    Default Draining Fire Pumps During Cold Weather

    For 30 years, our department has been draining the fire pumps on the rigs, (not the water tanks) when the outside temperatures gets below freezing. Is this really a problem? Temperatures here tonight are expected to be 18 degrees. However, has a fire pump really frozen in the short time it is exposed to the cold air? What is your departments policy? I can see if we were to sit at a call for hours not in pump mode. I have not seen it happen! Any comments? Thanks!


  2. #2
    Forum Member
    Join Date
    Nov 2006
    Location
    Cupcake NY
    Posts
    1,327

    Default

    how hard is it to turn three handles to drain the pump and the lines? Its a smart idea. Specially when you consider the amount of surface area that the plumbing presents. Ice was thought to be the blame for the Black Sunday fire forcing a change in our manuals which now require all lengths of hose to be disconnected and drained and reattached at the rear of the engine thus verifying that the water has escaped.

  3. #3
    Forum Member RspctFrmCalgary's Avatar
    Join Date
    May 2002
    Location
    Now in Victoria, BC. I'm from beautiful Jasper Alberta in the heart of the Can. Rockies - will always be an Albertan at heart!
    Posts
    6,329

    Default

    http://forums.firehouse.com/search.php?searchid=497915

    Tried to narrow the search down for you, but this is as close as I could get.

    There are a number of threads that should help you out.

    STAY SAFE OUT THERE, everyone!
    September 11th - Never Forget

    I respect firefighters and emergency workers worldwide. Thank you for what you do.

    Sheri
    IACOJ CRUSTY CONVENTION CHAIR
    Honorary Flatlander

    RAY WAS HERE FIRST

  4. #4
    Forum Member
    Join Date
    May 2005
    Location
    Ohio
    Posts
    465

    Default

    Drain 'em. We had an MVA last night and it was about 10 degrees or so. The pump to drive froze up in the short time they were there. Luckily they were able to crawl underneath and work the linkage manually.

    So yes, stuff can freeze in a short time when it is extremely cold.

  5. #5
    Forum Member MemphisE34a's Avatar
    Join Date
    Jan 2004
    Location
    Memphis, TN - USA
    Posts
    2,446

    Default

    Quote Originally Posted by vbladder View Post
    Temperatures here tonight are expected to be 18 degrees. However, has a fire pump really frozen in the short time it is exposed to the cold air?
    Have you not ever caught back, to back, to back, to back runs and been out of the house for longer than "a short period of time"??
    Robert Kramer
    cell #901-494-9437

    Management is making sure things are done right. Leadership is doing the right thing. The fire service needs alot more leaders and a lot less managers.

    "Everyone goes home" is the mantra for the pussification of the modern, American fire service.


    Comments made are my own. They do not represent the official position or opinion of the Fire Department or the City for which I am employed. In fact, they are normally exactly the opposite.

  6. #6
    MembersZone Subscriber
    Join Date
    Oct 2002
    Location
    Virginia Beach Virginia
    Posts
    32

    Default Great Comments

    Thanks fellas for the comments.

  7. #7
    Let's talk fire trucks! BoxAlarm187's Avatar
    Join Date
    Jan 2003
    Location
    Virginia
    Posts
    3,154

    Default

    We simply put the rig in pump and recirculate the water on every call we respond to when the temperature gets into the 20's and below (like tonight).
    Career Fire Captain
    Volunteer Chief Officer


    Never taking for granted that I'm privileged enough to have the greatest job in the world!

  8. #8
    Forum Member
    Join Date
    Apr 2004
    Location
    Bossier Parrish, Louisiana
    Posts
    10,380

    Default

    Ran wet pumps for years in the coldest reaches of the northeast and had very problems.

    The reality is that it will take longer for a wet pump to freeze than a dry pump because of the quanity of water in the pump. It takes much longer for the larger volume of water to freeze in a wet pump than the smaller amount left in the dry pump.

    In almost 23 years of northeast winter firefighting I have only seen a wet pump freeze 2or 3 times enroute to a call.

    The trick is circulating water every time the truck stops for the entire period of time the truck stops.

    A spray bottle of antifeeze carried on the truck applied every time a cap is put back on and sprayed into the valve itself will help with any freezing issues.

  9. #9
    Forum Member len1582's Avatar
    Join Date
    Feb 2002
    Location
    The State of N.J.
    Posts
    1,389

    Default

    A problem we've had in the past wasn't with the pumps themselves but the plumbing into and out of the pump freezing and fittings splitting. Not on the fire ground but with rigs left outside for a few days at our repair shop.

  10. #10
    Forum Member gunnyv's Avatar
    Join Date
    Jan 2001
    Location
    SE MI
    Posts
    1,409

    Default

    So many of the valves on our rigs leak the only way we could run dry is if there was no water in the tank. We have to leave the caps off the discharges so they'll drain and not fill the elbow with ice.

  11. #11
    Forum Member firefighterkid's Avatar
    Join Date
    May 2005
    Location
    Lacombe, Alberta, Canada
    Posts
    126

    Default

    Up here whenever its winter we have dry pumps and they stay dry until summer unless they are needed, the pump drain stays open so before we leave for a fire the driver must make sure it is closed.
    www.firehall.com - check it out

  12. #12
    Forum Member
    Join Date
    May 1999
    Location
    Berks County, PA
    Posts
    629

    Default

    We used to drain everything in the winter, but leaving the pump dry for extended periods can be hard on the packings. So, we now leave the pump wet, drain the individual discharge lines, circulate the pump if parked in the cold for long periods, and have had no problems with this.

  13. #13
    MembersZone Subscriber dadman's Avatar
    Join Date
    Dec 2003
    Location
    oHIo
    Posts
    251

    Default

    Quote Originally Posted by LaFireEducator View Post
    .
    A spray bottle of antifeeze carried on the truck applied every time a cap is put back on and sprayed into the valve itself will help with any freezing issues.
    Mixed or un-mixed antifreeze?
    How about a spray bottle with a light lube oil, like UltraLube, WD-40, LPS1?

  14. #14
    Back In Black ChiefKN's Avatar
    Join Date
    Feb 2003
    Location
    The Nice Part of New Jersey
    Posts
    6,981

    Default

    Quote Originally Posted by vbladder View Post
    For 30 years, our department has been draining the fire pumps on the rigs, (not the water tanks) when the outside temperatures gets below freezing. Is this really a problem? Temperatures here tonight are expected to be 18 degrees. However, has a fire pump really frozen in the short time it is exposed to the cold air? What is your departments policy? I can see if we were to sit at a call for hours not in pump mode. I have not seen it happen! Any comments? Thanks!
    YES, it could be a problem.

    Even if you keep the water circulating by keeping the pump operating and opening the tank fill and tank to pump.

    We have 45 degree elbows. We actually had water between the gate and the cap of the discharge freeze and split the pipe. The pump and the tank were drained, but we forgot to open the caps and the gates.
    I am now a past chief and the views, opinions, and comments are mine and mine alone. I do not speak for any department or in any official capacity. Although, they would be smart to listen to me.

    "The last thing I want to do is hurt you. But it's still on the list."

    "When tempted to fight fire with fire, remember that the Fire Department usually uses water."

  15. #15
    Forum Member BKDRAFT's Avatar
    Join Date
    Mar 2003
    Location
    Bay Area, California
    Posts
    1,146

    Default

    We drain the pumps here as well.

  16. #16
    Forum Member RRFD77's Avatar
    Join Date
    Jan 2007
    Location
    Western NY
    Posts
    30

    Default

    We drain the pump also for one simple reason that is what the captain wants me to do!
    Fir Na Tine

    "You can't help anyone, without getting there first!"

  17. #17
    MembersZone Subscriber dadman's Avatar
    Join Date
    Dec 2003
    Location
    oHIo
    Posts
    251

    Default

    We had an Engine go OOS the other day after a run.
    Wasn't able to get it inside due to mechanical problems and apparatus shuffle.
    The pump was drained, using all drain valves.
    After a few hours outside, any knook, cranny and low spot that had water or moisture froze up.
    The driver/left LD inlet/draft butterfly was left open. At the butterfly shaft lower bearing area, there's a low recessed valley in the pump/inlet housing. A little water was left there and couldn't be drained. Caused the butterfly to be stuck open.
    Various other discharges, aux inlets and small drain valves were frozen solid.
    Temp was about 10 deg F when Eng crapped and got to about 20 during maintenance.

    Moral of the story is, it's possible to have drained the pump in the station, go to a scene or mutual aid of some sort and not be required to get water going to the pump due to en-route cancel or a non-fire call.
    Going en-route, being parked for awhile and returning to quarters might be enough time to freeze up a pump and it's components if the pump wasn't completely drained and water free.

    I'm leaning towards keeping the pump filled, engaged while parked at scene and circulating water during any cold weather call. Fire, CO check, blocking traffic, cat in tree, coffee and fuel run, etc.

    It didn't take much to lock up some valves.

  18. #18
    MembersZone Subscriber mcaldwell's Avatar
    Join Date
    Apr 2003
    Location
    Panorama, British Columbia, Canada
    Posts
    3,022

    Default

    We have found the same thing; It's the small amount of water that causes the freeze ups.

    When we used to drain our old 79 front pump, it froze up somewhat regularly with just a tiny bit of water. It was better if we left the drains all open, so the water could settle out and drain, but that was a PITA when you really wanted to get the pump flowing fast.

    We do not drain the pumps on our new apparatus, and we have yet to have any kind of freeze up problem. We do circulate water on any standing response in freezing temps.
    Never argue with an Idiot. They drag you down to their level, and then beat you with experience!

    IACOJ

  19. #19
    Forum Member BKDRAFT's Avatar
    Join Date
    Mar 2003
    Location
    Bay Area, California
    Posts
    1,146

    Default

    Quote Originally Posted by mcaldwell View Post
    We have found the same thing; It's the small amount of water that causes the freeze ups.

    When we used to drain our old 79 front pump, it froze up somewhat regularly with just a tiny bit of water. It was better if we left the drains all open, so the water could settle out and drain, but that was a PITA when you really wanted to get the pump flowing fast.

    We do not drain the pumps on our new apparatus, and we have yet to have any kind of freeze up problem. We do circulate water on any standing response in freezing temps.
    Close the drains and prime it. Takes an extra 30 seconds top. After the pump is drained you can even leave all the drains closed. Then all you have to do is prime and your ready to pump.

  20. #20
    MembersZone Subscriber mcaldwell's Avatar
    Join Date
    Apr 2003
    Location
    Panorama, British Columbia, Canada
    Posts
    3,022

    Default

    Quote Originally Posted by BKDRAFT View Post
    Close the drains and prime it. Takes an extra 30 seconds top. After the pump is drained you can even leave all the drains closed. Then all you have to do is prime and your ready to pump.
    Yup, sure. Until the operator who doesn't get as much pump time as he should forgets and can't figure out for two minutes why he can't get a prime, or how the pump "Broke" cuz it's leaking all over. Or worse, the drain freezes OPEN, and you have one hell of a problem now. Training issues, sure. Fact of rural volley life, that too.

    Like I said, never had a single problem running wet pumps. Why fight it?
    Never argue with an Idiot. They drag you down to their level, and then beat you with experience!

    IACOJ

Thread Information

Users Browsing this Thread

There are currently 1 users browsing this thread. (0 members and 1 guests)

Similar Threads

  1. cold weather
    By lilyogi in forum Illinois
    Replies: 20
    Last Post: 03-15-2006, 09:07 AM
  2. Cold Weather/Draining Pumps
    By ramseycl in forum Firefighters Forum
    Replies: 21
    Last Post: 01-04-2005, 10:19 AM
  3. cold weather ops
    By DeputyChiefGonzo in forum Massachusetts
    Replies: 1
    Last Post: 01-15-2004, 10:42 PM
  4. Cold Weather Ops
    By Sleuth in forum The Engineer
    Replies: 10
    Last Post: 11-02-2002, 10:55 AM
  5. Draining pumps for cold weather operations.
    By FF13 in forum The Engineer
    Replies: 28
    Last Post: 01-23-2002, 02:04 PM