    Default Occupancy Load Signs in Bowling Alleys

    Hey everyone,

    I am a fire inspector in Ohio & was wondering if occupancy load signs are required for bowling alleys. If anyone has seen other bowling alley centers with occupancy load signs, please let me know. The owner says that he has not seen any signs in other bowling alleys. If anyone knows more about this, please get back to me asap. Thanks & be safe, and appreciate you taking the time to help out.

  2. #2
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,909

    Default

    does your city have a building code or fie code adopted?? If so what and and which edition??

    Yes they are required

    a bowling alley is considered a place of assembly

    from 2009 ibc


    1004.3 Posting of occupant load. Every room or space that is an assembly occupancy shall have the occupant load of the room or space posted in a conspicuous place, near the main exit or exit access doorway from the room or space. Posted signs shall be of an approved legible permanent design and shall be maintained by the owner or authorized agent.


    same as in 2009 IFC

    1004.3 Posting of occupant load. Every room or space that is an assembly occupancy shall have the occupant load of the room or space posted in a conspicuous place, near the main exit or exit access doorway from the room or space. Posted signs shall be of an approved legible permanent design and shall be maintained by the owner or authorized agent.


    Do you have a building official in your town?? If so the BO can help you

  3. #3
    MembersZone Subscriber

    Join Date
    Jul 2006
    Posts
    2

    Default

    Yes, 2011 ohio fire code... ok, thanks for the info & advice !

  4. #4
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,909

    Default

    http://publicecodes.cyberregs.com/st...011-000004.htm


    http://publicecodes.cyberregs.com/st...-P-2011-000004



    (3) 1004.3 Posting of occupant load.


    Every room or space that is an assembly occupancy shall have the occupant load of the room or space posted in a conspicuous place, near the main exit or exit access doorway from the room or space. Posted signs shall be of an approved legible permanent design and shall be maintained by the owner or authorized agent.
    Last edited by fire49; 04-06-2014 at 10:46 PM.

  5. #5
    Forum Member
    FWDbuff's Avatar
    Join Date
    Jul 2003
    Location
    Pee-Ayy!
    Posts
    7,412

    Default

    Being a bowling alley has nothing to do with it.

    "Bowling Alley" is specifically mentioned in both the IFC and the IBC. It's not a bowling alley- it's an A-3 and yes, it's required to have the loads posted.
    "Loyalty Above all Else. Except Honor."

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Room Occupancy Formula?
    By Keenque in forum Firefighters Forum
    Replies: 9
    Last Post: 02-15-2011, 02:56 PM
  2. Fire Station Occupancy Level
    By kd5smn in forum Federal FIRE ACT Grants & Funding
    Replies: 2
    Last Post: 03-17-2008, 06:34 PM
  3. Replies: 8
    Last Post: 01-27-2004, 03:50 PM
  4. Commercial Occupancy Firefighting SOP's
    By engine4capt in forum Fireground Tactics
    Replies: 4
    Last Post: 08-06-2003, 09:03 AM
  5. Flat load vs. accordian hose load
    By theotilus in forum Firefighters Forum
    Replies: 21
    Last Post: 07-30-2003, 11:03 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register