    Default Maximum flow in supply hose?

    I know the friction loss formula, but is there a ceiling maximum flow for supply hose? A hydraulics buff tells me that 3" hose cannot flow more than 750 gpm at any time. Anyone care to dispute?

  2. #2
    Forum Member
    firemonkey311's Avatar
    Join Date
    Nov 2007
    Posts
    361

    Default

    I was taught 700 gpm max. At that flow rate you have 40 psi friction loss. After that you risk bursting the hose.
    Hello. Fire dept.. You light'em, We fight'em!

    "hard working, gear jamming, nail driving, "jake". "

    IACOJ
    4-16-2010 "On the approach"

  3. #3
    MembersZone Subscriber

    Join Date
    Apr 2005
    Posts
    249

    Default

    Quote Originally Posted by firemonkey311 View Post
    I was taught 700 gpm max. At that flow rate you have 40 psi friction loss. After that you risk bursting the hose.
    unless I got it wrong it can't burst a hose. Think about it if you are trying to maintain 100 psi in the flow, Friction loss is dependant on several factors such as length and/or elevation and GPM trying to achieve. Service test on a annual test is at 250 psi. Also, if you are supplying another pumper on 3" you generally without question lay two lines and the most a "average" GPM one would be supplying is 1500.
    The evidence of God's presence far outweighs the
    proof of His absence.

  4. #4
    Forum Member
    firemonkey311's Avatar
    Join Date
    Nov 2007
    Posts
    361

    Default

    Quote Originally Posted by Lieutenant387 View Post
    unless I got it wrong it can't burst a hose. Think about it if you are trying to maintain 100 psi in the flow, Friction loss is dependant on several factors such as length and/or elevation and GPM trying to achieve. Service test on a annual test is at 250 psi. Also, if you are supplying another pumper on 3" you generally without question lay two lines and the most a "average" GPM one would be supplying is 1500.
    Good point.
    Hello. Fire dept.. You light'em, We fight'em!

    "hard working, gear jamming, nail driving, "jake". "

    IACOJ
    4-16-2010 "On the approach"

  5. #5
    Forum Member
    GTRider245's Avatar
    Join Date
    May 2005
    Location
    Augusta,GA
    Posts
    3,065

    Default

    We use 500 gpm as the max for one 3 inch line. Anything above that either requires dual 3 inches or 5 inch.
    Career Firefighter
    Volunteer Captain

    -Professional in Either Role-

    Quote Originally Posted by Rescue101 View Post
    I don't mind fire rolling over my head. I just don't like it rolling UNDER my a**.

  6. #6
    MembersZone Subscriber
    Edward Hartin's Avatar
    Join Date
    Nov 2002
    Location
    Gresham Oregon
    Posts
    97

    Default It Depends!

    The maximum flow is dependent on several factors including the working pressure of the hose, the length of lay, and application.

    Attack rated hose has a maximum working pressure of 275 (even though you would be unlikely to pump at that pressure). Supply rated hose (like some large diameter hose) has a maximum working pressure of 185 psi.

    Length of lay is also significant in that friction loss is directly proportional to the length of the hoseline. If lays are short, you can move more water through a given size line.

    Application has a significant impact in that in a relay, you only need to have 20 psi residual pressure at the end while supplying a master stream may require 80 or 100 psi nozzle pressure, and an elevated master stream adds in substantially more pressure for the appliance loss and elevation (adding to the line pressure required and moving you closer to the maximum working pressure). This is generally a greater concern with supply rated hose.

    Cheers,
    Ed Hartin, MS, EFO, MIFireE

  7. #7
    Forum Member

    Join Date
    Sep 2006
    Posts
    13

    Default

    Basically, its whatever the burst point is. However, when you go above 36psi in friction loss of the line, you are losing more flow due to turbulence and it is important to switch to a larger size, smaller tip, or pull another line.

  8. #8
    MembersZone Subscriber

    Join Date
    Sep 2006
    Location
    Northeast Coast
    Posts
    3,911

    Default

    Quote Originally Posted by firedrewski03 View Post
    Basically, its whatever the burst point is. However, when you go above 36psi in friction loss of the line, you are losing more flow due to turbulence and it is important to switch to a larger size, smaller tip, or pull another line.
    I'm not disputing this, but it is the first time I've heard of a magic number. Can you tell us where you found or heard this?

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. 2.5' hose maximum gpm
    By sdehring in forum The Engineer
    Replies: 6
    Last Post: 09-04-2006, 01:04 PM
  2. Efficient Flow Of Hose
    By vindicator in forum The Engineer
    Replies: 19
    Last Post: 10-24-2005, 08:33 PM
  3. ?????? Supply Hose ??????
    By ccmfcchief in forum Firefighters Forum
    Replies: 12
    Last Post: 09-22-2005, 09:49 AM
  4. How would you set up this water supply hose lay.
    By UB355 in forum The Engineer
    Replies: 6
    Last Post: 07-16-2001, 12:16 PM
  5. 5" Supply Hose
    By Neptune 33 in forum Volunteer Forum
    Replies: 26
    Last Post: 12-28-2000, 11:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts

Log in

Click here to log in or register