We are an all rural fire dept. We have no water supply in our township. I started about 3 years ago installing "Dry Hydrants" in some farm ponds along the road.We use our Brush truck to fill Tankers to shuttle water.
How many dept. are in the same situation?
and how much water can you flow during a tanker shuttle operation ?
How many tankers do you usually use in a SHUTTLE OPERATION ?
------------------
Chief Fairbanks
Fairbanks Fire/Rescue
+ Reply to Thread
Results 1 to 20 of 42
-
12-12-2000, 07:45 PM #1Chief FairbanksFirehouse.com Guest
Water Water no where .. Rural America
-
12-12-2000, 09:52 PM #2MetalMedicFirehouse.com Guest
You have the right idea... but you might need to re-think what truck you put on the dry hydrant to fill tankers. On your fire scene you will never be able to exceed the pumping capacity of the truck doing the filling. Ideally, you want to place the pump with the largest capacity on the fill site.
For us, the number of tankers will depend on how far you are from the fill site, and how much fire flow the fire demands. Most departments around here will have 3-5 tankers in service when they reach a 2nd alarm fire.
------------------
Richard Nester
Orrville (OH) Fire Dept.
-
12-13-2000, 05:17 AM #3BuckFirehouse.com Guest
You might want to look at using a turbo draft instead of installing dry hydrants. It's much cheaper and you can access any and I mean any water source.
In a tanker shuttle using all six of our 3000 gal tankers and our two 1500 gal pumper/tankers we can move 2500 gpm in a 1/2 mile shuttle,1500 gpm in a two mile shuttle and 840 gpm in a five mile shuttle.
email me if you want more info on the Turbo Drafts.
Buck
-
12-13-2000, 07:50 AM #4S. CookFirehouse.com Guest
Give the turbo draft a try. Drafting with a brush truck you can supply roughly 800gpm to a fill site or fire.
-
12-13-2000, 08:13 AM #5Sand Creek LynnFirehouse.com Guest
We were in a similar situation. Found a 6" diesel powered pump from govt. surplus.
Will fill tankers at 1800 GPM. $1200.00
And another $1000 or so in hose, fittings, misc.
If buying new tankers pay attention to getting the largest dump valves possible. If dumping into folding tank at the engine set up two, each being larger than the largest tanker so you can keep trucks shuttling instead of waiting to dump.
Check with any depts. you use as mutual aid to make sure hydrant connections, tanker cannections, etc. match theirs.
Never during practice dump a jug of liquid soap into an empty tanker and send it back to the fill site when the excitable new guy is filling tankers.
Lynn
-
12-13-2000, 10:28 AM #6AVF&R452Firehouse.com Guest
Lynn:
I bet that got his attention!! I will try that on the next drill. Smart***** probie has it coming.

Jim
-
12-13-2000, 11:13 AM #7CAP182Firehouse.com Guest
CHIEF,
I AGREE WITH BUCK AND S.COOK TAKE A GOOD LONG HARD LOOK AT THE TURBO DRAFTS THEY ARE THE ANSWER YOU ARE LOOKING FOR. IT TAKES OUT THE " I CANT GET CLOSE ENOUGH TO DRAFT " SITUAATION. WE HAVE 12 IN MY DEPT 1 ON EVERY ENG AND TANKER.
HOPE WE HELPED
-
12-13-2000, 02:30 PM #8FiRsqDvr45Firehouse.com Guest
The towns of Lee and Madbury NH have recently started mandating certain properties and developments to install 10 to 30 thousand gallon cisterns to provide a water source in non hydranted areas. This provides a drafting site for fire attack and tanker filling and allows for a little more time for the arrival of tankers and the set up of a shuttle operation. It may be an option to explore. The problem that we have found with the dry hydrants in ponds and such is that after a while they become clogged or they fill them selves in over time. It becomes and issue of whether or not the owner or FD is responsible for maintaining them and who is liable if they dont work and someone loses a life or a building. I know that back home in Minnesota some farmers have met with local FD's to mount FD fittings to there crop irrigation systems ( those long pipes with a plethora of spray guns on them in the fields)to be use for filling trucks. Some of those wells put out a decent amount of water and pressure. We start using tankers in Newington when we reach around the 2nd or 3rd alarm depending on district or when the hydrant system becomes taxed. Each alarm sends roughly one engine(of at least 1250gpm) for a fill unit to a predesignated site and 3 or 4 tankers. if memory serves me correctly each alarm is designed for around 300-500gpm.
I would like to hear more about this Turbo Draft you talked about alos Buck, sounds neat.
------------------
FF/EMT Jay Ellingson
Newington,NH FD
&
New England Dragway Safety Team (Sundaaayy!)
Be Safe!
-
12-13-2000, 05:50 PM #9LHS*Firehouse.com Guest
//how much water can you flow during a tanker shuttle operation ?
7700 gpm at 1 mile and 1105 at 15 miles
//How many tankers do you usually use in a SHUTTLE OPERATION
Depends on the need, none to 20
//you might need to re-think what truck you put on the dry hydrant to fill tankers. On your fire scene you will never be able to exceed the pumping capacity of the truck doing the filling. Ideally, you want to place the pump with the largest capacity on the fill site. //
We use the smallest pumper and a Couple Turbo Drafts, so yes a pump can pump three to 6 times its pump capacity.
For ISO to count your cisterns they need to be at least 30,000 gallons
-
12-14-2000, 10:46 PM #10HALFirehouse.com Guest
If your Brush Unit/Attack truck has a good size pump(300-400gpm),you could get close enough to draft with this lighter weight vehicle and pump into a TurboDraft to double + your flow to a porta tank or tanker fill site. This unit is very effective for accessing those out of reach fill sites,and maybe shortening shuttle distances or eliminating them all together.
-
12-15-2000, 12:30 PM #11DWCFirehouse.com Guest
How does the Turbo Draft work? It sounds like an excellent tool, but I don't exactly understand how it operates. What situations are best suited for its use?
-
12-15-2000, 01:32 PM #12LHS*Firehouse.com Guest
do a search on the forums for turbo draft and you can see pictures. It is basically a big foam eductor. Each gallon in brings 2 4 back out. Yesterday we lifted water 25 feet verticallty and flowed 1250 gpm to fill tankes 250 feet from the water source using soft hose
-
12-15-2000, 10:03 PM #13HALFirehouse.com Guest
Like LHS said, the TurboDraft is a big eductor(about 50 lbs.) Quik set-up, take a 2 1/2" or 3" from a pump discharge,and connect to TD inlet.Connect 5" LDH to outlet of TD and other end into pump intake valve.Submerge unit into 2 ft. of water.Open tank to pump, pressurize TD (150-175psi),the 5" will fill instantly. Quik water from a distance using conventional LDH and one attack line.The unit is portable and can be set up very fast! Check out the web-site WWW.TurboDraft.net
-
12-16-2000, 01:02 AM #14MetalMedicFirehouse.com Guest
I have not seen this "TurboDraft" device other than in an advertisement. I just checked out the webpage and it appears to be an overgrown jet-siphon like we use in multiple portable tank operations. From the design of the thing, it looks like it could become a victim to debris (ie. mud and gravel) in the water source. Also, can this thing fill directly into a tanker, or do you need to go through a pumper to defeat the back pressure a tanker would generate??
------------------
Richard Nester
Orrville (OH) Fire Dept.
-
12-16-2000, 05:22 AM #15BuckFirehouse.com Guest
///From the design of the thing, it looks like it could become a victim to debris (ie. mud and gravel) in the water source.///
I have never experienced a problem with the TD clogging. You can take a couple of empty foam buckets and float the TD 2' under the water and you don't have to worry about the mud.
If it did clog up all you have to do is close your intake and keep on pumping water to it to blow it out.
///Also, can this thing fill directly into a tanker, or do you need to go through a pumper to defeat the back pressure a tanker would generate?? ///
You need it to go back to the pumper to supply you with water because you need to constantly supply the TD. Unless you have a small pump ( 300 - 500 gpm) that is on a draft.
With a 500 gpm pump you can supply two Turbo Drafts and produce flow over 1200 gpm.
Buck
-
12-16-2000, 10:37 AM #16MetalMedicFirehouse.com Guest
So that brings me back to the original dilemma. If the Turbo Draft is used to nurse a pumper at the fill site that must then fill the tankers, how can you exceed the capacity of that pumper at the fire scene in a water shuttle?Originally posted by Buck:
[b}
///Also, can this thing fill directly into a tanker, or do you need to go through a pumper to defeat the back pressure a tanker would generate?? ///
You need it to go back to the pumper to supply you with water because you need to constantly supply the TD. Unless you have a small pump ( 300 - 500 gpm) that is on a draft.
With a 500 gpm pump you can supply two Turbo Drafts and produce flow over 1200 gpm.
Buck[/b]
[This message has been edited by MetalMedic (edited 12-16-2000).]
-
12-16-2000, 10:55 AM #17Sand Creek LynnFirehouse.com Guest
How do you use a turbo draft in winter when your pond is frozen?
Lynn
-
12-16-2000, 12:52 PM #18BuckFirehouse.com Guest
Metal Medic,
Are you telling me a pump will not pump over it's rated amount when it has a pressurized water source coming in?
AS LHS said we flowed 1250 gpm at a 25' lift 250' foot away from the water source. That is net gpm after you take away the water needed to supply the TD.
Now just think about this. Take a Booster truck that has a 500 gpm pump and put it at draft. Now use the water you pump off the booster to supply the Turbo Drafts and you can easily pump 1200 gpm out 250' and lift the water to 25'.
Using that system you just more than doubled your pump capacity.
///How do you use a turbo draft in winter when your pond is frozen?///
How do you draft when the pond is frozen?
I live in Texas and I don't have any experience dealing with frozen sources. But with water being being a very important part of our business I would figure out a way to deal with Frozen Water.
It seems like I read a article about Sister Bay, Wisconsin that does not seem to have a problem with frozen water.
Buck
-
12-16-2000, 05:49 PM #19Dalmatian90Firehouse.com Guest
It seems like I read a article about Sister Bay, Wisconsin that does not seem to have a problem with frozen water.
I don't seem to recall them mentioning Turbo drafts in the article I saw...they used lightweight hard suction.
Sandy Lynn's question was if/how Turbo Drafts work with ice.
I don't have experience with them, but I'd imagine they'd work. I'd think you'd might have to jiggle the hoses some, especially if the siphon moves in a way to kink them before charging. Kinking, of course, isn't something that's a problem with hard suction.
Anyone have deep freezing experience with them?
Matt
-
12-16-2000, 05:55 PM #20MetalMedicFirehouse.com Guest
First you tell me that you need a pumper because the TurboDraft cannot overcome the resistance of gravity on the water in the tanker... then you tell me that your water is coming into the pumper under pressure... make up your mind. If it can't push water into a tanker, would there be sufficient pressure to make any real difference in what is basically a glorified relay pumping situation?Originally posted by Buck:
Metal Medic,
Are you telling me a pump will not pump over it's rated amount when it has a pressurized water source coming in?
------------------
Richard Nester
Orrville (OH) Fire Dept.