    No its not a post about which ones better.


    I have heard many different things about SCBA's, bhat is actually in them. What kind of air?
    Ryan

    I.A.C.O.J. Probie

    You gain strength, courage, and confidence by every experience in which you really stop to look fear in the face. You must do the thing which you think you cannot do. -Eleanor Roosevelt

    Lets not forget those lost on 9-11-01

  2. #2
    Forum Member

    Join Date
    Dec 1999
    Location
    Swanton Fire Dept. Swanton, Vermont
    Posts
    479

    Default

    In 99.9% of the ones I know about it is the same air you are breathing in your station. (Or place you get them filled.)

    You only compress the air, run it through filters/dryer and then into the cascade. From the cascade the bottles are filled to your needs 2216/3000/4500psi.

    Rebreathers, (very limited use in Fire Service to my knowledge.) may give a shot of O2 in to the air to keep the O2 level up.

  3. #3
    MembersZone Subscriber
    SamsonFCDES's Avatar
    Join Date
    Jul 2003
    Posts
    1,708

    Default

    There can also be things like carbon monoxide and polutants from apparatus exhaust unless you have your compressor set up properly to draw air from the cleanest place possible.

    NASA developed a liquid air SCBA that last for a very long time but is open circute. It has just plain old air compressed and then chilled to be liquid, sort of like a propane tank.

    Rebreathers recylce the air from your lungs, have small oxygen bottles to add O2 into the mix, and CO2 scrubbers to clean out C02.

    Drager makes one that is still used for fire fighting in situation that require long duration use, IE 4 hours and such.

    But when it all comes down to it you are just breathing regular air.

    For SCUBA there are special mixes, IE NITROX and such that are designed to lessing the ill effects of diving deep and such. Some are helium and oxygen IIRC.
    -Brotherhood: I don't know half of you half as well as I should like; and I like less than half of you half as well as you deserve.
    -Mistakes: It could be that the purpose of you life is to serve as a warning to others.

    -Adversity: That which does not kill me postpones the inevitable.

    -Despair: Its always darkest before it goes Pitch Black.

  4. #4
    Forum Member

    Join Date
    Jun 2002
    Posts
    235

    Default

    OSHA has minimum requirements for breathing air used in SCBAs:

    1910.134(i)(1)(ii)
    Compressed breathing air shall meet at least the requirements for Grade D breathing air described in ANSI/Compressed Gas Association Commodity Specification for Air, G-7.1-1989, to include:

    Oxygen content of 19.5-23.5%;
    Hydrocarbon (condensed) content of 5 milligrams per cubic meter of air or less;
    Carbon monoxide (CO) content of 10 ppm or less;
    Carbon dioxide content of 1,000 ppm or less; and
    Lack of noticeable odor.

    You should have your air supply tested on a regular basis.

    I once had a situation where several firefighters became ill during a training session in a non IDLH atmosphere. We used some detector tubes to test the air and discovered that it contained contaminants. The dept. sent a sample out for a regular test and the results confirmed what we suspected. The compressor was repaired and additional tests were conducted to determine that the problem was resolved.

    We had another case where a dept filled their tanks from a cascade system that used bottles from a local industrial gas supplier. Once again, we had firefighters report being light headed during an exercise. We tested the air with our O2 meter and discovered that the level of oxygen in the air was low.

    Don't assume your air is Grade D unless it has been tested.
    Last edited by HM604OH; 11-15-2004 at 12:20 PM.

  5. #5
    Forum Member
    Rescue101's Avatar
    Join Date
    Jun 2001
    Location
    Bridgton,Me USA
    Posts
    8,162

    Default

    Ours is grade E and tested annually by an independant lab. T.C.

  6. #6
    Forum Member
    Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,702

    Default

    Ditto to Rescue101 except our testing is quarterly. I believe Grade E is required for SCUBA tanks.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?