Thread: Cafs sysytem

  1. #1
    Member
    Join Date
    Nov 2002
    Posts
    35

    Question Cafs sysytem

    I'm looking for some techniques on how to train personel on a cafs system. Anyone got some....


  2. #2
    Forum Member
    Join Date
    Nov 2004
    Posts
    710

    Default

    What training have you had with a CAFS system? or did they just dump the truck on you and say have at it. Best practice for CAFS is practice everything. If you are using it as a first line of attack the only way to practice is at a live fire training centre or by doing NFPA compliant live fire training.

    Cafs when used in interior attack is diiferent in the fact that it does not remove heat. To prevent flame spread simply coating the walls will prevent further combustion. Again the bad thing is - heat is not removed and roll over can still occur - somewhat reduces the chance but it can still occur. Finding the fire quickly is key, get a quick knockdown and ventilate, or ventilate and then knockdown!

    Excellent for exposure protection, just foam what you want to protect. Your cafs dealer should have some training tapes on how the cafs operates. As I said interior work is slightly dfferent with the CAFS.
    One thing - If you are using it for interior attack make sure the hose is rigid as regular hose will kink going around corners, and that really sucks!

  3. #3
    Forum Member rescue133lt's Avatar
    Join Date
    Jul 1999
    Location
    Gahanna, Ohio
    Posts
    41

    Default

    I agree with Dave, at least I agree with his first statement. The best way to really train with CAFS is in a live fire scenarios. Almost anyone can make foam with a CAFS system, but to get the ratios correct and to see how different ratios affect a fire takes an acutal fire.

    I disagree with Dave in that CAFS WILL absorb heat quite effectively. Dave, if you are having this problem I suggest that you reevaluate the ratios used on your truck. It could be that your operators are creating a "dry" foam. In that instance, you will have difficulty with heat absorbtion.

    Secondly I disagree with the statement about kinked hoses being a problem with a CAFS system. We have, in training and with the CAFS mfg. rep, kinked the hose back on itself with little or no noticeable decrease in the flow from the nozzle.
    Lt. John Kaltenbach
    Mifflin Fire - Rescue 133
    Gahanna, OH

    "Vermögen bevorzugt das tapfere!"

  4. #4
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    Coupla suggestions.
    Kinking the hose is more of a problem near the discharge end of the hose, the kink will shear the bubbles and may not have a chance to reform before exiting the valve and this makes the foam very wet, which isn't all that bad if you want to use this as a technique to adjust the wetness at the nozzle. The regular attack hose with foam in it may be too flexible near the nozzle. A solution to this is to use a short sectiong of hard hose like the reel-teck or piece of rubber hose then the valve. This gives the nozzleman much more control when shurting and opening the valve quickly, oh! yeah, just a reminder, ther is no water hammer action with slamming a CAFS valve shut.

    One other tip that might help with interior attack, with the discharge valve full open, lay your gloved fingers gently into the stream to create a great fan stream that will paint a wall or cieling in a New York Minute, also partially closing the discharge valve will strip some of the air from the bubbles to change the foam from dry to wet for different conditions. Momentarily shut the valve to build up the surge pressure and pop the valve open to blast the stream through both blackened sheet rock walls to extinguish a fire in the other room. Same technique works for hidden fires in the ceiling. Use the .3% concentrate setting to create a fast water draining foam and use .5 to 1% for long lasting tuff vapor and smoke sealing blankets but please use a wet setting to soak into the class A materials before you apply a long lasting blanket.

    Hope this helps.
    Attached Images Attached Images  
    Mark Cummins

  5. #5
    Forum Member
    Join Date
    Nov 2004
    Posts
    710

    Default

    My apologies, I didnt explain myself well enough. Foam does have heat reducing tendancies just not as efficient as water. After a class A fire we moved the remnants and the radiant heat in the ground was substantial, with water you dont have the same affect as the water drips through and cools everyhting, we found the foam blankets and retains the heat longer than with water. Good for a thermal barrier.

    The kinked hose prevention was a recommendation from our MFG. They recommended that the first section of hose be rigid to prevent kinks close to the nozzle and limitting the foams capabilities. This is precationary only and we dont want to take the chance of being the ones to find out that in the right circumstances a kinked hose will deminish your effectivness. This is a recomendation only!

    cfire3 has some good points - cafs is excellent for powering through drywall. Excellent for penetrating!

    Hope this clarifies
    Dave

  6. #6
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    Dave, thanks for the compliment.

    Have you tried the CAFS on slick ice, or used it in sub-freezing weather? I wish the guys up in the frozen eastern US knew how the foam freezes into a snow-like condition to improve traction and see how things that are covered with the frozen foam do not become icebound.

    The CAFS makes tank water a better choice than frozen hydrants for initial attack and the foam that freezes in the structures is much safer than the heavey and slick ice from water applications.
    Mark Cummins

  7. #7
    Forum Member
    Join Date
    Nov 2004
    Posts
    710

    Default

    Hey cfire3,

    Yeah we have used it in sub zero weather, it can actually get pretty dangerous. The foam freezes, but then the water freezes underneath the foam - can be a slip hazard especially with snow and ice on the ground. The foam itself becomes crusty - almost like styrofoam, retty intresting when it freezes. The main use for our cafs is rural fires so our main water source is tanker. Running at the proper mix our 300 gallon tank can last a long time. The CAFS system is very resource friendly.

    Im a little confused about your improved traction comment, do you have a secret for turning the foam into traction?
    Dave

  8. #8
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    Dave, no secret to the foam traction except we sometimes use the old lignin soap from the paper mills as the foaming agent, it has some resin in it that makes a squeeky non-slip foam. But the frozen foam you mentioned is the same as I was refering to, particularly when we apply the foam to the black ice or glazed ice that is nearly impossible to even stand up on. This type of ice forms from water applications and is supper slick.

    We increase the concentrate ratio up to 1% and back the water volume down to create a really dry foam that does not drain any water before it freezes, this foam has a texture, like you said, crusty or heavy snow, for a demonstration; find an area of ice formed with water and cover half of it with foam to see which side is easier to walk on. The foamed side is like walking in snow but if you aren't careful you can bust your, But it's a great improvement over the untreated side.
    Mark Cummins

  9. #9
    Forum Member
    Join Date
    Nov 2004
    Posts
    710

    Default

    lol, I honestly have never even thought of using it for traction. I geuss we are used to the slippery ground aound here! None the less we will give it a try - just need it to freeze again! Do you guys use this often for traction for rigs or personell?

  10. #10
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    Originally posted by Dave404
    lol, I honestly have never even thought of using it for traction. I geuss we are used to the slippery ground aound here! None the less we will give it a try - just need it to freeze again!

    Do you guys use this often for traction for rigs or personell?

    Hahaha, the good news is, down here in Texas, we don't get a lot of super cold weather but the bad news is the dozen or two times it does get really cold, nobody knows how to behave in it. So yes, we do actually use the foam to allow us to move around a little better.

    I have heard of some snowland brothers that have added a colored food dye to the foam to mark the snow covered roadways and other buried things like hydrants, entrances and covered cars.

    I guess if we added some sugar to the stuff?????? well, maybe better not go there,,,
    Mark Cummins

  11. #11
    Forum Member
    Join Date
    Nov 2004
    Posts
    710

    Default

    Never heard of the coloring of snow either - then again we only get a couple of big dumps of snow a year - never had a problem finding a hydrant. Intresting solutions - thats thinking outside the box for you.
    What type of CAFS are you guys running? Ours is a dedicated CAFS truck. 3cyl diesel engine runs the pump and compressor. 300 gal water and 2 - 5gallon pails of foam, with 2 spares in other compartments. Truck is also equiped with rescue tools air/hydraulic cutter spreader combo, medical equipment, ventilation and a cascade bottle. Mounted on an F-550 4x4 chasis. Only a two seater and because its classed as a mini pump, it is backed up with a pump and tanker.
    Ill try to add a picture!

  12. #12
    Forum Member
    Join Date
    Nov 2004
    Posts
    710

    Default

    Try this!
    Attached Images Attached Images  

  13. #13
    Forum Member
    Join Date
    Jan 2001
    Location
    Madison, NJ USA
    Posts
    159

    Default

    Hello all,

    My experiences with CAFS as an interior attack have been good. Both for fire knockdown and heat absorption capabilities. The key to any interior attack is to meet or exceed the critical application rate for extinguishment of the fire. CAFS is a delivery system. The extinguishment and cooling happens as a result of the water that is applied. For those who say cooling is poor with CAFS attack, I can only conclude that you are not flowing enough water (GPM). Our 1 3/4" attack lines flow approximately 100 GPM with 30-35 CFM of air, using a straight bore 15/16” tip. This is around the 3:1 ratio. Water is the prime ingredient. The class "A" foam makes the water more efficient and the application of the water and class "A" foam with CAFS makes it "SUPER" efficient. Whether you are using plain water or CAFS the basic principles of firefighter are still applicable, "Big Fire, Big Water" and "Put the Wet Stuff on the Red Stuff". For those who are having cooling issues with their CAFS, try a "wetter" mixture. Less air, more water.

    As far a kinking goes, no problems. We run our main pump discharge pressure at 80 to 100PSI for 1 3/4" handlines. If you run at a lower PSI, Yes, it will kink. Also I have experienced more kinking issues with rubber jacketed fire hose. The cloth jacketed fire hose lines have not given us any kinking problems.

    As far as freezing and safety goes, CAFS when it freezes to the ground is safer to walk on the plain water. It sounds like frozen snow when you walk on it and traction is improved. “CRUNCH, CRUNCH, CRUNCH……”

    I say this all the time, training is the key to successful CAFS operations. Also using a good quality class "A", UL listed, environmentally friendly foam works the best.

    Hope this helps.

    Be safe,

    Captain Lou
    "GOT FAOM?"

  14. #14
    Forum Member
    Join Date
    May 2004
    Location
    Is this heaven? No, it's Iowa....
    Posts
    50

    Default

    Like Captlou stated

    You can't absorb heat without water. Our attack setting is 2:1 and we are still usting the 2 1/2" attack line on well off structures. The only problems that we have had are people changing over the that wonderful, shaving cream thick "tree flock" that is drier then Thanksgiving stuffing. We had guys apply this to a collapsed garage fire shortly after we took delivery while just starting the overhaul process. They couldn't figure out why they couldn't put the remaining fire and hotspots out as they had coated the *%$# out of this pile. Only after running out of concentrate and reverting back to plain water were they able to get the fire out. A great assest became useless when combined with the human error. When you use it right, the results are beyond impressive. Long story short, you have still got have lots of water and as always, wet(foamy stuff) on the red stuff!!!

    Ryan

  15. #15
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    [QUOTE]Originally posted by Tallyho74
    [B]Like Captlou stated

    You can't absorb heat without water. Our attack setting is 2:1 and we are still usting the 2 1/2" attack line on well off structures.


    Ryan, great comments. I'm interested in your use of the 2 1/2 hose for structure fires, please tell me what type and size nozzle you use for the discharge? And can you descibe the 2:1 setting? Is that 2 cf of air(14.96 gallons) to 1 gpm? Which would be approx. an expansion of 15 gallons of foam per gallon of water.

    What CFM volume compressor does your CAFS have? and What pressure do you operate the 2 1/2?
    Mark Cummins

  16. #16
    Forum Member
    Join Date
    May 2004
    Location
    Is this heaven? No, it's Iowa....
    Posts
    50

    Default

    No problem. We are using a Hale CAFSpro system. We have a 220cfm compressor mated to a 1750gpm Q-max pump. We are using 1 3/8" TFT pistol grip smooth bores for 1 3/4" and 2 1/2" lines. They told us 2:1 in user training was most effective. Our air control is set at "0.5" as the preset. The setting should provide us 2 gallons water per CFM air i.e. 200gpm water/100cfm through 2 1/2" attack line. We usually run the pump at around 105-115psi. We found that there is very little friction loss. Compensating for that was causing a tremendous amount of nozzle reaction. The following (hopefully)is a pic of our Rescue Engine.

  17. #17
    Forum Member
    Join Date
    May 2004
    Location
    Is this heaven? No, it's Iowa....
    Posts
    50

    Default

    second attempt
    Attached Images Attached Images  

  18. #18
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    Now that's a beautiful ride. Not to mention a kick-ss capability. Thanks for the post.

    Would it be possible for you to post any pictures of your CAFS throwing the foam and describe the setings?

    I will try to do the same with a 1.5 hose using the pistol grip 1 3/8 smoothbore with no tip, Water- flowing 50 gpm @ 110 psi, Air- flowing 125 cfm @ 110 psi, concentrate set at .5%


    The Tolar creosote lumber mill fire called on every fire department in Hood County, there were 4 portable tank shuttle operations set up in the middle of the main highway and six engine crews fighting the fire for more than 4 hours. Then the call went out to Johnson County to send a CAFS unit from Joshua VFD.
    It took 30 minutes for the two CAFS hoses to completely extinguish the fire and stop the toxic smoke and polluted water run-off into the nearby creek. And the State paid $2,500 for the foam application because it was claimed to be a pollution reduction response.
    Attached Images Attached Images  
    Mark Cummins

  19. #19
    Forum Member
    Join Date
    Jan 2001
    Location
    Madison, NJ USA
    Posts
    159

    Default

    Hi all,

    I have a question for Tallyho74.

    Based on your nozzle seletion. If you had 250' of 1 3/4" hose stretched, charged and flowing CAFS on an interior attack. Now, that guy "MURPHY" shows up and for whatever reasons your air compressor stops and/or your foam pump stops working. All you are left with is plain water. My question is, What is your game plan for this situation to protect the firefighters on the line and to continue the operation? Aagin I base this question on your statement that you are flowing straight out of the 1 3/8" open bale of the nozzle with no tip.

    Thanks for the help.

    Captain Lou
    "Got Foam?"

  20. #20
    Forum Member
    Join Date
    Sep 2001
    Location
    Joshua Texas
    Posts
    178

    Default

    Originally posted by CaptLou
    Hi all,

    I have a question for Tallyho74.

    Based on your nozzle seletion. If you had 250' of 1 3/4" hose stretched, charged and flowing CAFS on an interior attack. Now, that guy "MURPHY" shows up and for whatever reasons your air compressor stops and/or your foam pump stops working. All you are left with is plain water. My question is, What is your game plan for this situation to protect the firefighters on the line and to continue the operation? Aagin I base this question on your statement that you are flowing straight out of the 1 3/8" open bale of the nozzle with no tip.

    Thanks for the help.

    Captain Lou
    "Got Foam?"


    I appologize for jumping in here but I get asked this question a lot too. It's a good question, and obviously the manufactures try their best to design a dependable unit, but "Murphy" does have his ways. Here's my solution, it's pretty simple, just partially close the full flow valve and the restriction creates a wide agle high velocity water spray pattern similar to a combo tip. The hose becomes twenty times heavier and the excess water starts runing out the front door just like the regular water applications do. Call for another tanker and look for a good hydrant.

    Mark Cummins