nozzle reaction force than a 1" @ 70. They flow the same GPM, but the bigger tips allows the water to move slower, lowering the reaction force.
The formula for a solid bore tip is Diameter (squared) x 29.71 x square root of nozzle pressure
GPM=D² x 29.71 x √NP
The 1¼ @ 100 psi flows 464 GPM.
Here's a link to Elkhart's technical section from their catalog. It's full of good information on general hydraulics.Last edited by txgp17; 01-27-2012 at 10:37 AM.
The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Water supply estimates for rural suppression
By 7Stones in forum Firefighters ForumReplies: 31Last Post: 04-09-2011, 01:32 PM

LinkBack URL
About LinkBacks