    I'm helping to instruct a local FFII course and the question of why it's necessary to walk on the left of the hose line while the hose is under service test pressure has come up.

    More interesting to me is that a read-through of the current version of NFPA 1962 shows that this requirement to walk the hose line 15 feet to the left only exists when using a hose testing machine and not when using fire apparatus as a pressure source.

    The relevant sections of NFPA 1962: 4.8.5.2.14.1 for use of a hose testing machine, and 4.8.6.13.1 for use of a stationary pump or fire department apparatus. The latter states that the inspection of couplings can be made from 15 feet away on either side of the hose line.

    The only explanation I can begin to come up with is that the threading on the couplings may cause the hose to flail to the right in the case of a failure, but this doesn't make much sense to me. It also doesn't account for why this does not apply to testing using fire apparatus.

    Thanks!

  2. #2
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,952

    Default

    I think it has been analyzed before maybe to a search

  3. #3

  4. #4
    Forum Member

    Join Date
    May 2013
    Posts
    971

    Default

    I can only guess that it's because test pressure is higher than usual operating pressure.

    Also, when actually operating, you're much less likely to have the option of which side to be on or how far away you can be.

    It's not about the threads on the couplings. (Probably the last thing that will fail.) It's about the way the hose itself is made and possibly how water moves through hose.

    We have always tested hose with apparatus and the instruction to stand to left has been on the books forever.
    Last edited by captnjak; 05-28-2014 at 01:09 PM.

  5. #5
    Forum Member

    Join Date
    Nov 2002
    Posts
    1,232

    Default

    We have gate valves used specifically for testing. They have a small hole drilled in the gate, so the "left side" rule is moot. if a hose fails, it's not going anyway because it will lose pressure immediately.
    HBofCJ likes this.

  6. #6
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,085

    Default

    Quote Originally Posted by johnsb View Post
    We have gate valves used specifically for testing. They have a small hole drilled in the gate, so the "left side" rule is moot. if a hose fails, it's not going anyway because it will lose pressure immediately.
    we just gate em down
    HBofCJ likes this.
    ?

  7. #7
    Forum Member

    Join Date
    Nov 2002
    Posts
    1,232

    Default

    Quote Originally Posted by slackjawedyokel View Post
    we just gate em down

    That works too, ours are just older valves that are spares so they usually have one or two per battalion.
    HBofCJ likes this.

  8. #8
    Forum Member
    FFWALT's Avatar
    Join Date
    Jul 2000
    Location
    Nebraska
    Posts
    368

    Default

    Our department has 2 hose testers and both have built in valves that operate on the same concept as the gate valve with a hole in it. When a coupling fails, and I have witnessed this, the hose doesn't go anywhere. The coupling goes out 10' or so, the hose deflates where it was laying and the only movement appears to be as it shrinks back to the unpressurized position because the valves do not allow for a significant flow that would whip the hose around.

    Walt.
    Last edited by FFWALT; 06-08-2014 at 12:18 AM. Reason: Completing the thought.
    HBofCJ likes this.
    Train like you want to fight.
    www.kvfd.net

  9. #9
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    103

    Default

    Quote Originally Posted by slackjawedyokel View Post
    we just gate em down
    And the parts departments from the valve and pump manufacturers thank you.
    BoxAlarm187 likes this.
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

  10. #10
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,085

    Default

    Quote Originally Posted by Johngagemn View Post
    And the parts departments from the valve and pump manufacturers thank you.
    explain please
    ?

  11. #11
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,701

    Default

    Um, is it the left of the hose when facing the "pump" end or left of the hose when facing away from the "pump" end?
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  12. #12
    Forum Member

    Join Date
    Nov 2009
    Posts
    3,952

    Default

    Just walk on the wild side

    http://m.youtube.com/watch?v=0KaWSOlASWc

  13. #13
    Forum Member

    Join Date
    Sep 2008
    Location
    SW Oregon
    Posts
    73

    Default

    Excellent answers all and thank you. About the same one here. We cracked the attached nozzle, then worked up to the required pressure, but flowing very little volume, then beened down. This also helped the pump cooler which sometimes did not work. Seemed to work. We had to do the 5 minute overpressure test back then. We used an old engine.

    That was when we were even more careful and tried to stand well clear of all the hose lines. This was about in 1972, so again, you get an idea of safe progress since then. All done in 2 hot weeks. I can not think of any compelling reason why such a technique would strain or damage a gate valve. We had a little flow going. What am I missing here?

    HB of CJ (old coot) Retarded Engineer. Long ago and far away. Who woulda' thunked it? ISO Class 1 back then.

  14. #14
    Forum Member

    Join Date
    May 2013
    Posts
    971

    Default

    We also do it at height of summer. I wonder why. And who came up with it? A guy who never had to do it?

  15. #15
    MembersZone Subscriber

    Join Date
    Apr 2009
    Location
    SW Missouri
    Posts
    1,156

    Default

    Quote Originally Posted by captnjak View Post
    We also do it at height of summer. I wonder why. And who came up with it? A guy who never had to do it?
    You're not alone brother.

  16. #16
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,280

    Default

    Quote Originally Posted by captnjak View Post
    We also do it at height of summer. I wonder why. And who came up with it? A guy who never had to do it?
    My career FD always did it in July and August. This despite us requesting to do it in the early spring.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  17. #17
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,701

    Default

    Ours was cancelled a year or so ago due to it being too cold out.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  18. #18
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    103

    Default

    Quote Originally Posted by slackjawedyokel View Post
    explain please
    Too may things to go wrong. Also, running valves throttled down that far is a good way to torch the seals if something starts to flow. Running the pump at enough pressure to test hose you need to flow a MINIMUM of 100 to 150 GPM to avoid overheat and especially recirculation cavitation damage (much worse in single stage pumps). You can buy a whole fleet of hose testing pumps for what it will cost you in the life shortening of your fire pump that happens when you hose test. Fire pumps aren't made to deadhead high pressure. They are made to move water.
    BoxAlarm187 likes this.
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

  19. #19
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,085

    Default

    Quote Originally Posted by Johngagemn View Post
    Too may things to go wrong. Also, running valves throttled down that far is a good way to torch the seals if something starts to flow. Running the pump at enough pressure to test hose you need to flow a MINIMUM of 100 to 150 GPM to avoid overheat and especially recirculation cavitation damage (much worse in single stage pumps). You can buy a whole fleet of hose testing pumps for what it will cost you in the life shortening of your fire pump that happens when you hose test. Fire pumps aren't made to deadhead high pressure. They are made to move water.
    I guess I still don't understand -- when hose testing we hook to a hydrant bring the hose up to pressure, gate the discharges, I open the tank fill about 1/4 let the tank just overflow, lay a hand on the steamer and make sure the pumps still cool. been doing it that way for years, with no problems.
    ?

  20. #20
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    103

    Default

    At 300+ psi you can and will cook the ball and seals on your tank fill valve that way. Throttling a vale under that kind of pressure while flowing causes things like this:
    Name:  Scorched Valve.jpg
Views: 128
Size:  9.6 KB

    Simply put, you are using the pump and associated systems on your truck in a manner they were never designed to be used. When do you ever pump a pressure that high and then gate a valve back so far?

    Certainly excusable to do if necessary if you are in a life hazard situation as people come before equipment. Doing it for the purpose of testing hose is being unnecessarily harsh on your equipment for absolutely no good reason. There are tools specifically designed for that task that present much less danger to the personnel involved in the testing and no risk to expensive equipment.
    Last edited by Johngagemn; 08-06-2014 at 03:55 PM.
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

  21. #21
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,085

    Default

    to be clear , I fill the hoses at a moderate pressure ((roughly 50 psi) bleed the air, gate the valves down to a "trickle" lock em, then pressure up. I don't try and gate em down against high pressure. I guess I have just been lucky.
    ?

  22. #22
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    103

    Default

    You have. Lots of people get lucky. How long do you want to press your luck is the question.

    What happens when someone forgets to throttle one of those discharge valves and a line bursts while someone is walking it? What if you weren't moving enough water and the pump was overheating badly? You have someone who winds up with a broken leg or worse, and/or someone who gets scalded badly by boiling water. You can say "it won't happen because I'm careful" all you want. Lots of others who have been hurt on the job for no good reason have said the same thing.

    The question you should be asking yourself is this: why would you intentionally put your firefighters at risk and abuse your equipment that way?
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

  23. #23
    Forum Member

    Join Date
    Mar 2003
    Posts
    2,085

    Default

    Quote Originally Posted by Johngagemn View Post
    You have. Lots of people get lucky. How long do you want to press your luck is the question.

    What happens when someone forgets to throttle one of those discharge valves and a line bursts while someone is walking it? What if you weren't moving enough water and the pump was overheating badly? You have someone who winds up with a broken leg or worse, and/or someone who gets scalded badly by boiling water. You can say "it won't happen because I'm careful" all you want. Lots of others who have been hurt on the job for no good reason have said the same thing.

    The question you should be asking yourself is this: why would you intentionally put your firefighters at risk and abuse your equipment that way?
    I have asked the question , the answer is we have more pressing needs which not having can also put the men in a dangerous situation , in a perfect world our underfunded department would either A purchase a hose testing machine or B sub it out. Hose testing is a some what controlled situation as opposed to an emergency response, you are right there is a chance someone will forget to gate the valve down, but it is slim as we gate the valve down and crack the nozzle again to check, even with the valves gated down we check for "creep" from a distance. As far as the pump boiling , the operator never leaves the pump panel and almost constantly keeps his hand on the steamer to check for heat build up.
    ?

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Hose Testing
    By kdwilson in forum The Off Duty Forums
    Replies: 22
    Last Post: 06-06-2008, 07:21 PM
  2. Hose Testing
    By vortek222 in forum Firefighters Forum
    Replies: 8
    Last Post: 12-25-2007, 12:04 PM
  3. Hose testing
    By RFDACM02 in forum Firefighters Forum
    Replies: 15
    Last Post: 12-02-2006, 09:58 AM
  4. Hose testing
    By Muttly92094 in forum Firefighters Forum
    Replies: 18
    Last Post: 12-30-2005, 04:38 PM
  5. Hose and Hose Testing Machine?
    By sdff1520 in forum Federal FIRE ACT Grants & Funding
    Replies: 11
    Last Post: 03-30-2005, 12:59 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register