    Arrow Nursing Homes & Sprinklers

    Should all nursing homes be required to install sprinkler systems?

    KANSAS CITY, Mo. (AP) - Advocates of automatic sprinklers for
    nursing and group homes pointed to Monday's deadly blaze at an
    Anderson group home as a grim reminder of why the systems should be
    standard equipment in long-term care facilities.
    Ten people died and at least 18 were sent to hospitals early
    Monday after a fire broke out at the Anderson Guest House, a care
    home for the elderly and mentally ill. The home had smoke alarms
    but no sprinklers.
    "You can't prevent fires from happening at all times," said
    Susan Feeney, a spokeswoman for the American Health Care
    Association, a trade group representing nursing homes. "However,
    having automatic sprinkler systems and other fire safety devices
    can save lives, which is critically important for very vulnerable
    patient populations, including the frail, elderly and disabled."
    It's unclear how Monday's victims died, either by burns or smoke
    inhalation, or whether they were adequately warned by smoke alarms.
    In Missouri, only certain types of long-term care facilities are
    required to have comprehensive sprinkler systems and only in
    certain circumstances, such as those that house residents on a
    second floor. The one-story Anderson Guest House was built before
    1980 and was not required to have sprinklers.
    "We'll definitely be looking to see what the investigation
    finds and looking at what changes might be needed and then
    certainly we'll see whether any of our current regulations were
    violated," said Nanci Gonder, a spokeswoman for the Department of
    Health and Senior Services. "The investigation should yield
    information about what happened, maybe about how the response
    happened. We'll be looking at all of that."
    About 80 percent of nursing homes have comprehensive automatic
    sprinkler systems, according to a January survey of American Health
    Care Association members. Gonder said the survey did not include
    group homes, which often face less-stringent requirements by the
    states that license them.
    The association began pushing for mandatory sprinklers for all
    nursing homes after deadly blazes in facilities in Connecticut in
    Tennessee.
    In February 2003, a patient suffering from dementia and multiple
    sclerosis set fire to her bed and burned down the Greenwood Health
    Center in Hartford, Conn., killing 16 residents. Six months later,
    in September 2003, a fire killed 15 patients in Nashville, Tenn.
    Neither nursing home had an automatic sprinkler system.
    Recently, the federal agency that oversees the safety of nursing
    homes issued a proposed regulation calling for all nursing
    facilities to have comprehensive sprinkler systems. The agency has
    asked for comments about how much time an estimated 2,500 older
    facilities without sprinklers should have to comply with its
    proposed rule.
    Currently, federal regulations require that newly constructed
    nursing homes or those undergoing major renovations to include
    sprinkler systems. But states are free to enact more-stringent
    requirements. Fourteen now require nursing homes to have sprinkler
    systems to operate, according to the American Health Care
    Association.
    "It is most certain this will happen," Feeney said of the
    regulation.
    But Feeney noted the proposed regulation would not affect group
    homes, which are not subject to the same federal oversight.
    Still, she said the deadly Missouri blaze could lead to a push
    for individual states to toughen their fire-safety requirements
    governing group homes.
    Evvie Munley, senior policy analyst for the American Association
    of Homes and Services for the Aging, said her group has long
    supported comprehensive sprinkler systems for nursing homes as long
    as the facilities are given adequate money and time to meet the
    requirement. She noted some owners may choose to build new
    facilities rather than retrofit older buildings.
    And she said there could be support for requiring other types of
    long-term care facilities to add sprinkler systems.
    "I think no one is going to oppose the idea of sprinklers for
    long-term care facilities with vulnerable populations, but the same
    considerations would apply - resources and a phase in to allow
    people to contract for this and acquire it," Munley said. "No one
    would oppose sprinklering for facilities with vulnerable
    populations."

    (Copyright 2006 by The Associated Press. All Rights Reserved.)

    Smoke alarms are not enough. The elderly can not react quickly enough to evacuate a building. Their physical limitations can prevent them from a successful escape. Surely, sprinkler systems would save lives. Your opinions?
    Last edited by NJFFSA16; 11-28-2006 at 01:45 AM.
    Proudly serving as the IACOJ Minister of Information & Propoganda!
    Be Safe! Lookouts-Awareness-Communications-Escape Routes-Safety Zones

    *Gathering Crust Since 1968*
    On the web at www.section2wildfire.com

  2. #2
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,870

    Default

    An obvious no-brainer. Any building that houses elderly, infirm or persons otherwise unable to exit rapidly should be fully sprinklered.

  3. #3
    Forum Member

    Join Date
    Apr 2004
    Location
    Bossier Parrish, Louisiana
    Posts
    10,630

    Default

    This is an issue that the fire service really needs to push. The fact that we allow facilities like this to exist without sprinklers is a national disgrace. Unfortunatly, I have seen fire chiefs use unsprinklered facilities as a justification for more apparatus amd manpower, while, they have made no efforts to push for mandatory un-grandfathered sprinkler ordiances in thier communties. This issue, and sprinkler ordiances in general, often get the typical blasea fire department response that prevention in general often gets.

  4. #4
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    It is a no brainer... but remember, when it comes to installations of sprinkler systems, the bean counters are the ones who will be out in force crying how "expensive" it is. The nursing home industry is huge, and they have a huge lobby pushing for higher payments from Medicare and insurance than for fire safety.

    Of course, the entertainiment industry doesn't do us any favors by
    misrepresenting the way a sprinkler system operates...
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  5. #5
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default I'm going to draw a dinstinction here...

    ...in the full knowledge that nuance is not rewarded on this forum, between acute-care nursing homes and much smaller sheltered care or group homes.

    It is easy to mock the expense arguments, but the fact is that for small (<20 bed) facilities, the sprinkler requirement is a deal-breaker. Most of these small homes are run by small business people or non-profits, and have little clout. In fact, the stand in opposition to the acute-care nursing home lobby, which would like everyone over 70 in an acute-care environment whether they need that level of care or not.

    Forcing small, community-based facilities out of business is bad public policy. Here in New Hampshire, these facilities literally take people off the street. I have a friend in the business, and he has literally admitted people out of homeless shelters, or out of ERs after they were scooped from the gutter. Also here in New Hampshire, the state has gotten very agressive (frankly more aggresive than they have the right to be under existing legislation and administrative rules) about forcing any life safety issue they think might possibly be helpful. As a result, the number of sheltered-care beds has declined by 40% in 10 years. So what happened to these people? They are either in acute-care nursing homes, and great cost to the state and great cost to their own well-being, or they are back on the street.

    I am a big believer that mandates from government should never be unfunded. If you require sprinklers, you need to be sure the rates the state pays for these people's care covers that cost. Sadly, this is not currently the case anywhere in New England.

    All a long way of saying, "No, it's not a no-brainer".

  6. #6
    Forum Member

    Join Date
    Jan 1999
    Location
    Berwyn Heights, MD, USA
    Posts
    124

    Default

    I'm in line with randsc.

    Ideally, a nonsprinklered nursing home would go out of business.

    Unfunded government mandates keep businesses and employment down.

    That being said, the medicare / medicaid & other state & federal laws should be changed such that, among other things, sprinklers are required to recieve reimbursement.

  7. #7
    Forum Member
    DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,584

    Default

    The cost of installing a sprinkler system is miniscule compared the the dollar figure of the wrongful death lawsuits that will come about from a fire in a nursing home that leads to patient deaths.

    The cost of design and installation can be financed.

    Here in Massachusetts, sprinklers are required to be retrofitted to restaurants and nightclubs that seat over X amount of people ( don't have the exact number in front of me at this time). There was a grace period to allow for the owners of said properties to have the systems installed. Some have dragged their feet and are now crying to the media that it's too expensive, will disrupt their business, etc. etc. etc.
    Last edited by CaptainGonzo; 11-28-2006 at 10:59 AM.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  8. #8
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default Nope

    Quote Originally Posted by CaptainGonzo
    The cost of installing a sprinkler system is miniscule compared the the dollar figure of the wrongful death lawsuits that will come about from a fire in a nursing home that leads to patient deaths.

    The cost of design and installation can be financed.

    Here is Massachusetts, sprinklers are required to be retrofitted to restaurants and nightclubs that seat over X amount of people ( don't havr the exact number in front of me at this time). There was a grace period to allow for the owners of said properties to havre the systems installed. Some have dragged their feet and are now crying to the media that it's too expensive, will disrupt their business, etc. etc. etc.

    With all due respect, you're wrong. That "miniscule" cost is puching providers out of business every day. Banks like to see an adequate cash flow before they finance anything. You want to require sprinklers for everything, fine. But if you do, the reimbursement rates MUST rise.

  9. #9
    MembersZone Subscriber
    Diane E's Avatar
    Join Date
    Dec 1998
    Location
    Maryland (but always a Long Islander first)
    Posts
    1,103

    Default

    You need to help push the issue:

    HR 1131 Fire Sprinkler Incentive Act -- will never make the floor for a vote this year because it's too costly (can you put a cost on a life?), 165 cosponsors.

    HR 4491 -- Nursing Home Fire Safety Act of 2005 -- 23 cosponsors! This legislation would require the Secretary of Health and Human Services to establish programs of direct loans and grants for retrofitting nursing facilities with automatic fire sprinkler systems. Gives priority to grant applications that demonstrate a need or hardship.

    Both measures have companion bills in the Senate and both will have to be re-introduced in the 110th Congress in January. HR 1131 will need a strong Republican backer since Rep. Curt Weldon lost.
    "When I was young, my ambition was to be one of the people who made a difference in this world. My hope is to leave the world a little better for my having been there."
    -- Jim Henson (1936 - 1990)

  10. #10
    Forum Member
    nmfire's Avatar
    Join Date
    Nov 2002
    Location
    Maryland (DC Suburb)
    Posts
    5,738

    Default

    You need a 3rd option for "Glad we have no nursing homes in my district"
    Even the burger-flippers at McDonald's probably have some McWackers.

  11. #11
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default That's more like it

    Something like the Nursing Home Fire Safety Act is what is required if a large (not "miniscule") cost is to be imposed on providers.

    I do think there is a arguement to be made that this is a state rather the federal responsibility, but that is a whole other thread.

  12. #12
    Forum Member
    res54cuecaptain's Avatar
    Join Date
    Jun 2006
    Location
    Somewhere over the rainbow....
    Posts
    276

    Default

    Yes, and DONT FORGET THE ATTIC!!!!!!

    http://kdka.com/topstories/local_story_309192331.html
    http://cms.firehouse.com/content/art...4&sectionId=45

    Nov 5, 2006 11:43 pm US/Eastern

    Senior Citizen Complex Goes Up In Flames
    Slideshow: Fire Guts Senior-Citizen Complex
    (KDKA) CABOT They're calling it one of the biggest fires in Butler County in years - startling even veteran firefighters.

    At about 11:30am Concordia Haven independent living apartments erupted in flames.

    Flames consumed the facility's roof in minutes.

    Officials say the wind helped spread the fire.

    About 137 residents live at the complex and fire crews rushed to make sure everyone was accounted for.

    Crews had a problem putting out the fire because of a shortage of water.

    Tankers rolled in to try to quench the flames.

    "I've lost everything except the clothes I have on," said resident Robert Waltenbaugh.

    His apartment was severely damaged, but he says he and his friend will make it.

    "Most of the men have been through the war.. World War two they seen a bunch of crap there. This is just another setback," he said.

    Despite the destruction, all of the residents and the firefighters escaped without injury.

    Most of the people were in church when the fire started.

    Concordia says it will house all of the displaced residents in a new facility nearby.

    The cause of the fire remains under investigation.

    ( MMVI, CBS Broadcasting Inc. All Rights Reserved.)




    Pennsylvania Senior Living Facility Destroyed
    137 senior citizens were displaced, but no reported injuries


    Updated: 11-09-2006 04:15:57 PM


    E-MAIL THIS STORY PRINT THIS STORY


    Michelle Simon
    Firehouse.com User-Submitted Photostory

    On Sunday, November 5, 2006 a fire destroyed a 114 unit, three story senior living facility located in Winfield Township, Butler County, Pa. The fire, which broke out at 11:30 Sunday morning, started in the roof area.

    Sixteen fire departments and over one hundred firefighters in a three county area battled the blaze for over two hours before bringing it under control. Because of no hydrants in the area, water had to be shuttled in from tankers filling from nearby ponds.

    Although there is no definite cause as yet, investigators believe the fire may have started in a roof area electrical room. The third floor of the complex was completely destroyed and heavy smoke and water damage was incurred on the first and second. Damages are estimated to exceed $10 million.

    Although all 137 senior citizens of the Concordia Haven complex are displaced, there were no reported injuries.

    watch the video (first and second one on the fire) to see what i mean. it was a hell of a fire...and a scary first half-hour when the original call was "Large fire, through the roof, residents trapped on the 3rd floor balconies."

    The building was a pretty good building as far as alarm and sprinkler systems are concerned. But, THE ATTIC WAS HOLLOW. Sadly, i THINK there MIGHT HAVE BEEN one or two firewalls in the middle of the building, which wouldnt have done much good. The fire got up to the attic and roof and spread like a wildfire from there.

    I wasnt personally at the call, but i know some guys who were, and everyone there did a hell of a job getting everyone out safely.

    http://www.hoopieworld.com/incidents...0506_cabot.htm
    Some more pictures there, especially the enroute ones showing the heavy smoke (they were 2nd due ambulance, and were there in about 5 minutes after the call came in)
    Last edited by res54cuecaptain; 11-28-2006 at 02:27 PM.
    First in, Last out, nobody left behind.....

  13. #13
    Forum Member
    furlofmalta's Avatar
    Join Date
    Nov 2006
    Location
    Northern California
    Posts
    59

    Default

    If I remember correctly we had this issue in California a few years back...
    The answer to the question is an obvious yes.
    Other mandates should include break away doors, multiple means of emergency egress, etc.

  14. #14
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default Funny you should mention that...

    Quote Originally Posted by furlofmalta
    If I remember correctly we had this issue in California a few years back...
    The answer to the question is an obvious yes.
    Other mandates should include break away doors, multiple means of emergency egress, etc.
    ..."that" being break away doors. Would you believe that in NH the Bureau of Health Facilities and Fire Marsh. want to mandate them, but the Bureau of Elderly and Adult Services wants to forbid them (they're a "wander" hazard)? And naturally, none of these agencies actually has written their requirements into their administrative rules, they are informal (but strictly enforced). So what the hell is the provider supposed to do?

    What makes this sort of bureaucratic crap especially irritating is that state agencies are operating outside the scope of their powers as defined by statute and administrative rules. The Bureau of Health Facilities admin rules expired 5 years ago. So why don't they just write these things into the rules? Because in NH, unfunded mandates are prohibited by the state constitution, and state law requires a cost-benefit analysis before new admin rules are enacted. So by keeping it on the QT, they hope to do whatever they like.

    This is the sort of thing that causes providers and property owners to cringe when they see the FD coming.

  15. #15
    IACOJ BOD
    FlyingKiwi's Avatar
    Join Date
    May 2002
    Location
    New Zealand
    Posts
    4,757

    Default

    ALL care hospices, elderly homes etc were required to do this a few years back down here after a spate of death fires.

    Did some bleat, did some go out of business, yes.

    Should they have been in the business if their facilities were not adequate?

    Should they have been allowed to care for elderly and or infirm without adequate protection in the first place?

    Did some of them have below minimum night time staff to cope with an emergency?

    Was there a settling period where adjustments were made, yes.

    Have we had any deaths to fire since. NO.

    Answer is obvious really.
    Psychiatrists state 1 in 4 people has a mental illness.
    Look at three of your friends, if they are ok, your it.

  16. #16
    Forum Member
    furlofmalta's Avatar
    Join Date
    Nov 2006
    Location
    Northern California
    Posts
    59

    Default

    Quote Originally Posted by randsc
    ..."that" being break away doors. Would you believe that in NH the Bureau of Health Facilities and Fire Marsh. want to mandate them, but the Bureau of Elderly and Adult Services wants to forbid them (they're a "wander" hazard)? And naturally, none of these agencies actually has written their requirements into their administrative rules, they are informal (but strictly enforced). So what the hell is the provider supposed to do?

    What makes this sort of bureaucratic crap especially irritating is that state agencies are operating outside the scope of their powers as defined by statute and administrative rules. The Bureau of Health Facilities admin rules expired 5 years ago. So why don't they just write these things into the rules? Because in NH, unfunded mandates are prohibited by the state constitution, and state law requires a cost-benefit analysis before new admin rules are enacted. So by keeping it on the QT, they hope to do whatever they like.

    This is the sort of thing that causes providers and property owners to cringe when they see the FD coming.
    I can't really remember the issue in Ca exactly but I think the same sort of beauracratic bs happened here as well.
    I think it took multiple MCIs at these places within the span of a year or two to finally force the issue.
    Hopefully New Hampshire shows more passion than Ca. and expidites the process.

  17. #17
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default

    Quote Originally Posted by FlyingKiwi
    ALL care hospices, elderly homes etc were required to do this a few years back down here after a spate of death fires.

    Did some bleat, did some go out of business, yes.

    Should they have been in the business if their facilities were not adequate?

    Should they have been allowed to care for elderly and or infirm without adequate protection in the first place?

    Did some of them have below minimum night time staff to cope with an emergency?

    Was there a settling period where adjustments were made, yes.

    Have we had any deaths to fire since. NO.

    Answer is obvious really.
    How is this level or care funded in NZ? Here, it is almost entirely Medicaid. The state and feds decide what level the reimbursement is at. So the provider has no control over revenue. Aggressive regulatory actions remove much of the provider's control over expenses. Staying solvent is a challenge to say the least.

    I asked my fried if this was really a business he wanted to be in. He said he would literally make more money by selling the real estate to be broken up into apartments, and parking his money in something like T-bills. So I asked him why the hell he didn't do that, and quit working 90 hours a week and dealing with the hassles from the state. His reply? "These people have no where else to go"

    Many of the providers approach sainthood. I hate to see them run down because they are stuck between a rock and a hard place, neither of their own making. I repeat, this is NOT a no-brainer.

  18. #18
    IACOJ BOD
    FlyingKiwi's Avatar
    Join Date
    May 2002
    Location
    New Zealand
    Posts
    4,757

    Default

    We have a mix of government pension that is paid for out of tax during your working life, and state benefits that are paid out of everyone elses tax. Along with personal contributions, weighted against value etc.

    Sometimes it gets tricky even for us to work the damn system out.

    I agree where someone is providing a "Social Service" for the state/city that the state/city should then be accountable for funding sprinklers, protection etc. This would be more of a homeless shelter style of arrangement as opposed to a Retirement Home / care facility.


    Long term care facilities that provide medical care should NOT even have been allowed to open their doors without adequate protection in the first place.

    If you are going to run a BUSINESS looking after the infirm or mentally ill, then having adequate protection for these people is part of the price of running the business.

    Whatever charity you provide to other cases is irrelevant. And yes he may be a "saint" but that does NOT negate his primary responsibilities to those in his care.
    Psychiatrists state 1 in 4 people has a mental illness.
    Look at three of your friends, if they are ok, your it.

  19. #19
    Forum Member

    Join Date
    Jan 1999
    Location
    Berwyn Heights, MD, USA
    Posts
    124

    Default

    this isn't a simple solution.

    If you mandate sprinklers, it will be more expensive to stay in business. Ergo, some care centers will go out of business, and some that would open will not.

    This will leave the marginal patients, namely the poor, without a care center. They will likely be forced to stay with their families, if they have any, who will not provide 24h care (they have to work), and are not likely to live in a sprinklered building.

    So, yes, you can, with a rule change, drastically reduce the likelihood of a senior citizen dying in a fire at a senior home. However, you will have likely increased the likelihood of senior citizen's dying in private homes. It is likely to be a net loss, because at least in a non sprinklered group home, you've got people awake and on duty 24/7.

  20. #20
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default

    Quote Originally Posted by SBrooks
    this isn't a simple solution.

    If you mandate sprinklers, it will be more expensive to stay in business. Ergo, some care centers will go out of business, and some that would open will not.

    This will leave the marginal patients, namely the poor, without a care center. They will likely be forced to stay with their families, if they have any, who will not provide 24h care (they have to work), and are not likely to live in a sprinklered building.

    So, yes, you can, with a rule change, drastically reduce the likelihood of a senior citizen dying in a fire at a senior home. However, you will have likely increased the likelihood of senior citizen's dying in private homes. It is likely to be a net loss, because at least in a non sprinklered group home, you've got people awake and on duty 24/7.
    Exactly right, thank you.

  21. #21
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,870

    Exclamation

    Its to bad that everyone needs to politic their case: safety vs. cost effectiveness. I'm sorry to say that I don't beluieve the majority of these facilities are in existance for the good of the elderly, yet the good of some peoples wallets. Yeah, yeah, non-profit! with the top offices earning large salaries. As Fire Service professionals we are charged with providing a minimum level of safety to the public.

    It is a No Brainer! I guess by a few arguements poor people don't deserve to live in safe facilities? Why do we have any codes at all? Most of these low-income homeless-elderly housing facilities take State and Federal funds; this should require minimum safety requirements. What's stopping someone from converting an old farmhouse in a rural area miles from the nearest vollie firehouse and no water? Nothing! We have many around our area. So a fire occurs in a facility where there are too few providers, no sprinklers, a long FD response with a water supply issue. Great! I hope I can afford to retire to an upscale nursing home.

    For those who say it isn't as easy as requiring sprinklers: What would you suggest the minimum safety standards be for an facility that houses people incapable of self-preservation?

  22. #22
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default With all due respect...

    [QUOTE=FlyingKiwi]

    Long term care facilities that provide medical care should NOT even have been allowed to open their doors without adequate protection in the first place.

    If you are going to run a BUSINESS looking after the infirm or mentally ill, then having adequate protection for these people is part of the price of running the business.

    [QUOTE]

    This is BS. Facilities open with adequate protection as defined by applicable law. In this case, the issue is whether changes can be made to that law AFTER the fact, without adjusting reimbursement levels.

    My analogy would be this. A municipality contracts with a fire district for a particular level of protection, for example, that a firehouse will be staffed with an engine company and a truck company, and in exchange the municipality will kick in a million dollars to the fire district budget. (am quite common arrangement in the States) There is then a bad fire, and the municipality decides it would feel more comfortable with TWO engine companies and a truck company. Should the municipalty be able to mandate that staffing level without adjusting its payment to the fire district?

    Look, like I said above, sprinkler everything if you want. Just be sure that the legislation mandating sprinklers includes a funding mechanism.

    To pretend that these things are cost-free is just silly.

  23. #23
    MembersZone Subscriber
    Diane E's Avatar
    Join Date
    Dec 1998
    Location
    Maryland (but always a Long Islander first)
    Posts
    1,103

    Default

    SBrooks this isn't a simple solution. If you mandate sprinklers, it will be more expensive to stay in business. Ergo, some care centers will go out of business, and some that would open will not.
    Which is why legislation with tax incentives and grants is important.

    Insurance premiums would be effected, too. Companies offer discounts for fire sprinklers. Better to pay out for a little water damage then for death. Wouldn't you rather put a family member in a safe environment?

    We kill between 3500 - 4000 people in this country each year due to fires (yes, not all of them are in places that would be sprinklered) and no one seems to bat an eye! If they're dumb enough to not have a working smoke alarm, then maybe a mandate is needed!? Obviously public education isn't working.

    There are also other options that may prove to be less expensive and use less water -- ever hear of Marrioff? http://www.marioff.com/

    Other sources of info:

    http://www.homefiresprinkler.org/hfsc.html

    http://www.nfsa.org/
    "When I was young, my ambition was to be one of the people who made a difference in this world. My hope is to leave the world a little better for my having been there."
    -- Jim Henson (1936 - 1990)

  24. #24
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default If you would actually read the thread...

    Quote Originally Posted by RFDACM02
    Its to bad that everyone needs to politic their case: safety vs. cost effectiveness. I'm sorry to say that I don't beluieve the majority of these facilities are in existance for the good of the elderly, yet the good of some peoples wallets. Yeah, yeah, non-profit! with the top offices earning large salaries. As Fire Service professionals we are charged with providing a minimum level of safety to the public.

    It is a No Brainer! I guess by a few arguements poor people don't deserve to live in safe facilities? Why do we have any codes at all? Most of these low-income homeless-elderly housing facilities take State and Federal funds; this should require minimum safety requirements. What's stopping someone from converting an old farmhouse in a rural area miles from the nearest vollie firehouse and no water? Nothing! We have many around our area. So a fire occurs in a facility where there are too few providers, no sprinklers, a long FD response with a water supply issue. Great! I hope I can afford to retire to an upscale nursing home.

    For those who say it isn't as easy as requiring sprinklers: What would you suggest the minimum safety standards be for an facility that houses people incapable of self-preservation?
    ...you would see that no one is suggesting that sprinklers not be mandated. What we (mostly me, I guess) suggest is that the reimbursement rates paid to providers need to reflect the cost of complying with the mandate.

    Otherwise, as SBrooks points out, what you will have is a dearth of providers, leading to people living in separate apartments with no attendents or fire safety equipment at all.

    As for the idea that cost-benefit analysis has no place in public safety discussions: Grow Up. If cost-benefit doesn't apply, I want all construction to be masonary. I want steel roofing, laid over full rafters. I want truss constrction banned. I want all interior flooring to be ceramic tile or poured concrete. I want a firehouse on every corner, manned 24/7 with two companies of 5 men each. It's a NO BRAINER! Every one of these things would prevent fire deaths and injuries!

  25. #25
    Forum Member

    Join Date
    Oct 2006
    Posts
    775

    Default DianeC

    Quote Originally Posted by DianeC
    Which is why legislation with tax incentives and grants is important.

    Insurance premiums would be effected, too. Companies offer discounts for fire sprinklers. Better to pay out for a little water damage then for death. Wouldn't you rather put a family member in a safe environment?

    We kill between 3500 - 4000 people in this country each year due to fires (yes, not all of them are in places that would be sprinklered) and no one seems to bat an eye! If they're dumb enough to not have a working smoke alarm, then maybe a mandate is needed!? Obviously public education isn't working.

    There are also other options that may prove to be less expensive and use less water -- ever hear of Marrioff? http://www.marioff.com/

    Other sources of info:

    http://www.homefiresprinkler.org/hfsc.html

    http://www.nfsa.org/
    I agree with everything in your post. This is the sort of reasonable and responsible approach that is needed. Therefore, it stands no chance at all of ever happening.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. More residential fire sprinklers in local ordinances
    By DaSharkie in forum Firefighters Forum
    Replies: 0
    Last Post: 12-05-2005, 10:10 AM
  2. UTah County Uerges Home Sprinklers
    By UTFFEMT in forum Utah
    Replies: 0
    Last Post: 06-20-2005, 02:13 PM
  3. fire drills in personal care / nursing homes
    By btfcsta3 in forum Firefighters Forum
    Replies: 0
    Last Post: 01-12-2004, 03:33 PM
  4. California Wildfires..Please Watch Over our Brothers and Sisters
    By captstanm1 in forum Firefighters Forum
    Replies: 28
    Last Post: 10-31-2003, 10:07 AM
  5. Replies: 0
    Last Post: 08-24-2003, 12:07 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register