O.K. folks - I need some help.
It seems the "powers that be" here at my paying gig (a.k.a. office job) want to put all new extinguishers on our floor. I thought that was downright spiffy until I found out they ordered all Halotron Units.
Info. this is a 24 Hour office environment (i.e. someone is here around the clock) including a small kitchen (pretty much a residential type - non commercial). Cube-ville office space with 1 Laptop/Desktop per cube, A control center with large desks having 3-5 computers and 10-14 monitors each. 3 Extra large display walls (super huge monitors) and 2 separate computer / telecommunications rooms complete with Uninterpretable Power Supply (UPS) systems (Battery Banks). Also included are the usual assortment of office type files & other "ordinary combustibles"
Now I agree that with the large amount of electronic equipment (and the critical nature of some of the mainframe & telecom equipment) that some Halotron is a good thing. I am however not thrilled that (from what little I know) these are not rated for Class A use.
If I am wrong in my thinking or understanding of Halotron please let me know - otherwise please help me find some information / literature that I can use to help educate these folks that keeping a couple of these Dry Chem units we already have is a good idea.
Thanks in advance.
+ Reply to Thread
Results 1 to 3 of 3
-
11-13-2006, 04:03 PM #1
Help/Info Needed - Halotron Extinguishers
Take Care - Stay Safe - God Bless
Stephen
FF/Paramedic
Instructor
-
11-14-2006, 12:29 PM #2
Disregard - I found the info I needed online. Halotron IS actualy Class A rated at 11 Lbs and larger extinguisher sizes. (Althought I'm still not entirely thrilled about having all Halotron cans).
Take Care - Stay Safe - God Bless
Stephen
FF/Paramedic
Instructor
-
11-16-2006, 05:24 AM #3
Sweet, glad I could help you out!
:PJason Knecht
Assistant Chief
Altoona Fire Rescue
Altoona, WI
IACOJ - Director of Cheese and Whine
http://www.cheddarvision.tv/
EAT CHEESE OR DIE!!
Thread Information
Users Browsing this Thread
There are currently 1 users browsing this thread. (0 members and 1 guests)
Similar Threads
-
3%-6% foam in water extinguishers
By smokeater81 in forum Firefighters ForumReplies: 61Last Post: 12-12-2010, 05:40 PM -
ISO Company Personnel
By FIRE549 in forum Firefighters ForumReplies: 20Last Post: 05-16-2007, 06:15 PM -
SOP's for Volunteer FD
By rumlfire in forum Volunteer ForumReplies: 14Last Post: 08-01-2006, 10:35 PM -
Thermal Imaging SOG's
By wtfd92 in forum Firefighters ForumReplies: 23Last Post: 06-27-2001, 08:41 PM -
Do Extinguishers hide accelerants
By SJNorman in forum Fire InvestigationReplies: 10Last Post: 05-06-2001, 08:49 PM

LinkBack URL
About LinkBacks