    If you really want to move "big water" hook two fives on your hydrant and feed both sides of your pump. You would be amazed on how much water you can get out of plug. Believe me, you will safely exceed the tested gpm of any hydrant. You are not "making water" or gaining pressure, you're just make the hole that the water flows through bigger.

    Yeah, I'd agree with the whole don't go crazy with putting too much pressure on 5". It tends to hurt people "very much badly" when it starts jumping around.
    Last edited by FDAIC485; 05-07-2007 at 06:58 PM.
    I believe them bones are me. Some say we are born into the grave. I feel so alone, gonna end up a big ol' pile a them bones

    -J. Cantrell

  2. #27
    Forum Member

    Join Date
    Apr 2006
    Posts
    228

    Default

    Quote Originally Posted by Tom65 View Post
    I work in a small Federal Government departmant in Eastern Oregon.
    I was talking to one of our new Capt.about changing from 3inch to 5 inch hose. He told me that the chief would not change to 5 inch because it is to heavy and our hydrents have to low pressure.
    what can I do to change there minds?
    You'll have much less friction loss with the 5" hoseline. I'm quite sure the main supplying the hydrant is not 3", so taking a 5" hose off the hydrant won't give you pressure problems. Always go with the 5" if you can....You can never have too much water. I wouldn't say carry one or the other though. We carry both in the bed. 500' of 5" and 750' of 3".

  3. #28
    MembersZone Subscriber
    mcaldwell's Avatar
    Join Date
    Apr 2003
    Location
    Panorama, British Columbia, Canada
    Posts
    3,022

    Default

    We too use 4" PRV's for our LDH, and they flow beautifully.

    We have the adapters to use the 2.5 intakes and discharges if desired, and they work well in training to supply our monitors at full pump capacity (1050 imperial pumps). We have not flow tested anything though to see if there is a measurable difference in the two supplies.

    Unless you are supplying a large pump over 1500 gpm, I would not expect to notice a large difference between 5 inch into a steamer vs 5 inch into a 3" intake. A short 3" intake is still capable of receiving 2000+ gpms of water with adequate pressure.
    Never argue with an Idiot. They drag you down to their level, and then beat you with experience!

    IACOJ

  4. #29
    Forum Member

    Join Date
    Jan 2007
    Posts
    1,063

    Default

    We have been using a butterfly valve on the intake side of the pump. In the past we were directed to take the butterfly valve off during drafting operations. This is a time consuming process that requires a rubber mallet and lots of foul language.

    Anyway all of our new engines are able to pull a draft through the butterfly valve, give it a try.

  5. #30
    Forum Member

    Join Date
    Oct 2005
    Posts
    1,154

    Default

    Standard supply LDH is 180psi operating, annual test to 200psi.

    There is "Attack" LDH that operates at higher pressure for feeding standpipes, possibly master streams in industrial situations.

    Normally through the PIV on the steamer when water supply is from a constant source -- hydrant or drafting. To the tank fill when it's a leader line from a tanker dump site.

  6. #31
    Forum Member

    Join Date
    Jan 2004
    Posts
    124

    Default

    We use the TFT Ball intake valves on our engines. You do not have to remove them to draft. We have used the piston intake valves in the Past. We recently purchased two TFT Jumbo intake valves. The TFT valves are finished off with 6" hose thread on the pump operator's side and finished off with 5" storz on the other side. Our normal operations call for the 5" supply line to be connected on the side away from the pump operator. If drafting we use the pump operators side. We also carry adapters to hook suction to the storz side and 5" to the drafting side.
    The TFT BIV will allow a draft of about 700 gpm to 800 gpm.
    The TFT Jumbo intake is supposed to allow over 1000gpm at draft, but we have not had a chance to test it.
    We are split, about half the time we are able to use hydrants, the other half we use tanker shuttles.
    The 5" hose makes the pump operators job alot easier for us. It allows for the full flow for almost all of our hydrants up to 1000' away. The 5" hose to me is not much worse to load than the canvas 2 1/2" we used to carry.

  7. #32
    Forum Member

    Join Date
    Nov 2006
    Location
    Cupcake NY
    Posts
    1,327

    Default

    All you have to do is ask HER!

  8. #33
    MembersZone Subscriber

    Join Date
    Sep 2000
    Location
    Westchester Co., NY USA
    Posts
    567

    Default

    Same concurrance here in regard to LDH. WE have utilized 5" for nearly 15 years now and it solved much of our supply problems experienced when using dual 2 1/2 or 3" lines. With the LDH you are basically taking the water main and laying it on top of the street. The one thing I can say however in regard to it not being fully charged with water is that you can run the risk of collapsing the hose and you must get all the air out as well. This is true with any supply hose, which is why I am not a fan of putting the LDH intake on the passenger side. I always keep my leg against the hose as I am charging lines and watching my residual, it has been my experience that I can feel the hose softening if a supply issue occurs...long before I will see it on the gauge or hear it in the RPM's.

    Tom 65...I feel for you. Some of those arguments as to why your Chief doesn't want to switch are invalid and IMO utterly ridiculous. It takes 6
    2 1/2" lines to equal a 5" line. Too heavy? Since when is that an argument for not getting something that works better? Are the irons too heavy? Is it better to lay 2 lines and pack that much hose then just the 1 LDH? Contact Angus and see if they can give you a copy of their Hi-Vol video. It has some good info in there. Thousands of departments can't be wrong. Sexless couplings eliminate the need for many adapters and so forth.

  9. #34
    55 Years & Still Rolling
    hwoods's Avatar
    Join Date
    Jun 2002
    Location
    Glenn Dale Md, Heart of the P.G. County Fire Belt....
    Posts
    10,740

    Lightbulb Well.................

    Time to hear from the Party Pooper....... We do not use anything larger than 3 inch for supply line, and have no interest in changing. Here's the scoop:

    Water Supply...... We have a largely outstanding water system, with only a few problem areas, which are being addressed.

    Apparatus....... About 6 or 7 of the approximately 90 Engines in the County carry LDH. One Station ( www.clintonvfd.org ) operates several Engines with 2,000+ GPM Pumps and large loads of 5 inch hose. they respond as the Water Supply Company on all 2nd Alarms County Wide.

    Operations...... Our SOPs are pretty tight on water supply, here's an example: Box Alarms get 4 Engines, 2 Trucks, (Ladders) and a Squad (Heavy Rescue) The first Engine drops a Supply line at the Hydrant nearest the Fire on his way in. (Dual lines for Heavy Smoke/Fire visable) 2nd Engine picks up the Hydrant and pumps the line to the First Engine. 3rd Engine drops a line at a different Hydrant, stretches in to the Building, 4th Engine picks up the 3rd Engine's line. We ALWAYS put an Engine on the Hydrant. ALWAYS.
    Never use Force! Get a Bigger Hammer.
    In memory of
    Chief Earle W. Woods, 1912 - 1997
    Asst. Chief John R. Woods Sr. 1937 - 2006

    IACOJ Budget Analyst

    I Refuse to be a Spectator. If I come to the Game, I'm Playing.

    www.gdvfd18.com

  10. #35
    Forum Member

    Join Date
    Dec 1999
    Location
    Swanton Fire Dept. Swanton, Vermont
    Posts
    479

    Default

    Quote Originally Posted by hwoods View Post
    Time to hear from the Party Pooper....... We do not use anything larger than 3 inch for supply line, and have no interest in changing. Here's the scoop:

    Water Supply...... We have a largely outstanding water system, with only a few problem areas, which are being addressed.

    Apparatus....... About 6 or 7 of the approximately 90 Engines in the County carry LDH. One Station ( www.clintonvfd.org ) operates several Engines with 2,000+ GPM Pumps and large loads of 5 inch hose. they respond as the Water Supply Company on all 2nd Alarms County Wide.

    Operations...... Our SOPs are pretty tight on water supply, here's an example: Box Alarms get 4 Engines, 2 Trucks, (Ladders) and a Squad (Heavy Rescue) The first Engine drops a Supply line at the Hydrant nearest the Fire on his way in. (Dual lines for Heavy Smoke/Fire visable) 2nd Engine picks up the Hydrant and pumps the line to the First Engine. 3rd Engine drops a line at a different Hydrant, stretches in to the Building, 4th Engine picks up the 3rd Engine's line. We ALWAYS put an Engine on the Hydrant. ALWAYS.
    It sounds like you are set for your situation. You also have the luxury of the number of pieces available to you and one company set up as your water supply for big jobs county wide.

    Most places are not as fortunate as you are with redundant 2 and 1 responses (2 engines and a ladder X 2).

    When I took over as Chief we did not have LDH. We needed it and now have used it for about 8 years now. Even the people who did not want it did not complain that they had a 5" line supplying them at the working fires they were running the attack engine at.

  11. #36
    Forum Member
    MemphisE34a's Avatar
    Join Date
    Jan 2004
    Location
    Memphis, TN - USA
    Posts
    2,531

    Default

    Quote Originally Posted by hwoods View Post
    Time to hear from the Party Pooper....... We do not use anything larger than 3 inch for supply line, and have no interest in changing. Here's the scoop:

    Water Supply...... We have a largely outstanding water system, with only a few problem areas, which are being addressed.

    Apparatus....... About 6 or 7 of the approximately 90 Engines in the County carry LDH. One Station ( www.clintonvfd.org ) operates several Engines with 2,000+ GPM Pumps and large loads of 5 inch hose. they respond as the Water Supply Company on all 2nd Alarms County Wide.

    Operations...... Our SOPs are pretty tight on water supply, here's an example: Box Alarms get 4 Engines, 2 Trucks, (Ladders) and a Squad (Heavy Rescue) The first Engine drops a Supply line at the Hydrant nearest the Fire on his way in. (Dual lines for Heavy Smoke/Fire visable) 2nd Engine picks up the Hydrant and pumps the line to the First Engine. 3rd Engine drops a line at a different Hydrant, stretches in to the Building, 4th Engine picks up the 3rd Engine's line. We ALWAYS put an Engine on the Hydrant. ALWAYS.
    Chief,

    Even so, you could still flow more water at lower pump discharge pressures if you made the change to 5" and used your same SOP.
    RK
    cell #901-494-9437

    Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.

    "Everyone goes home" is the mantra for the pussification of the modern, American fire service.


    Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.

  12. #37
    55 Years & Still Rolling
    hwoods's Avatar
    Join Date
    Jun 2002
    Location
    Glenn Dale Md, Heart of the P.G. County Fire Belt....
    Posts
    10,740

    Thumbs up Yep...................

    Quote Originally Posted by MemphisE34a View Post
    Chief,

    Even so, you could still flow more water at lower pump discharge pressures if you made the change to 5" and used your same SOP.

    Bob's right, of course, and there is no one single reason that most of us don't like the stuff. For instance, I bounce over charged 3 inch line on a regular basis, but NOBODY drives over charged 5 inch. (I did see a Camaro try it once, the line burst and threw the car about 10 - 12 feet, almost turned it over) and the usual complaints about the weight when repacking it. And, our "Bread and butter" Fires don't require that kind of Fire flow. As I noted above, we have a system, and it works well for us.
    Never use Force! Get a Bigger Hammer.
    In memory of
    Chief Earle W. Woods, 1912 - 1997
    Asst. Chief John R. Woods Sr. 1937 - 2006

    IACOJ Budget Analyst

    I Refuse to be a Spectator. If I come to the Game, I'm Playing.

    www.gdvfd18.com

  13. #38
    MembersZone Subscriber

    Join Date
    Jan 2007
    Location
    Pa Wilds
    Posts
    600

    Smile Time for an old guy to weigh in on the discussion

    I have read with interest some of these comments concerning the use of LDH. There are several entries asking for help with practices that enhance the movement of large volumes of water. TRAINING6604 asked about reducing the LDH to 2 1/2 “, and putting the water into the gated intakes (Pony Suction). This is definitely not the way to connect LDH. Generally, 2 ½ “ pipe is designed for flows up to 250 gpm, at this flow an elbow has about 1.5 psi loss but the losses increase by the square of the flow. (Hazen – Williams formula) Putting 500 gpm through the elbow will cause a drop of about 6 psi per elbow and 1000 gpm will cause 24 lbs loss. Combine this with the fact that most pony suctions have at least three (3) – 90 degree bends you will rapidly negate any advantage that you gained by laying 5” in the street. It is best to attach a 6” X Storz directly to the steamer connection. A combination gate and relay relief valve set at 150 to 180 psi will ensure that the attack engine is able to continue to supply attack lines without interruption while switching over from tank water to the LDH supply. You will need to set the operating point of the relief valve above the highest hydrant pressure that you normally encounter in your system. We have some hydrants in our system that approach 200 psi static, but with increasing fire flow, rapidly drop below our SOP set pressure for relief valves at 180 psi.
    Repeated radio chatter by pump operators can be reduced to nearly none by the following actions.
    1. Initial attack lines on residential fires (2- 1 ¾ + 2 ½) - Connect the relay engine to the hydrant, but do not place the pump in gear. Allow the hydrant to push right through the engine. Hydrants in the range of 50 to 60 psi at 600 gpm will deliver adequate volume to the attack engine at a distance of 700 feet or more. (Fl=K*Q*Q*L) Fl=1/15 * 6 * 6 * 7 or Fl = 16.8 psi Losses in the relay pump would be about 20 psi so at 600 gpm the attack engine would see at least 14 psi on the intake (compound) gauge. Why place the relay engine in the loop? Just in case there is a sudden increase in the required water. Be aware that the pump will be rotating due to the water flow, and it might be necessary to temporarily stop water flow (attack pumper switches to tank supply for 10 seconds or so) while the engineer shifts into pump gear.

    CAUTION! If you place the relay engine in gear, you can expect to generate about 60 to 80 psi above incoming hydrant pressure. Thus discharge pressure would be 140 psi and incoming at the attack engine would be 125 psi. Now the attack engine at idle will be developing 200+ psi making it difficult for the attack crews to control nozzles and hose lines and defeating any pressure governor control or relief valves.

    2. Multiple apartment or small commercial structure (10,000 sq ft.) calls for about 1000 gpm (3 – 1 ¾ + 2 – 2 ½) or some similar combination . Place the relay engine in gear, but keep the rpm just slightly above idle and not more than 100 psi discharge pressure. As long as the attack engine has an incoming pressure below 80 psi, the relief valve or pressure governor should be able to control pressure fluctuations.
    3. In the event that master streams will be supplied (2 – master streams with 1 ¾” tips) 1600 gpm can be delivered by the relay engine at 150 psi and still have about 40 psi incoming at the attack pumper.
    4. Maximizing the relay engine at 180 psi should result in the delivery of nearly 2000 gpm through the 700 feet of 5” hose. If you are running the attack engine, you can carefully take the intake pressure right down to zero without risking failure of the relay. Contrary to some thinking, you can ‘t “suck the intake shut” , but might cause cavitation if you turn the rpm up too high. The intake hose will begin to collapse, but the reduced cross section will cause an increase in friction until the internal pressure in the hose exactly matches the air pressure on the outside of the hose. (turbulence losses in the intake) This high velocity and violent shaking can tear the inner liner out of old or poorly bonded hose, so be careful.
    5. Summarizing steps 50 psi = Level 1, 100 psi = level 2, 150psi = level 3 & max (180) psi should cover all the needed discharge pressures for the relay engine. Radio chatter = “Engine 12 boost your output to level 2” (100 psi) and you are done on the radio. You don’t need to bump 10 lbs at a time.

  14. #39
    Forum Member

    Join Date
    May 2007
    Posts
    87

    Default

    Have used both, the gain of 5 inch is obviously more water than 3 inch. I have only really seen one substantial argument for 3 inch over 5 inch, that is you can pack more 3" on the truck than 5" which I suppose is true. Where I am atleast it is a mute point. We have a freakin working hydrant almost every block so 1000' of 5" generally does the job for us on our engines. Besides Im a truckie.....we dont need no stinkin' hoses! Stay safe all.
    Gary
    Firefighter/EMT-B
    -------------------
    Stay Safe
    Leather Forever......F.O.O.L.S.

  15. #40

    Join Date
    May 2007
    Posts
    3

    Smile

    The only problem I have with 5'' is that you must have a good water supply, It takes a lot of water to fill 500' of 5'', but I am a fan of it, there is no reason to use smaller when you have bigger!!

  16. #41
    MembersZone Subscriber
    CKirk922's Avatar
    Join Date
    Apr 2005
    Location
    Watching From The Sideline Now
    Posts
    260

    Default Teach me to learn

    Why do some departments still pull two crosslays on initial attack up to a 200x200 fully engulfed structure and proceed to pee on it? Because someone at some level has dropped the ball and not learned the lesson about big fire=big water. That same department will drop in excess of 1200 feet of 2 1/2 or 3 inch hose and connect directly to a hydrant and wonder why they have no water. The facts are out there and imbedded in this entire thread. Large diameter simply allows flows with less friction, lower pump pressures, and more manageable water supplies. If you can get LDH hose onto your rigs and use it then you will see the benifits. It may not be needed for the 10x10 shed fire, but it will be there when you do need it. It is not a cure all for poor tactics and poor training, but like any other tool of the fire service, when you need it, YOU NEED IT! Plan for the biggest fire you might have to fight and you will find that employing some of these tools and techniques on smaller fires will make the big ones easier to manage.

    These are my own views, not those of my department or officers within my department.

  17. #42
    MembersZone Subscriber

    Join Date
    Feb 2007
    Location
    Kansas
    Posts
    492

    Default

    Quote Originally Posted by Geinandputitout View Post
    We have been using a butterfly valve on the intake side of the pump. In the past we were directed to take the butterfly valve off during drafting operations. This is a time consuming process that requires a rubber mallet and lots of foul language.

    Anyway all of our new engines are able to pull a draft through the butterfly valve, give it a try.
    We have Butterflies on our intakes also. The majority of our larger fires involve drafting and we have had no problems.

    T.J.

  18. #43
    Forum Member

    Join Date
    Nov 2009
    Posts
    5

    Default

    5 inch hose has less friction loss.

    honestly unless your fighting a huge fire it shouldnt make much of a differance.

    if you have a call that requires more than 350gpm for any length of time post pics on the site

    that's 7, 50 gallon barrels of water every 60 sec... think about it
    Last edited by Sine; 11-12-2009 at 11:05 AM.

  19. #44
    Back In Black
    ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Quote Originally Posted by Sine View Post
    5 inch hose has less friction loss.

    honestly unless your fighting a huge fire it shouldnt make much of a differance.

    if you have a call that requires more than 350gpm for any length of time post pics on the site

    that's 7, 50 gallon barrels of water every 60 sec... think about it
    Thanks for reviving this two and a half year old thread.

    I was really curious to see if the friction loss was still less.

    .
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  20. #45
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,301

    Default

    Quote Originally Posted by Sine View Post
    5 inch hose has less friction loss.

    honestly unless your fighting a huge fire it shouldnt make much of a differance.

    if you have a call that requires more than 350gpm for any length of time post pics on the site

    that's 7, 50 gallon barrels of water every 60 sec... think about it
    You had to revive a thread this old to post this bit of genius? Golly thanks.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  21. #46
    ...
    ... is offline
    Forum Member

    Join Date
    Sep 2009
    Posts
    420

    Default

    I'd carry both!

  22. #47
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,301

    Default

    Quote Originally Posted by FireRescue61 View Post
    I'd carry both!
    My volly FD does.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  23. #48
    Forum Member
    PaladinKnight's Avatar
    Join Date
    Aug 2006
    Posts
    2,413

    Default

    All of these years and I just learned that 350 gallons will fit into seven 50 gallon barrels.

    I had no idea. This is amazing!

    I wonder if that is just water, or if it applies to other things as well.
    HAVE PLAN.............WILL TRAVEL

  24. #49
    Forum Member

    Join Date
    Jan 2010
    Posts
    122

    Default

    We still carry 2200 ft. of 3" supply line on each of our two engines, and have no desire to switch to LDH. What we have works very well for our area, which is mostly very rural residential structures. We do have a few large barns, and a multi-building mental retardation institution. This institution is the only area in our district that is supplied by hydrants.

    We have some very long driveways and lanes in our area. We use the 3" line because it is better suited to getting us water super quick for the initial attack. If we need more water than 2 3" lines will supply, we can always lay more lines or a LDH line from a mutual aid company as more apparatus and personnel arrive on scene. The problem with 5" for us is that we can dump the tank from our second in engine and never have a drop of it reach the attack engine. With 3" we can use one hose to supply the attack engine until more water arrives. Our system is expandable as the need for water grows. Our first in engine is never going to flow more than 350gpm on the initial attack with the initial crew on that engine (1 2.5" @250gpm and 1 1.5" @90gpm). As more crews arrive, we can flow more water, but there is also lots of extra supply line available at that point. Don't even get me started about the 1.5" attack lines, that's a completely different topic, and I disagree with my departments decision on that one, especially when our pre-connects are 250ft.

    LDH is awesome once you have a water supply established, but sucks for initial attack using two engines with 700gal and 1000gal respectively on board, without hydrants.

  25. #50
    MembersZone Subscriber

    Join Date
    Jan 1999
    Location
    SCHAUMBURG, IL.
    Posts
    133