Everyone:
I am curious what other depts are using for Fire Department connections. Our community has recently started requiring 4" storz connections. What is your department requiring on new sprinkler/standpipe systems and why?
Mark
+ Reply to Thread
Results 1 to 20 of 20
Thread: FDC & Large Diameter Hose
-
12-30-2005, 07:43 AM #1MembersZone Subscriber
- Join Date
- Jun 2003
- Location
- Barnstead, NH
- Posts
- 217
FDC & Large Diameter Hose
-
01-02-2006, 08:12 PM #2
New construction: 4 inch FDC's, because we went to 4" LDH a couple of years ago. We carry adapters for the standard 2.5" FDC's.
"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
Lt. Ray McCormack, FDNY
-
01-03-2006, 01:56 PM #3
Our township requires 4" stortz on all new construction, and I think on extensive remodels. Don't know the reason for the requirement.
Stay Safe & Bring 'em Home!
Eddie C.
I.A.F.F. Local 3008
"Doin' it for lives n' property"
** "The comments made here are this person's views and not that of the organizations to which I am affiliated" **
-
08-19-2008, 12:25 PM #4MembersZone Subscriber
- Join Date
- Jun 2007
- Location
- Berwyn, Illinois
- Posts
- 4
-
08-19-2008, 02:55 PM #5
You may want to look at this thread before you decide on LDH at all.
http://forums.firehouse.com/showthre...537#post979537"we will bankrupt ourselves in the vain attempt at absolute security"
Pres. / General Dwight D. Eisenhower
-
08-19-2008, 03:16 PM #6
2.5" FDC's are still the norm in our jurisdiction, although a handful of occupancies have installed 5" FDC's to match the LDH we carry.
I prefer the 2.5" FDC for a couple of reasons. First, several of the 5" FDC's don't have any tension release (i.e. 30-degree elbow) built into them, so the entire weight of the 5" being pulled up to the FDC itself. This can cause premature separation of the hose from the swivel with enough weight and/or time, and obviously presents a safety hazard.
The other reason is the limited operating pressure of the 5" LDH we carry (185psi). If we're going to a multi-story building that requires higher pressures to meet the fire conditions, nozzle selection, or any other factor, I would hate to think that the line I have supplying the FDC from my pumper would be the limiting factor in water availability.
As RJK said, there is redundancy in having the 2nd 2.5" line on a standard FDC too.Career Fire Lieutenant
Volunteer Chief Officer
Never taking for granted that I'm privilged enough to have the greatest job in the world!
-
08-19-2008, 05:59 PM #7
Sure, but solved easily enough with a $100 adapter. Most of our LDH inlets are less than 18-24 inches off the ground though, so there are only a couple of feet suspended.
Good point, and also easily solved. I have ordered up some 250psi LDH for just this role (and for supplying the triple 2.5 manifold on an extended attack scenario). We keep a couple of short 50' rolls in the engineers compartment so they can be rolled out to the FDC when needed. It is still engineers choice around here.The other reason is the limited operating pressure of the 5" LDH we carry (185psi). If we're going to a multi-story building that requires higher pressures to meet the fire conditions, nozzle selection, or any other factor, I would hate to think that the line I have supplying the FDC from my pumper would be the limiting factor in water availability.
If you have true High-Rise construction (i.e. more than our 6-7 storey limit) and anticipate needing more than 250-300PSI, you would certainly need to reconsider using your LDH. It seems like most high-rise depts use low pressure nozzles or smooth bores to overcome that challenge.
Can't argue that, but the time savings in rolling out a single 100 length of LDH is very nice when you are manpower limited. I think it is dept preference, and I don't think we can argue for or against either technique that definitively.As RJK said, there is redundancy in having the 2nd 2.5" line on a standard FDC too.
Never argue with an Idiot. They drag you down to their level, and then beat you with experience!
IACOJ
-
08-19-2008, 08:22 PM #8
You make some excellent points. I'll address each of them individually...
As for the adapters, you're correct about that. This will take a change of the county ordinance to get the contractor to take care of installing these. The FD isn't going to spring for the adapter when they feel it's the responsibility of the developer and/or occupant to supply it.
High-pressure LDH is an option also. In the interest of standardization, our department buys each size of hose the same (be it 1.75", 2.5" 3", etc), so I don't know if that's going to work for us. I commend your department for thinking forward on this matter.
As for the nozzles, we're carrying 50PSI breakaway nozzles that most people operate (and rightfully so, IMHO) with the fog nozzle taken off. This does obviously keep us from needing that extra 50PSI through the FDC supply hose, but there may be a chance for extra long stretches in some occupancies. Just thinking ahead on that...
You're also right about manpower and it's effect in estabishing a flow to a FDC. I didn't want to appear to come across that 2.5" is the only way, I was simply giving some thoughts on what I've seen work in my particular locality. I again thank you for taking the time to post some well-constructed thoughts.Last edited by BoxAlarm187; 08-19-2008 at 08:25 PM.
Career Fire Lieutenant
Volunteer Chief Officer
Never taking for granted that I'm privilged enough to have the greatest job in the world!
-
08-19-2008, 10:17 PM #9MembersZone Subscriber
- Join Date
- Dec 2002
- Location
- Central NJ
- Posts
- 1,214
I don't understand the point of 5" FDC's versus double or triple 2 1/2's. You can move a few hundred GPM through short single lays of 3" hose. Its easier to drag, and not so hard to move when charged. It seems like the storz connection on FDC's is becoming the new in vogue idea, maybe I'm missing the major advantage, but I just don't see it.
-
08-20-2008, 08:28 AM #10
"we will bankrupt ourselves in the vain attempt at absolute security"
Pres. / General Dwight D. Eisenhower
-
08-20-2008, 10:00 AM #11
-
08-20-2008, 12:58 PM #12
Not LDH. I think seatbelts, enclosed cabs, SCBA, improved PPE, and automatic dishwashers in the [station] kitchens are great innovations.
- - - - - - - - - - -
It is obvious that there is a large generation gap here, and no matter what I think and say will be agreeable. That's why they pay me to stay at home, away from the crowds. Stay safe and you will experience this too... before your past-time is up here on planet earth.
Last edited by 1OLDTIMER; 08-20-2008 at 02:39 PM.
"we will bankrupt ourselves in the vain attempt at absolute security"
Pres. / General Dwight D. Eisenhower
-
08-20-2008, 01:21 PM #13
And sometimes it justifies itself.
When we switched to LDH for our various supply roles, we were amazed at how much better and easier it worked. Our pumper worked half as hard and did twice the work overnight.
Mind you we started with an old undersized and overworked pumper and a marginal hydrant system, so we saw the benefits day one. Larger pumpers might not see the need or benefit on day to day ops. At least until they start needing that kind of water.
Once you get past the arguement that "The hose is heavy", LDH just makes life easier.Never argue with an Idiot. They drag you down to their level, and then beat you with experience!
IACOJ
-
08-20-2008, 02:39 PM #14
Career Fire Lieutenant
Volunteer Chief Officer
Never taking for granted that I'm privilged enough to have the greatest job in the world!
-
08-24-2008, 08:02 AM #15
LDH Transport:
Wrong thread...moved post:
Last edited by 1OLDTIMER; 08-24-2008 at 11:52 AM.
"we will bankrupt ourselves in the vain attempt at absolute security"
Pres. / General Dwight D. Eisenhower
-
08-24-2008, 11:38 AM #16Forum Member
- Join Date
- May 2001
- Location
- Greensboro, NC USA
- Posts
- 1,265
My Dept's Fire Prevention Bureau starting allowing (and encouraging I think) commercial occupancies to install 4" Storz FDC's.
My Dept uses double jacketed 4" LDH, service tested to 300 psi.
A while back I saw one from the street that looked too big. Turns out it was 5". And it was just two buildings down from the Fire Prevention Bureau offices. If we'd had a fire we'd be screwed as we don't carry 4"-5" adapters. A few companies have them, but only a handful.
I think going with 4" was a mistake. At flows above 1,000 GPM the friction loss makes long lays impractical, unless you're using 2,000 GPM two stage pumps.Last edited by txgp17; 08-24-2008 at 08:05 PM.
The American people will never knowingly adopt Socialism. But under the name of 'liberalism' they will adopt every fragment of the Socialist program, until one day America will be a Socialist nation, without knowing how it happened. --Norman Mattoon Thomas, 6 time presidential candidate for the Socialist Party of America
-
08-24-2008, 09:17 PM #17Forum Member
- Join Date
- Dec 2007
- Posts
- 115
This is a case of one size fits all does not work. LDH for a FDC is over kill in may occupancies because the automatic sprinkler demands are so low. Take a look at what NFPA 13, The Installation Of Sprinkler System requires for a sprinkler system in the following occupancies:
Light Hazard .10/1500 or about 150 gpm
Occupancies with Quantity/combustibility low
ow rates of heat release
Churches
Clubs
Offices
Museums
Residential
Restaurant seating areas
Ordinary Group 1 .15/1500 or about 225 gpm
Occupancies with
Low to moderate amount of combustibles
Moderate rates of heat release
Storage less than 8 feet
Automobile parking and showrooms
Beverage manufacturing
Laundries
Restaurant service areas
Ordinary, Group 2 .20/1500 or about 300 gpm
Occupancies with Moderate combustible load
Moderate rates of heat release
Storage less than 12 feet high
Dry cleaners
Mercantile
Printing and publishing
Wood products
Machining and assembly
Can you feed these occupancies with one or two 2.5" or 3" hose?Fire Sprinklers Save Firefighters’ Lives Too!
Check out below "Hands On Fire Protection Seminars". Chubb as reduced the cost of a 1 day seminar to $175 for fire and building officials.
-
08-29-2008, 10:02 AM #18MembersZone Subscriber
- Join Date
- May 2008
- Posts
- 6
Engine to FDC connection
Just for clarification - all of you that are having to pump to 4" Storz FDCs - are all your engines set up with large diameter discharges? If not - how are you setting up to feed the FDC?
Thanks,
Mike
-
08-30-2008, 05:50 PM #19
5" storz here with a 30 degree elbow.
"Loyalty Above all Else. Except Honor."
-
08-31-2008, 12:47 AM #20
Only one of our ladders has a 4" discharge, and it is only used for relay pumping. We usually discharge through a 2 1/2" port.
You can often feed your pump capacity (i.e. <1500gpm) through a good 2 1/2" discharge into a short lay of 4" hose. Considering you only need to push a few hundred gpm's into most FDC's, the standard discharge is more than adequate. Particularly with the reduced FL of the LDH.Never argue with an Idiot. They drag you down to their level, and then beat you with experience!
IACOJ
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
Why the 1 3/4 and fog nozzle for standpipe operations?
By stugats in forum Firefighters ForumReplies: 71Last Post: 02-20-2009, 06:24 PM -
ISO Company Personnel
By FIRE549 in forum Firefighters ForumReplies: 20Last Post: 05-16-2007, 06:15 PM -
World Of Fire Report: 04-07-04
By PaulBrown in forum World of Fire Daily ReportReplies: 0Last Post: 04-09-2004, 06:46 AM -
What a load! FE Nozzles and hose debate
By imtxff44 in forum Firefighters ForumReplies: 62Last Post: 10-20-2003, 12:38 PM -
Large Diamter Hose
By Ed Kline in forum Firefighters ForumReplies: 10Last Post: 04-10-2001, 01:01 AM

LinkBack URL
About LinkBacks