    Has anyone actually tested the two methods out. I agree a relay with a boosting pumper at the hydrant would have greatly assisted this operation. I feel that had a significant impact on the supplying pumper as well. I still feel the 2 discharges would be a great benefit to the aerial than the one. I am impressed with the interest and the knowledge being shared. Still looking for a definative answer though. I don't have the ablity to test the flow on another station's truck and I am not sure they want to test their own...just saying.


  2. #22
    Forum Member FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    9,680

    Default

    You can test the flow without using an aerial. Set up this test a deluge gun with whatever size tip you use on the aerial. Lay out the hose as you would to supply the aerial and feed the deluge that way. Use 2 - 2 1/2's into the five and then the 5 into the gun. Then set it up with the 5 with an adapter to the discharge and see which one works better. Use a pitot gauge to check the deluge guns nozzle pressure for accuracy.

    The friction loss up the ladderand through the ladder pipe or mounted nozzle will be the same regardless of what system you use to feed aerial. What your concern is, if I am reading you correctly is which hose methode would more efficiently move the water. Frankly, unless the difference is massive, say, 30 pound or more, the speed of hoking up the single 5 inch would still make it more viable to me.

    Remember to hook the 5 inch to the discharge that comes straight off the pump for the most efficiency.
    “The person who risks nothing, does nothing, has nothing, is nothing, and becomes nothing. He may avoid suffering and sorrow, but he simply cannot learn and feel and change and grow and love and live.” Leo F. Buscaglia

    This place gets weirder and weirder every day...

  3. #23
    Forum Member
    Join Date
    Nov 2007
    Posts
    554

    Default

    Quote Originally Posted by mebmikec View Post
    goodmorning, I may not have been clear on the original post. My theory was 2 lines (2.5in. coming off 2 2.5in. discharges), length at most 100ft. of hose going straight into aerial pump via a 2.5in. to 5in. siamese. I feel that the short length would require less than 100psi at the pump to supply aerial at least 1,000GPM. The original connection was a single 2.5in. discharge with an adapter into a 100ft. section of 5in. straight into the aerial's master intake. I am glad that others are sharing similar opinions, ideas and options. With that said, I am learning the original hook up wasn't as bad as I had previously thought. Thanks.
    So, no 5" at all. Two 100' lengths of 2-1/2"?

    I would suggest 3" coupled 2-1/2". The difference in friction loss vs. 2-1/2" will take a load off the engine. Still, the 5" coupling directly on a main pump manifold discharge and the 5" hose will be most efficient hydraulically. Operationally, it all comes down to what is fastest, easiest and safest with what you have to work with.

  4. #24
    MembersZone Subscriber
    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,776

    Default

    Just to be able to show the work so to speak, what is at the tip of the aerial and at what elevation? Or better yet, the known psi at the base of the aerial to accomplish the goal GPM? (done through testing your aerial)

    If we're using the same pumper and aren't able to factor the individual discharge piping as Kuh Shise noted, then it appears the question is:

    which is better: (2) 100 ft. 2.5" lines supplying the aerial or (1) 5" LDH at 100 ft? The difference being the single 2.5" discharge into the 5" vs. two 2.5 discharges into 100 ft. of 2.5" hose then into a siamese 2.5" to 5" intake on the aerial?

  5. #25
    MembersZone Subscriber
    Join Date
    Jan 2007
    Location
    Pa Wilds
    Posts
    566

    Default

    mebmikec: 100 ft. of 2 1/2 at 500 gpm has a loss of around 62 psi per 100 ft. From experience (35 yrs teaching pumps at the local level in Pa.) most 2 1/2" discharges have about 20 psi loss at 500 gpm (full flow 2 1/2" valves). So the dual 2 1/2" hook-up to the aerial should require the following... 20 psi in the pump house + 62 psi hose loss + 20 psi residual at the aerial = 102 psi engine pressure. Using a single outlet adapted to 100 ft. of 5" needs... 80 psi in the pump house (Fl varies with the square of the flow .. so doubling the flow to 1,000 gpm out a single discharge raises the pump house loss by 4X) + 6 psi hose loss + 20 psi residual = 106 psi engine pressure. Not much difference. However, if the valve was a 2 1/2 with a 2" waterway the losses in the pump house would rise to about 200 psi using a single valve. Hazen Williams formula had the pipe diameter in the bottom of the formula. It varies with the diameter to the 4.87 power (almost 5th) 2 to the 5th = 32 while 2.5 to the 5th is 93 or about 3 times more loss using the smaller waterway.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Calculating Aerial Discharge
    By rfdffemtmpo in forum The Engineer
    Replies: 6
    Last Post: 07-16-2009, 11:18 AM
  2. Supplying sprinkler systems
    By GreenJT in forum Firefighters Forum
    Replies: 16
    Last Post: 05-08-2006, 11:20 PM
  3. 2.5 inch discharge
    By Eng47ine in forum The Engineer
    Replies: 11
    Last Post: 06-02-2004, 09:59 AM
  4. quint vs. engine vs. aerial
    By bhumphreys in forum Apparatus Innovation
    Replies: 0
    Last Post: 04-06-2004, 05:12 PM
  5. Supplying the 1st in Engine
    By airems in forum The Engineer
    Replies: 10
    Last Post: 09-15-2001, 04:47 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts