1. #26
    Senior Member
    Dalmatian90's Avatar
    Join Date
    Mar 2000
    Posts
    3,120

    Default

    It has a very good water system - if the FD tapped into the bigger mains, 15,000 gpm+ could have been available. How much did they flow - water dept data indicated about 3,300 gpm total - 17 engines, 15,000 gpm possible and 3,300 gpm was flowed.

    Four and a half years earlier I was at a fire in a town with a hydrant system that could deliver 900gpm. 30 minutes after the initial 911 call somewhere in the neighborhood of 13,000gpm was being delivered onto the mill and no conflagaration occured, although it was starting to get hairy for a few minutes with siding sliding down the multiple wood-frame exposures on two sides, telephone poles on fire, and even the first two 5" lines laid to draft melted about 45 minutes into the fire from radiant heat. Amazing what can happen when you combine a bunch of rural departments that know long lays & drafting with an excellent water supply pre-plan and some good on-the-spot modifications to the plan (since the original game plan focused on cutting off extension from one wing to the other, and actually both were ignited simultaneously by an arsonist).

    It is interesting however to look at CILFD's 1250 arguement.

    Had all the source pumps been 1250s, we probably would've been down into the 10-11,000gpm range.

    Had all the source pumpers been 2000s and 6" hose used, we'd easily be into the 18,000gpm range, and probably pushing into 20,000+. And yes, we could have delivered it to the fire.

    Don't know if 20,000gpm would've helped. But I don't know if 10,000 would've been enough either -- as Ladders were retreating from one of the streets, 1.75" and 2.5" lines were being stretched through alleys in anticipation of multiple wood-frames becoming involved very shortly...13,000gpm flowing and the fire was doubtful. My corner had 3,000gpm flowing, and if we had another 1,000 it would've been well appreciated.

    I'm not too familiar on engine sizes, but our '95 Spartan/Marion with a 350hp Cummins has pushed 1800gpm from draft, so I'd think engines in the 350-400hp range should be able to drive the 2000gpm pumps. Our area already looks at engines in that hp range for the pumpers since most have 1000-1500 gallon tanks and come in at 40,000# on single rear axles with rolling to sometimes long & steep hills to climb.

    (By the way, I got lost in Holyoke once. It was a surreal experience -- you expected tumbleweeds to go rolling down some of the streets, just lots of big, abandoned buildings and no one around for blocks at a time. Just me, my truck, and some garbage blowing through the streets...weird. At least in other distressed cities I've driven through I always saw signs of life, sometimes scary life, but at least life!)

  2. #27
    Forum Member

    Join Date
    Aug 2001
    Location
    Syracuse, NY
    Posts
    76

    Default Apples vs. Oranges . . .

    Many excellent points raised here, and good food for thought for apparatus committees. cilfd raises some valid points, however remember that experience with "fixed pumping systems" is not entirely transferable to mobile fire apparatus (I have worked with both). While the basic principles, hydraulics and physics are the same, nearly everything else is not. It was correctly pointed out that many of the "high horsepower" diesel engines are specified more for road performance than for pump power. The variables of water supply, terrain gradient, and application systems (not to mention "pilot error") are just a few of the reasons that so many different combinations of chassis, engines and pumps are offered and sold. This increases the possibility of "getting it wrong", and what is correct and usable for one department may be a horrible mismatch for another.

    Again, you must do the work. You know your local conditions and capabilities, the rest of us don't. 2000+ gpm pumps are not overkill if they are appropriate. Likewise, a 1000 gpm pump for certain high-fire-volume applications would be like bringing a knife to a gunfight.
    This is not a "one-size-fits-all" subject. Buy the size that fits.

    A good topic, and interesting reading. Thanks to all who contributed.

  3. #28
    Member

    Join Date
    Dec 2001
    Location
    Elizabeth, NJ
    Posts
    42

    Default

    Must agree with the posts that stated a department should spec out apparatus that meet their requirements. Many apparatus committees fail to realize that their needs are totally different then the demo that was brought around or that new piece that another city just purchased.

    A department with a good hydrant and water main system should consider purchasing 2000 GPM pumps. With the proper hose evolutions and training a department can easily utilize a 2000 GPM pump at certain incidents.

    As far as wasting taxpayers money,a 400HP engine is about $1800 more than a 350HP engine and if a department is purchasing equipment for the future a larger capacity pump goes alot more toward fire protection than some of the other items that we feel are necessary on apparatus. Who knows what will happen with water supplies in 10 years. If we aren't progressive we still be using apparatus with 300 gal. water tanks.

  4. #29
    Forum Member
    Fire304's Avatar
    Join Date
    Jun 2002
    Location
    At the Helm
    Posts
    1,174

    Default

    [QUOTE]Originally posted by BCRJP
    Many apparatus committees fail to realize that their needs are totally different then the demo that was brought around or that new piece that another city just purchased.[QUOTE]

    Not only different from the next town or demo, but possibly very different from the other pieces sitting in the barn. I am lucky to work in a very progressive FD where the chief and officers are not afraid of new stuff, that overkill 2000GPM pumper is also a CAFS truck with built in Amkus system, unlike anything anyone else uses around here. We've all seen the dept, or maybe work in one, where the chief believes there is only one way to work it, they way he learned, so the troops are charging into a building with 1 1/2 lines fed by dual 2 1/2's because that new stuff (1 3/4" and 5") is too damned expensive and the old stuff was good enough when the old man was a pup.

    It has just occured to me that the 500HP engine on my tower could probably drive that Q-max to 3000+ GPM but it is probably limited to 2000 by the 2 6" intakes we have on it. The HP is required to drive the truck, yes it cost a lot, but when trying to merge onto the interstate some times I wish I had 600HP.

    Good posts by all, I didn't realize what a hot issue this would become when I started this thread, I thank all who have posted, and I do enjoy being called out to defend my thinking, its the only way we can move ourselves forward. Bravo to all!

  5. #30
    Junior Member

    Join Date
    Jul 2002
    Location
    NY
    Posts
    3

    Default

    Does anybody have any problems doing the annual pump test on these large pumps ? Joe T

  6. #31
    Junior Member

    Join Date
    Jul 2002
    Posts
    24

    Default

    You know a significant part of this thread is made up of conjecture not facts. A 350 HP engine, a small motor with a small transmission will in fact spin a 1750 gpm pump all day. Or with dual suctions 2000 gpm. So where is the added cost? There isn't any. YOu don't have to add any discharges. A 370 hp will spin a 2000 at draft.

    Electronically controlled engines and transmissions will not make use of a centrifugal pumps ability at a positive pressure source like a hydrant, they are limited electronically, unlike their older brothers.

    A hale, waterous or darley pedestal pump 2000 gpm always costs less than a traditional midship 1250 pump, ALWAYS.

    As far as big hose having trouble supplying big pumps, our shift does a 2000 gpm two master stream drill every other shift using 5 inch hose. We have flowed 8000 gpm with four rigs and 12 guys. ISO syas the downtown water systems rates at 12,000 plus. All three times we have helped supply our 1x4, 1x5 ladder pipe 1 x 6 and 14 guns (4000, 5000, 6000 and 14,000 gpm) we never had any problem either at draft, via relay or using the water systems.

    Our neighbors have two 6000 gpm pumps on order (INSTEAD OF RELYING ON 2750 TO 3500 GPM ENGINES), with 500 hp motors, they will lay dual 7 1/4" hose instead of todays, triple 6 inch lines. The water is there, have you figured out how to move it effectively? The little volunteers to the right of us have 6 - 3500 gpm pumps, guess what? They were the same cost of a 1500 gpm midship pump. The motor selected was selected to move the rig down the road not special to spin the pump(like most fire trucks)I think two of their rigs spin two Hale 8 FG's on the same shaft. So horsepower isn't a limitation. If you don't draft a modern pump you have 30% more horsepower than needed to operate off a fire hydrant system. So what does that mean? Any 300 horsepower engine will spin a 2000 to 2250 pump from a hydrant system, that is ANY 300 or larger hp motor.

    Hose is just as important as the pump, I guess that is why we have 12,000 feet of 6 inch (soon to be 7 1/4 or double 5 brand) chasing us around on one rig when needed.

    Waste of money? Hardly, better use of spending less money.

    Now the issues of pumping 100 gpm versus 3500, with a fleet of 16 2750's to 10,000 gpm pumpers, not stationary pumps, I think I can state the facts, we use 175 rpm less at 100 gpm as we do at 2750. Ya think that will wear the rig out prematurely???

    The pumps are designed to do an entire flow range and do so well. We pump test them every year using 8 inch hard suction without any problem.

    As far as your own needs go, starting with a 2000 gpm pedestal pump with all stainless plumbing is probably the smartest thing you could do. It will last the test of time, make full use of any static or pressurized water source without a cost penalty. Certainly any quint should start with a 2250 minimum.

    Three guys can make 3000 gpm flow easily if someone lays the rig out right. I believe something like 10% of the fires account for 90% of the dollar loss due to fires. So why not setup for the big as well as the small fire? Now if you believe the "what difference would it make comment"?? Then why respond on a fully invloved building?

    Can one 5 inch line supply a 2000 gpm pump, sure can, the issue is hydrant pressure, hose length and flow, we do it every few days.

    I doubt the fire cares how "OVERSIZED" the pumper is, the hydrants are, the water mains or water storage in town are. The real issue will the fire go out with a 2000 or a 150 gpm pump, yes. I guess we could fill our stations full of say 10 sizes of apparatus or one do anything piece, the choice is yours, this is America.

    Oh those corpus rigs that flowed 4750 gpm, are offically rated as two pumps per rig or one 2750 and one 2000 pump off the same engine because NFPA stops at 3500 pn their rating system, but the same test was done at 4750 gpm for the same time periods and lift. They lay four 5 inch lines each, all 1250 feet long to supply the rigs.

    Using Hale valves their LDH discharges only flowed 2250 gpm. Kinda limited with only five LDH discharges per rig though.

  7. #32
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,171

    Default

    My turn to drag one out of the past.

    Any change in thoughts or ideas since this topic was originated back in the stone ages?

    My POC FD has a 2000 GPM Hale Q-Max pump in our newest pumper. We haven't got a chance of supplying it with our hydrant system and frankly we knew that when we bought it. BUT, we can supply it easily from draft from the creek that passes through town, OR we can supply roughly 1400 gpm at 200 psi at the pump. We bought it mainly to utilize the 2000 gpm pump from draft for some target hazards where we knew the municipal supply would never be enough if a good fire got going. Our hydrants suply it just fine for normal residential, or merchantile type fires.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  8. #33
    Forum Member
    SFD_E73_RET's Avatar
    Join Date
    Jun 2006
    Location
    KC area
    Posts
    305

    Default

    It sounds to me like you have 2000 gpm pumps for the right reasons. I see some urban departments who never draft and don't even carry hard suction run 2000 gpm pumps, why? You can get over 2000 gpm out of a smaller pump with good hydrants. Spend your money on big power and big brakes.

  9. #34
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    I can go along with FyredUp's post. We have many areas we can (and do) draft from as a supply engine.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  10. #35
    MembersZone Subscriber

    Join Date
    Jul 2006
    Location
    Outside Philadelphia
    Posts
    519

    Default

    We have 2-2250gpms pumps, 1-2000gpm pump. Public water system won't supply it. We do have an extremely large target hazard with their own water supply that will easily put that much out, with plenty to spare.
    A Fire Chief has ONLY 1 JOB and that's to take care of his fireman. EVERYTHING else falls under this.

  11. #36
    Back In Black
    ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Quote Originally Posted by FyredUp View Post
    My turn to drag one out of the past.

    Any change in thoughts or ideas since this topic was originated back in the stone ages?

    My POC FD has a 2000 GPM Hale Q-Max pump in our newest pumper. We haven't got a chance of supplying it with our hydrant system and frankly we knew that when we bought it. BUT, we can supply it easily from draft from the creek that passes through town, OR we can supply roughly 1400 gpm at 200 psi at the pump. We bought it mainly to utilize the 2000 gpm pump from draft for some target hazards where we knew the municipal supply would never be enough if a good fire got going. Our hydrants suply it just fine for normal residential, or merchantile type fires.
    Can you supply it from draft via one steamer connection?
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  12. #37
    Forum Member

    Join Date
    Nov 2005
    Location
    British Columbia
    Posts
    450

    Default

    I think that is what most departments that purchase pumps larger then 1500 gpm don't understand, you can't produce more then 1500 gpm from draft with only one 6" hard suction. If you want 2000+ gpm you need to have two 6" suction going into the pump. How many Engines with pumps rated larger then 1500 gpm do you see carrying four lengths of 6" hard suction?

  13. #38
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    We have a steamer connection on driver side, officer side, and front. Same setup on both our engines. All engines have 2 or 3 lengths of hard sleeves.

    Getting water into it is not a problem and though we have tried many times....we have yet to make the ocean go down an inch.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  14. #39
    Back In Black
    ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Quote Originally Posted by Bones42 View Post
    We have a steamer connection on driver side, officer side, and front. Same setup on both our engines. All engines have 2 or 3 lengths of hard sleeves.

    Getting water into it is not a problem and though we have tried many times....we have yet to make the ocean go down an inch.
    How much hard sleeve do you carry on the engine?
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  15. #40
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    2 or 3 lengths on each. Minimum of 20'

    Not a big deal to get hard sleeves from the other engines...we aren't miles apart and if a draft is needed for that volume, there is a few minutes available to get them.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  16. #41
    Back In Black
    ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Quote Originally Posted by Bones42 View Post
    2 or 3 lengths on each. Minimum of 20'

    Not a big deal to get hard sleeves from the other engines...we aren't miles apart and if a draft is needed for that volume, there is a few minutes available to get them.
    Yea, no, I get it... Just curious.

    You'll certainly have time to put it together.
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  17. #42
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,685

    Default

    No problem, was a lot of discussion when speccing out the new engine.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  18. #43
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,171

    Default

    Quote Originally Posted by ChiefKN View Post
    Can you supply it from draft via one steamer connection?
    Nope and we know that. And that is why when we installed our dry hydrant we had twin 6 inch dry hydrants installed about 6 feet apart. Works GREAT.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  19. #44
    Back In Black
    ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Quote Originally Posted by FyredUp View Post
    Nope and we know that. And that is why when we installed our dry hydrant we had twin 6 inch dry hydrants installed about 6 feet apart. Works GREAT.
    Sweet......
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  20. #45
    Forum Member
    FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    10,171

    Default

    Quote Originally Posted by ChiefKN View Post
    Sweet......
    Yes, it is. It is located close to a large cheese factory and the County Nusing Home, mental lock up facility, and elderly/low income housing apartments. We have 3500 feet of 5 inch hose and can cover a good portion of the "business district" from that dry hydrant. It is designed to be used to supplemet the village's haydrant system.
    Crazy, but that's how it goes
    Millions of people living as foes
    Maybe it's not too late
    To learn how to love, and forget how to hate

  21. #46
    Forum Member

    Join Date
    Feb 2009
    Location
    virginia
    Posts
    537

    Default

    Quote Originally Posted by SFD_E73_RET View Post
    It sounds to me like you have 2000 gpm pumps for the right reasons. I see some urban departments who never draft and don't even carry hard suction run 2000 gpm pumps, why? You can get over 2000 gpm out of a smaller pump with good hydrants. Spend your money on big power and big brakes.
    Remember that is 2000 gpm at draft at 150 psi. Start pumping higher pressures and that rating drops down. the hydrant prssure coming in helps to increase the pump max gpm. but operates on the same higher pressure less flow curve. Start pumping to high rises 20+ floors even attached to hydrants the gpm rating is going to drop. by having larger pumps on urban engines it lessens the need to tandem pump to obtain those high pressures and bigger flows.