    I've used them on occassion, and can't complain as they worked great. The two biggest scenerios are fires in enclosed trailers and hay bales. They work better on hay bale fires if you have a foam eductor hooked up and stuck into a bucket of soapy water (I'm sure you could use class a foam, but a bottle of dawn and a 5 gallon bucket is a helluva lot cheaper).


  2. #22
    MembersZone Subscriber ffmedcbk1's Avatar
    Join Date
    Aug 2003
    Location
    Ohio
    Posts
    781

    Default

    does any one have research or trial of using a peircing nozzle on a suspected backdraft?

    Just a thought about it....IFSTA said way back in fire school to open vertically, I'd say why would I put a ff on the roof of an explosive building?

    The small hole of the peircing nozzle should do the trick of steaming it out given the three criteria of a true fog attack (high heat, underventilated, no savable lives in the compartment) (all the Layman haters post now, but do realize I am a smoothbore guy)

    What do you think or have expirience with?

    Also, since I am a sb guy, I'd unscrew the 15/16th off the Akron valve and attach the peircing nozzle right there....no shutting down and draining the line

  3. #23
    MembersZone Subscriber CKirk922's Avatar
    Join Date
    Apr 2005
    Location
    Watching From The Sideline Now
    Posts
    260

    Default Same Line Of Thought

    Quote Originally Posted by ffmedcbk1 View Post
    does any one have research or trial of using a peircing nozzle on a suspected backdraft?

    Just a thought about it....IFSTA said way back in fire school to open vertically, I'd say why would I put a ff on the roof of an explosive building?

    The small hole of the peircing nozzle should do the trick of steaming it out given the three criteria of a true fog attack (high heat, underventilated, no savable lives in the compartment) (all the Layman haters post now, but do realize I am a smoothbore guy)

    What do you think or have expirience with?

    Also, since I am a sb guy, I'd unscrew the 15/16th off the Akron valve and attach the peircing nozzle right there....no shutting down and draining the line
    I was wondering whether there are test trials out there, too.
    Personally, I'd be a bit leary about the GPMs being able to significantly affect a backdraft situation. I think most of the nozzles we checked into rated around 125 GPM. There are some heavy hitters on the market that more than double that, but they are larger, more cumbersome units.
    It's a great question, though. I wish I could find some research data on the subject.

  4. #24
    Forum Member Bones42's Avatar
    Join Date
    Mar 2001
    Location
    Pt. Beach, NJ
    Posts
    10,248

    Default

    DocVBFDE14, thanks Doc. The only ones I have seen (and have) had the hose connection at the rear.
    "This thread is being closed as it is off-topic and not related to the fire industry." - Isn't that what the Off Duty forum was for?

  5. #25
    Forum Member pkfd7505's Avatar
    Join Date
    Mar 2004
    Posts
    404

    Default

    Quote Originally Posted by Bones42 View Post
    DocVBFDE14, thanks Doc. The only ones I have seen (and have) had the hose connection at the rear.
    Bones, here is a link to a company that has a few different types, some are even made to hook up to an extinguisher. I've never used any from this manufacturer, but their site may have more info that someone may want.

    http://www.piercingnozzle.com/PAGES/...S/OVERVIEW.HTM

    PKFPD
    IACOJ and proud of it


    Don't argue with an idiot; people watching may not be able to tell the difference.

  6. #26
    Forum Member
    Join Date
    Feb 2005
    Location
    Somewhere
    Posts
    478

    Default

    Quote Originally Posted by fireman4949 View Post
    I'm seeing a lot of posts saying use them for attic fires...Are you guys really serious? I can't imagine ever using one in an attic.

    What ever happened to opening up the ceiling and sticking a conventional nozzle in there and putting the fire out? The GPM flow from a piercing nozzle is inadequate to extinguish a heavily involved attic fire. Getting even a substantial knock-down is doubtful at best, not to mention the time wasted connecting and using the stupid thing.

    If there is that much fire in an attic, you absolutely need the GPM (and the stream reach) of a conventional nozzle to put it out. If there is not that much fire, why ever use a piercing nozzle to begin with?
    Like you said, different tactics, different training, different philosopy.

    If you look back at my post, we have only used them on attic fires that are not fully involved. We have a lot of prefab homes in our area that were made in the 70's. Note, these are not trailer homes, but homes that were built in a factory with the intention that they would be put on a foundation and never moved.

    They used radiant heating built into the sheetrock in the ceilings.

    About 10 years later, a local company started a manufacturing a loose insulation product made of recycled newspapers. Company lasted about ten years and went out of business.

    Because it was cheap and local, a lot of people filled their attics with this stuff.

    Over time, the fire retardent in this insulation has begun to degrade. It will now smolder and produce heat and smoke, but not really flame. Because it is insullation, it holds heat really well and the thermal imagers are really good at pinpointing the hot spots.

    Now back to those radiant heat ceilings I mentioned. Those are starting to break down too. We get at least one fire a year started by a short in those things. The short catches the cellulose insulation on fire. We get a hot smoky punky type fire that can generate a lot of heat and eventually can build up enough heat catch the whole roof on fire.

    If we catch it in the punky stage, we have found the piercing nozzle is tremendous. You can go through the roof or the sheetrock below, but the idea is make the steam work for us.

    A straight stream attack uses the cooling power of water to put to fire out. You put so much water on the fire that it can't generate enough heat to stay burning. It works, it's easy.

    A steam attack removes heat in the production of the steam, but it can also displace oxygen. The steam can also penetrate the cellulose insulation.

    The old method for handling these fires was open up the roof and use scoop shovels to throw all the insulation out onto the ground outside an overhaul it there. It was labor intensive, it took hours, it generated tremendous damage to the home. The last time we did it, it took 6 hours, one fire fighter almost fell through the ceiling below. We ended up removing almost 50% of the roof to get to all the insulation.

    Using piercing nozzles, we open up less of the roof, we spend less time on scene, we generate almost no water damage.

    This is a specialized attack for a specific circumstance.

    As far as hay fires go, when we using a piercing nozzle on a thousand pound bale, we don't have to then open up the bale and spread it out to overhaul it. That is part of the point of using the nozzle.

    In the past 5 years we have fought well over 30 haystack fires and never had a rekindle using this method.

  7. #27
    Forum Member fireman4949's Avatar
    Join Date
    Oct 2005
    Location
    Tallahassee, Florida
    Posts
    2,323

    Default

    kd7fds,

    Please correct me if I am wrong, but if I understand what you are describing correctly, you're saying that you no longer remove the cellulose insulation after the fire is out.
    If you do in fact remove it, why not just wet it down with a controlled stream as you go?

    Recycled cellulose insulation is everywhere in this area. Every fire I have ever fought that involves the attic, removal of the insulation is a basic step in overhaul. There are times that we have shoveled it out from inside the attic, but more often, it is removed simply by pulling the ceilings.
    I have seen this stuff smolder for hours on end. I am never comfortable leaving any of it in place (in the fire area) due to the high possibility of a rekindle.

    Drywall and insulation is relatively cheap as compared to the alternative.

    Therefore, since we will be removing the stuff anyway, using a piercing nozzle for attack seems pointless. Not to mention that a small smoldering section of insulation (or structural component) will produce virtually no steam at all unless water is applied directly to the burning surface. That being the case, a controlled stream from a conventional nozzle will cause less water damage, ensure extinguishment and reduce the possibility of a rekindle.
    Fire Lieutenant/E.M.T.
    IAFF Local 2339
    K of C 4th Degree
    "LEATHER FOREVER"
    Member I.A.C.O.J.
    http://www.tfdfire.com/
    "Fir na tine"

  8. #28
    Forum Member BKDRAFT's Avatar
    Join Date
    Mar 2003
    Location
    Bay Area, California
    Posts
    1,145

    Default

    We have them for both of our ARFF trucks. They are operated with air to drill through the plane and then you open up the nozzle. We haven't used it on a real incident but use them in training. I think they are pointless personally. We only use them on cargo planes not on commercial flights. Don't want to be drilling into someones head.

  9. #29
    MembersZone Subscriber
    Join Date
    Feb 2002
    Posts
    478

    Default

    We have used one as an efective basement nozel and to hit voids in roof or walls. There are a lot of house-trailers with double roofs in this area and we are able to slow down or extinguish with a piercing nozel.
    Stay Safe ~ The Dragon Still Bites!

  10. #30

    Join Date
    Jun 2007
    Posts
    2

    Default

    Just used a piercing nozzle about two weeks ago. One of those big trash compactor dumpsters at the rear of a store caught fire. Seat of fire located somewhere in the middle of the dumpster. Dumpster had two screw-off caps on side walls. Opened up the screw cap, stuck the piercing nozzle in the hole and flooded the seat of the fire putting it out. Worked fantastic. Other than that, collects dust.

    I'm afraid it's one of those "we use it once a year" type of equipment. It's great when you need it...but you won't need it 99% of the time.

  11. #31
    Forum Member
    Join Date
    Feb 2005
    Location
    Somewhere
    Posts
    478

    Default

    We found we don't have to remove near as much of it.

    Prior to this technique, we had one or two rekindles.

    Since then, not so much.

  12. #32
    MembersZone Subscriber CKirk922's Avatar
    Join Date
    Apr 2005
    Location
    Watching From The Sideline Now
    Posts
    260

    Default Specific brands

    Quote Originally Posted by pkfd7505 View Post
    Bones, here is a link to a company that has a few different types, some are even made to hook up to an extinguisher. I've never used any from this manufacturer, but their site may have more info that someone may want.

    http://www.piercingnozzle.com/PAGES/...S/OVERVIEW.HTM

    The nozzles you are looking at are manufactured by flamefighter for the other company. Flamefighter has a line of nozzles that are more structural oriented and are 45 degree side connects allowing the user to use a striking tool and ram them through obstructions.

    try flamefighter.com for more info on them.

    We've looked at the chimp, gorilla, akron, flamefighter, augustus?, and one other brand that I can't seem to place...It might have been elhart (flamefighters nozzle renamed)

  13. #33
    Forum Member
    Join Date
    Mar 2007
    Posts
    64

    Thumbs up P. Nozzle

    Quote Originally Posted by fireman4949 View Post
    I'm seeing a lot of posts saying use them for attic fires...Are you guys really serious? I can't imagine ever using one in an attic.

    What ever happened to opening up the ceiling and sticking a conventional nozzle in there and putting the fire out? The GPM flow from a piercing nozzle is inadequate to extinguish a heavily involved attic fire. Getting even a substantial knock-down is doubtful at best, not to mention the time wasted connecting and using the stupid thing.

    If there is that much fire in an attic, you absolutely need the GPM (and the stream reach) of a conventional nozzle to put it out. If there is not that much fire, why ever use a piercing nozzle to begin with?

    Basements/cellars, I can see a possible benefit for one being used, but since we have very, very few of them here in Florida, it's not much of an issue to us.

    Car fires...I see them as a complete waste of time. Halligan the hood and put it out. One line, one nozzle.
    If you have a piercing nozzle on a preconnect, I'd sure like to see how it is used to extinguish a fully involved vehicle. Two lines would have to be deployed. Again, wasting time, manpower and energy.

    Hay rolls...Yes, this may be a good application for a piercing nozzle. But again, simply because one is used, it will not keep you from having to physically open up (overhaul) the roll to ensure that it is completely extinguished.

    I guess I've just been taught different tactics than some others have. Perhaps it's because of manpower issues, or perhaps it's more of a regional thing. Either way, I honestly think piercing nozzles are a 99% waste of time, money and energy.

    Just my humble opinion.
    ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ ~~~~~~~~~~~~~~~

    I see a lot of post with the same comments. "they are worthless, they are stupid, they don't work, yadda yadda yadda blah blah blah"
    Most if not all of these comments are coming from guys that have never used one.
    I am here to tell you that they are an amazing tool. First of all, you need to think outside of the box, and secondly, you need to get if off of the truck. They don't do squat in the compartment.
    They are amazing on an attic fire. You say that you need the GPM to put the fire out. I agree. Are you using a 2 1/2? I seriously doubt it,,, you are probably using an 1 3/4" at about 150 gpm. You can put 150 gpm plus with foam through a piercing nozzle, and zero nozzle reaction.
    The best senerio is to hit it before it vents. Can you imagine a 150 gpm sprinkler head in an attic that is super heated? That is a ton of steam. As long as no one is in the attic, the steam does an incredible job of snuffing the fire. If there is a chance of a backdraft, the p. nozzle is the perfect tool. The nozzle only makes a hole the size of the shaft, so It won't introduce any oxygen and it begins to cool the fire. 150 gpmX 212. Dude those are huge numbers, and it is quick. Use your second line and keep the initial line for protection.
    Same with a basement fire. Use a chain saw and make a small hole and shove your 150+gpm sprinkler head over the fire. What better way to keep your crews safe.
    There are a ton of uses for a p. nozzle, and I have used ours dozens of times.
    Most guys are stand-offish at first, then realize just how great they are.

    Give them a try.

  14. #34
    Forum Member DeputyChiefGonzo's Avatar
    Join Date
    Aug 2000
    Location
    Somewhere between genius and insanity!
    Posts
    13,215

    Default

    Actually... most car hoods are made of either composites or aluminum. In a roaring engine compartment fire, the hood will be melted away by the time you arrive!

    PS: we have a few piercing nozzles... never used one in 26+ years on "da job".
    Last edited by CaptainGonzo; 11-01-2007 at 07:46 PM.
    ‎"The education of a firefighter and the continued education of a firefighter is what makes "real" firefighters. Continuous skill development is the core of progressive firefighting. We learn by doing and doing it again and again, both on the training ground and the fireground."
    Lt. Ray McCormack, FDNY

  15. #35
    Forum Member footrat's Avatar
    Join Date
    Aug 2007
    Location
    Porterdale, GA
    Posts
    192

    Default

    http://www.piercingnozzle.com/PAGES/PRODUCTS/S300.HTM

    We have these on our newer engines. They work well, but on our truck, we have 400 ft of forestry line for the piercing nozzle. Thus, it never gets used, because no one wants to reload the forestry line. Typically, we'll just halligan the hood to death and fog it instead.

  16. #36
    Forum Member
    Join Date
    Mar 2003
    Posts
    1,510

    Default

    Pros -- hidden voids such as "rain roofs" built over a flat roof. Slows a fire down untill you can get it opened.
    Cons -- they will sometimes clog up when driven through a multi layered tar roof. Also the are usually steel and do a good job conducting electricity.

  17. #37
    Forum Member Lifeguard911's Avatar
    Join Date
    Jan 2007
    Location
    Chaffee County, Colorado
    Posts
    119

    Default

    We have used the same home-made nozzle for about 20 years. It was made using a 4' length of 1 1/2 pipe with a pattern of 1/4" holes drilled in the last 18" of the pipe. One end was mated to a 1 1/2" valve and the other end to a chrome-moly tip with a sharp point. It is a heavy beast but when we need it, we use it. We do not keep it a compartment, but have it pre-connected on one side of the hose bed. Preconnect is the way to go as you don't waste time taking one nozzle off so you can attach the penetrator. Like any preconnect, you grab it and advance it.
    It is great for hay bales and trash truck fires. As for having to tear the bales apart anyway to extinguish them, we don't. The ranchers don't want a big pile of wet hay around, so once the fire is contained, the pile is broken up and allowed to burn in smaller piles to get rid of the hay. We have used it for car fires, but advance it with another line with a "regular" nozzle attached also.
    I agree that those saying a penetrator is worthless have rarely used them. Like any piece of equipment, you have to use it to get better with it.

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. Wanna lose Weight or Build Muscle
    By backdraft663 in forum The Off Duty Forums
    Replies: 20
    Last Post: 06-16-2010, 01:00 AM
  2. Pros And Cons Of An Engineer Postion ?
    By florafd1 in forum Firefighters Forum
    Replies: 22
    Last Post: 01-10-2007, 10:00 PM
  3. Deciding to go. PRos and Cons
    By Firechic02 in forum Firefighters Forum
    Replies: 10
    Last Post: 02-08-2005, 10:01 AM
  4. AFFF or FFFP
    By Lallo in forum Firefighters Forum
    Replies: 6
    Last Post: 03-18-2002, 08:34 PM
  5. Water Thief pro's and cons
    By Ward Watson in forum Firefighters Forum
    Replies: 1
    Last Post: 04-15-2001, 02:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts