    Default PPV for exposure control

    I read the following statement in a SOP in regard to PPV & exposure control.
    Once smoke has cleared, the exit should be closed, the building
    sealed, so that it will "over pressurize" the exposure. Over pressurized air will force hot gases back across the beaches, or back
    down common attic spaces towards the fire area. This can prevent fire spread extension.
    The second most critical exposure would then receive PPV in a similar manner.
    The next priority would be the fire occupancy.

    Does anyone have any experience doing this? Does it work?


  2. #2
    Forum Member DeputyMarshal's Avatar
    Join Date
    Apr 2005
    Location
    Connecticut, USA
    Posts
    2,638

    Default

    Quote Originally Posted by Geinandputitout View Post
    I read the following statement in a SOP in regard to PPV & exposure control.
    Once smoke has cleared, the exit should be closed, the building
    sealed, so that it will "over pressurize" the exposure. Over pressurized air will force hot gases back across the beaches, or back
    down common attic spaces towards the fire area. This can prevent fire spread extension.
    The second most critical exposure would then receive PPV in a similar manner.
    The next priority would be the fire occupancy.

    Does anyone have any experience doing this? Does it work?
    Air isn't going to go anywhere unless it is flowing from high pressure to low pressure.

    You can't pressurize a "sealed" building. Assuming that the intent is to close all building openings except the one being used for PPV, pressurizing the building is just going to force air out of the building through whatever breaches it can find. Those breaches may be the ones related to the fire or they may be through areas previously untouched by the fire. IOW, if you aren't controlling the escape of air and products of combustion you may very well be pushing it right into your exposures.

    If you are doing PPV, you want to control two kinds of openings: openings where you're supplying positive pressure to push air in and openings where you want that pressure and entrained products of combustion to come out. You need both openings for PPV to do anything useful.
    "Nemo Plus Voluptatis Quam Nos Habant"

    The Code is more what you'd call "guidelines" than actual rules.

  3. #3
    Forum Member
    Join Date
    Oct 2005
    Posts
    1,154

    Default

    Over pressurized air will force hot gases back across the beaches, or back
    down common attic spaces towards the fire area.
    This can prevent fire spread extension.



    For the love of all that is holy...

    I hope you either grossly mis-read that SOP...

    Or you grossly mis-typed that SOP...

    And I'm one of the supporters of appropriately used PPV here!

    Translation of the line above: Use positive pressure in a common void space in a building with an uncontrolled fire.

    Is the purpose to that SOP to deliberately create blowtorch conditions pushing the fire back into the faces of the hose team attacking the seat? (And we warn about opposing hose streams pushing fire on crews...)

    Or is simply to burn the roof off quicker so the ladder pipes can go to work 30 minutes sooner?

  4. #4
    Forum Member
    Join Date
    Jan 2007
    Posts
    1,063

    Default Read it and weep?


  5. #5
    Forum Member DeputyMarshal's Avatar
    Join Date
    Apr 2005
    Location
    Connecticut, USA
    Posts
    2,638

    Default

    Quote Originally Posted by Geinandputitout View Post
    Bottom of page 2
    That doesn't say what the SOP you provided says. That may be what it was intended to say but it isn't what it actually says.

    The Phoenix SOP works. (The whole SOP taken together including the important tactical considerations listed near the top of page 1. Those considerations still apply to what's written near the bottom of page 2.)

    The SOP at the beginning of the post by itself doesn't make any sense to me. Hopefully other steps and considerations are intended but didn't make it into the written version of the SOP.
    "Nemo Plus Voluptatis Quam Nos Habant"

    The Code is more what you'd call "guidelines" than actual rules.

  6. #6
    Forum Member
    Join Date
    Jan 2007
    Posts
    1,063

    Default ...

    Well of course the SOP taken as a segment doesn't provide the entire picture. No sentence out of any SOP would...

    Back to the original post. Has anyone ever used this tactic and what was the result?

  7. #7
    MembersZone Subscriber Edward Hartin's Avatar
    Join Date
    Nov 2002
    Location
    Gresham Oregon
    Posts
    97

    Default Defensive PPV

    We have used this tactic quite successfully on many occasions. However, a few thoughts and words of caution.

    What is being described is 1) sequential ventilation to clear a smoke logged exposure, and 2) pressurization of an uninvolved space to prevent further infiltration of smoke. The first is a ventilation tactic and the second is a confinement tactic that I call "anti-ventilation" (a term borrowed from the Swedes).

    Concern with pushing fire on the attack crews is not justified. What you are doing is pressurizing a sealed space, not moving air (as you would in PPV). However, I would be wary of using this tactic in situations where fire has extended to common (to the fire occupancy and exposure) void spaces.

    An example: We had an apartment fire on Floor 2 of a two-story, wood-frame building last night. Companies arrived with persons reported in the fire unit. A rapid attack on the fire and quick primary search controlled the fire and determined that no occupants were present. The fire unit and adjacent unit on Floor 2 were both smoke logged. PPV was used to clear the smoke from the adjacent unit and it was then pressurized to prevent further infiltration of smoke. Concurrently, PPV was used to clear smoke from the fire unit.

    As with all ventilation and anti-ventilation tactics, the key is understanding fire behavior and effectively integrating ventilation and fire control tactics.

    Cheers,
    Ed Hartin, MS, EFO, MIFireE

  8. #8
    MembersZone Subscriber
    Join Date
    May 1999
    Location
    Here, There, Everywhere
    Posts
    4,191

    Default

    Quote Originally Posted by Geinandputitout View Post
    More poor tactics from the same inexperienced clowns who can't maintain company integrity, or standardized assignments at a job and insist that fog nozzles should be used off standpipes for safety reasons!

    If your objective is to force fire throughout the cockloft and loose the entire block...then by all means follow this advice.

    If you value your life and the lives and property of others, I would treat everything they say with a grain of salt.

    FTM-PTB

    PS- I did read it and I did weep this is a prime example of the leadership some men have to deal with....at least when they aren't on the seminar circut.
    Last edited by FFFRED; 02-28-2007 at 11:02 AM.

  9. #9
    Forum Member ThNozzleman's Avatar
    Join Date
    Jun 2002
    Location
    Jefferson City, TN
    Posts
    4,334

    Default

    You can't pressurize a "sealed" building.
    Sure you can. I think you guys missed the point of the exposure being the building that is pressurized with the fan, not the burning building.

  10. #10
    Forum Member DeputyMarshal's Avatar
    Join Date
    Apr 2005
    Location
    Connecticut, USA
    Posts
    2,638

    Default

    Quote Originally Posted by ThNozzleman View Post
    Sure you can.
    No, you cannot. You need at least one controlled opening to add pressure. Tie a knot in the neck of a balloon and then try to inflate it and you'll see what I mean.

    (Unless, of course, you have some method of lowering the pressure of the entire space surrounding the "sealed building" thus increasing the relative pressure inside.)

    The point is that the SOP, as presented, is vague. I'm sure that there is some legitimate purpose behind it but that purpose and the means to achieve it didn't make it into the written SOP.
    "Nemo Plus Voluptatis Quam Nos Habant"

    The Code is more what you'd call "guidelines" than actual rules.

  11. #11
    MembersZone Subscriber dmleblanc's Avatar
    Join Date
    Jul 2001
    Location
    Not the end of the earth but I can see it from here...
    Posts
    2,318

    Default

    I am assuming that the "exposure" you are speaking of would be an area or occupancy that is actually physically attached to the fire area? Say, another occupancy sharing a common attic or cockloft? If that is so, I could see the tactic having some merit, if, and only if, you are certain of where the fire is and therefore where it is going to go.

    It would seem to me that if you can pressurize the uninvolved areas, you will force the fire and products of combustion to stay out of those areas. However, as with any use of PPV, you will need to make sure that you are not pushing those gases to OTHER currently uninvolved areas (like, the attached exposure on the other side of the fire )

    As for myself, I can't speak with experience here, because we have very few multiple occupancy buildings. What I consider an "exposure" is the building next door, i.e., physically apart from the fire building. Therefore, our experience with PPV has been limited to ventilating the actual fire building.
    Chief Dwayne LeBlanc
    Paincourtville Volunteer Fire Department
    Paincourtville, LA

    "I have a dream. It's not a big dream, it's just a little dream. My dream — and I hope you don't find this too crazy — is that I would like the people of this community to feel that if, God forbid, there were a fire, calling the fire department would actually be a wise thing to do. You can't have people, if their houses are burning down, saying, 'Whatever you do, don't call the fire department!' That would be bad."
    — C.D. Bales, "Roxanne"

  12. #12
    MembersZone Subscriber mcaldwell's Avatar
    Join Date
    Apr 2003
    Location
    Panorama, British Columbia, Canada
    Posts
    3,022

    Default

    The principle is the same as how every modern commercial residential/hotel or high-rise air handling system works.

    In a large building, the air handlers provide the PP, usually in the stairwell first, then through the hallways, and finally exiting the building through the units. In a "perfect" fire scenario, this keeps the stairwells clear of smoke, confines it to the hallway of origin, and hopefully the unit or room as well.

    I see this as just being the artificial method of creating the same system once we have compromised the buildings mechanical ventilation (by alarm interconnect or manually killing power), or physical restrictions (by propping doors, etc).

    Of course it needs some care, like all PPV, but the idea works. You are not moving masses of air within the building, just creating a small pressure differential. The PP airstream rapidly loses velocity in a stairwell or long hallway. In our training, we regularly pressurize the upper floors of our hotels this way, and there is no noticable "wind" on the upper floors, but the smoke (artifical in our scenarios) does easily move away from the PP ventilated area.

    If you are using this in close proximity to the fire, and in conflict with interior ops, you are certainly asking for trouble.
    Never argue with an Idiot. They drag you down to their level, and then beat you with experience!

    IACOJ

  13. #13
    MembersZone Subscriber
    Join Date
    May 1999
    Location
    Here, There, Everywhere
    Posts
    4,191

    Default

    Quote Originally Posted by dmleblanc View Post
    I am assuming that the "exposure" you are speaking of would be an area or occupancy that is actually physically attached to the fire area? Say, another occupancy sharing a common attic or cockloft? If that is so, I could see the tactic having some merit, if, and only if, you are certain of where the fire is and therefore where it is going to go.

    It would seem to me that if you can pressurize the uninvolved areas, you will force the fire and products of combustion to stay out of those areas. However, as with any use of PPV, you will need to make sure that you are not pushing those gases to OTHER currently uninvolved areas (like, the attached exposure on the other side of the fire )

    As for myself, I can't speak with experience here, because we have very few multiple occupancy buildings. What I consider an "exposure" is the building next door, i.e., physically apart from the fire building. Therefore, our experience with PPV has been limited to ventilating the actual fire building.
    In a taxpayer/stripmall any adjoining occupancies within the building are exposures as are any buildings on side 2,3(dependant on distance) or 4. At least in any reference text or in practice anywhere I've ever seen.

    FTM-PTB
    Last edited by FFFRED; 02-28-2007 at 12:02 PM.

  14. #14
    MembersZone Subscriber dmleblanc's Avatar
    Join Date
    Jul 2001
    Location
    Not the end of the earth but I can see it from here...
    Posts
    2,318

    Default

    Quote Originally Posted by FFFRED View Post
    In a taxpayer/stripmall any adjoining occupancies within the building are exposures as are any buildings on side 2,3(dependant on distance) or 4. At least in any reference text or in practice anywhere I've ever seen.

    FTM-PTB

    I realize that....I'm just saying that we don't have many occupancies that fit that description (like maybe 2 buildings in our area), and we've never had a fire in one.
    Chief Dwayne LeBlanc
    Paincourtville Volunteer Fire Department
    Paincourtville, LA

    "I have a dream. It's not a big dream, it's just a little dream. My dream — and I hope you don't find this too crazy — is that I would like the people of this community to feel that if, God forbid, there were a fire, calling the fire department would actually be a wise thing to do. You can't have people, if their houses are burning down, saying, 'Whatever you do, don't call the fire department!' That would be bad."
    — C.D. Bales, "Roxanne"

  15. #15
    MembersZone Subscriber
    Join Date
    May 1999
    Location
    Here, There, Everywhere
    Posts
    4,191

    Default

    Quote Originally Posted by dmleblanc View Post
    I realize that....I'm just saying that we don't have many occupancies that fit that description (like maybe 2 buildings in our area), and we've never had a fire in one.
    10-4

    FTM-PTB

  16. #16
    Forum Member ThNozzleman's Avatar
    Join Date
    Jun 2002
    Location
    Jefferson City, TN
    Posts
    4,334

    Default

    No, you cannot. You need at least one controlled opening to add pressure.
    Well, I'm pretty sure we're all aware of that...even you stated as much in your first post. Anyone I know would take a "sealed building" to mean no exits for the pressurized air to escape through.
    Your post...
    You can't pressurize a "sealed" building. Assuming that the intent is to close all building openings except the one being used for PPV, pressurizing the building is just going to force air out of the building through whatever breaches it can find. Those breaches may be the ones related to the fire or they may be through areas previously untouched by the fire. IOW, if you aren't controlling the escape of air and products of combustion you may very well be pushing it right into your exposures.
    Taking the last sentence of your post, I assumed you had missed the point that the fan is being used to pressurize the exposure in this instance, preventing fire, heat, and smoke from entering through poke-throughs and other openings between it and the fire building. To me, you were clearly describing pushing heat, fire, and smoke into the exposure from the fire building. This could only happen if the fan were used only on the fire building, not the exposure which is not the procedure described by the opening post in this thread.

  17. #17
    Forum Member
    Join Date
    Aug 2006
    Posts
    13

    Default

    While I can see how in theory this could work, and it seems as though some have used it successfully, let me say that we absolutely do not do this. It may be available to us, but I have never seen or heard of it being used. Any sort of PPV during fire attack is used very cautiously. When we have a strip mall will common attic we simply send crews into the exposure, pull ceiling and direct hose streams. We try to keep things as simple as possible and that PPV tactic sounds a bit tricky and risky, especially if there are crews operating in the fire occupancy.

    FFFRED, I can't say that I disagree with the fog nozzles on the standpipes. We have them so we have fog capabilities for shielding and for hydraulic ventilation. We have low flow nozzles, but obviously what these advertise to do, and what they really do aren't usually the same. Many downtown companies do put smooth more nozzles on their highrise packs. I don't think the potential benefits of a fog nozzle are worth anything if you can't get more than a dribble to come out. So far we have never had a problem with the adjustable fogs, but it just takes once.

    Please don't flame me too hard, I am very sensitive.
    http://www.bshifter.com

  18. #18
    MembersZone Subscriber
    Join Date
    Sep 2004
    Posts
    44

    Default References of PPV Containment

    For the users of this Confinement PPV Tactics:

    Do you have any written references you might be able to share for people to learn this tactic?

    I have seen one and investigated the source and I'm not convinced this is a good tactic.

  19. #19
    MembersZone Subscriber Edward Hartin's Avatar
    Join Date
    Nov 2002
    Location
    Gresham Oregon
    Posts
    97

    Default Reference Source

    While I do not always agree with the authors, this is an excellent reference on all things positive pressure: Positive Pressure Attack for Ventilation and Firefighting by Garcia, Kauffmann, & Schelble. It is available from Fire Engineering Books or through Amazon.

    Cheers,
    Ed Hartin, MS, EFO, MIFireE

  20. #20
    MembersZone Subscriber
    Join Date
    Sep 2004
    Posts
    44

    Default Your Example

    Hartin,

    In your example, it seemed the fire was out when you used the fan. Did I read that write?

    If so, do you or have you ever confined the active fire with positive pressure in adjacent occupancies? Could you share any experience with that tactic?

    TPLUMB

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Lockout/Tagout SOG's
    By Maness in forum Firefighters Forum
    Replies: 1
    Last Post: 10-28-2005, 02:41 PM
  2. World Of Fire Report: 05-31-05
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 06-01-2005, 07:26 AM
  3. Gun Control
    By StoveBolt in forum The Off Duty Forums
    Replies: 22
    Last Post: 07-15-2004, 12:19 PM
  4. World Of Fire Report: 09-17-03
    By PaulBrown in forum World of Fire Daily Report
    Replies: 0
    Last Post: 09-18-2003, 12:29 PM
  5. RFP's
    By D Littrell in forum Apparatus Innovation
    Replies: 1
    Last Post: 09-08-2000, 06:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts