    Default Does anyone have .................

    something like this ? I was out driving by our Meijer's store that is being built and when I found the FDC it was 5 " Stortz vs the 2 two andd halfs we normally see. The closest hydrant is about 100' feeet away and I thought this would be a much better and easier way to feed the sprinkler system. So like I said anyone else got an LDH sprinkler intake ?
    IACOJ both divisions and PROUD OF IT !
    Pardon me sir.. .....but I believe we are all over here !
    ATTENTION ALL SHOPPERS: Will the dead horse please report to the forums.(thanks Motown)
    RAY WAS HERE 08/28/05
    LETHA' FOREVA' ! 010607
    I'm sorry, I haven't been paying much attention for the last 3 hours.....what were we discussing?
    "but I guarentee you I will FF your arse off" from>
    http://www.firehouse.com/forums/show...60#post1137060post 115

  2. #2
    Forum Member
    NFD159's Avatar
    Join Date
    Feb 2003
    Location
    Northwood, OH
    Posts
    253

    Default LDH sprinkler intake

    We were just out this morning doing a pre plan on the new NAMSA building and discovered the same thing 5" locking storz connection with a (private) hydrant within about 100'.
    Last edited by NFD159; 03-02-2004 at 06:39 PM.

  3. #3
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,586

    Default

    We still have 3" conections for standpipes and sprinklers, but since we went to 4" hose, all new construction with sprinklers and standpipes will have 4" LDH connections for same! We use 4" to 2 1/2" adapters to feed sprinklers and standpipes.
    Last edited by CaptainGonzo; 03-02-2004 at 09:53 PM.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  4. #4
    Forum Member

    Join Date
    Feb 2004
    Posts
    46

    Default

    All our FDCs are 3", but our SOPs state that we supply them with 5"hose via a 21/2x5" adaptor. We keep the adaptor and 50' of hose together in a comp. for this purpose. I really dont understand this. Maybe ya'll do?? Also, rode by one of our new apartment complexes the other day and found they had 1 1/2" intakes on each building for the residential sprinkler systems. Also, the complex had dry hydrants (in addition to standard hydrants) and we dont have a piece of hard suction hose on the whole dept....lol

  5. #5
    Senior Member
    shammrock54's Avatar
    Join Date
    Jul 2001
    Posts
    445

    Default

    We make all new construction that require sprinkler to have 4" LDH couplings.
    Member IACOJ & IACOJ EMS Bureau
    New England FOOL
    "LEATHER FOREVER"
    As always these are strictly my own opinions and views

  6. #6
    MembersZone Subscriber
    ullrichk's Avatar
    Join Date
    Jan 2002
    Location
    Deleted by the forum gremlins
    Posts
    1,663

    Default

    I've seen them, I like them, but I don't have any in my jurisdiction.

    The Storz on the steamer connection of a hydrant is a trick setup, too. I don't have any of those either.
    ullrichk
    a.k.a.
    perfesser

    a ship in a harbor is safe. . . but that's not what ships are for

  7. #7
    55 Years & Still Rolling
    hwoods's Avatar
    Join Date
    Jun 2002
    Location
    Glenn Dale Md, Heart of the P.G. County Fire Belt....
    Posts
    10,740

    Smile Not Here.................

    Haven't seen any yet. All of everything in Maryland (well, almost) has 2.5 NFH Couplings because many years ago, the Maryland Fire Service got together and had a law passed that REQUIRED all Fire Hose Couplings to be National Standard Fire Hose Thread. Since Storz doesn't have threads.......... There is LDH in Maryland, but I have no idea how they got past the law. Stay Safe....
    Never use Force! Get a Bigger Hammer.
    In memory of
    Chief Earle W. Woods, 1912 - 1997
    Asst. Chief John R. Woods Sr. 1937 - 2006

    IACOJ Budget Analyst

    I Refuse to be a Spectator. If I come to the Game, I'm Playing.

    www.gdvfd18.com

  8. #8
    Forum Member
    firenresq77's Avatar
    Join Date
    Oct 2000
    Location
    Northwest Ohio
    Posts
    5,213

    Default

    Like 159 said, we got one at the new NAMSA building, and I believe we may have them at 1 or 2 of the other newer buildings, but I'll have to check........

  9. #9
    Forum Member

    Join Date
    Jul 2003
    Location
    Plymouth Meeting, PA
    Posts
    298

    Default

    In my first due and from what I have seen driving around, most new buildings have 5" storz connection at the FDC. I do not know if this is required by code or not, but I am assuming that it is. I am also seeing a lot of hydrants being placed approx. 100' from the connection. Hope this helps.

  10. #10
    MembersZone Subscriber

    Join Date
    Mar 2000
    Location
    Dayton, OH
    Posts
    180

    Default

    We are getting more and more connections with 5in inlets around here. We don't require it, but its nice.

    At least in Ohio hydrant need to be within 75 feet.

    Cheers,
    Scott

  11. #11
    Forum Member
    CaptOldTimer's Avatar
    Join Date
    Jun 1999
    Location
    Virginia
    Posts
    7,273

    Default

    All the building around here that have FDC are of the 2-1/2" inlets. My department supplies them via 4" LDH with a 4" storz X 2-1/2" adapter.

    This works well. We try to make sure the lay out is short. I am still under belief that suppling FDC's with LDH is wrong and using the 2 2-1/2" hose lines or 2 3" hose lines to supply a FDC is far better.

    The 2-1/2 and 3 inch hose can withstand higher pressures than the LDH, but the LDH can flow more water with less friction loss.

    I know that I am opening a can of worms here, but hoses being used that are the smaller line are constructed to handle the higher pressure.

    I have seen pressures as high as 250 to 300 pounds or better going into FDC's to get the correct pressure up on higher floors or to supply the system correctly.

    I am also in favor of NOT having any hose intakes or discharges on the pump operator side of the apparatus for safety. Have them all on the right side or rear of the apparatus. Another BIG can of worms here. :-)





    Stay Safe & Well out there.....

  12. #12
    Forum Member
    Trkco1's Avatar
    Join Date
    Jun 2001
    Location
    New Jersey
    Posts
    270

    Default

    Having a 5 inch stortz FDC intake for a single story warehouse or commerical occupancy sounds like a great idea. But I would be a little skeptical using it on any mid or high rise building because of the pressures needed for the upper floors.
    FTM-PTB-EGH-RFB-KTF

  13. #13
    MembersZone Subscriber

    Join Date
    Dec 2000
    Posts
    1,719

    Default

    The Little Twp. only has two occupancies with FDCs (grocery store & nursing home).

    Both are double 2 1/2" connections and our SOG is to connect two 3" lines to them.
    FTM-PTB-DTRT

  14. #14
    MembersZone Subscriber
    Duffman's Avatar
    Join Date
    Aug 2002
    Location
    Chicago area
    Posts
    780

    Default

    Our code requires a 5" storz connection.
    "We shouldn't be opening firehouses in Baghdad and closing them in New York City."

    IACOJ

  15. #15
    Forum Member
    StayBack500FT's Avatar
    Join Date
    Apr 2002
    Posts
    2,236

    Default

    We have 4" storz on ours.
    May we never forget our fallen, worldwide.

    I.A.C.O.J. Safety/Traffic Control Officer

    E6511

    "Who's Who Among American Teachers" - 2005, 2006 Honoree

  16. #16
    MembersZone Subscriber
    ullrichk's Avatar
    Join Date
    Jan 2002
    Location
    Deleted by the forum gremlins
    Posts
    1,663

    Default

    Originally posted by CaptOldTimer
    The 2-1/2 and 3 inch hose can withstand higher pressures than the LDH, but the LDH can flow more water with less friction loss.

    I know that I am opening a can of worms here, but hoses being used that are the smaller line are constructed to handle the higher pressure.

    LDH is available in supply and attack pressure ratings. Make sure you have the right stuff and you have all of the advantages of LDH with none of the drawbacks. (Except weight!)
    ullrichk
    a.k.a.
    perfesser

    a ship in a harbor is safe. . . but that's not what ships are for

  17. #17
    dazed and confused
    Resq14's Avatar
    Join Date
    Dec 2000
    Location
    New England
    Posts
    1,993

    Default

    We've been requiring 5" Storz FDC's for a while.
    God Bless America!Remember all have given some, but some have given all.
    Google Is Your Friend™Helpful forum tip - a "must see" if you're new here
    Click this to search FH Forums!

  18. #18
    Keepin it real
    Fyrechicken's Avatar
    Join Date
    Oct 2001
    Location
    Erial, New Jersey
    Posts
    287

    Default

    We went thru about 3 years ago and had all properties with a FDC change over to a single 4" Storz connection.
    Peace to our fallen brothers...

    9/11/01 NYC WTC

    7/4/02 Gloucester City, NJ

    -=IACOJ=- The proof is in the crust

    ......Work hard, play hard, and always have fun along the way......

  19. #19
    MembersZone Subscriber
    tyler101's Avatar
    Join Date
    Feb 2002
    Location
    Ashland, OH
    Posts
    471

    Default

    I didn't know that Storz was spelled with a "T".

  20. #20
    Forum Member
    Weruj1's Avatar
    Join Date
    Dec 1999
    Location
    NW Ohio
    Posts
    7,857

    Default

    let me help ya with that it is actually STORTZ........not pronounced "stores"
    IACOJ both divisions and PROUD OF IT !
    Pardon me sir.. .....but I believe we are all over here !
    ATTENTION ALL SHOPPERS: Will the dead horse please report to the forums.(thanks Motown)
    RAY WAS HERE 08/28/05
    LETHA' FOREVA' ! 010607
    I'm sorry, I haven't been paying much attention for the last 3 hours.....what were we discussing?
    "but I guarentee you I will FF your arse off" from>
    http://www.firehouse.com/forums/show...60#post1137060post 115

  21. #21
    Forum Member
    NFD159's Avatar
    Join Date
    Feb 2003
    Location
    Northwood, OH
    Posts
    253

    Default Storz vs Stortz

    Ok, in my original reply to weruj, I spelled it Stortz also, then I noticed several other people had it spelled Storz, so I edited my post and changed the spelling. Now I googled it and found sites with it spelled both ways. Lets just say the connections for the BFH.

  22. #22
    Forum Member
    StayBack500FT's Avatar
    Join Date
    Apr 2002
    Posts
    2,236

    Default

    I have always used "storz"....but I also eat black olives with dark mustard too...go figure?
    May we never forget our fallen, worldwide.

    I.A.C.O.J. Safety/Traffic Control Officer

    E6511

    "Who's Who Among American Teachers" - 2005, 2006 Honoree

  23. #23
    MembersZone Subscriber
    CrossBro1's Avatar
    Join Date
    Feb 2003
    Posts
    187

    Default

    All new construction in my city is required to install LDH connections

  24. #24
    MembersZone Subscriber
    Dickey's Avatar
    Join Date
    Feb 2000
    Location
    Wisconsin
    Posts
    5,112

    Default

    We have a city ordinance and building code that if you have a sprinkler, you must have a 4" STORTZ coupling for the sprinkler connection. That was enacted a long time ago, not sure when. Buildings that had the 2 2 1/2" fittings were to be retrofitted to match the 4" Stortz within a certain time limit. Used it once, was much better working with one big hose with an easy connection vs. 2 smaller hoses with threads. Just makes things a little quicker.

    Keep your head down and your powder dry.
    ____________________________
    Lt.Jason Knecht
    Altoona Fire Rescue
    Altoona, WI

  25. #25
    MembersZone Subscriber
    fieldseng2's Avatar
    Join Date
    May 2002
    Location
    St. Louis, MO
    Posts
    826

    Default

    All of our new construction commercial, assisted living, nursing homes, Apts. and the like have 5" storz intakes.

    Fortunately, we haven't had to use them for real, yet.