    Default Front vs Side intakes

    Just a quick question from a new pump operator.

    What is everyones opinion on using the front vs the side intake when working off a hydrant?

    I had to spend alot of time practicing nosing hydrants as part of my drivers training. Alot of PO's in my department live and die by it. I'm not totally against it but to me it seems like you would lose flow because of all the bends made by the pipe just to reach the pump. Now, we run 4" LDH and we keep a 25ft section in the officer side front compartment and to me, it would be just as easy to get close to the hydrant, hook up the 4" and be done with it. Plus I would think that you wouldnt lose any extra flow because of not having any bends in the hose.

    Has anyone done their own tests to see which one yields the best result? And if so, how did you perform the test? Any info would be greatly appreciated.

    Thanks in advance,
    Kevin

  2. #2
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,280

    Default

    The side intakes offer a straight shot into the pump, more water/less friction loss. Front suctions have numerous elbows, both 45 and 90 degree that adds friction loss and costs you water. You can generally expect a 20 to 30% loss in flow with a front suction. A rear suction is better than a front suction.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  3. #3
    Let's talk fire trucks!
    BoxAlarm187's Avatar
    Join Date
    Jan 2003
    Location
    Virginia
    Posts
    3,348

    Default

    We haven't run front intakes since we rid ourselves of our 1985 ALF's in 2001. Since that time, we've exclusively used our side intakes and had great success with them.

    Why don't we continue to buy them? 40% capacity loss in the pump, the added weight, and the added cost.
    Career Fire Captain
    Volunteer Chief Officer


    Never taking for granted that I'm privileged enough to have the greatest job in the world!

  4. #4
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,701

    Default

    We have fronts on our engines and use them fairly often. Little bit of time spent w engineering and planning can reduce your the losses due to bends. Front suctions can be run by hose that gives much smoother bends than traditional piping. Still not as good flow as the sides, but you can get awfully close. All comes down to your needs. I have waterfront drafting locations that I can't pull my truck sideways so we need to use the front.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  5. #5
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,908

    Default

    When it comes to the ease of aligning the hydrant and the intake, the front or rear is far easier as you can use all the room you need to position the line, with the side intake the hose always seems to be too long or too short.

  6. #6
    MembersZone Subscriber

    Join Date
    Jul 2003
    Location
    Somewhere, USA
    Posts
    15

    Default

    Basically, if you have positioning issues - front intakes make it easier (but you lose capacity to the pump). If you need full capacity of the pump, side intake is the only way to go. It's a trade off. Training your drivers to properly position for a side intake takes time but is worth the effort as far as water capacity goes. Front intakes are great for a quick and easy connection, or for the lazy drivers or those who just can't seem to grasp side intake positioning.

    Need water for a big fire? Side intake.
    Need ease of connection? Front intake.

  7. #7
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,280

    Default

    Hooking to a hydrant using a side intake is a piece of cake. We carry 25 and 50 foot sections of 5 inch LDH for hydrant hook ups. Judge which one you need and make the connection, if one isn't enough add the other. Frankly, I have never found where the 50 wouldn't reach, most often the 25 works.

    If we lay in we most often go in the rear intake.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  8. #8
    Forum Member

    Join Date
    Nov 2002
    Posts
    1,232

    Default

    Quote Originally Posted by FyredUp View Post
    Hooking to a hydrant using a side intake is a piece of cake. We carry 25 and 50 foot sections of 5 inch LDH for hydrant hook ups. Judge which one you need and make the connection, if one isn't enough add the other. Frankly, I have never found where the 50 wouldn't reach, most often the 25 works.

    If we lay in we most often go in the rear intake.
    We also have the short sections that we carry in wells at the bottom of the pump panels. They make life much easier. None of the dept's I've been on have ever had a rear intake, but that would be better that a front intake on a city dept. My rural POC dept has front intakes because of drafting, my fulltime dept. quit orderig them about 20 years ago.

  9. #9
    Forum Member
    MemphisE34a's Avatar
    Join Date
    Jan 2004
    Location
    Memphis, TN - USA
    Posts
    2,531

    Default

    If you have a good water system, you evidently don't have to worry about it.

    We have 56 engines in service with front intakes and there has never been a problem of not having enough water - even on the big ones.
    RK
    cell #901-494-9437

    Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.

    "Everyone goes home" is the mantra for the pussification of the modern, American fire service.


    Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.

  10. #10
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,280

    Default

    Quote Originally Posted by MemphisE34a View Post
    If you have a good water system, you evidently don't have to worry about it.

    We have 56 engines in service with front intakes and there has never been a problem of not having enough water - even on the big ones.
    That may be true but you will never get as much water as through a side intake.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  11. #11
    Forum Member
    MemphisE34a's Avatar
    Join Date
    Jan 2004
    Location
    Memphis, TN - USA
    Posts
    2,531

    Default

    Quote Originally Posted by FyredUp View Post
    That may be true but you will never get as much water as through a side intake.
    Truthfully, that depends on the capacity of the hydrant, but I get your point.
    RK
    cell #901-494-9437

    Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.

    "Everyone goes home" is the mantra for the pussification of the modern, American fire service.


    Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.

  12. #12
    Forum Member

    Join Date
    Apr 2004
    Location
    Bossier Parrish, Louisiana
    Posts
    10,676

    Default

    Quote Originally Posted by Tower9Truckie View Post
    Basically, if you have positioning issues - front intakes make it easier (but you lose capacity to the pump). If you need full capacity of the pump, side intake is the only way to go. It's a trade off. Training your drivers to properly position for a side intake takes time but is worth the effort as far as water capacity goes. Front intakes are great for a quick and easy connection, or for the lazy drivers or those who just can't seem to grasp side intake positioning.

    Need water for a big fire? Side intake.
    Need ease of connection? Front intake.
    Simple solution .... Gate the 2.5" outlets before opening the hydrant and add 2.5" or 3" into your auxiliary suction(s) after you have water flowing.

    It's always good practice to do that, even if you are flowing into the side of the apparatus.

    And then you can flow big water.
    Johngagemn likes this.
    Train to fight the fires you fight.

  13. #13
    Forum Member

    Join Date
    Nov 2007
    Posts
    630

    Default

    Quote Originally Posted by LaFireEducator View Post
    Simple solution .... Gate the 2.5" outlets before opening the hydrant and add 2.5" or 3" into your auxiliary suction(s) after you have water flowing.

    It's always good practice to do that, even if you are flowing into the side of the apparatus.

    And then you can flow big water.
    Is having three connections to the hydrant actually simpler than one?

  14. #14
    Forum Member

    Join Date
    Nov 2007
    Posts
    630

    Default

    Quote Originally Posted by MemphisE34a View Post
    Truthfully, that depends on the capacity of the hydrant, but I get your point.

    Sounds like you have had to work with 4 inch mains.

  15. #15
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,280

    Default

    Quote Originally Posted by LaFireEducator View Post
    Simple solution .... Gate the 2.5" outlets before opening the hydrant and add 2.5" or 3" into your auxiliary suction(s) after you have water flowing.

    It's always good practice to do that, even if you are flowing into the side of the apparatus.

    And then you can flow big water.
    If it is a good hydrant hook another 5 inch to one of the 2 1/2 inch hydrant outlets and hook that into another steamer connection on your engine. More than likely it will give you all the water left in the hydrant with a whole lot less messing around.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  16. #16
    Forum Member
    Johngagemn's Avatar
    Join Date
    Jun 2004
    Location
    Woodbury, MN
    Posts
    103

    Default

    Quote Originally Posted by firepundit View Post
    Is having three connections to the hydrant actually simpler than one?
    It sure is when you start collapsing that first supply line down and don't want to have to kill the hydrant to get a second one. BTDT, it's not fun. Takes 5 seconds to properly dress a hydrant with a second outlet gate valve before you open it up. You train that way it becomes second nature. Saved my bacon a few times having that available.
    Just a guy...

    Lieutenant - Woodbury, MN FD (Retired)
    Road Captain - Red Knights MC, MN4

    Disclaimer: The facts and opinions expressed above are mine, and mine alone, and are not intended to represent the views of any company I have ever worked for, past or present.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Rescue Tools on Front, Side, or Rear?
    By rmoore in forum University of Extrication
    Replies: 7
    Last Post: 12-03-2010, 01:18 AM
  2. Replies: 30
    Last Post: 08-07-2010, 03:29 AM
  3. Right Side, Left Side, Wrong Side Driving
    By BryanLoader in forum The Off Duty Forums
    Replies: 0
    Last Post: 07-10-2003, 08:52 AM
  4. Front vs. Side Intake
    By TowerPower in forum Apparatus Innovation
    Replies: 25
    Last Post: 01-01-2002, 02:24 PM
  5. 5" INTAKES AND DISCHARGES
    By ffglenn in forum The Engineer
    Replies: 4
    Last Post: 07-26-2001, 08:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register