Has anybody ever built a burn building on a limited budget? I am looking for plans, advice, and techniques that will save on money.
Labor would be volunteer.
Likely will be purly concrete construction, with a bit of metal work.
We have an abundance of oil field industry materials to draw from. Heavy gauge pipe, sucker rod (inch thick rods used in wells), etc...
We are a volunteer department that would like to have live burn training available in our area (nearest training facility is 70 miles away).
If anybody has any plans, pictures, or advice, please let me know.
Thaks
+ Reply to Thread
Results 1 to 20 of 21
Thread: Burn Building on a Budget?
-
09-15-2003, 06:56 PM #1
Burn Building on a Budget?
-Brotherhood: I don't know half of you half as well as I should like; and I like less than half of you half as well as you deserve.
-Mistakes: It could be that the purpose of you life is to serve as a warning to others.
-Adversity: That which does not kill me postpones the inevitable.
-Despair: Its always darkest before it goes Pitch Black.
-
09-16-2003, 12:58 PM #2MembersZone Subscriber
- Join Date
- Nov 2002
- Location
- Western NC
- Posts
- 156
I have been toying with this idea myself, although I will be the first to admit I have not researched either NFPA or OSHA regs on such. I considered posting my idea here to get input and see what everyone knew of the regs and how feasable it may be, so this is as good a time as any.
My idea centers upon the use of ocean shipping containers, the 20 and 40 foot models. We have several welders on the department, and some talented fabricators to work on this.
Basicly, I would like to take 2 40 foot containers, and join them with a 20 foot to make an H. Regular size doorways would be cut where they join, leaving the structural integity ok. Vents would be added at the top, as well as a provision on one or two for a 4x8 section of plywood to serve as a roof for ventilation exercises. Later down the road a 20 foot model could be added on top of one of the 40's and metal stairs added to connect them. These containers are regularly stacked 4-6 high loaded, so one empty with some reenforcemnet would be fine. A window for RIT excercise could be cut out and formed in a few of the containers, and covered with plywood when not in use or for ventilation/forcible entry training.
The doors can be left as, and more can be added on the sides. You would need to make some provision for water drainage but slits on the side should be fine, and sliding vents could be added along the tops to regulate tempurature. these containers are extremly strong, deigned to holds tons of goods and be stacked 4-6 high when loaded
I figure wuth us doing the labor ourselves, buying the cheapest containers (too worn for shipping but still fine for us) we could do the whole basic deal for about $10,000-$12,000.
Waht do you think guys, is this feasable?Last edited by radioguy; 09-16-2003 at 01:09 PM.
-
09-16-2003, 01:17 PM #3
Personally, I would do lots and lots of research before I built a building that I will put FF's in and burn. Thoughts of the amount of safety devices needed alone are running through my head. Search for threads on these forums involving Lairdsville. That was a town that did a burn drill without much (if any) of an idea on what they were doing. Hopefully soon, the guy in charge will be spending more time in jail. Can they be built? Sure, but I would suggest calling some companies that sell/build such buildings and get advice from them. Talk to the people who run the one 70 miles away and contact who built theirs. It makes sense to do it, but don't skimp, do it right.
-
09-16-2003, 02:00 PM #4MembersZone Subscriber
- Join Date
- Jul 1999
- Location
- Flanders, NJ
- Posts
- 13,537
Stop. Before taking another step, invest in a copy of NFPA 1403 and follow it to the T.
-
09-16-2003, 02:21 PM #5MembersZone Subscriber
- Join Date
- Nov 2002
- Location
- Western NC
- Posts
- 156
Just found 1403 available for free download hereOriginally posted by GeorgeWendtCFI
Stop. Before taking another step, invest in a copy of NFPA 1403 and follow it to the T.
http://www.nfpa.org/Codes/CodesandSt...responders.asp
This whole container idea has been a kind of back of the mind daydream of mine for a few months, now time to print this and see if it is feasable.
-
09-16-2003, 02:23 PM #6
Burn building on a budget? I hope it is a large budget. There is no way to build a safe, compliant, burn building that will last without a significant amount of cash unless you can get a whole bunch of donated cash and or material.
"We shouldn't be opening firehouses in Baghdad and closing them in New York City."
IACOJ
-
09-16-2003, 02:42 PM #7MembersZone Subscriber
- Join Date
- Nov 2002
- Location
- Western NC
- Posts
- 156
Now looking over NFPA 1403, I am somewhat suprised at the lack of standards for burn building construction laid down in the standard. There are plenty of refrences to the burn activities and such, but very little on the actual construction. The strictest thing called for in an annual inspection by an engineer familiar with burn building, removal of thermal barriers to inspect for damage beneath (none in a steel building) and core samples of concrete walls.
here is the standard for non-gas fired training center buildings.
Chapter 6 Non–Gas-Fired Training Center Buildings
6.1 Student Prerequisites.
6.1.1* Prior to being permitted to participate in live fire training
evolutions, the student shall have received training to
meet the job performance requirements for Fire Fighter I in
NFPA 1001, Standard for Fire Fighter Professional Qualifications,
related to the following subjects:
(1) Safety
(2) Fire behavior
(3) Portable extinguishers
(4) Personal protective equipment
(5) Ladders
(6) Fire hose, appliances, and streams
(7) Overhaul
(8) Water supply
(9) Ventilation
(10) Forcible entry
6.1.2* Students participating in a live fire training evolution
who have received the required minimum basic training from
other than the authority having jurisdiction shall not be permitted
to participate in any live fire training evolution without
presenting prior written evidence of having successfully completed
the prescribed minimum training to the levels specified
in 6.1.1.
6.2 Structures and Facilities.
6.2.1* Strict safety practices shall be applied to all structures
selected for live fire training evolutions.
6.2.2* Training center burn buildings shall be inspected visually
for damage prior to live fire training evolutions.
6.2.2.1 Damage shall be documented.
6.2.2.2* The structural integrity of the building shall be evaluated
and documented annually by a licensed professional engineer
with burn building experience and expertise.
6.2.2.3* Part of the burn building evaluation shall include,
once every five years, the removal and reinstallation of a representative
area of thermal linings (if any) to inspect the hidden
conditions behind the linings.
6.2.2.4 The engineer shall core solid structural concrete slabs
and walls that have been exposed to temperatures in excess of
149°C (300°F) to check for hidden delaminations and to test
compressive strength once every 10 years for conventional
(Portland) concrete and every three years for refractory (calcium
aluminate) concrete.
6.2.2.5 Where the burn building damage is severe enough to
affect the safety of the students, training shall not be permitted.
6.2.3 All doors, windows and window shutters, roof scuttles
and automatic ventilators, mechanical equipment, lighting,
manual or automatic sprinklers, and standpipes necessary for
the live fire training evolution shall be checked and operated
prior to any live fire training evolution to ensure they operate
correctly.
6.2.4* All safety devices, such as thermometers, oxygen and
toxic and combustible gas monitors, evacuation alarms, and
emergency shutdown switches, shall be checked prior to any
live fire training evolutions to ensure they operate correctly.
6.2.5 Training center burn buildings shall be left in a safe
condition upon completion of live fire training evolutions.
6.2.6 Debris hindering the access or egress of fire fighters
shall be removed prior to the beginning of the next training
exercises.
6.2.7 In preparation for live fire training, an inspection of the
structure shall be made to determine that the floors, walls,
stairs, and other structural components are capable of withstanding
the weight of contents, participants, and accumulated
water.
6.2.8 Property adjacent to the training site that could be affected
by the smoke from the live fire training evolution, such
as railroads, airports or heliports, and nursing homes, hospitals,
or other similar facilities, shall be identified.
6.2.9 The persons in charge of the properties described in
6.2.8 shall be informed of the date and time of the evolution.
6.2.10* Streets or highways in the vicinity of the training site
shall be surveyed for potential effects from live fire training
evolutions, and safeguards shall be taken to eliminate any possible
hazard to motorists.
6.2.11 Pedestrian traffic in the vicinity of the training site shall
be kept clear of the operations area of the live burn by the use
of fire lines.
6.2.12 Awareness of weather conditions, wind velocity, and
wind direction shall be maintained, including a final check for
possible changes in weather conditions immediately before
actual ignition.
6.2.13 The water supply for any individual live fire training
evolution shall be assessed based on the extent of the evolutions
to be performed.
6.2.13.1 Consideration shall be given to the control and extinguishment
of the fire and the provision of necessary backup
lines to protect personnel.
6.2.13.2 The minimum water supply and delivery for live fire
training evolutions shall meet the criteria identified in
NFPA 1142, Standard on Water Supplies for Suburban and Rural
Fire Fighting.
6.2.13.3 A minimum reserve of additional water in the
amount of 50 percent of the fire flow demand determined in
accordance with 6.2.13.2 shall be available to handle exposure
protection or unforeseen situations.
6.2.13.4* Separate sources shall be utilized for the supply of
attack lines and backup lines in order to preclude the loss of
both water supply sources at the same time.
Exception: A single source shall be sufficient at a training center facility
where the water system has been engineered to provide adequate
volume for the evolutions conducted and a backup power source or
backup pumps, or both, are in place to ensure an uninterrupted supply
in the event of a power failure or malfunction.
6.2.14 Areas for the staging, operating, and parking of fire
apparatus that are used in the live fire training evolution shall
be designated.
6.2.14.1 An area for parking fire apparatus and vehicles that
are not a part of the evolution shall be designated so as not to
interfere with fireground operations.
6.2.14.2 Consideration shall be given to locating this area in
order to facilitate prompt response of apparatus in the event
of an emergency.
6.2.14.3 Where required or necessary, parking areas for police
vehicles or for the press shall be designated.
6.2.14.4 A parking area for an ambulance or an emergency
medical services vehicle shall be designated.
6.2.14.5 Consideration shall be given to locating this area to
facilitate prompt response in the event of a personal injury to
participants in the evolution.
6.2.14.6 Consideration shall be given to the designation and
layout of ingress/egress routes in order to ensure their availability
in the event of an emergency.
6.2.15 Prior to conducting actual live fire training evolutions,
a preburn briefing session shall be conducted for all participants.
6.2.15.1 All facets of each evolution to be conducted shall be
discussed in the preburn briefing, and assignments shall be
made for all crews participating in the training session.
6.2.15.2 The location of simulated victims shall not be required
to be disclosed, provided that the possibility of victims
is discussed during the preburn briefing.
6.2.15.3 A preburn plan shall be prepared and shall be utilized
during the preburn briefing sessions.
6.2.15.4 All features of the training areas and structure shall
be indicated on the preburn plan.
6.2.16 Prior to conducting any live fire training, all participants
shall be required to conduct a walk-through of the structure
in order to have a knowledge of and familiarity with the
layout of the building and to facilitate any necessary evacuation
of the building.
6.2.17 All spectators shall be restricted to an area outside the
operations area perimeter established by the safety officer.
6.2.17.1 Control measures such as ropes, signs, and fire line
markings shall be posted to indicate the perimeter of the operations
area.
6.2.17.2 Visitors who are allowed within the operations area
perimeter to observe operations shall be escorted at all times.
6.2.17.3 Visitors who are allowed within the operations area
perimeter shall be equipped with and shall wear complete
protective clothing according to manufacturer’s instructions
and in accordance with 6.4.17.1 through 6.4.17.7.
6.2.18 All possible sources of ignition, other than those that
are under the direct supervision of the person responsible for
the start of the training fire, shall be removed from the operations
area.
6.3 Fuel Materials.
6.3.1 The fuels that are utilized in live fire training evolutions
shall have known burning characteristics that are as controllable
as possible.
6.3.2 Unidentified materials, such as debris found in or
around the structure that could burn in unanticipated ways,
react violently, or create environmental or health hazards,
shall not be permitted to be used.
6.3.3 Fuel materials shall be used only in the amounts necessary
to create the desired fire size.
6.3.4* Pressure-treated wood, rubber, and plastic, and straw or
hay treated with pesticides or harmful chemicals shall not be
permitted to be used.
6.3.5 The fuel load shall be limited to avoid conditions that
could cause an uncontrolled flashover or backdraft.
6.3.6* The use of flammable or combustible liquids, as defined
in NFPA 30, Flammable and Combustible Liquids Code, shall
not be permitted to be used in live fire training evolutions in
structures.
Exception: Limited quantities of combustible liquid with a flash point
above 38°C (100°F) shall be permitted to be used in a training center
burn building that has been specifically engineered to accommodate
this fuel.
6.3.7* The instructor-in-charge shall assess the selected fire
room environment for factors that can affect the growth, development,
and spread of the fire.
6.3.8* The instructor-in-charge shall document fuel loading
including all of the following:
(1) Furnishings
(2) Wall and floor coverings and ceiling materials
(3) Type of construction of the structure, including type of
roof and combustible void spaces
(4) Dimensions of room
6.3.9* The training exercise shall be stopped immediately
when the instructor-in-charge determines through ongoing
assessment that the combustible nature of the environment
represents a potential hazard.
6.3.10 The exercise shall continue only when the actions have
been taken to reduce the hazard.
6.4 Safety.
6.4.1 A safety officer shall be appointed for all live fire training
evolutions.
6.4.2* The safety officer shall have the authority, regardless of
rank, to intervene and control any aspect of the operations
when, in his or her judgment, a potential or actual danger,
accident, or unsafe condition exists.
6.4.3 The responsibilities of the safety officer shall include,
but shall not be limited to, the following:
(1) Prevention of unsafe acts
(2) Elimination of unsafe conditions
6.4.4 The safety officer shall provide for the safety of all persons
on the scene including students, instructors, visitors, and
spectators.
6.4.5 The safety officer shall not be assigned other duties that
interfere with safety responsibilities.
6.4.6 The safety officer shall be knowledgeable in the operation
and location of safety features available within the burn
building, such as emergency shutoff switches, gas shutoff
valves, and evacuation alarms.
6.4.7* The instructor-in-charge of the live fire training evolutions
shall determine, prior to each specific evolution, the
number of training attack lines and backup lines that are
necessary.
6.4.7.1 Backup lines shall be provided to ensure protection
for personnel on training attack lines.
6.4.7.2 Each hoseline shall be capable of delivering a minimum
of 360 L/min (95 gpm).
6.4.7.3 The instructor-in-charge shall assign the following
personnel:
(1) One instructor to each functional crew, which shall not
exceed five students
(2) One instructor to each backup line
(3) Additional personnel to backup lines to provide mobility
(4) One additional instructor for each additional functional
assignment
6.4.8* Additional safety personnel, as deemed necessary by
the safety officer, shall be located strategically within the structure
to react to any unplanned or threatening situation or
condition.
6.4.9 A method of fireground communications shall be established
to enable coordination among the incident commander,
the interior and exterior sectors, the safety officer,
and external requests for assistance.
6.4.10* A building evacuation plan shall be established, including
an evacuation signal to be demonstrated to all participants
in an interior live fire training evolution.
6.4.11 Emergency medical services shall be available on site to
handle injuries.
6.4.12 Written reports shall be filled out and submitted on all
injuries and on all medical aid rendered.
6.4.13 A search of the structure shall be conducted to ensure
that no unauthorized persons, animals, or objects are in the
building immediately prior to ignition.
6.4.14 No person(s) shall play the role of a victim inside the
building.
6.4.15 Fires shall not be located in any designated exit paths.
6.4.16 The training session shall be curtailed, postponed, or
canceled, as necessary, to reduce the risk of injury or illness
caused by extreme weather conditions.
6.4.17 Each participant shall be equipped with full protective
clothing and self-contained breathing apparatus (SCBA).
6.4.17.1 All participants shall be inspected by the safety officer
prior to entry into a live fire training evolution to ensure
that the protective clothing and SCBA are being worn according
to manufacturer’s instruction and are in serviceable condition.
6.4.17.2 Protective coats, trousers, hoods, footwear, helmets,
and gloves shall have been manufactured to meet the requirements
of NFPA 1971, Standard on Protective Ensemble for Structural
Fire Fighting.
6.4.17.3 Self-contained breathing apparatus (SCBA) shall
have been manufactured to meet the requirements of
NFPA1981, Standard on Open-Circuit Self-Contained Breathing Apparatus
for the Fire Service.
6.4.17.4* Where station or work uniforms are worn by any
participant, the station or work uniform shall have been
manufactured to meet the requirements of NFPA 1975, Standard
on Station/Work Uniforms for Fire and Emergency Services.
6.4.17.5 Personal alarm devices shall have been manufactured
to meet the requirements of NFPA 1982, Standard on
Personal Alert Safety Systems (PASS).
6.4.17.6 All students, instructors, safety personnel, and other
personnel shall wear all protective clothing and equipment
specified in this chapter according to manufacturer’s instructions
whenever they are involved in any evolution or fire suppression
operation during the live fire training evolution.
6.4.17.7* All students, instructors, safety personnel, and other
personnel participating in any evolution or operation of fire
suppression during the live fire training evolution shall
breathe from an SCBA air supply whenever operating under
one or more of the following conditions:
(1) In an atmosphere that is oxygen deficient or contaminated
by products of combustion, or both
(2) In an atmosphere that is suspected of being oxygen deficient
or contaminated by products of combustion, or
both
(3) In any atmosphere that can become oxygen deficient or
contaminated, or both
(4) Below ground level
6.4.18 One person who is not a student shall be designated as
the “ignition officer” to control the materials being burned.
6.4.18.1 The ignition officer shall wear full protective clothing,
including self-contained breathing apparatus (SCBA), as
required in 6.4.17.1 through 6.4.17.7, when performing this
control function.
6.4.18.2 A charged hoseline shall accompany the ignition officer
when he or she is igniting any fire.
6.4.18.3* The decision to ignite the training fire shall be
made by the instructor-in-charge in coordination with the
safety officer.
6.4.18.4 The fire shall be ignited by the ignition officer in
the presence of and under the direct supervision of the
safety officer.
6.5 Instructors.
6.5.1 All instructors shall be qualified to deliver fire fighter
training according to the authority having jurisdiction.
6.5.2* The participating student-to-instructor ratio shall not
be greater than 5 to 1.
6.5.3 Additional instructors shall be designated when factors
such as extreme temperatures or large groups are present,
and classes of long duration are planned.
6.5.4 The instructor-in-charge shall be responsible for full
compliance with this standard.
6.5.5 Prior to the ignition of any fire, instructors shall ensure
that all protective clothing and equipment specified in this chapter
are being worn according to manufacturer’s instructions.
6.5.6 Instructors shall take a head count when entering and
exiting the building during an actual attack evolution conducted
in accordance with this standard.
6.5.7 Instructors shall monitor and supervise all assigned students
closely during the live fire training evolution.
6.5.8 The instructor-in-charge shall consider the circumstances
of each training session and make provisions for the
rest and rehabilitation of members operating at the scene,
including medical evaluation and treatment, food and fluid
replenishment, and relief from climate conditions, in accordance
with the circumstances of the training session. (See
Annex D.)
6.5.9 Where concurrent, multiple, live fire training evolutions
are being conducted in a specifically designed burn
building, the identity of the instructor-in-charge shall be clear
to all participants.
6.5.10 It shall be the instructor-in-charge’s responsibility to
coordinate overall burn building fireground activities to ensure
proper levels of safety.
-
09-16-2003, 03:43 PM #8Forum Member
- Join Date
- Jan 1999
- Location
- MA
- Posts
- 1,744
Fire tactics
Go there and read.....then read some more. Talk with Batt 18 ( the forums) Paul grimwood in real life. He probably has as much time in containers and most of us do breathing.
There are plans out there for containers as flashover simulators, as fire attack structures, plus also backdraft simulators (you can't go inside that one!)
Bottom line is, research, research, research. Do I think there is value in your ideas...yes. But as has been said, make sure you follw the standards and accepted practices to the letter.
-
09-16-2003, 04:21 PM #9MembersZone Subscriber
- Join Date
- Jul 1999
- Location
- Flanders, NJ
- Posts
- 13,537
Also, trained instructors and solid procedures are every bit as important as construction.
-
09-16-2003, 06:35 PM #10Junior Member
- Join Date
- Jun 2003
- Location
- Phoenix Arizona
- Posts
- 11
Burn Suilding Alternatives
Check out Fire Tactics
Last edited by jimibinaz; 09-18-2003 at 08:19 PM.
-
09-16-2003, 06:42 PM #11Junior Member
- Join Date
- Jun 2003
- Location
- Phoenix Arizona
- Posts
- 11
Mobile Burn Units
stay safe
Last edited by jimibinaz; 09-18-2003 at 08:06 PM.
-
09-16-2003, 07:15 PM #12Member
- Join Date
- May 2002
- Location
- Starkville, MS
- Posts
- 32
Samson,
Be careful of your construction materials if you are going to burn class A fuels. I have heard of brick burn facilities that started out burning pallets and such, and then switched to LP gas because of the expense of replacing deteriorating brick. The bricks in the gas fueled facilities last longer because the temperature does not get as hot (because of the fuel and/or automated controls).
radioguy,
I have similar ideas for a local training facility - we should touch base through email. You definitely want to check out the wealth of info on Paul Grimwood's site, firetactics.com.
-
09-16-2003, 08:06 PM #13Junior Member
- Join Date
- Jun 2003
- Location
- Phoenix Arizona
- Posts
- 11
I think you can get a 40 foot unit.
DiggerLast edited by jimibinaz; 09-18-2003 at 08:05 PM.
-
09-18-2003, 12:20 PM #14MembersZone Subscriber
- Join Date
- Nov 2002
- Location
- Western NC
- Posts
- 156
The more I investigate this, the more it seems feasable. The biggest problem for me at least is finding a suitable location, one that has enough flat area for parking and training (we are in the mountains), is available for use, and is far enough from homes and business locatiosn that we will not bother them with smoke.
We have soem very talented welders, plumbers, and heavy equipment owenr/operaters on our deprtment, so we will be able to do a lot of the work ourselves.
Another aspect I am going to have to do a great deal of research into is water runoff. I am sure there are a large number of state and federal regulations regarding this, I know we are exempted on real fire scenes but I doubt a training facility will get the same exemptions. the required water drainage system my cost more than anything else......
We talked about the idea of this the other night, and we think it could be a winning idea. We have a severe lack of decent training facilities in the area, and many departments would be able to take advantage of this facility. I would like to see it made available to everyone, for those departments that can afford to pay on a cost per man hour basis, and for thsoe that are on a tighter budget instead of paying a trade for labor assisting with upkeep or helping provide us with materials for training such as old vehicles, pallets, etc. that way the facility would be available for all and it would help us offset the cost and time needed to keep it up.
-
09-18-2003, 02:10 PM #15MembersZone Subscriber
- Join Date
- Oct 2002
- Posts
- 177
Water runoff will be a major obstacle...most new training facilities I have scene have water treatment plants and restore the water to a certain standard....Check you state and fed pollution control.
-
09-21-2003, 07:02 PM #16
would it be possible to get grants at either the state, federal, local or corporate level to help cover the costs? i don't know if it will work, but it's an idea
If my basic HazMat training has taught me nothing else, it's that if you see a glowing green monkey running away from something, follow that monkey!
FF/EMT/DBP
-
09-22-2003, 04:56 PM #17
I got slated earlier today for 'plugging' our new book. I can tell ya, I am just passing on info here. We have written a book with design plans also on CD for those interested. There are a whole range of container based designs for single and multi-compartments; L Blocks; H Blocks; U blocks and multi levels etc. You can get these here in the book 3D Firefighting But George W is right! The quality of the instructors, and training, are even mnore important than your construction.
Be safe.........
-
09-22-2003, 05:27 PM #18Member
- Join Date
- May 2002
- Location
- Starkville, MS
- Posts
- 32
Paul,
That is great news that you are including sample plans in your book. It will go a long way toward legitimizing designs for those who want to build it themselves.
I agree about with you on the quality of instruction being highly dependent on the quality of the instructor when it comes to this type of training. In your upcoming book, do you set forth any guidelines or minimum standards for a qualified instructor?
-
09-22-2003, 06:14 PM #19
Absolutely yes! We try to cover every angle on quality, standards and qualification of instructors. This text and associated CD is based upon every question that has ever come through my mail box over the past five years concerning CFBT live fire training and the 3D techniques. I think the answers are here in one text. How to design and construct CFBT facilities; how to teach in them; how to learn in them; and how to put the 3D techniques into practise for real.
-
09-24-2003, 02:08 PM #20
I was gone a few days and lost track of this thread.
I am very excited that Mr Grimwood has visited this thread. I appreciate your input very much.
Put me down as interested in your book, where can I order it?
I have only recently discovered Tactical FireFighting. I have come across some of your work before, and I seem to recall seeing you on a TV program of some sort, IIRC it involved a test burn in a room with an observation window. (sorry if I am recalling another person).
I have a few questions concering safty features.
Do you (or anybody else) use any sort of dry sprinkler system? I was envisioning a robust/fire hardened sprinkler sytem with sprinkler heads made from thick steel. A Charged line could be hooked up to the system when live burning training activities are on going. If there was some sort of difficulty or safety concern, the sprinkler system is only a valve away.
That was one safety mechanisim that seemed easy enough to implement.
Thanks.-Brotherhood: I don't know half of you half as well as I should like; and I like less than half of you half as well as you deserve.
-Mistakes: It could be that the purpose of you life is to serve as a warning to others.
-Adversity: That which does not kill me postpones the inevitable.
-Despair: Its always darkest before it goes Pitch Black.
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)

LinkBack URL
About LinkBacks