    Default Low Pressure Nozzles

    We have run multiple tests, used them in the field and it is obvious that low pressure nozzles have advantages. Looking for your opinions. Who is running with 50psi fog or 75psi fog nozzles with breakaway smooth bore? What is your smooth bore diameter?

    We are almost set to go 150gpm at 50psi fog, break away with 7/8" tip.

    My only big concern is hose kinking. We staff with 4, so if one is at the hydrant, this leaves an officer plus nozzleman, I am not convinced that two persons will be able to manage the kinks, or maybe they will. What do you think?

    Should we go 150gpm at 75psi in order to reduce the kinks, even if it increases nozzle reaction?

    Hmmm, these are my sticking points. ANY HELP?

    Oh by the way we are looking to replace automatic TFT's.


  2. #2
    MembersZone Subscriber
    Join Date
    May 1999
    Location
    Here, There, Everywhere
    Posts
    4,191

    Default

    Quote Originally Posted by PITT8TRUCK
    We have run multiple tests, used them in the field and it is obvious that low pressure nozzles have advantages. Looking for your opinions. Who is running with 50psi fog or 75psi fog nozzles with breakaway smooth bore? What is your smooth bore diameter?

    We are almost set to go 150gpm at 50psi fog, break away with 7/8" tip.

    My only big concern is hose kinking. We staff with 4, so if one is at the hydrant, this leaves an officer plus nozzleman, I am not convinced that two persons will be able to manage the kinks, or maybe they will. What do you think?

    Should we go 150gpm at 75psi in order to reduce the kinks, even if it increases nozzle reaction?

    Hmmm, these are my sticking points. ANY HELP?

    Oh by the way we are looking to replace automatic TFT's.
    Some questions first...

    -How do you stretch? Do you pull preconnects...or do you pull what is needed?
    -Do you backstretch or do you perform in-line (forward) lay mostly...I would guess the later.
    -What is the deployment like? Is it come off in a bundle/pile or is it nicely payed out by the nozzle man or whomever?
    -What type of load?
    -How long is this memeber at the hydrant, what are his duties after the water supply is secured?
    -Do you assign someone to chase kinks?

    FTM-PTB

  3. #3
    Early Adopter cozmosis's Avatar
    Join Date
    Jan 1999
    Location
    Arkansas
    Posts
    1,921

    Default

    Quote Originally Posted by PITT8TRUCK
    My only big concern is hose kinking. We staff with 4, so if one is at the hydrant, this leaves an officer plus nozzleman, I am not convinced that two persons will be able to manage the kinks, or maybe they will. What do you think?
    We are switching to nozzles very similar to yours in the near future. Many of our members were concerned about hose kinking. However, in side-by-side tests using a flowmeter with our current TFT automatic nozzles, the fixed gallonage nozzles delivered more water while kinked in two than the old nozzles.

  4. #4
    Forum Member Tillerman17's Avatar
    Join Date
    Dec 2004
    Location
    New York state of mind
    Posts
    139

    Default

    Replacing the TFT"S is a good start. Have you considered simply using a simple shutoff with a 15.16th tip in place of the fog nozzles. You will have the flow you need and avoid the headaches with the fog nozzles. lastly, since raising the PDP is out of the question why not make your hydrant man follow the kinks up th line after charging the hydrant? He doesn't stay there does he? Good luck.
    Never trust a smiling dog.
    The uniform you're given is free, but it comes with a history. Do the right thing when you're in it.
    PTB, EGH, FTM.

  5. #5
    Forum Member Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,645

    Default

    We use Akron Breakapart Assault nozzles. 75psi 175gpm. Smooth slug is 7/8". Have not had a problem with kinking hose and plenty of gpm. Easy for 1 guy, even easier with a backup.

    We switched from 100psi TFT's to these on all of our 1 3/4" lines. Gives you everything in a simple way, wide fog, narrow fog, straight stream, solid stream.

    I hate Saberjet nozzles, move this for that, move this for that. Too complicated.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  6. #6
    MembersZone Subscriber E229Lt's Avatar
    Join Date
    May 2000
    Posts
    2,987

    Default

    Should we go 150gpm at 75psi in order to reduce the kinks, even if it increases nozzle reaction?

    I think you should be setting you flow goal at 180 gpm. JMO

  7. #7
    MembersZone Subscriber
    Join Date
    Feb 1999
    Location
    Pittsburgh, PA USA
    Posts
    29

    Default

    We use mainly preconnected attack lines, 150, 200, 250, anything longer needed is connected off of a 3" leader line. We use a minuteman hose load all have a hundred feet on your shoulder and we normally stretch from the pumper. We have hydrants every 300ft and good water pressure so we normally forward lay with the engine and it is positioned near the building leaving room for the truck. The hydrant person is to make connections, follow the supply line back to the engine, grab a tool, and follow the line in to his officer. He or she should be chasing the kinks. But I will be honest, training and discipline of hose management are definetly needed. Always a bundle of people at the tip.

    Thanks again

  8. #8
    MembersZone Subscriber
    Join Date
    Feb 2001
    Location
    Sturgis, MI. U.S.A.
    Posts
    198

    Question Honest Question

    What are the advantages to lower line & nozzle pressures?

  9. #9
    Forum Member Tillerman17's Avatar
    Join Date
    Dec 2004
    Location
    New York state of mind
    Posts
    139

    Default

    Quote Originally Posted by TriTownship600
    What are the advantages to lower line & nozzle pressures?
    TriTown, Simply put, fog nozzles requiring 100psi at the tip call for higher PDP to achieve the required GPM's. Low pressure fogs require less PDP making your life on the knob a little easier. 50psi smooth bore tips are while requiring less PDP will deliver 185 GPM making your life even easier.
    Never trust a smiling dog.
    The uniform you're given is free, but it comes with a history. Do the right thing when you're in it.
    PTB, EGH, FTM.

  10. #10
    Forum Member FyredUp's Avatar
    Join Date
    Jul 1999
    Location
    Rural Wisconsin, Retired from the burbs of Milwaukee
    Posts
    9,847

    Default

    PITT8TRUCK...

    Both my volly and career FD use the 200 at 75 psi combo nozzle.

    My career fd uses it with a 15/16 slug tip behind the combo nozzle on 1 3/4 inch hose. My volly FD uses it with a 1 1/4 inch slug behind the combo nozzle on 2 inch hose.

    We have not had an issue with kinking. These are fixed gallonage nozzles and not automatics.

    We have been using these for several years and our guys love them. If I can be of further help let me know.

    FyredUp

  11. #11
    MembersZone Subscriber
    Join Date
    Dec 2002
    Location
    Central NJ
    Posts
    1,214

    Default

    Consider this option...

    A 150 GPM at 75 PSI combo tip (akron assault) with 1" smooth bore slug.

    This offers you two seperate flow capabilities without any pump discharge pressure change.

    Figure it this way...

    The 150@75 tip has FL of 35 PSI per 100' and a NP of 75. 35+75= 110 PDP fpr 100' line.

    The 1" tip (210 GPM) has a FL of 62 PSI per 100' and a NP of 50. 62+50= 112

    For any match of combo tip and smooth bore tip ideally you want a combination that doesnt require a pump pressure change to allow the smooth bore tip to flow its rated flow, for simplicity sake. To determine which two tips are a good match, simply make sure the friction loss for the goven flow rating plus nozzle pressure for each nozzle tip (smooth bore and combo tip combination) adds up to the same number.

    To calculate the difference...

    Combo tip first: Nozzle pressure+friction loss=PDP (for given length of line)
    Subtract 50 from the above calculation to determine the FL difference at 50 PSI tip pressure. Look up on a chart the closest FL to your answer and thats the SB tip flow youll need. Find the closest SB tip/flow match.

    7/8"=160 GPM
    15/16"= 180 GPM
    1"= 210 GPM

    You can also opt for akron Assault 150@50 tip with 7/8" smooth bore for essentially equivalent flows at the same tip pressure (50).

    Hopefully I explained that correctly and did all my math right!
    Last edited by MG3610; 03-16-2006 at 04:53 PM.

  12. #12
    Forum Member Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,645

    Default

    MG3610, last night during drill we ran the flow meter to check. We used 1 3/4" line at 150' with Akron breakapart nozzle, the smootbore is 7/8". At approx. 125psi, gpm from nozzle was 175 with adjustable and 185 without.

    I agree entirely with you on the nozzle choice as it gives those common flows with common pressure and lots of options.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  13. #13
    Forum Member
    Join Date
    Jul 2004
    Location
    Virginia Beach Virginia
    Posts
    125

    Default

    On our Engine we have a Elkhart SM 30F nozzle on 2 crosslay's, 15/16 smooth bore on our 2nd 1 3/4. On our 1 1/2 trash line we use a marauder akron 95gpm nozzle. For our high rise hose we us the LA 200 @ 75psi break a way to a 15/16 smooth bore nozzle.

  14. #14
    Forum Member
    Join Date
    Feb 2004
    Location
    California
    Posts
    584

    Default

    Just a thought on the 50psi vs 75psi, if you go with the 50 psi, its one less thing for the engineer to worry about, just 50 psi for smoothbore and fog.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. What a load! FE Nozzles and hose debate
    By imtxff44 in forum Firefighters Forum
    Replies: 62
    Last Post: 10-20-2003, 12:38 PM
  2. Relief Valve
    By koziol41 in forum The Engineer
    Replies: 6
    Last Post: 02-07-2003, 08:53 PM
  3. AFFF or FFFP
    By Lallo in forum Firefighters Forum
    Replies: 6
    Last Post: 03-18-2002, 08:34 PM
  4. Low Pressure (75psi) Nozzles
    By emmett in forum Meet and Greet
    Replies: 2
    Last Post: 06-08-2000, 10:17 PM
  5. Low Pressure Break Apart Nozzles
    By BFD 210 in forum Fireground Tactics
    Replies: 30
    Last Post: 01-29-2000, 12:41 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts